    1.  i would recommend obtaining 90.1-2001 and 2004 as the
    requirements of 2001 and the methodologies of 2004 differ from 2010.<br>
    2.  don't forget 179d requirements over-ride requirements of 90.1.<br>
    3.  do you have the 179d energy simulation guide?  this one is free
    from the nrel website. 40467.pdf is the name of it.<br>
    4.  the irs bulletins on the revisions for partially qualifying have
    changed over the years.  most recently (02/12) with an option to use
    two different percentage sets if the building is not fully
    qualifying until 12/31/2013.  i.e. 10% building, 15% hvac/swh, 25%
    lighting OR 10% building, 20% hvac/swh, 20% lighting.  the old
    16-2/3% for each discipline expired at the end of 2008.<br>
    5.  and if you're looking at partially qualifying don't forget a
    partially qualifying is each discipline by itself so you can't have
    a partially qualifying hvac/lighting only or hvac/arch.  it would be
    one simulation partially hvac, another partially bldg, or lighting. 
    and in the case of lighting you can use the interim lighting rules
    which doesn't require simulation.<br>
    6. can't help you with the use of phase change materials.<br>
    7.  the simulations start the same between leed and epact but a)
    you'll see more savings with epact, b) the baseline requirements are
    different (see the 179d simulation guide), and MOST importantly the
    179d certification is a certification of what is installed on the
    project.  i.e. who is field verifying what is there?  you are.  and
    you're certifying this to the irs.  this can make a large difference
    as far as hvac due to your having field measure fan flow, motor
    volts, and motor amps used.  as these should be less than nameplate
    data you'll see more energy savings.  yes, i realize some of the
    language in 179d reads equipment "that will be installed" but if
    you're using only catalog data (which can differ from nameplate) due
    to trying to certify before the building is constructed you won't
    see as much 179d savings.  don't forget you're also certifying
    building envelope installation and field measured lighting levels
    (there are lighting contractors that can provide this) per the 179d
    requirements. <br>
    8.  the 179d savings are an energy cost savings basis.  you have to
    break out the percent cost of energy used by each discipline from
    the total cost of the building based on the percentage energy used
    by each discipline.  see page 9 of the 40467.pdf from nrel.<br>
    <meta http-equiv="Content-Type" content="text/html;
      charset=ISO-8859-1">
    <title>Energy Savings Modeling and Inspection Guidelines for
      Commercial Building Federal Tax Deductions, Second Edition</title>
    <span style="font-size: 11.000000pt; font-family:
      'TimesNewRomanPSMT'"></span><br>
    <br>
    <img src="cid:part1.03050904.07020203@gmail.com" alt=""><br>
    9.  remember you're only comparing energy for building envelope,
    hvac/swh, and lighting.  as misc/other energies are energy neutral
    they don't impact your savings directly (unlike in leed).<br>
    10.  solar pv savings do not apply to 179d, and neither does
    external lighting (it's all internal lighting).  we could have a lot
    higher savings where i'm at if we could include external lighting
    due to stringent site lighting reductions trying to keep our skies
    dark and federally funded telescopes having great views.  solar
    thermal (swh) does apply.<br>
    <br>
    regardsl,<br>
    <br>
    On 12/1/12 2:44 PM, CleanTech Analytics wrote:
    <blockquote
cite="mid:CALKTE9TPisD-0CLvPhUaVbp5vMu3Z-fDKj6ML=jD3cdMYtEUEQ@mail.gmail.com"
      type="cite">Dear List-<br>
      I am researching the EPAct §179D Energy Efficient Commercial
      Buildings Tax Deduction, specifically the segment for $.60 per
      square foot building floor area for building envelopes that
      contribute to %50 better than ASHRAE 2001.   The main question I
      am attempting to figure out is if Phase Change Materials could be
      used in conjunction with ASHRAE 90.1 2007 or 2010 prescriptive
      insulation and fenestration requirements (or better) to achieve
      the tax credit. The projects that this would apply to are
      currently going for LEED but may not be going for EPAct.  I am
      trying to figure out how the envelope contribution to the %50
      better than ASHRAE 2001 requirement is segmented to understand if
      these projects could be applicable for the credit due to the
      advanced Phase Change Material envelopes. <br>
      <br>
      I understand that the procedure to follow is ASHRAE 90.1 2004, and
      the baseline to be 50% above is ASHRAE 90.1 2001.<br>
      <ul>
        <li> Question 1: Is the calculation for %50 reduction similar to
          the LEED % of cost approach or if it is a % of energy basis?</li>
      </ul>
      The part I do not know is the multipliers to segment the envelope
      only portion and associated modeling procedures.  If this is based
      on minimum R values and maximum U values than our product would
      not contribute to the %50, while if it is based on %50 energy
      reduction from the baseline envelope energy use than phase change
      materials could contribute to the credit and receive the $.60 per
      square foot building area.<br>
      <ul>
        <li>Question 2:  How is the envelope segmented from the HVAC and
          lighting systems when applying for envelope only EPAct?</li>
      </ul>
      I have a budget to buy any required literature, but do not want to
      misuse funds by buying unnecessary publications.<br>
      <ul>
        <li>Question 3: Should I get ASHRAE 90.1 2001 and ASHRAE 90.1
          2004, or can I find this info in the ASHRAE 2010 version I
          already own? </li>
        <li>Question 4: Is there any other reference materials that are
          advised (free or purchased) to better understand EPAct rules
          and requirements?</li>
      </ul>
      Thank you in advance to anyone who shares their insights..
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>