    you're welcome james.  now if i could only get a straight answer on
    how to address baseline system sizing/outdoor air rates when the
    proposed building is evaporatively cooled with 100% outdoor air ....
    sizing a baseline building system of packaged dx just doesn't sit
    right when the proposed is providing 20,000 cfm with 100% outdoor
    air.  and i get mixed comments from reviewers about too much energy
    savings ... or providing too much outdoor air in the baseline ...<br>
    <br>
    On 10/17/11 9:31 AM, Jim Dirkes wrote:
    <blockquote
      cite="mid:004b01cc8cea$44423f90$ccc6beb0$@buildingperformanceteam.com"
      type="cite">
      <meta http-equiv="Content-Type" content="text/html;
        charset=ISO-8859-1">
      <meta name="Generator" content="Microsoft Word 14 (filtered
        medium)">
      <style><!--
/* Font Definitions */
@font-face
        {font-family:Wingdings;
        panose-1:5 0 0 0 0 0 0 0 0 0;}
@font-face
        {font-family:Wingdings;
        panose-1:5 0 0 0 0 0 0 0 0 0;}
@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
        {font-family:Tahoma;
        panose-1:2 11 6 4 3 5 4 4 2 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0in;
        margin-bottom:.0001pt;
        font-size:12.0pt;
        font-family:"Times New Roman","serif";
        color:black;}
a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:blue;
        text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {mso-style-priority:99;
        color:purple;
        text-decoration:underline;}
p
        {mso-style-priority:99;
        mso-margin-top-alt:auto;
        margin-right:0in;
        mso-margin-bottom-alt:auto;
        margin-left:0in;
        font-size:12.0pt;
        font-family:"Times New Roman","serif";
        color:black;}
span.EmailStyle18
        {mso-style-type:personal-reply;
        font-family:"Calibri","sans-serif";
        color:#1F497D;}
.MsoChpDefault
        {mso-style-type:export-only;
        font-size:10.0pt;}
@page WordSection1
        {size:8.5in 11.0in;
        margin:1.0in 1.0in 1.0in 1.0in;}
div.WordSection1
        {page:WordSection1;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
      <div class="WordSection1">
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">Dear
            Patrick,<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">Thank
            you for sharing this GBCI response!  It is very informative
            and, while I won’t admit that I’ve been modeling anything
            incorrectly, I <u>am</u> going to change a couple of things
          </span><span
            style="font-size:11.0pt;font-family:Wingdings;color:#1F497D">J</span><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">.<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">In
            particular, I have heard on several occasions that the
            Increased Ventilation credit was a clear case of “IEQ vs.
            energy”; you make a decision to trade one against the
            other.  After reading the GBCI response below and then
            double-checking with ASHRAE 90.1, I find that they are
            consistent with each other and effectively allow no penalty
            for the increased energy caused by increased ventilation. 
            Very curious, considering there is no science which
            demonstrates a health benefit for outdoor airflows greater
            than that required by ASHRAE 62.1!<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">The
            other item is that I failed to notice (and still can’t find)
            anything in 621.1 which says that unoccupied ventilation
            should be zero.  I guess that is OK, but is also curious,
            since a portion of the ventilation calcs in 62.1 include
            consideration for off-gassing materials (which are always
            present.)<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">All
            in all, I’m smarter than I was as a result of your post, so
            it’s a good day!  Thanks again.<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
        <div>
          <p class="MsoNormal" style="text-align:center" align="center"><b><span
style="font-size:13.5pt;font-family:"Calibri","sans-serif";color:#1F497D">The
                Building Performance Team<br>
              </span></b><b><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">James
                V. Dirkes II, P.E., BEMP , LEED AP<br>
              </span></b><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">1631
              Acacia Drive NW<br>
              Grand Rapids, MI 49504<br>
              616 450 8653<o:p></o:p></span></p>
        </div>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
