I'm confused by both the original post and the subsequent replies.
What does this have to do with weather data or with eQUEST?<br>
<br>
Weather files do not list the ASHRAE climate region. If you got a
weather file from the EERE site, then that's an EnergyPlus EPW
weather file. The ASHRAE Climate Zone shown on an EPW STAT file is
calculated by the EnergyPlus weather processor in converting the
source weather file into an EPW. It has no bearing on the weather
file itself. If you think that the Climate Zone is in error, that
only means<br>
the algorithm used by the EnergyPlus weather processor to calculate
the ASHRAE Climate Zone may be faulty for international locations.
<br>
<br>
Referring to this as a bug in eQUEST, or suggesting the problem
might be the eQUEST *.BIN weather file are further off the mark.<br>
<br>
Joe<br>
<pre class="moz-signature" cols="90">Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 108D
Moraga CA 94556
<a class="moz-txt-link-abbreviated" href="mailto:yjhuang@whiteboxtechnologies.com">yjhuang@whiteboxtechnologies.com</a>
<a class="moz-txt-link-abbreviated" href="http://www.whiteboxtechnologies.com">www.whiteboxtechnologies.com</a>
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
</pre>
<br>
On 12/3/2012 6:27 AM, Chuck Khuen wrote:
<blockquote
cite="mid:8AA6B105F2E64D53ADF954197EFC6E13@ChuckNotebook"
type="cite">
<div dir="ltr">
<div style="font-family: 'Calibri'; color: rgb(0, 0, 0);
font-size: 12pt;">
<div>We are now producing weather files in BIN format for
pretty much anywhere outside the US at
weatheranalytics.com. Not free but simple and quick.</div>
<div> </div>
<div>Chuck</div>
<div>_________________<br>
Chuck Khuen<br>
Co-Founder, EVP<br>
Weather Analytics <br>
weatheranalytics.com<br>
781-856-5383<br>
<br>
</div>
<div style="font-style: normal; display: inline; font-family:
'Calibri'; color: rgb(0, 0, 0); font-size: small;
font-weight: normal; text-decoration: none;">
<div style="font: 10pt tahoma;">
<div> </div>
<div style="background: none repeat scroll 0% 0% rgb(245,
245, 245);">
<div style=""><b>From:</b> <a moz-do-not-send="true"
title="waseem@edsglobal.com"
href="mailto:waseem@edsglobal.com">Waseem Shah Khan</a>
</div>
<div><b>Sent:</b> Monday, December 03, 2012 1:34 AM</div>
<div><b>To:</b> <a moz-do-not-send="true"
title="bldg-sim@lists.onebuilding.org"
href="mailto:bldg-sim@lists.onebuilding.org">bldg-sim@lists.onebuilding.org</a>
</div>
<div><b>Subject:</b> Re: [Bldg-sim] Bldg-sim Digest, Vol
60, Issue 21</div>
</div>
</div>
<div> </div>
</div>
<div style="font-style: normal; display: inline; font-family:
'Calibri'; color: rgb(0, 0, 0); font-size: small;
font-weight: normal; text-decoration: none;">Dear <span
style="font-family: arial,sans-serif; font-size: 13px;">Eleni,</span>
<div><span style="font-family: arial,sans-serif; font-size:
13px;"><br>
</span></div>
<div><font face="arial, sans-serif">I am from india, Same
problem with me, there is a bug in eQuest for
international climate zone. it will only for US.</font></div>
<div class="gmail_extra"><br>
<br>
<div class="gmail_quote">On Sat, Dec 1, 2012 at 2:30 AM, <span
dir="ltr"><<a moz-do-not-send="true"
href="mailto:bldg-sim-request@lists.onebuilding.org"
target="_blank">bldg-sim-request@lists.onebuilding.org</a>></span>
wrote:<br>
<blockquote style="border-left: 1px solid rgb(204, 204,
204); margin: 0px 0px 0px 0.8ex; padding-left: 1ex;"
class="gmail_quote">Send Bldg-sim mailing list
submissions to<br>
<a moz-do-not-send="true"
href="mailto:bldg-sim@lists.onebuilding.org">bldg-sim@lists.onebuilding.org</a><br>
<br>
To subscribe or unsubscribe via the World Wide Web,
visit<br>
<a moz-do-not-send="true"
href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org"
target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
or, via email, send a message with subject or body
'help' to<br>
<a moz-do-not-send="true"
href="mailto:bldg-sim-request@lists.onebuilding.org">bldg-sim-request@lists.onebuilding.org</a><br>
<br>
You can reach the person managing the list at<br>
<a moz-do-not-send="true"
href="mailto:bldg-sim-owner@lists.onebuilding.org">bldg-sim-owner@lists.onebuilding.org</a><br>
<br>
When replying, please edit your Subject line so it is
more specific<br>
than "Re: Contents of Bldg-sim digest..."<br>
<br>
Today's Topics:<br>
<br>
1. International Climate Zone specification<br>
(<a moz-do-not-send="true"
href="mailto:elenisoulti@co2engineering.eu">elenisoulti@co2engineering.eu</a>)<br>
<br>
<br>
---------- Forwarded message ----------<br>
From: <a moz-do-not-send="true"
href="mailto:elenisoulti@co2engineering.eu">elenisoulti@co2engineering.eu</a><br>
To: "<a moz-do-not-send="true"
href="mailto:bldg-sim@lists.onebuilding.org">bldg-sim@lists.onebuilding.org</a>"
<<a moz-do-not-send="true"
href="mailto:bldg-sim@lists.onebuilding.org">bldg-sim@lists.onebuilding.org</a>>,
