<font size=3>Just a quick guess.  Have you confirmed the outdoor air
entering the building (infiltration plus ventilation air) during those
winter months?  Also confirm HVAC systems run hours.  A
balancing report is a good place to start.  Logging fan and pump
hours helps especially if the BAC is already keeping those logs. 
<br><br>
<br><br>
At 09:50 PM 02/12/2012, chik king ho wrote:<br>
<blockquote type=cite class=cite cite="">Hi all,<br><br>
I have simulated a building in Hong Kong by using Equest. In Hong Kong,
winter is from Nov. to Feb. But I found that my simulation in HVAC part
(end-use: space cooling + heat reject + vent. fan + pumps & aux.) in
winter is much lower than the actual energy consumption in HVAC. So,
could anyone help me to find why this happens and how can I solve it? inp
and pd2 flies are attached for reference.<br><br>
Henry<br><br>
<br>