        <div>
          <div style="border:none;border-top:solid #B5C4DF
            1.0pt;padding:3.0pt 0in 0in 0in">
            <p class="MsoNormal"><b><span
style="font-size:10.0pt;font-family:"Tahoma","sans-serif";color:windowtext">From:</span></b><span
style="font-size:10.0pt;font-family:"Tahoma","sans-serif";color:windowtext">
                <a class="moz-txt-link-abbreviated" href="mailto:bldg-sim-bounces@lists.onebuilding.org">bldg-sim-bounces@lists.onebuilding.org</a>
                [<a class="moz-txt-link-freetext" href="mailto:bldg-sim-bounces@lists.onebuilding.org">mailto:bldg-sim-bounces@lists.onebuilding.org</a>] <b>On
                  Behalf Of </b>Patrick J. O'Leary, Jr.<br>
                <b>Sent:</b> Monday, October 17, 2011 11:46 AM<br>
                <b>To:</b> <a class="moz-txt-link-abbreviated" href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a>;
                <a class="moz-txt-link-abbreviated" href="mailto:bldg-sim@lists.onebuilding.org">bldg-sim@lists.onebuilding.org</a><br>
                <b>Subject:</b> [Bldg-sim] usgbc response to outdoor air
                question<o:p></o:p></span></p>
          </div>
        </div>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">back in september there was a thread about
          what the outdoor air rate in a baseline simulation should be
          compared to a proposed simulation, specifically when one is
          adding 30% more outdoor air to meet the ieqc2 requirement and
          earn 1 leed point.  there were differences of opinions about
          the flow rates between baseline and proposed being either the
          same (as required in 90.1 app g) or the baseline being the
          calculated per 62.1 and the proposed being as designed.<br>
          <br>
          so i submitted a support request to the usgbc and the reply i
          received is below, but in short the response is that unless
          you're using dcv optionally the outdoor air rates in the
          baseline and proposed energy simulations for eac1 should be
          the same.  the response below gives the standard responses to
          differing outdoor air rate scenarios.<br>
          <br>
          regards,<br>
          patrick<o:p></o:p></p>
        <p>[Fwd: Case 00531150: General LEED Questions<o:p></o:p></p>
        <p>-------- Original Message --------<o:p></o:p></p>
        <table class="MsoNormalTable" border="0" cellpadding="0"
          cellspacing="0">
          <tbody>
            <tr>
              <td style="padding:0in 0in 0in 0in" nowrap="nowrap"
                valign="top">
                <p class="MsoNormal" style="text-align:right"
                  align="right"><b>Subject: <o:p></o:p></b></p>
              </td>
              <td style="padding:0in 0in 0in 0in">
                <p>Case 00531150: General LEED Questions [
                  ref:00D49UeD.5004GN692:ref ]<o:p></o:p></p>
              </td>
            </tr>
            <tr>
              <td style="padding:0in 0in 0in 0in" nowrap="nowrap"
                valign="top">
                <p class="MsoNormal" style="text-align:right"
                  align="right"><b>Date: <o:p></o:p></b></p>
              </td>
              <td style="padding:0in 0in 0in 0in">
                <p>Mon, 17 Oct 2011 06:54:51 +0000 (GMT)<o:p></o:p></p>
              </td>
            </tr>
            <tr>
              <td style="padding:0in 0in 0in 0in" nowrap="nowrap"
                valign="top">
                <p class="MsoNormal" style="text-align:right"
                  align="right"><b>From: <o:p></o:p></b></p>
              </td>
              <td style="padding:0in 0in 0in 0in">
                <p>"No reply GBCI" <a moz-do-not-send="true"
                    href="mailto:no-reply@gbci.org"><no-reply@gbci.org></a>
                  <a moz-do-not-send="true"
                    href="mailto:no-reply@gbci.org"><no-reply@gbci.org></a><o:p></o:p></p>
              </td>
            </tr>
            <tr>
              <td style="padding:0in 0in 0in 0in" nowrap="nowrap"
                valign="top">
                <p class="MsoNormal" style="text-align:right"
                  align="right"><b>To: <o:p></o:p></b></p>
              </td>
              <td style="padding:0in 0in 0in 0in">
                <p>patrick@<o:p></o:p></p>
              </td>
            </tr>
          </tbody>
        </table>
        <p><o:p> </o:p></p>
        <p class="MsoNormal">Dear Patrick,<br>
          <br>
          Thank you for contacting the Green Building Certification
          Institute. <br>
          <br>
          You ask very good questions related to the relationship
          between ASHRAE Standards 62.1 and 90.1, and how these