"<a moz-do-not-send="true"
href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a>"
<<a moz-do-not-send="true"
href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a>><br>
Cc: <br>
Date: Fri, 30 Nov 2012 20:58:48 +0000<br>
Subject: [Bldg-sim] International Climate Zone
specification<br>
Dear all,<br>
<br>
I am using eQUEST for a project in Spain and I have
used the weather data from the EERE (Energy Efficiency
& Renewable Energy) website. The climate zone
described in the weather file doesn't seem to agree
with the one I calculate according to the ASHRAE 90.1
description for International climate zones, based on
the precipitation levels. Has anyone had any similar
problems with weather data outside the US? Any
suggestions about dealing with this?<br>
<br>
Thank you in advance.<br>
<br>
Kind regards,<br>
<br>
Eleni<br>
<br>
-- <br>
Eleni Soulti<br>
<br>
On behalf of<br>
<br>
CO2 Engineering<br>
<br>
Oficina Sevilla<br>
<br>
Cartuja - Edificio Marie Curie<br>
<br>
C/Leonardo da Vinci 18, Planta1 3ºB<br>
<br>
41092 Sevilla | España<br>
<br>
T. (0034) 679883055 begin_of_the_skype_highlighting (0034)
679883055 end_of_the_skype_highlighting<br>
<br>
London Office<br>
<br>
17, Bishops Close<br>
<br>
E17 9RP London | UK<br>
<br>
T. (0044) 7969235926 begin_of_the_skype_highlighting (0044)
7969235926 end_of_the_skype_highlighting<br>
<br>
Oficina Huelva.<br>
<br>
Plaza Hermanos Costalero nº 2, 6º A<br>
<br>
21001 Huelva | España<br>
<br>
T. (0034) 647143558 begin_of_the_skype_highlighting (0034)
647143558 end_of_the_skype_highlighting<br>
<br>
w. <a moz-do-not-send="true"
href="http://www.co2engineering.eu" target="_blank">www.co2engineering.eu</a><br>
<br>
e. <a moz-do-not-send="true"
href="mailto:elenisoulti@co2engineering.eu"
target="_blank">elenisoulti@co2engineering.eu</a><br>
<br>
<br>
<br>
<br>
<br>
_______________________________________________<br>
Bldg-sim mailing list<br>
<a moz-do-not-send="true"
href="mailto:Bldg-sim@lists.onebuilding.org">Bldg-sim@lists.onebuilding.org</a><br>
<a moz-do-not-send="true"
href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org"
target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
<br>
</blockquote>
</div>
<br>
<br clear="all">
<div> </div>
-- <br>
<p style="background-color: white; margin: 0cm 0cm 0pt;
font-size: small;"><span style="color: rgb(34, 34, 34);">Kind
Regards,</span></p>
<p style="background-color: white; margin: 0cm 0cm 0pt;
font-size: small;"><span style="color: rgb(34, 34, 34);"><br>
<font face="georgia, serif"><i>Waseem Shah Khan</i></font></span></p>
<p style="margin: 0px 0px 0pt; font-size: small;"><span
style="font-family: 'Times New Roman',serif; color:
rgb(34, 34, 34);">Energy Analyst<br>
<i>Environmental Design Solutions Pvt. Ltd. </i></span></p>
<p style="margin: 0px 0px 0pt; font-size: small;"><span
style="font-family: 'Times New Roman',serif; color:
rgb(34, 34, 34);"><a moz-do-not-send="true"
href="http://www.edsglobal.com/" target="_blank">www.edsglobal.com</a></span></p>
<b style="background-color: rgb(255, 255, 255);
font-family: arial,sans-serif; color: rgb(34, 34, 34);
font-size: 12px;">Environmental Design Solutions Pvt.
Ltd. [EDS]</b><br style="background-color: rgb(255, 255,
255); font-family: arial,sans-serif; color: rgb(34, 34,
34); font-size: 12px;">
<span style="background-color: rgb(255, 255, 255);
font-family: arial,sans-serif; color: rgb(34, 34, 34);
font-size: 12px;">D - 1/25 </span><br
style="background-color: rgb(255, 255, 255);
font-family: arial,sans-serif; color: rgb(34, 34, 34);
font-size: 12px;">
<span style="background-color: rgb(255, 255, 255);
font-family: arial,sans-serif; color: rgb(34, 34, 34);
font-size: 12px;">Vasant Vihar</span><br
style="background-color: rgb(255, 255, 255);
font-family: arial,sans-serif; color: rgb(34, 34, 34);
font-size: 12px;">
<span style="font-family: 'Times New Roman',serif; color:
rgb(34, 34, 34);">New Delhi 110057,India</span><br>
<p style="margin: 0px 0px 0pt; font-size: small;"><span
style="font-family: 'Times New Roman',serif; color:
rgb(34, 34, 34);">Mob:+91.9999535880 <br>
Tel: +91.11.2614.7085</span></p>
<p style="margin: 0px 0px 0pt; font-size: small;"><span
style="font-family: 'Times New Roman',serif; color:
rgb(34, 34, 34);">Fax: +91 11 40568633</span></p>
<br>
</div>
<p>
</p>
<hr>
_______________________________________________<br>
Bldg-sim mailing list<br>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message
to <a class="moz-txt-link-abbreviated" href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
</div>
</div>
</div>
<pre wrap="">
<fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
Bldg-sim mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a>
To unsubscribe from this mailing list send a blank message to <a class="moz-txt-link-abbreviated" href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
</blockquote>
</body>
</html>