Patrick, <div>For your fan power calc you may be able to use <a href="http://energy-models.com/tools/leed-fan-calculator">http://energy-models.com/tools/leed-fan-calculator</a></div><div>Also the LEED tutorial provides good insight as to ASHRAE interpretation. <br>
<br><div class="gmail_quote">On Fri, Dec 16, 2011 at 2:55 PM, Patrick J. O'Leary, Jr. <span dir="ltr"><<a href="mailto:poleary1969@gmail.com">poleary1969@gmail.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
i'm currently looking at the requirements for modeling a building to demonstrate energy savings per the epact 2005/irs 179d requirements & am trying to determine the proper method for calculating baseline fan power.  has anyone else done this yet?<br>

<br>
per the NREL manual, Appendix G Section, Wording Changes and Corresponding Sections in Standard 90.1-2001:<br><br>
"G3.1.2.9 Supply Fan Power:  The Reference Building model fan power shall be determined based on § 6.3.3.1 in Standard 90.1-2001"<br>
<br>
in 90.1-2001 section 6.6.3.1 is the section with the table that lists how to calculate the allowable system fan power.<br>
<br>
my question is, "for epact 2005/irs 179d energy modeling is the correct supply fan power to use in the baseline building the same as the allowable fan system power?"  this seems odd when comparing it to 90.1-2004 and having to calculate a baseline fan power (table g3.1.2.9) in lieu of using the fan power limitation (6.5.3.1) and plugging that number into the equation Pfan listed in section g.3.1.29.  it sort of just seems too easy.<br>

<br>
regards,<br>
patrick<br>
<br>
<br>
______________________________<u></u>_________________<br>
Bldg-sim mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" target="_blank">http://lists.onebuilding.org/<u></u>listinfo.cgi/bldg-sim-<u></u>onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">BLDG-SIM-UNSUBSCRIBE@<u></u>ONEBUILDING.ORG</a><br>
</blockquote></div><br><br clear="all"><div><br></div>-- <br><div><div>Jeremiah D. Crossett</div><div>Setanta Energy & Water</div></div><div>Phone: 503-688-8951</div><div>Email: <span style="border-collapse:collapse;font-family:arial,sans-serif;font-size:13px"><a href="mailto:jeremiah@setnrgh2o.com" style="color:rgb(0,0,204)" target="_blank">jeremiah@setnrgh2o.com</a></span></div>
<div><a href="http://www.setnrgh2o.com/" target="_blank">http://www.setnrgh2o.com/</a></div><br>
</div>