<html dir="ltr">
<head>
<meta http-equiv="Content-Type" content="text/html; charset=iso-8859-1">
<style id="owaParaStyle">P {
        MARGIN-TOP: 0px; MARGIN-BOTTOM: 0px
}
</style>
</head>
<body fPStyle="1" ocsi="0">
<div style="direction: ltr;font-family: Tahoma;color: #000000;font-size: 10pt;">
<p>Chris,</p>
<p> </p>
<p>...to match actual data, you'll need 2 runs...Jan - Feb and Nov - Dec, then merge the two runs.</p>
<p> </p>
<p>Jeff</p>
<div>
<p> </p>
<div><font color="#0000ff" size="2" face="Tahoma">8=!  8=)  :=)  8=)  ;=)  8=)  8=(  8=)  8=()  8=)  8=|  8=)  :=')  8=)8=?<br>
<br>
Jeff S. Haberl, Ph.D.,P.E., FASHRAE..............jhaberl@tamu.edu<br>
<br>
Professor............................................................Office Ph: 979-845-6507<br>
<br>
Department of Architecture.............................Lab Ph:979-845-6065<br>
<br>
Energy Systems Laboratory.............................FAX: 979-862-2457<br>
<br>
Texas A&M University.....................................77843-3581<br>
<br>
College Station, Texas, USA, 77843..................URL:www.esl.tamu.edu<br>
<br>
8=/  8=)  :=)  8=)  ;=)  8=)  8=()  8=)  :=)  8=)  8=!  8=)  8=? 8=)8=0<br>
</font></div>
</div>
<div style="FONT-FAMILY: Times New Roman; COLOR: #000000; FONT-SIZE: 16px">
<hr tabindex="-1">
<div style="DIRECTION: ltr" id="divRpF136661"><font color="#000000" size="2" face="Tahoma"><b>From:</b> bldg-sim-bounces@lists.onebuilding.org [bldg-sim-bounces@lists.onebuilding.org] on behalf of Chris Jones [cj@enersave.ca]<br>
<b>Sent:</b> Monday, December 03, 2012 8:29 AM<br>
<b>To:</b> chik king ho; bldg-sim@lists.onebuilding.org; Equest<br>
<b>Subject:</b> Re: [Bldg-sim] [Equest-users] Problems of energy simulation(HVAC part) in winter<br>
</font><br>
</div>
<div></div>
<div><font size="3">Just a quick guess.  Have you confirmed the outdoor air entering the building (infiltration plus ventilation air) during those winter months?  Also confirm HVAC systems run hours.  A balancing report is a good place to start.  Logging fan
 and pump hours helps especially if the BAC is already keeping those logs.  <br>
<br>
<br>
<br>
At 09:50 PM 02/12/2012, chik king ho wrote:<br>
<blockquote class="cite" type="cite">Hi all,<br>
<br>
I have simulated a building in Hong Kong by using Equest. In Hong Kong, winter is from Nov. to Feb. But I found that my simulation in HVAC part (end-use: space cooling + heat reject + vent. fan + pumps & aux.) in winter is much lower than the actual energy
 consumption in HVAC. So, could anyone help me to find why this happens and how can I solve it? inp and pd2 flies are attached for reference.<br>
<br>
Henry<br>
<br>
<br>
_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
<br>
To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</blockquote>
<p>>><br>
Christopher Jones, P.Eng.<br>
Suite 1801, 1 Yonge Street<br>
Toronto, ON M5E1W7<br>
Tel. 416-203-7465<br>
Fax. 416-946-1005<br>
email cj@enersave.ca<br>
</font></p>
</div>
</div>
</div>
</body>
</html>