Hi Chris,<br><br>If you want to get your project done in time and within the budget I would highly recommend Scenario 1. I think that Scenario 2 is a result of not thinking the zoning through before doing the take-offs from CAD drawings. <br>
<br>When I start a model I spend a few hours at least looking at what's going on in the building: what are the mechanical zones, wall constructions, roof constructions, floor plans - where do you have an exposed roof due to the floor above having a smaller foot print, do the floor to floor heights vary, etc., etc. If you don't do this you can really create a nightmare for later.<br>
<br>Cheers,<br><br>Carol<br><br><div class="gmail_quote">On Wed, Jun 22, 2011 at 10:47 AM, Chris Jones <span dir="ltr"><<a href="mailto:cj@enersave.ca">cj@enersave.ca</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex;">
I am wondering how the typical equest model is zoned. Two scenarios:<br>
<br>
1. Create a zoning diagram combining like spaces on perimeters and like spaces in interiors based on the HVAC type and distribution. Combine storage rooms with exhaust only with adjacent space where the transfer air comes from, etc. Plunk this zoning diagram into equest.<br>
<br>
2. Plunk the architectural drawing into equest and every space becomes an equest space - every closet, elevator/duct shaft, office, small interior meeting room, janitor closets - all a space in equest.<br>
<br>
I had always assumed that the scenario 1 would be used. I am now finding (by way of reviewing LEED submissions) that many people use scenario 2. It seems very inefficient to me and certainly increases the cost of doing a review.<br>
<br>
What is typical?<br>
<br>
<br>
<br>
Chris Jones<br>
14 Oneida Avenue<br>
Toronto, ON M5J 2E3.<br>
Tel. <a href="tel:416-203-7465" value="+14162037465" target="_blank">416-203-7465</a><br>
Fax. <a href="tel:416-946-1005" value="+14169461005" target="_blank">416-946-1005</a><br>
<br>
<br>
______________________________<u></u>_________________<br>
Bldg-sim mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" target="_blank">http://lists.onebuilding.org/<u></u>listinfo.cgi/bldg-sim-<u></u>onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">BLDG-SIM-UNSUBSCRIBE@<u></u>ONEBUILDING.ORG</a><br>
</blockquote></div><br><br clear="all"><br>-- <br>Carol Gardner PE<br>