<!DOCTYPE HTML PUBLIC "-//W3C//DTD HTML 4.0 Transitional//EN">
<HTML xmlns="http://www.w3.org/TR/REC-html40" xmlns:v = 
"urn:schemas-microsoft-com:vml" xmlns:o = 
"urn:schemas-microsoft-com:office:office" xmlns:w = 
"urn:schemas-microsoft-com:office:word" xmlns:x = 
"urn:schemas-microsoft-com:office:excel" xmlns:m = 
"http://schemas.microsoft.com/office/2004/12/omml"><HEAD>
<META content="text/html; charset=us-ascii" http-equiv=Content-Type>
<META name=GENERATOR content="MSHTML 9.00.8112.16430"><!--[if !mso]>
<STYLE>v\:* {
        BEHAVIOR: url(#default#VML)
}
o\:* {
        BEHAVIOR: url(#default#VML)
}
w\:* {
        BEHAVIOR: url(#default#VML)
}
.shape {
        BEHAVIOR: url(#default#VML)
}
</STYLE>
<![endif]-->
<STYLE>@font-face {
        font-family: MS Mincho;
}
@font-face {
        font-family: Cambria Math;
}
@font-face {
        font-family: Calibri;
}
@font-face {
        font-family: Tahoma;
}
@font-face {
        font-family: Stylus BT;
}
@font-face {
        font-family: @MS Mincho;
}
@font-face {
        font-family: Consolas;
}
@page WordSection1 {size: 8.5in 11.0in; margin: 1.0in 1.0in 1.0in 1.0in; }
P.MsoNormal {
        MARGIN: 0in 0in 0pt; FONT-FAMILY: "Calibri","sans-serif"; FONT-SIZE: 11pt
}
LI.MsoNormal {
        MARGIN: 0in 0in 0pt; FONT-FAMILY: "Calibri","sans-serif"; FONT-SIZE: 11pt
}
DIV.MsoNormal {
        MARGIN: 0in 0in 0pt; FONT-FAMILY: "Calibri","sans-serif"; FONT-SIZE: 11pt
}
A:link {
        COLOR: blue; TEXT-DECORATION: underline; mso-style-priority: 99
}
SPAN.MsoHyperlink {
        COLOR: blue; TEXT-DECORATION: underline; mso-style-priority: 99
}
A:visited {
        COLOR: purple; TEXT-DECORATION: underline; mso-style-priority: 99
}
SPAN.MsoHyperlinkFollowed {
        COLOR: purple; TEXT-DECORATION: underline; mso-style-priority: 99
}
P.MsoPlainText {
        MARGIN: 0in 0in 0pt; FONT-FAMILY: Consolas; FONT-SIZE: 10.5pt; mso-style-priority: 99; mso-style-link: "Plain Text Char"
}
LI.MsoPlainText {
        MARGIN: 0in 0in 0pt; FONT-FAMILY: Consolas; FONT-SIZE: 10.5pt; mso-style-priority: 99; mso-style-link: "Plain Text Char"
}
DIV.MsoPlainText {
        MARGIN: 0in 0in 0pt; FONT-FAMILY: Consolas; FONT-SIZE: 10.5pt; mso-style-priority: 99; mso-style-link: "Plain Text Char"
}
P.MsoAcetate {
        MARGIN: 0in 0in 0pt; FONT-FAMILY: "Tahoma","sans-serif"; FONT-SIZE: 8pt; mso-style-priority: 99; mso-style-link: "Balloon Text Char"
}
LI.MsoAcetate {
        MARGIN: 0in 0in 0pt; FONT-FAMILY: "Tahoma","sans-serif"; FONT-SIZE: 8pt; mso-style-priority: 99; mso-style-link: "Balloon Text Char"
}
DIV.MsoAcetate {
        MARGIN: 0in 0in 0pt; FONT-FAMILY: "Tahoma","sans-serif"; FONT-SIZE: 8pt; mso-style-priority: 99; mso-style-link: "Balloon Text Char"
}
P.MsoListParagraph {
        MARGIN: 0in 0in 0pt 0.5in; FONT-FAMILY: "Calibri","sans-serif"; FONT-SIZE: 11pt; mso-style-priority: 34
}
LI.MsoListParagraph {
