Chou,<br>
In Type56/TRNBuild the term "VENTILATION" just means a flow of air
whether it is hot, cold, or neutral. It isn't necessarily tied in
any way to the HVAC system. The "HEATING" and "COOLING" types are
used to calculate sensible loads for the space. Those types don't
have anything to do with how that energy is delivered to the space.<br>
<br>
Typically, there are two kinds of simulations that I do with
Type56:<br>
<br>
Early on in a project, I need to determine the peak heating and
cooling loads for the space and I need to get a very basic idea of
how much energy the building will consume over the year. In order to
do this, I use VENTILATION types to put the outdoor (fresh) air
requirements into the zone. and I use HEATING and COOLING types to
define set points. I allow the "system" to have unlimited power
because all I really care about is the maximum hourly value and the
annual sum. The annual sum gives a very rough idea of how much
energy is required by the building. You have to do one of two things
in order to get how much energy is required by the HVAC system:
either define a simple COP for the heating and cooling system or use
other TRNSYS models that take heating and cooling load as an input
and return the power consumed (note, there are very few of these
components)<br>
<br>
The second kind of simulation is much more common in TRNSYS. In
this, you use the VENTILATION type to deliver hot or cold air to the
space and you use a thermostat model (such as Type108) to turn on
and off equipment that controls the flow of air. In this case, you
disable the HEATING and COOLING types because you don't care about
loads. The equipment of the system (fans, pumps, heat pumps,
furnaces, chillers, etc.) will compute their source energy
requirements as a function of their inlet conditions and the
building will simply react to the ventilation air that it receives.<br>
<br>
Kind regards,<br>
David<br>
<br>
On 12/18/2011 05:21, Chou Shen wrote:
<blockquote
cite="mid:CAP9LdPOfB4FxZz4KOVFwkut6cTYmXoE-kFepAgmfx9FMo_CoVg@mail.gmail.com"
type="cite">Hi everyone<br>
<br>
I began to learn TRNSYS a couple of days ago and I came across
some questions right now. I wonder if somebody happens to know
TRNSYS well.The questions are:<br>
1. When Editing type 56, in the Ventilation lable, the Heating and
Cooling option can be set up by defining airchange rate and
temperature & RH of air flow; while in both the Cooling lable
and Heating lable, the cooling and heating option can be set up by
defining cooling / heating power (does that mean I need to
estimate the cooling / heating load before set this block up?),
and the setpoint temperature & RH. As a result, type 56
provides two methods to define HVAC system. Do I need to set up
both the labes to get it work?. <br>
<br>
2. In addition to adding the information of HVAC in type 56, do I
need to creat the HVAC system in to get the information of energy
consumption of HVAC system?<br>
<br>
Thanks!<br clear="all">
<br>
-- <br>
Chou Shen<br>
Graduate Research Assistant<br>
Department of Civil, Architectural & Environmental Engineering<br>
Missouri University of Science and Technology<br>
<br>
<br>
<br>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<br>
<pre wrap="">_______________________________________________
Bldg-sim mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a>
To unsubscribe from this mailing list send a blank message to <a class="moz-txt-link-abbreviated" href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
</blockquote>
<br>
<pre class="moz-signature" cols="72">--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
</body>
</html>