<div>Nick,</div><div><br></div><div>I mostly agree with your approach, however I disagree on one point - even though desk lamps may be plugged-in and not permanently installed, if they are part of the overall lighting plan, then I think that they should be included in the proposed model and not in the baseline.  If you have low footcandles in a space, but for whaterver reason, task lighting is not required (this architectural studio uses giant multi-touch computers for drawing), then task lights should be modeled equally in both models.</div>
<div><br></div><div>--</div><div>Karen</div><div><br></div><div><br><br><div class="gmail_quote">On Thu, Nov 17, 2011 at 4:36 AM, Carol Gardner <span dir="ltr"><<a href="mailto:gems@spiritone.com" target="_blank">gems@spiritone.com</a>></span> wrote:<br>

<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
  
    
  
  <div bgcolor="#FFFFFF" text="#000000">
    tb,<br>
    <br>
    After, you have read through this  couple of times, or looked at it
    in an Excel table, you will figure out the changes you have to make
    and make them. Always remember, do the proposed case first and then
    back out the baseline, which must meet the applicable code. <br>
    <br>
    I think in a case like this building you would have had a different
    result if you had attached, or put into the form, what you were
    trying to do and how you did it. Your explanation is quite good and
    it gives the reviewers something to look at besides numbers. Then
    you get to exercise both sides of your brain.<br>
    <br>
    Cheers,<br>
    <br>
    Carol<div><div><br>
    <br>
    <br>
    On 11/16/2011 10:26 PM, Tom Butler wrote:
    </div></div><blockquote type="cite"><div><div>
      
      
      
      
      <div>
        <p class="MsoNormal">Sorry for the long attachment here, but
          this LEED v2.2 EAc1 comment has me really confused so I want
          to post it in its entirety.</p>
        <p class="MsoNormal"> </p>
        <p><span style="font-size:9.0pt"><span>1.<span style="font:7.0pt "Times New Roman"">    </span></span></span><span style="font-size:9.0pt">The
            EAc1 Narrative describes the interior lighting design target
            for all studio spaces is 20 fc and that task lights have
            been modeled identically in the Baseline and Proposed case.
            However, according to the IESNA Lighting Handbook, ninth
            edition, the minimum horizontal design illuminance for art
            studios is 50 fc and for reading areas with handwritten
            tasks is 30 fc. The ASHRAE allowances represent the power
            allowance required to meet the minimum IESNA illuminance
            requirements for various space types. It is inappropriate to
            claim savings for designs that do not meet the minimum
            lighting level requirements and model the additional
            lighting power in the Baseline for lighting in the Proposed
            that is required to perform the anticipated tasks.<br>
            <br>
            Also, Table 1.4 reports that 4.02 kW of process lighting has
            been modeled in both cases, and it is assumed that this
            represents the task lighting. Process lighting is limited to
            the exempt interior lighting applications described in
            Section 9.2.2.3. Task lighting is regulated and thus not
            considered a process load. Section 9.6.3(b) does provide an
            additional allowance for task lighting when the Space by
            Space Method is used, but this may not be used for lighting
            required to raise the ambient lighting to meet the required
            lighting levels. If this additional allowance is used in the
            Proposed design, the Baseline must be modeled with the same
            power as the Proposed up to the 0.35 W/square foot
            allowance. Please remove all task lighting power from the
            Baseline model that is required to meet the IESNA
            recommended illuminance levels. If any of the additional
            allowance from Section 9.2.2.3 is applied to the Baseline
            case, provide calculations verifying that this additional
            lighting is not required in the Proposed case to meet the
            required illuminance levels and confirming that this only
            represents the portion of the additional allowance that is
            used in the Proposed case.<br>
            <br>
          </span></p>
        <p class="MsoNormal">My first question; isn’t low ambient-task
          specific a commonly accepted energy use reduction strategy?
          Why would I model a lighting design in the proposed solution
          which isn’t installed and how would one determine, without an
          extensive lighting design effort, the appropriate lighting
          power to achieve 50fc, or 30fc? (not quite sure which one they
          want) </p>
        <p class="MsoNormal">Second, the spaces in question are
          architecture college studios. If the task lighting is a plug
          in desk lamp, provided by the student, then am I correct in
          assuming it’s not regulated by 9.2.2.3? I’ve assumed 60W per
          lamp as plug load, but there no way that the lamp type or
          light distribution can be controlled as defined in 9.6.3.b,
          nor is it a given that a lamp will be used. </p>
        <p class="MsoNormal"> </p>
        <p class="MsoNormal">I’m at a loss as to how to respond to this.
          </p>
        <p class="MsoNormal"> </p>
        <p class="MsoNormal">Thanks for any input.</p>
        <p class="MsoNormal"> </p>
        <p class="MsoNormal">tb</p>
        <p class="MsoNormal"> </p>
        <p class="MsoNormal"><b><span style="font-size:10.0pt;color:gray">Tom Butler</span></b></p>
        <p class="MsoNormal"><b><span style="font-size:10.0pt;color:gray">Residential Green
              Building Services Project Manager</span></b></p>
        <p class="MsoNormal"><b><span style="font-size:10.0pt;color:gray">Tel: <a href="tel:404-604-3635" value="+14046043635" target="_blank">404-604-3635</a></span></b></p>