        MARGIN: 0in 0in 0pt 0.5in; FONT-FAMILY: "Calibri","sans-serif"; FONT-SIZE: 11pt; mso-style-priority: 34
}
DIV.MsoListParagraph {
        MARGIN: 0in 0in 0pt 0.5in; FONT-FAMILY: "Calibri","sans-serif"; FONT-SIZE: 11pt; mso-style-priority: 34
}
SPAN.EmailStyle17 {
        FONT-FAMILY: "Calibri","sans-serif"; COLOR: windowtext; mso-style-type: personal-compose
}
SPAN.BalloonTextChar {
        FONT-FAMILY: "Tahoma","sans-serif"; mso-style-priority: 99; mso-style-link: "Balloon Text"; mso-style-name: "Balloon Text Char"
}
SPAN.PlainTextChar {
        FONT-FAMILY: Consolas; mso-style-priority: 99; mso-style-link: "Plain Text"; mso-style-name: "Plain Text Char"
}
.MsoChpDefault {
        mso-style-type: export-only
}
DIV.WordSection1 {
        page: WordSection1
}
OL {
        MARGIN-BOTTOM: 0in
}
UL {
        MARGIN-BOTTOM: 0in
}
</STYLE>
<!--[if gte mso 9]><xml>
 <o:shapedefaults v:ext="edit" spidmax="2050" />
</xml><![endif]--><!--[if gte mso 9]><xml>
 <o:shapelayout v:ext="edit">
  <o:idmap v:ext="edit" data="1" />
 </o:shapelayout></xml><![endif]--></HEAD>
<BODY lang=EN-US vLink=purple link=blue>
<DIV dir=ltr align=left><SPAN class=571570616-20072011><FONT size=2 
face=Arial>Hi Nick,</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=571570616-20072011><FONT size=2 
face=Arial></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=571570616-20072011><FONT size=2 
face=Arial>To keep it simple, I would just derate the schedules, your 10/15% 
reduction but on an hourly basis (ie one or more hours are moved 
to 0%/setback) and apply the RESET-PRIORITY and MIN-RESET-FLOW 
keywords.  I think averaging it out beforehand and explaining as part of 
your modelling methodology in your report would take less time and be easier to 
explain.  I would start with a small test model, to make sure you have 
the right percentages. </FONT></SPAN></DIV>
<DIV> </DIV>
<DIV><SPAN class=571570616-20072011></SPAN><FONT face=Arial><FONT size=2>S<SPAN 
class=571570616-20072011>haun</SPAN></FONT></FONT></DIV>
<DIV><FONT face=Arial><FONT size=2><SPAN 
class=571570616-20072011></SPAN></FONT></FONT> </DIV>
<DIV><FONT face=Arial><FONT size=2><SPAN class=571570616-20072011>
<STYLE>
st1\:*{behavior:url(#ieooui) }
</STYLE>

<STYLE>
<!--
 /* Style Definitions */
 p.MsoNormal, li.MsoNormal, div.MsoNormal
        {mso-style-parent:"";
        margin:0in;
        margin-bottom:.0001pt;
        mso-pagination:widow-orphan;
        font-size:12.0pt;
        font-family:"Times New Roman";
        mso-fareast-font-family:"Times New Roman";}
span.GramE
        {mso-style-name:"";
        mso-gram-e:yes;}
@page Section1
        {size:8.5in 11.0in;
        margin:1.0in 1.25in 1.0in 1.25in;
        mso-header-margin:.5in;
        mso-footer-margin:.5in;
        mso-paper-source:0;}
div.Section1
        {page:Section1;}
-->
</STYLE>

<DIV class=Section1>
