    back in september there was a thread about what the outdoor air rate
    in a baseline simulation should be compared to a proposed
    simulation, specifically when one is adding 30% more outdoor air to
    meet the ieqc2 requirement and earn 1 leed point.  there were
    differences of opinions about the flow rates between baseline and
    proposed being either the same (as required in 90.1 app g) or the
    baseline being the calculated per 62.1 and the proposed being as
    designed.<br>
    <br>
    so i submitted a support request to the usgbc and the reply i
    received is below, but in short the response is that unless you're
    using dcv optionally the outdoor air rates in the baseline and
    proposed energy simulations for eac1 should be the same.  the
    response below gives the standard responses to differing outdoor air
    rate scenarios.<br>
    <br>
    regards,<br>
    patrick<br>
    <p>[Fwd: Case 00531150: General LEED Questions</p>
    <p>-------- Original Message --------</p>
    <table class="moz-email-headers-table" border="0" cellpadding="0"
      cellspacing="0">
      <tbody>
        <tr>
          <th align="right" nowrap="nowrap" valign="baseline">Subject: </th>
          <td>
            <p>Case 00531150: General LEED Questions [
              ref:00D49UeD.5004GN692:ref ]</p>
          </td>
        </tr>
        <tr>
          <th align="right" nowrap="nowrap" valign="baseline">Date: </th>
          <td>
            <p>Mon, 17 Oct 2011 06:54:51 +0000 (GMT)</p>
          </td>
        </tr>
        <tr>
          <th align="right" nowrap="nowrap" valign="baseline">From: </th>
          <td>
            <p>"No reply GBCI" <a moz-do-not-send="true"
                class="moz-txt-link-rfc2396E"
                href="mailto:no-reply@gbci.org"><no-reply@gbci.org></a>
              <a moz-do-not-send="true" class="moz-txt-link-rfc2396E"
                href="mailto:no-reply@gbci.org"><no-reply@gbci.org></a></p>
          </td>
        </tr>
        <tr>
          <th align="right" nowrap="nowrap" valign="baseline">To: </th>
          <td>
            <p>patrick@<br>
            </p>
          </td>
        </tr>
      </tbody>
    </table>
    <p><br>
    </p>
    Dear Patrick,<br>
    <br>
    Thank you for contacting the Green Building Certification Institute.
    <br>
    <br>
    You ask very good questions related to the relationship between
    ASHRAE
    Standards 62.1 and 90.1, and how these standards are applied across
    multiple LEED Rating System prerequisites and credits.<br>
    <br>
    The simple answer to your question is that, for systems without
    demand
    controlled ventilation, the outdoor air included in EA Credit 1
    energy
    simulations must be the same in the Baseline and Proposed cases. If
    the
    project is attempting IEQ Credit 2 Increased Ventilation, then the
    values calculated in IEQc2 must be used in the EAc1 Basline and
    Proposed case energy models. Note that IEQc2 does not limit the
    project
    to providing only 30% more outdoor air than AHRAE 62.1 Ventilation
    Rate
    Procedure minimums, so higher amounts are acceptable, as long as
    they
    are modeled identically in both the Baseline and Proposed case
    energy
    models.<br>
    <br>
    The following generic LEED Review Comment applies to ventilation
    systems that do not have demand controlled ventilation:<br>
    <br>
    It is unclear whether the minimum outside air rates (in CFM) were
    modeled identically in the Baseline and Proposed case for all zones
    not
    having Demand Control Ventilation in the Proposed case. Please
    confirm
    that minimum outside airflow (in units of cfm) was modeled
    identically
    in the Baseline and Proposed cases using the proposed case rates.
    Additionally, please verify that all systems in both the baseline
    and
    proposed case are modeled with zero outside air flow when fans are
    cycled on to meet unoccupied setback temperatures unless health or
    safety regulations mandate an alternate minimum flow during
    unoccupied
    periods (in which case, the unoccupied outside air rates should be
    modeled identically in the Baseline and Proposed case).<br>
    <br>
    The situation becomes a bit more complicated in you have systems
    that
    have demand controlled ventilation (often implemented as Carbon
    Dioxide
    control of outdoor air or as programmed control of outdoor air based
    on
    occupancy sensors.) In this case the Baseline case energy model must
    include the minimum outdoor air as determined by the ASHRAE 62.1
    Ventilation Rate Procedure calculations for all systems having
    demand
    controlled ventilation. <br>
    <br>
    The following generic LEED Review Comment applies to ventilation
    systems that do have demand controlled ventilation:<br>
    <br>
    Demand control ventilation was modeled for credit in the proposed
    case.
    Appendix G allows schedule changes for demand control ventilation as
    approved by the rating authority (Table G3.1#4(Baseline)). As the
    LEED
    Certification rating authority, GBCI requires that the outside air
    ventilation rates for the Baseline case be modeled using minimum
    ASHRAE
    62.1-2004 (or 2007 for LEED-NC 2009 projects) rates wherever credit
    is
    taken for demand control ventilation in the Proposed case. The
    proposed
    case minimum rates at design conditions should be modeled as
    designed.
    Please verify that the Baseline Case model reflects ASHRAE 62.1-2004
    (or 2007) minimum rates for any spaces where credit is taken for
    demand
    control ventilation, or revise the model accordingly. For all other
    spaces, please confirm that minimum outside airflow (in units of
    cfm)
    was modeled identically in the Baseline and Proposed cases.
