<font color="#333333"><font><font face="tahoma,sans-serif">Brendan, </font></font></font><div><font color="#333333"><font><font face="tahoma,sans-serif">I suppose there is a trade off between the options of all buildings in one file and individual models.</font></font></font></div>
<div><font color="#333333"><font><font face="tahoma,sans-serif">The all buildings in one file option treats other buildings as shading objects in E+ and as wind shields & shading in design builder, but does not allow for the use of zone multipliers. </font></font></font></div>
<div><font color="#333333"><font><font face="tahoma,sans-serif"><br></font></font></font></div><div><font color="#333333"><font><font face="tahoma,sans-serif">The individual model option allows for zone multipliers and this means shorter simulation run time.</font></font></font></div>
<div><font color="#333333"><font><font face="tahoma,sans-serif"><br></font></font></font></div><div><font color="#333333"><font><font face="tahoma,sans-serif">So I guess it depends on your use; if you want fast run time, single models are best but if you want to model the geographical features more accurately than multi model would be best. </font></font></font><span style="font-family:tahoma,sans-serif;color:rgb(51,51,51)">If you set the project up in DB, then export to E+ than the other models will be shading objects, for existing buildings this is what I like to do. </span></div>
<div><font color="#333333"><font><font face="tahoma,sans-serif">The logic is that for existing buildings the owners are likely to make changes to individual zones, so use of zone multipliers may not provide useful info.<br>
<br></font></font></font></div><div><font color="#333333" face="tahoma, sans-serif">hope this helps and best of regards- </font></div><div><div><div><font color="#336666"><i><br></i></font></div><div><b><span style="background-color:rgb(255,255,255)"><font size="1" color="#336666"><b style="font-family:Verdana,sans-serif"><br>
</b></font></span></b></div><div><div style="text-align:center"><b><span style="background-color:rgb(255,255,255)"><font size="1" color="#000099"><b style="font-family:Verdana,sans-serif">Jeremiah D. Crossett</b><span style="font-family:Verdana,sans-serif"> </span><font face="Verdana, sans-serif">| Senior </font><font face="Verdana, sans-serif">Analyst</font><font face="Verdana, sans-serif"> | Phase Change Energy Solutions</font></font></span></b></div>
<b><div style="text-align:center"><b><span style="background-color:rgb(255,255,255)"><font size="1"><font face="Verdana, sans-serif" color="#000099">120 E. Pritchard St. | Asheboro, NC 27203 | Mobile 503-688-8951</font></font></span></b></div>
<span style="color:rgb(153,153,153);background-color:rgb(255,255,255)"><div style="text-align:center"><b style="background-color:transparent"><b style="font-family:Verdana,sans-serif;font-size:8pt"><a href="http://www.phasechange.com" target="_blank">www.phasechange.com</a> </b></b></div>
</span></b></div><div><div style="text-align:center"> <img src="http://i.imgur.com/Sldxf.jpg"></div><b><b style="background-color:rgb(255,255,255);font-family:Verdana,sans-serif"><font color="#0000fe"><br></font></b></b></div>
<div><b style="background-color:rgb(255,255,255);color:rgb(0,0,254);font-family:Verdana,sans-serif;font-size:13px"><b><span style="font-size:10pt"><br></span></b></b></div><div><font color="#0000fe" face="Verdana, sans-serif"><span style="font-weight:800"><br>
</span></font></div></div>
<br><br><div class="gmail_quote">On Fri, Feb 1, 2013 at 12:31 PM, Hall, Brendan <span dir="ltr"><<a href="mailto:BHall@karpinskieng.com" target="_blank">BHall@karpinskieng.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
<div lang="EN-US" link="blue" vlink="purple">
<div>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">Jeremiah,<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">How has simulating more than one building at once in designbuilder worked out for you? How easy is it to combine and separate the building results? Any other
quirks that you ran across? I have a campus project where I need to simulate several buildings and I am trying to decide whether to try and do them in the same file. Thanks.<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">Brendan Hall, PE, LEED AP
</span><span style="font-size:8.0pt;font-family:"Calibri","sans-serif";color:#1f497d">BD+C</span><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"><u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">Engineer, Mechanical<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:13.5pt;font-family:"Arial","sans-serif";color:red">karpinski<br>
</span><span style="font-size:7.5pt;font-family:"Arial","sans-serif";color:#1f497d">ENGINEERING<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#1f497d">3135 Euclid Avenue</span><span style="font-size:11.0pt;font-family:"Arial","sans-serif";color:#1f497d"><br>
</span><span style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#1f497d">Cleveland, OH 44115</span><span style="font-size:11.0pt;font-family:"Arial","sans-serif";color:#1f497d"><br>
</span><b><span style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#c00000">P</span></b><span style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#1f497d"> <a href="tel:216.391.3700%20x%203111" value="+12163913700" target="_blank">216.391.3700 x 3111</a><u></u><u></u></span></p>
<p class="MsoNormal"><b><span lang="SV" style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#c00000">E</span></b><b><span lang="SV" style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#1f497d"> </span></b><span lang="SV" style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#1f497d"> </span><u><span style="font-size:10.0pt;font-family:"Arial","sans-serif";color:blue"><a href="mailto:bhall@karpinskieng.com" target="_blank"><span lang="SV">bhall@karpinskieng.com</span></a></span></u><span lang="SV" style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#1f497d"><br>
</span><b><span lang="SV" style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#c00000">W</span></b><span lang="SV" style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#1f497d">
</span><u><span lang="SV" style="font-size:10.0pt;font-family:"Arial","sans-serif";color:blue">www.</span></u><u><span style="font-size:10.0pt;font-family:"Arial","sans-serif";color:blue"><a href="http://www.karpinskieng.com/" title="http://www.karpinskieng.com/" target="_blank"><span lang="SV">karpinskieng.com</span></a></span></u><span lang="SV" style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#1f497d"><u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"><u></u> <u></u></span></p>
<div style="border:none;border-top:solid #b5c4df 1.0pt;padding:3.0pt 0in 0in 0in">
<p class="MsoNormal"><b><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif"">From:</span></b><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif""> <a href="mailto:bldg-sim-bounces@lists.onebuilding.org" target="_blank">bldg-sim-bounces@lists.onebuilding.org</a> [mailto:<a href="mailto:bldg-sim-bounces@lists.onebuilding.org" target="_blank">bldg-sim-bounces@lists.onebuilding.org</a>]
<b>On Behalf Of </b>Jeremiah Crossett<br>
<b>Sent:</b> Monday, December 17, 2012 12:23 PM<br>
<b>To:</b> David GARCIA-SANCHEZ<br>
<b>Cc:</b> <a href="mailto:bldg-sim@lists.onebuilding.org" target="_blank">bldg-sim@lists.onebuilding.org</a><br>
<b>Subject:</b> Re: [Bldg-sim] multi-energy simulation at neighbourhood scale<u></u><u></u></span></p>
</div><div class="im">
<p class="MsoNormal"><u></u> <u></u></p>
<div>
<p class="MsoNormal"><span style="font-family:"Georgia","serif";color:#333333">I have found Design Builder as an interface to Energy Plus to work well for cityscape models. For instance the model image pasted into this email is for two buildings owned by the
same owner so I made both models in the same file. Also the micro climate factors of solar shading from the city scape and can be modeled in Design Builder/E+, and Design Builder CFD can be used to model site wind factors. </span><u></u><u></u></p>