<P class=MsoNormal><I><SPAN style="FONT-FAMILY: Arial; FONT-SIZE: 10pt">Shaun 
Martin LEED AP</SPAN></I></P>
<P class=MsoNormal><I><SPAN 
style="FONT-FAMILY: Arial; FONT-SIZE: 10pt">Principal</SPAN></I></P>
<P class=MsoNormal><I><SPAN style="FONT-FAMILY: Arial; FONT-SIZE: 10pt">Shaun 
Martin Consulting</SPAN></I></P>
<P class=MsoNormal><I><SPAN style="FONT-FAMILY: Arial; FONT-SIZE: 10pt">Suite 
<?xml:namespace prefix = u1 /><u1:Street u2:st="on"><u1:address 
u2:st="on"><?xml:namespace prefix = st1 ns = 
"urn:schemas-microsoft-com:office:smarttags" /><st1:Street 
w:st="on"><st1:address w:st="on">200 - 420 West Hastings 
Street</u1:address></u1:Street></st1:address></st1:Street></SPAN></I><o:p></o:p></P>
<P class=MsoNormal><u1:place u2:st="on"><u1:City u2:st="on"><st1:place 
w:st="on"><st1:City w:st="on"><I><SPAN 
style="FONT-FAMILY: Arial; FONT-SIZE: 10pt">Vancouver</SPAN></I></st1:City><I><SPAN 
style="FONT-FAMILY: Arial; FONT-SIZE: 10pt"></u1:City> <u1:State 
u2:st="on"><st1:State w:st="on">BC</u1:State></st1:State>   
<u1:PostalCode u2:st="on"><st1:PostalCode w:st="on">V6B 
1L1</u1:PostalCode></st1:PostalCode></SPAN></I></st1:place></u1:place></P>
<P class=MsoNormal><I><SPAN 
style="FONT-FAMILY: Arial; FONT-SIZE: 10pt">604-789-1095</SPAN></I></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: Arial; COLOR: blue; FONT-SIZE: 10pt"><A 
title=blocked::mailto:smartin@shaunmartinconsulting.com 
href="blocked::mailto:smartin@shaunmartinconsulting.com"><I><SPAN 
title=blocked::mailto:smartin@shaunmartinconsulting.com><SPAN 
title=blocked::mailto:smartin@shaunmartinconsulting.com><SPAN 
title=blocked::mailto:smartin@shaunmartinconsulting.com><FONT 
color=#000000>smartin@shaunmartinconsulting.com</FONT></SPAN></I></SPAN></SPAN></A></SPAN></P>
<P class=MsoNormal><SPAN class=GramE><I><SPAN 
style="FONT-FAMILY: Arial; FONT-SIZE: 10pt">member</SPAN></I></SPAN><I><SPAN 
style="FONT-FAMILY: Arial; FONT-SIZE: 10pt"> CAGBC, 
ASHRAE</SPAN></I></P></DIV></SPAN></FONT></FONT></DIV>
<DIV><BR></DIV>
<DIV dir=ltr lang=en-us class=OutlookMessageHeader align=left>
<HR tabIndex=-1>
<FONT size=2 face=Tahoma><B>From:</B> bldg-sim-bounces@lists.onebuilding.org 
[mailto:bldg-sim-bounces@lists.onebuilding.org] <B>On Behalf Of </B>Nick 
Caton<BR><B>Sent:</B> Wednesday, July 20, 2011 8:45 AM<BR><B>To:</B> James 
Hansen; Eurek, John S NWO; David Eldridge; 
bldg-sim@lists.onebuilding.org<BR><B>Subject:</B> Re: [Bldg-sim] How have you 
approached... (UNCLASSIFIED)<BR></FONT><BR></DIV>
<DIV></DIV>
<DIV class=WordSection1>
<P class=MsoNormal>Thanks so much for the suggestions!<SPAN 
class=571570616-20072011><FONT color=#0000ff size=2 
face=Arial> </FONT></SPAN><o:p></o:p></P>
<P class=MsoNormal><o:p> </o:p></P>
<P class=MsoNormal>I myself have tread the “extensive, realistic 
fractional/thermostat scheduling” path before under similar circumstances.  