        <p class="MsoNormal"><b><span style="font-size:10.0pt;color:gray">Fax: <a href="tel:404-872-5009" value="+14048725009" target="_blank">404-872-5009</a></span></b><span style="font-size:10.0pt;color:gray"><br>
            <b>Email: </b></span><span style="font-size:10.0pt"><a href="mailto:amcfarland@southface.org" target="_blank"><b><span style="color:blue">tbutler@southface.org</span></b></a></span></p>
        <p class="MsoNormal"><b><span style="font-size:10.0pt;color:gray">Web: </span></b><span style="font-size:10.0pt"><a href="http://www.southface.org/" target="_blank"><b><span style="color:blue">www.southface.org</span></b></a></span></p>


        <p class="MsoNormal"><span style="font-size:10.0pt;color:gray">241 Pine Street NE,
            Atlanta, GA 30308</span></p>
        <p class="MsoNormal"><span style="color:gray"> </span></p>
        <p class="MsoNormal"><a href="http://www.greenprints.org/" target="_blank"><span style="font-size:12.0pt;font-family:"Times New Roman","serif";color:windowtext;text-decoration:none"><img alt="Description: sf logo without tag" border="0" height="21" width="105"></span></a></p>


        <p class="MsoNormal"><b><span style="font-size:10.0pt;color:black">Building know-how for
              a sustainable future</span></b></p>
        <p class="MsoNormal"><b><span style="font-size:10.0pt;color:black"> </span></b></p>
        <p class="MsoNormal"><a href="http://twitter.com/#%21/southfaceenergy" target="_blank"><span style="font-size:12.0pt;font-family:"Garamond","serif";color:black;text-decoration:none"><img alt="cid:image016.png@01CC251F.C8476DC0" border="0" height="24" width="24"></span></a><a href="http://www.linkedin.com/company/southface" target="_blank"><span style="font-size:12.0pt;font-family:"Garamond","serif";color:black;text-decoration:none"><img alt="cid:image017.png@01CC251F.C8476DC0" border="0" height="24" width="24"></span></a><a href="http://www.facebook.com/southface.energy" target="_blank"><span style="color:black;text-decoration:none"><img alt="cid:image018.png@01CC251F.C8476DC0" border="0" height="24" width="24"></span></a><a href="http://www.youtube.com/southfaceenergy" target="_blank"><span style="font-size:12.0pt;font-family:"Garamond","serif";color:black;text-decoration:none"><img alt="cid:image019.png@01CC251F.C8476DC0" border="0" height="24" width="24"></span></a></p>


        <p class="MsoNormal"><b><span style="font-size:10.0pt;color:black"> </span></b></p>
        <p class="MsoNormal"><b><span style="font-size:10.0pt;color:black"> </span></b></p>
        <p class="MsoNormal"><b><i><span style="font-size:10.0pt;color:#5F5F5F">Get involved with
              </span></i></b><span style="font-size:12.0pt;font-family:"Times New Roman","serif";color:#4F6228"><a href="http://www.southface.org/get-involved/become-a-member/" target="_blank"><b><span style="font-size:10.0pt;color:#4F6228">Southface</span></b></a></span><b><i><span style="font-size:10.0pt;color:#5F5F5F"> today!</span></i></b></p>


        <p class="MsoNormal"><a href="http://www.twitter.com/southfaceenergy" target="_blank"><span style="color:windowtext;text-decoration:none"><img alt="cid:image003.jpg@01CB96C8.7598B9C0" border="0" height="20" width="20"></span></a><i><span style="color:black"> </span></i><a href="http://www.linkedin.com/companies/southface" target="_blank"><span style="color:windowtext;text-decoration:none"><img alt="cid:image004.jpg@01CB96C8.7598B9C0" border="0" height="20" width="20"></span></a><i><span style="color:black"> </span></i><a href="http://www.facebook.com/pages/Southface/92291631957" target="_blank"><span style="color:windowtext;text-decoration:none"><img alt="cid:image005.jpg@01CB96C8.7598B9C0" border="0" height="20" width="20"></span></a></p>


        <p class="MsoNormal"> </p>
      </div>
      <br>
      
      <br>
      </div></div><pre>_______________________________________________
Bldg-sim mailing list
<a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>    </blockquote>
    <br>
  </div>

<br>_______________________________________________<br>
Bldg-sim mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br></div>