Maher<br>
The central plant with air source heat pump and possibly boiler backup
(gas/electric) can be modelled using EE4. The EE4 Version 1.70
Modelling Guide provides guidance in Section 4.6.4. The modelling
guide can be downloaded from
<a href="http://canmetenergy-canmetenergie.nrcan-rncan.gc.ca/eng/software_tools/ee4/modelling_guide.html" eudora="autourl">
http://canmetenergy-canmetenergie.nrcan-rncan.gc.ca/eng/software_tools/ee4/modelling_guide.html</a>
<br><br>
Use the seasonal efficiency of the air source heat pump. The
"ground source" is the heat exchanger. In your case the heat
exchanger is the air. You could be modelling a sea-water source
heat-pump with backup boiler. <br><br>
The only caveat is that you cannot model a water-source heat pump HVAC
system if you use the Combination Ground Source Heat Pump plant.
<br><br>
<br>
At 02:52 PM 21/10/2011, Maher Hemod wrote:<br>
<blockquote type=cite class=cite cite="">Content-class:
urn:content-classes:message<br>
Content-Type: multipart/alternative;<br>
<x-tab> </x-tab>
boundary="----_=_NextPart_001_01CC9022.89EEB8B3"<br><br>
<font size=2> <br>
<br>
Hi every one <br>
any one can help How can I modle centrlized air source heat pump in EE4
1.7 (Canadain energy simulation tools )?<br>
</font><font size=2 color="#062D32">Maher Hemod, EIT</font><br>
<font size=2 color="#8C9B34">Design Engineer<br>
Building Simulation Specialist</font><br>
<font size=2 color="#8C9B34"><b>ph.</b></font>
<font size=2 color="#062D32"> 604.888.7779</font><br>
<font size=2 color="#8C9B34"><b><a href="mailto:sabah.ali@rpeng.ca">
maher.hemod@rpeng.ca</a></b></font> <br>
<font face="Times New Roman, Times"> <br>
</font>_______________________________________________<br>
Bldg-sim mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" eudora="autourl">
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</blockquote>
<x-sigsep><p></x-sigsep>
<br>
Chris Jones<br>
14 Oneida Avenue<br>
Toronto, ON M5J 2E3.<br>
Tel. 416-203-7465<br>
Fax. 416-946-1005<br><br>
</body>
</html>