Upon facing a VERY large project, where the amount of explicit scheduling 
required for that approach is compounded by the sheer quantity and variety of 
occupied spaces benefiting from this relay setup, I am challenged with 
brainstorming any acceptable (by LEED reviewer) means of approximating the same 
behavior/savings by simplifying the problem…<o:p></o:p></P>
<P class=MsoNormal><o:p> </o:p></P>
<P class=MsoNormal>Here are some alternative ideas we’ve come up with so far 
 – I would very much appreciate others’ thoughts on these, or any further 
related LEED/USGBC experiences to share as well:<o:p></o:p></P>
<P style="TEXT-INDENT: -0.25in; mso-list: l0 level1 lfo1" 
class=MsoListParagraph><![if !supportLists]><SPAN 
style="mso-list: Ignore">1.<SPAN 
style="FONT: 7pt 'Times New Roman'">       
</SPAN></SPAN><![endif]>90.1 already prescribes how we quantify the savings of 
occupancy sensors for installed lighting  (10 or 15% flat deduction on the 
LPD).  Rather than define & justify the quantity and timing of 
unoccupied hours between varying space types (murky waters at best), one could 
instead reduce the loads incident on the affected systems by the same 
percentage.  This might be accomplished by applying this 10/15% deduction 
to the affected spaces’ fractional load schedules (occupancy, equipment & 
lighting).  One would need to tread carefully to avoid “double-dipping” on 
any spaces already claiming a LPD deduction for occupancy sensors.  
Baseline model’s schedules would remain unaffected and would be documented 
alongside the modified ones to illustrate the difference. <o:p></o:p></P>
<P style="TEXT-INDENT: -0.25in; mso-list: l0 level1 lfo1" 
class=MsoListParagraph><![if !supportLists]><SPAN 
style="mso-list: Ignore">2.<SPAN 
style="FONT: 7pt 'Times New Roman'">       
</SPAN></SPAN><![endif]>(Simpler to model, but requiring slightly more 
documentation):  Let’s say a hospital has an annual average of 85% 
occupancy for all its patient rooms.  Treating every other room normally, 
select a representative sampling (considering envelope loads) of 15% of the 
patient rooms.  Model those selected rooms as “empty” (set people, lights 
and equipment loads = 0) but still conditioned to maintain the thermostat 
setpoint (against loads incident from the envelope & neighboring spaces). 
Apply the 0% minimum turndown behavior to those “empty” rooms only.  
Baseline model would receive identical treatments, excepting the 0% turndown 
behavior.  Documentation would include illustrating which zones were 
sampled against the others, and justification for the net annual “occupancy 
rate” used for each space type.<o:p></o:p></P>
<P class=MsoNormal><o:p> </o:p></P>
<P class=MsoNormal>I have mixed feelings – obviously any simplification of the 
problem has the potential to under/overstate the savings that might be found 
with a more exhaustive scheduling approach, but may result in as good or even a 
