<p class="MsoNormal"><span lang="EN-US">Hi Paula</span></p>
<p class="MsoNormal"><span lang="EN-US"> </span></p>
<p class="MsoNormal"><span lang="EN-US">Thanks for your patient reply. You
explained the 3 items in details, but my question still exists. For each item:</span></p>
<p class="MsoNormal"><span lang="EN-US">1.<span style="mso-spacerun:yes">
</span>The function "Monthly Heating/Cooling loads" also provides the
max heating/cooling loads with unit of Btu/hr, in addition to the monthly
average sum of all gains and losses of your space. And the former item is what
I called the 1st loads.</span></p>
<p class="MsoNormal"><span lang="EN-US"> </span></p>
<p class="MsoNormal"><span lang="EN-US">2. The function "Hourly
gains/losses" provides the gains of each kind of energy flow by hour on
any particular day, so we can get the hourly gains/losses on the
hottest/coldest day. That particular gains/losses makes the max cooling/heating
loads and this item is what I called the 2nd loads.</span></p>
<p class="MsoNormal"><span lang="EN-US"> </span></p>
<p class="MsoNormal"><span lang="EN-US">3. Behavior of specific transfer of energy
is provided with the average hourly value by month, the hourly value is kind of
gains, so if I focus at the right month and hour, and make sum of all the
specific hourly gains I can get the max cooling/heating loads. That is what I
called the 3rd loads</span></p>
<p class="MsoNormal"><span lang="EN-US"> </span></p>
<p class="MsoNormal"><span lang="EN-US">In this way, the three functions can
reflect the same index, the max cooling/heating loads and I think they should
be consistent with each other, but actually they don't. </span></p>
<p class="MsoNormal"><span lang="EN-US"> </span></p>
<p class="MsoNormal"><span lang="EN-US">I hope I present the issues clearly. </span></p>
<br>Thanks!<br><br>-- <br>Chou Shen<br>Graduate Research Assistant<br>Department of Civil, Architectural & Environmental Engineering<br>Missouri University of Science and Technology<br><br><br><br>