          standards are applied across multiple LEED Rating System
          prerequisites and credits.<br>
          <br>
          The simple answer to your question is that, for systems
          without demand controlled ventilation, the outdoor air
          included in EA Credit 1 energy simulations must be the same in
          the Baseline and Proposed cases. If the project is attempting
          IEQ Credit 2 Increased Ventilation, then the values calculated
          in IEQc2 must be used in the EAc1 Basline and Proposed case
          energy models. Note that IEQc2 does not limit the project to
          providing only 30% more outdoor air than AHRAE 62.1
          Ventilation Rate Procedure minimums, so higher amounts are
          acceptable, as long as they are modeled identically in both
          the Baseline and Proposed case energy models.<br>
          <br>
          The following generic LEED Review Comment applies to
          ventilation systems that do not have demand controlled
          ventilation:<br>
          <br>
          It is unclear whether the minimum outside air rates (in CFM)
          were modeled identically in the Baseline and Proposed case for
          all zones not having Demand Control Ventilation in the
          Proposed case. Please confirm that minimum outside airflow (in
          units of cfm) was modeled identically in the Baseline and
          Proposed cases using the proposed case rates. Additionally,
          please verify that all systems in both the baseline and
          proposed case are modeled with zero outside air flow when fans
          are cycled on to meet unoccupied setback temperatures unless
          health or safety regulations mandate an alternate minimum flow
          during unoccupied periods (in which case, the unoccupied
          outside air rates should be modeled identically in the
          Baseline and Proposed case).<br>
          <br>
          The situation becomes a bit more complicated in you have
          systems that have demand controlled ventilation (often
          implemented as Carbon Dioxide control of outdoor air or as
          programmed control of outdoor air based on occupancy sensors.)
          In this case the Baseline case energy model must include the
          minimum outdoor air as determined by the ASHRAE 62.1
          Ventilation Rate Procedure calculations for all systems having
          demand controlled ventilation. <br>
          <br>
          The following generic LEED Review Comment applies to
          ventilation systems that do have demand controlled
          ventilation:<br>
          <br>
          Demand control ventilation was modeled for credit in the
          proposed case. Appendix G allows schedule changes for demand
          control ventilation as approved by the rating authority (Table
          G3.1#4(Baseline)). As the LEED Certification rating authority,
          GBCI requires that the outside air ventilation rates for the
          Baseline case be modeled using minimum ASHRAE 62.1-2004 (or
          2007 for LEED-NC 2009 projects) rates wherever credit is taken
          for demand control ventilation in the Proposed case. The
          proposed case minimum rates at design conditions should be
          modeled as designed. Please verify that the Baseline Case
          model reflects ASHRAE 62.1-2004 (or 2007) minimum rates for
          any spaces where credit is taken for demand control
          ventilation, or revise the model accordingly. For all other
          spaces, please confirm that minimum outside airflow (in units
          of cfm) was modeled identically in the Baseline and Proposed
          cases. Additionally, please verify that all systems in both
          the baseline and proposed cases are modeled with zero outside
          air flow when fans are cycled on to meet unoccupied setback
          temperatures unless health or safety regulations mandate an
          alternate minimum flow during unoccupied periods (in which
          case, the unoccupied outside air rates should be modeled
          identically in the Baseline and Proposed case).<br>
          <br>
          Finally, even though you don't address energy recovery in your
          question, whether or not you have energy recovery in your
          ventilation systems may affect how much better (or worse) your
          Proposed case energy models perform in relation to your
          Baseline case energy models. <br>
          <br>
          The following generic LEED Review Comment addresses energy
          recovery in EAc1 energy models as it relates to ventilation
          systems.<br>
          <br>
          Energy recovery is modeled for credit in the Proposed case.