better estimation provided with solid documentation and execution.  Does 
anyone think the above approaches could work well, or have any suggestions to 
refine the strategies?  <o:p></o:p></P>
<P class=MsoNormal><o:p> </o:p></P>
<P class=MsoNormal>Thanks again!<o:p></o:p></P>
<P class=MsoNormal><o:p> </o:p></P>
<P class=MsoNormal>~Nick<o:p></o:p></P>
<P class=MsoNormal><o:p> </o:p></P>
<P class=MsoNormal><o:p> </o:p></P>
<P class=MsoNormal><IMG id=Picture_x0020_1 alt=cid:489575314@22072009-0ABB 
src="cid:571570616@20072011-2F6C" width=119 height=37><B><SPAN 
style="FONT-FAMILY: 'Stylus BT','sans-serif'; COLOR: #2d4d5e"><o:p></o:p></SPAN></B></P>
<P class=MsoNormal><B><SPAN 
style="FONT-FAMILY: 'Stylus BT','sans-serif'; COLOR: #2d4d5e"><o:p> </o:p></SPAN></B></P>
<P class=MsoNormal><B><SPAN 
style="FONT-FAMILY: 'Stylus BT','sans-serif'; COLOR: #2d4d5e; FONT-SIZE: 12pt">NICK 
CATON, P.E.</SPAN></B><B><SPAN 
style="FONT-FAMILY: 'Stylus BT','sans-serif'; COLOR: #2d4d5e; FONT-SIZE: 12pt"><o:p></o:p></SPAN></B></P>
<P class=MsoNormal><SPAN style="COLOR: #cc9900; FONT-SIZE: 7.5pt">SENIOR 
ENGINEER<o:p></o:p></SPAN></P>
<P class=MsoNormal><SPAN 
style="COLOR: #cc9900; FONT-SIZE: 7.5pt"><o:p> </o:p></SPAN></P>
<P class=MsoNormal><SPAN style="COLOR: #2d4d5e; FONT-SIZE: 10pt">Smith & 
Boucher Engineers</SPAN><SPAN 
style="FONT-FAMILY: 'Times New Roman','serif'; COLOR: #cc9900; FONT-SIZE: 7.5pt"><o:p></o:p></SPAN></P>
<P class=MsoNormal><SPAN style="COLOR: #2d4d5e; FONT-SIZE: 10pt">25501 west 
valley parkway, suite 200<o:p></o:p></SPAN></P>
<P class=MsoNormal><SPAN style="COLOR: #2d4d5e; FONT-SIZE: 10pt">olathe, ks 
66061<o:p></o:p></SPAN></P>
<P class=MsoNormal><SPAN style="COLOR: #2d4d5e; FONT-SIZE: 10pt">direct 
913.344.0036<o:p></o:p></SPAN></P>
<P class=MsoNormal><SPAN style="COLOR: #2d4d5e; FONT-SIZE: 10pt">fax 
913.345.0617<o:p></o:p></SPAN></P>
<P class=MsoNormal><SPAN style="COLOR: #1f497d"><A 
title=blocked::www.smithboucher.com href="www.smithboucher.com"><SPAN 
style="COLOR: blue; FONT-SIZE: 10pt">www.smithboucher.com</SPAN></A></SPAN><U><SPAN 
style="COLOR: blue; FONT-SIZE: 10pt"> </SPAN></U><o:p></o:p></P>
<P class=MsoPlainText><o:p> </o:p></P>
<P class=MsoPlainText>-----Original Message-----<BR>From: James Hansen 
[mailto:JHANSEN@ghtltd.com] <BR>Sent: Wednesday, July 20, 2011 8:40 AM<BR>To: 
Eurek, John S NWO; Nick Caton; bldg-sim@lists.onebuilding.org<BR>Subject: RE: 
[Bldg-sim] How have you approached... (UNCLASSIFIED)<o:p></o:p></P>
<P class=MsoPlainText><o:p> </o:p></P>
<P class=MsoPlainText>I agree with John, I've done this on a model before and 
its painful.  Assuming there are 10 hours in a work day, I set up 10 
different occupancy and lighting schedules, each schedule being essentially 
identical except for a different hour of zero occupancy / lighting.  I then 
applied these 10 schedules to the different office zones on a floor so that 
specific areas were vacant from 8am-9am, some vacant from 9am-10am, etc.  
