<font color="#000066"><font face="comic sans ms,sans-serif">I've always found the default plug & lighting loads in eQuest to be on the high-side which has a significant affect on space temperatures and space conditioning energy.<br>

</font></font><br><div class="gmail_quote">On Wed, Mar 7, 2012 at 12:27, RobertWichert <span dir="ltr"><<a href="mailto:robert@wichert.org">robert@wichert.org</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">

I am trying to learn E-Quest and I am trying to model a building that I have already modeled with Energy Pro.  The gas usage from E-Quest is very very low compared to both actual and Energy Pro.  It is a hot water reheat VAV system with a boiler and a water cooled condenser.  The actual gas use is 17891 Therms, from the bills.  Energy Pro predicts 17600 Therms.  E-Quest predicts 580 Therms.  This makes no sense to me, but it is clearly my error.  I have gone over the inputs several times.<br>


<br>
Is there anything that occurs to anybody that would make gas usage that far off?<br>
<br>
Electrical from E-Quest is 453 MWh.  Electrical from Energy Pro is 422 MWh.  Electrical actual is 543 MWh.  The building has lots of unaccounted-for process equipment, so I'm not so worried about being low on electrical.  It's not too far off.  But the gas use is just way too low.  Hot water is showing up at 3 Therms a month.<br>


<br>
<br>
This is the first model I have done with E-Quest, so I apologize for even asking.  It's obviously something stupid that I have done.<br>
<br>
<br>
-- <br>
Robert Wichert P.Eng. LEED AP<br>
<a href="tel:%2B1%20916%20966%209060" value="+19169669060" target="_blank">+1 916 966 9060</a><br>
FAX <a href="tel:%2B1%20916%20966%209068" value="+19169669068" target="_blank">+1 916 966 9068</a><br>
<br>
<br>
<br>
<br>
<br>
<br>
<br>
==============================<u></u>=================<br>
<br>
______________________________<u></u>_________________<br>
Bldg-sim mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" target="_blank">http://lists.onebuilding.org/<u></u>listinfo.cgi/bldg-sim-<u></u>onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">BLDG-SIM-UNSUBSCRIBE@<u></u>ONEBUILDING.ORG</a><br>
</blockquote></div><br><br clear="all"><br>-- <br>Chris Flood BSc (Eng)<br>Senior Building Analyst<br>