    Additionally, please verify that all systems in both the baseline
    and
    proposed cases are modeled with zero outside air flow when fans are
    cycled on to meet unoccupied setback temperatures unless health or
    safety regulations mandate an alternate minimum flow during
    unoccupied
    periods (in which case, the unoccupied outside air rates should be
    modeled identically in the Baseline and Proposed case).<br>
    <br>
    Finally, even though you don't address energy recovery in your
    question, whether or not you have energy recovery in your
    ventilation
    systems may affect how much better (or worse) your Proposed case
    energy
    models perform in relation to your Baseline case energy models. <br>
    <br>
    The following generic LEED Review Comment addresses energy recovery
    in
    EAc1 energy models as it relates to ventilation systems.<br>
    <br>
    Energy recovery is modeled for credit in the Proposed case. Please
    provide further information regarding the energy recovery
    efficiency,
    verify that outside air is modeled with zero flow in both the
    Baseline
    and Proposed cases during unoccupied periods when fans are cycled on
    to
    meet unoccupied setback temperatures unless health or safety
    regulations mandate an alternate minimum flow during unoccupied
    periods
    (in which case, the unoccupied outside air rates should be modeled
    identically in the Baseline and Proposed Case), and indicate the
    bypass
    mechanism used to bypass the energy recovery during mild conditions.
    <br>
    <br>
    I hope that helps, but if you have any further questions or
    concerns,
    please feel free to use the contact form at
    <a moz-do-not-send="true" class="moz-txt-link-freetext"
      href="http://www.gbci.org/contactus">http://www.gbci.org/contactus</a>
    and select "Follow up to GBCI Response,"
    inputting your case number from this email's subject line.<br>
    <br>
    Best Regards,<br>
    <br>
    Dan Katzenberger, P.E., CEM, BEMP, LEED-AP BD+C<br>
    <br>
    Green Building Certification Institute <br>
    2101 L Street NW, Suite 500 <br>
    Washington, DC 20037 <br>
    800-795-1746 (phone)<br>
    202 828-5110 (fax) <br>
    <a moz-do-not-send="true" class="moz-txt-link-abbreviated"
      href="http://www.gbci.org/contactus">www.gbci.org/contactus</a><br>
    <br>
    The text above represents a staff opinion of a particular issue, and
    does NOT set any precedent to be upheld during a LEED Certification
    Review. For official rulings in advance of a LEED Certification
    Review,
    customers should utilize the Formal Inquiries process available in
    LEED
    Online that results in a Project Credit Interpretation Ruling
    (Project
    CIR) and possibly a LEED Interpretation (formerly CIRs or Public
    Rulings). Applications for LEED Certification will be thoroughly
    reviewed based on USGBC Member balloted and approved LEED Rating
    Systems, with addenda, and USGBC approved LEED Interpretations, or
    Project CIRs administered by GBCI, as applicable. Please note that
    certain inquiries submitted to USGBC are forwarded to GBCI for reply
    as
    appropriate.<br>
    <br>
    <br>
    _______________________________<br>
    CUSTOMER EMAIL ADDRESS: <br>
    patirck@<br>
    <br>
    CUSTOMER INQUIRY:<br>
    I am trying to verify what the minimum outdoor airflow rate required
    for EAc1 is and am not sure if this requires a CIR. <br>
    <br>
    If the Proposed outdoor air ventilation is a minimum of 30% higher
    than
    the minimum required by ASHRAE 62 in order to achieve 1 LEED point
    for
    credit IEQC2 is the Baseline outdoor air rate also 30% higher than
    the
    minimum required by ASHRAE 62? or would the Baseline outdoor air
    ventilation rate be the minimum outdoor air rate per ASHRAE 62
    calculations. <br>
    <br>
    In other words, if ASHRAE 62 requires a minimum of 1,000 CFM of
    outdoor
    air, and 1,300 CFM is provided to attain 1 LEED point via IEQC1, is
    the
    Baseline outdoor air flow rate 1,000 CFM or 1,300 CFM in the energy
    simulation? <br>
    <br>
    90.1-2007/2004 both say the minimu    m outdoor airflow rates shall
    be
    the same for both the proposed and baseline building designs, as
    does
    the user manual. <br>
    <br>
    But this logic seems to reward the Proposed simulation by
    conditioning
    the additional outdoor air supplied (300 cfm in the example above)
    to
    achieve IEQC1 in the Baseline system as well as the proposed. <br>
    <br>
    The logic of using the minimum required in the Baseline case is
    reflected in EAC1 in the equipment efficiency requirements. Baseline
    efficiencies are the minimum required, e.g. SEER 13 for packaged
    units.
    <br>
    <br>
    It is the intent of the requirement that I am not sure is clear.
    Increasing the outdoor air ventilation rate increases the energy
    used
    to condition the outdoor air, so if the intent is to put the onus on
    Proposed design to show energy reduction/LEED compliance over the
    90.1/62 requirements shouldn't the Baseline outdoor air be the
    minimum
    air flow rate per the ASHRAE 62 calculations? This puts the onus on
    the
    design team to provide a design that compensates for the increase in
    energy to meet IEQC2 by providing some method of processing the
    increase in outdoor air while still reducing energy consumption.<br>