And then for my system, I assumed relatively consistent 10% non-occupied 
conditions and reduced the OA at the system level accordingly.  If your 
non-occupied conditions are more drastic (30%), obviously you can set up your 
schedules differently.<o:p></o:p></P>
<P class=MsoPlainText><o:p> </o:p></P>
<P class=MsoPlainText>However, if your primary air is also cooling (and not some 
sort of DOAS chilled water VAV box), then you are going to also have to specify 
10 separate thermostat schedules (really 20 with heating and cooling) so that 
the rooms do not have unmet load hours.  I'm assuming you go into setback 
mode when the offices are unoccupied.<o:p></o:p></P>
<P class=MsoPlainText><o:p> </o:p></P>
<P class=MsoPlainText>However, this was under v2.0, so that was a long time ago 
and reviewers were not as critical in their reviews.<o:p></o:p></P>
<P class=MsoPlainText><o:p> </o:p></P>
<P class=MsoPlainText>GHT Limited<o:p></o:p></P>
<P class=MsoPlainText>James Hansen, P.E., LEED AP<o:p></o:p></P>
<P class=MsoPlainText>Senior Associate<o:p></o:p></P>
<P class=MsoPlainText>1010 N. Glebe Road, Suite 200<o:p></o:p></P>
<P class=MsoPlainText>Arlington, VA  22201-4749<o:p></o:p></P>
<P class=MsoPlainText>703-243-1200 (office)<o:p></o:p></P>
<P class=MsoPlainText>703-338-5754 (cell)<o:p></o:p></P>
<P class=MsoPlainText>703-276-1376 (fax)<o:p></o:p></P>
<P class=MsoPlainText>www.ghtltd.com<o:p></o:p></P>
<P class=MsoPlainText><o:p> </o:p></P>
<P class=MsoPlainText>-----Original Message-----<o:p></o:p></P>
<P class=MsoPlainText>From: bldg-sim-bounces@lists.onebuilding.org 
[mailto:bldg-sim-bounces@lists.onebuilding.org] On Behalf Of Eurek, John S 
NWO<o:p></o:p></P>
<P class=MsoPlainText>Sent: Wednesday, July 20, 2011 9:31 AM<o:p></o:p></P>
<P class=MsoPlainText>To: Nick Caton; 
bldg-sim@lists.onebuilding.org<o:p></o:p></P>
<P class=MsoPlainText>Subject: Re: [Bldg-sim] How have you approached... 
(UNCLASSIFIED)<o:p></o:p></P>
<P class=MsoPlainText><o:p> </o:p></P>
<P class=MsoPlainText>Classification: UNCLASSIFIED<o:p></o:p></P>
<P class=MsoPlainText>Caveats: NONE<o:p></o:p></P>
<P class=MsoPlainText><o:p> </o:p></P>
<P class=MsoPlainText>Nick,<o:p></o:p></P>
<P class=MsoPlainText><o:p> </o:p></P>
<P class=MsoPlainText>I would do it with schedules.  This would be the long 
method.<o:p></o:p></P>
<P class=MsoPlainText><o:p> </o:p></P>
<P class=MsoPlainText>I have the same controls and have not got around to model 
it.  I would also<o:p></o:p></P>
<P class=MsoPlainText>make many schedules.  A different schedule for 
occupancy, lights, equipment,<o:p></o:p></P>
<P class=MsoPlainText>ect.  Also if this applies to a lot of rooms, you'd 
likely make multiple<o:p></o:p></P>
<P class=MsoPlainText>schedules, one assuming that the room is empty from 9~10 
another room empty<o:p></o:p></P>
<P class=MsoPlainText>from 2~3.  (The inverse for meeting rooms, if you 
have multiple meeting<o:p></o:p></P>
<P class=MsoPlainText>rooms, not all meetings will happen at the same 
time.)<o:p></o:p></P>
<P class=MsoPlainText><o:p> </o:p></P>
<P class=MsoPlainText><o:p> </o:p></P>