          Please provide further information regarding the energy
          recovery efficiency, verify that outside air is modeled with
          zero flow in both the Baseline and Proposed cases during
          unoccupied periods when fans are cycled on to meet unoccupied
          setback temperatures unless health or safety regulations
          mandate an alternate minimum flow during unoccupied periods
          (in which case, the unoccupied outside air rates should be
          modeled identically in the Baseline and Proposed Case), and
          indicate the bypass mechanism used to bypass the energy
          recovery during mild conditions. <br>
          <br>
          I hope that helps, but if you have any further questions or
          concerns, please feel free to use the contact form at <a
            moz-do-not-send="true" href="http://www.gbci.org/contactus">http://www.gbci.org/contactus</a>
          and select "Follow up to GBCI Response," inputting your case
          number from this email's subject line.<br>
          <br>
          Best Regards,<br>
          <br>
          Dan Katzenberger, P.E., CEM, BEMP, LEED-AP BD+C<br>
          <br>
          Green Building Certification Institute <br>
          2101 L Street NW, Suite 500 <br>
          Washington, DC 20037 <br>
          800-795-1746 (phone)<br>
          202 828-5110 (fax) <br>
          <a moz-do-not-send="true" href="http://www.gbci.org/contactus">www.gbci.org/contactus</a><br>
          <br>
          The text above represents a staff opinion of a particular
          issue, and does NOT set any precedent to be upheld during a
          LEED Certification Review. For official rulings in advance of
          a LEED Certification Review, customers should utilize the
          Formal Inquiries process available in LEED Online that results
          in a Project Credit Interpretation Ruling (Project CIR) and
          possibly a LEED Interpretation (formerly CIRs or Public
          Rulings). Applications for LEED Certification will be
          thoroughly reviewed based on USGBC Member balloted and
          approved LEED Rating Systems, with addenda, and USGBC approved
          LEED Interpretations, or Project CIRs administered by GBCI, as
          applicable. Please note that certain inquiries submitted to
          USGBC are forwarded to GBCI for reply as appropriate.<br>
          <br>
          <br>
          _______________________________<br>
          CUSTOMER EMAIL ADDRESS: <br>
          patirck@<br>
          <br>
          CUSTOMER INQUIRY:<br>
          I am trying to verify what the minimum outdoor airflow rate
          required for EAc1 is and am not sure if this requires a CIR. <br>
          <br>
          If the Proposed outdoor air ventilation is a minimum of 30%
          higher than the minimum required by ASHRAE 62 in order to
          achieve 1 LEED point for credit IEQC2 is the Baseline outdoor
          air rate also 30% higher than the minimum required by ASHRAE
          62? or would the Baseline outdoor air ventilation rate be the
          minimum outdoor air rate per ASHRAE 62 calculations. <br>
          <br>
          In other words, if ASHRAE 62 requires a minimum of 1,000 CFM
          of outdoor air, and 1,300 CFM is provided to attain 1 LEED
          point via IEQC1, is the Baseline outdoor air flow rate 1,000
          CFM or 1,300 CFM in the energy simulation? <br>
          <br>
          90.1-2007/2004 both say the minimu    m outdoor airflow rates
          shall be the same for both the proposed and baseline building
          designs, as does the user manual. <br>
          <br>
          But this logic seems to reward the Proposed simulation by
          conditioning the additional outdoor air supplied (300 cfm in
          the example above) to achieve IEQC1 in the Baseline system as
          well as the proposed. <br>
          <br>
          The logic of using the minimum required in the Baseline case
          is reflected in EAC1 in the equipment efficiency requirements.
          Baseline efficiencies are the minimum required, e.g. SEER 13
          for packaged units. <br>
          <br>
          It is the intent of the requirement that I am not sure is
          clear. Increasing the outdoor air ventilation rate increases
          the energy used to condition the outdoor air, so if the intent
          is to put the onus on Proposed design to show energy
          reduction/LEED compliance over the 90.1/62 requirements
          shouldn't the Baseline outdoor air be the minimum air flow
          rate per the ASHRAE 62 calculations? This puts the onus on the
          design team to provide a design that compensates for the
          increase in energy to meet IEQC2 by providing some method of
          processing the increase in outdoor air while still reducing
          energy consumption.<o:p></o:p></p>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
Bldg-sim mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
    </blockquote>
    <br>
  </body>
</html>