    <big><font size="-1"><big><font face="Arial">Hello Eleanor,<br>
            Adding to Vikram's advice -- You may then also apply the
            heat recovery to the individual IU units instead of the
            DOAS.<br>
            <br>
            But, an important question for experts who may be
            experienced with working real-life Chilled Beam systems is
            --<br>
            <br>
            Whether </font></big></font></big>or not the OA moved
    through the active chilled beams is completely (100%) Outside Air
    only <u>OR</u> Whether some of the supply air is still
    recirculated?<br>
    I presume it'll depend on latent loads but I understand that for
    most occupied zones some air is actually recirculated back to the
    AHU's to control the RH and balance the system!?<br>
    Please correct me if that is any different from anyone's real-life
    experience and what Vikram is referring to is the experience you all
    share? Vikram, your veiws?<br>
    We are modeling a couple of chilled beam and slab systems but with
    little live examples and experiences to corroborate on this aspect.<br>
    <br>
    Your inputs would be valuable . . . .<br>
    Thanks,<br>
    Neeraj<br>
    <br>
    <small>Neeraj Kapoor<br>
      t: +91.99581.70018<br>
      Kalpakrit Sustainable Environments Pvt. Ltd.<br>
      New Delhi, India</small><br>
    <br>
    <br>
    On 12-08-2011 17:13, Sami, Vikram wrote:
    <blockquote
cite="mid:5CFB01489F62D143B61289AF32DC98B104287BA70D@chi01exmb.perkinswill.net"
      type="cite">
      <pre wrap="">If you are using an active chilled beam, then you don't need to model the doas - just use 100% OA for your ahu.

Sent from a mobile device

 -----Original Message-----
From:   沈洁 [<a class="moz-txt-link-freetext" href="mailto:shenjie820730@hotmail.com">mailto:shenjie820730@hotmail.com</a>]
Sent:   Friday, August 12, 2011 04:25 AM Central Standard Time
To:     <a class="moz-txt-link-abbreviated" href="mailto:bldg-sim@lists.onebuilding.org">bldg-sim@lists.onebuilding.org</a>
Subject:        [Bldg-sim] DOAS and chilled beam/radiator

Hi, all;

I’m simulating a project with chilled beam/radiator plus dedicated fresh air system, I search from archive, it seems most of you using DOAS (a dummy zone) and IU/FCU to simulate, DOAS provide the fresh air and IU/FCU use the “Outdoor air from” DOAS, the radiator use baseboard instead with zero fan energy power.

But the DOAS in my project is 1) variable speed to reduce the fresh air energy base on occupancy schedule; 2) wheel heat recovery with exhaust air; 3) during the transition period, the DOAS will bypass the wheel to provide maximum fresh air to offset all the heating and cooling demand and chilled beam and radiator will shut off.

Now, my method is :

1)  using VAV system to represent DOAS , enter the “ Design supply/return “ flow to show the DOAS fresh air and exhaust air volume;

2) Define the wheel heat recovery with fresh air and exhaust air, and operation control is “OA exhaust DT”

3) Define the dummy with the same maximum fresh air volume, and also control the cool and heat temperature (otherwise the heat recovery will not work at all).

It seems works very well. But when I reading hourly report, I found the fresh air volume keeps the maximum all the time, so the fan running at the rated power the whole year, which results in the large fan energy consumpation.

How can I make the DOAS’s fresh air volume variable and fan variable according to the acutal IU/FC’s fresh air volume ??

Any comments and suggestions will be appreciated.


Eleanor Shen (沈洁)
Consultant
Environmental Resources Management

Tel: +8621-5385 3050, ext:158
Fax: +8621-6469 2185
Email: <a class="moz-txt-link-abbreviated" href="mailto:eleanor.shen@erm.com">eleanor.shen@erm.com</a> <a class="moz-txt-link-rfc2396E" href="mailto:j@erm.com"><mailto:j@erm.com></a>

<a class="moz-txt-link-abbreviated" href="http://www.erm.com">www.erm.com</a> <a class="moz-txt-link-rfc2396E" href="http://www.erm.com/"><http://www.erm.com/></a>

ERM Chinese Web Page

<a class="moz-txt-link-abbreviated" href="http://www.ermcn.com">www.ermcn.com</a> <a class="moz-txt-link-rfc2396E" href="http://www.ermcn.com/"><http://www.ermcn.com/></a>

*** ERM is granted Class A EIA License by China SEPA***
***ERM is named the 2008 Environmental Advisor of the Year (Acquisitions Monthly) ***

This email and any files transmitted with it are confidential and intended solely for the addressee.  If you are not the named addressee you should not disseminate, distribute, copy, or alter this email.
_______________________________________________
Bldg-sim mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
    </blockquote>
  </body>
</html>