<P class=MsoPlainText>"Is Freedom a small price to pay to stop Global 
Warming?"<o:p></o:p></P>
<P class=MsoPlainText><o:p> </o:p></P>
<P class=MsoPlainText>John Eurek PE, LEED AP<o:p></o:p></P>
<P class=MsoPlainText>Mechanical Engineer,<o:p></o:p></P>
<P class=MsoPlainText><o:p> </o:p></P>
<P class=MsoPlainText>-----Original Message-----<o:p></o:p></P>
<P class=MsoPlainText>From: 
bldg-sim-bounces@lists.onebuilding.org<o:p></o:p></P>
<P class=MsoPlainText>[mailto:bldg-sim-bounces@lists.onebuilding.org] On Behalf 
Of Nick Caton<o:p></o:p></P>
<P class=MsoPlainText>Sent: Tuesday, July 19, 2011 3:59 PM<o:p></o:p></P>
<P class=MsoPlainText>To: bldg-sim@lists.onebuilding.org<o:p></o:p></P>
<P class=MsoPlainText>Subject: [Bldg-sim] How have you 
approached...<o:p></o:p></P>
<P class=MsoPlainText><o:p> </o:p></P>
<P class=MsoPlainText>I have a precedent question for everyone... this is not a 
"how to" procedural<o:p></o:p></P>
<P class=MsoPlainText>question for any particular software, but to simply feel 
out what has worked<o:p></o:p></P>
<P class=MsoPlainText>for others in the past:<o:p></o:p></P>
<P class=MsoPlainText><o:p> </o:p></P>
<P class=MsoPlainText> <o:p></o:p></P>
<P class=MsoPlainText><o:p> </o:p></P>
<P class=MsoPlainText>Here's a quick description of the situation at-hand:  
a VAV terminal unit<o:p></o:p></P>
<P class=MsoPlainText>with a "normal" minimum damper position (say, 30%) is tied 
by relay to the<o:p></o:p></P>
<P class=MsoPlainText>space occupancy sensor, which also controls the 
lights.  Upon sensing space<o:p></o:p></P>
<P class=MsoPlainText>vacancy, the minimum airflow damper position is reset to 
0% (airflow is<o:p></o:p></P>
<P class=MsoPlainText>permitted to stop, provided thermostat temperature set 
point is satisfied).<o:p></o:p></P>
<P class=MsoPlainText>Upon sensing occupancy, the preset minimum damper position 
is restored.<o:p></o:p></P>
<P class=MsoPlainText><o:p> </o:p></P>
<P class=MsoPlainText> <o:p></o:p></P>
<P class=MsoPlainText><o:p> </o:p></P>
<P class=MsoPlainText>For LEED/USGBC-reviewed energy models, can anyone relate 
success in modeling<o:p></o:p></P>
<P class=MsoPlainText>this or a similar energy-saving behavior in the proposed 
model, distinct from<o:p></o:p></P>
<P class=MsoPlainText>the baseline?  If so, what approach did you use to 
model this behavior and/or<o:p></o:p></P>
<P class=MsoPlainText>quantify the energy savings? <o:p></o:p></P>
<P class=MsoPlainText><o:p> </o:p></P>
<P class=MsoPlainText> <o:p></o:p></P>
<P class=MsoPlainText><o:p> </o:p></P>
<P class=MsoPlainText>I was discussing the possibilities with some colleagues 
and have a few ideas<o:p></o:p></P>
<P class=MsoPlainText>for approaches that might all be justifiable, ranging from 
simple (and quick)<o:p></o:p></P>
<P class=MsoPlainText>to complex (and time-consuming).  <o:p></o:p></P>
<P class=MsoPlainText><o:p> </o:p></P>
<P class=MsoPlainText> <o:p></o:p></P>
<P class=MsoPlainText><o:p> </o:p></P>
<P class=MsoPlainText>There are likely multiple "right" answers here, but I am 
hoping to identify<o:p></o:p></P>
<P class=MsoPlainText>some precedent to understand what we can anticipate the 
LEED reviewership<o:p></o:p></P>
<P class=MsoPlainText>will accept.  <o:p></o:p></P>
<P class=MsoPlainText><o:p> </o:p></P>
<P class=MsoPlainText> <o:p></o:p></P>
<P class=MsoPlainText><o:p> </o:p></P>
<P class=MsoPlainText>Thanks in advance!<o:p></o:p></P>
<P class=MsoPlainText><o:p> </o:p></P>
<P class=MsoPlainText> <o:p></o:p></P>
<P class=MsoPlainText><o:p> </o:p></P>
<P class=MsoPlainText>~Nick<o:p></o:p></P>
<P class=MsoPlainText><o:p> </o:p></P>
<P class=MsoPlainText> <o:p></o:p></P>
<P class=MsoPlainText><o:p> </o:p></P>
<P class=MsoPlainText>cid:489575314@22072009-0ABB<o:p></o:p></P>
<P class=MsoPlainText><o:p> </o:p></P>
<P class=MsoPlainText> <o:p></o:p></P>
<P class=MsoPlainText><o:p> </o:p></P>
<P class=MsoPlainText>NICK CATON, P.E.<o:p></o:p></P>
<P class=MsoPlainText><o:p> </o:p></P>
<P class=MsoPlainText>SENIOR ENGINEER<o:p></o:p></P>
<P class=MsoPlainText><o:p> </o:p></P>
<P class=MsoPlainText> <o:p></o:p></P>
<P class=MsoPlainText><o:p> </o:p></P>
<P class=MsoPlainText>Smith & Boucher Engineers<o:p></o:p></P>
<P class=MsoPlainText><o:p> </o:p></P>
<P class=MsoPlainText>25501 west valley parkway, suite 200<o:p></o:p></P>
<P class=MsoPlainText><o:p> </o:p></P>
<P class=MsoPlainText>olathe, ks 66061<o:p></o:p></P>
<P class=MsoPlainText><o:p> </o:p></P>
<P class=MsoPlainText>direct 913.344.0036<o:p></o:p></P>
<P class=MsoPlainText><o:p> </o:p></P>
<P class=MsoPlainText>fax 913.345.0617<o:p></o:p></P>
<P class=MsoPlainText><o:p> </o:p></P>
<P class=MsoPlainText>www.smithboucher.com <o:p></o:p></P>
<P class=MsoPlainText><o:p> </o:p></P>
<P class=MsoPlainText> <o:p></o:p></P>
<P class=MsoPlainText><o:p> </o:p></P>
<P class=MsoPlainText><o:p> </o:p></P>
<P class=MsoPlainText>Classification: UNCLASSIFIED<o:p></o:p></P>
<P class=MsoPlainText>Caveats: NONE<o:p></o:p></P>
<P class=MsoPlainText><o:p> </o:p></P>
<P class=MsoPlainText><o:p> </o:p></P>
<P 
class=MsoPlainText>_______________________________________________<o:p></o:p></P>
<P class=MsoPlainText>Bldg-sim mailing list<o:p></o:p></P>
<P 
class=MsoPlainText>http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org<o:p></o:p></P>
<P class=MsoPlainText>To unsubscribe from this mailing list send  a blank 
message to BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG<o:p></o:p></P>
<P class=MsoPlainText><o:p> </o:p></P>
<P class=MsoPlainText><o:p> </o:p></P>
<P class=MsoPlainText>The information contained in this communication is 
confidential, may be privileged, and is intended only for the use of the 
addressee.  It is the property of GHT Limited.  Unauthorized use, 
disclosure or copying of this communication or any part thereof is strictly 
prohibited and may be unlawful.  If you have received this communication in 
error, please notify me immediately by return e-mail or by e-mail to 
ght@ghtltd.com, and destroy this communication and all copies thereof, including 
all attachments.  Thank you.<o:p></o:p></P>
<P class=MsoPlainText><o:p> </o:p></P>
<P class=MsoPlainText><o:p> </o:p></P>
<P class=MsoPlainText><o:p> </o:p></P>
<P class=MsoNormal><o:p> </o:p></P></DIV></BODY></HTML>