I just need a clarification, and rather wait for a response from LEED, i figured i'd ask you guys. I looked through the archives and couldn't find anything that adressed this issue. <div><br></div><div><div>In the most recent version of the LEED Online template, i have entered in my unmet hours as follows:</div>
<div><br></div><div> proposed baseline</div><div>unmet heating 8 91</div><div>unmet cooling 120 1</div>
<div><br></div><div>Now, if you sum them up and take the difference you get 128-92 = 36 which is a pass in my book. However the LEED Online template is saying that it isn't a pass because:</div><div>91-8 = 83 (Fail)</div>
<div>120-1 = 119 (Fail)</div><div><br></div><div>so what i then did was enter in numbers as follows:</div><div><br></div><div><div> proposed baseline</div><div>unmet heating 299 250</div>
<div>unmet cooling 299 250</div></div><div><br></div><div>This should not be allowed to pass because proposed = 598 and baseline = 500 unmet hours, even the difference is 98 ours, which fails, but the LEED Online passes this scenario.</div>
<div><br></div><div>Any thoughts or has anyone dealt with this recently?</div><div>-- <br>Rob Hudson<br>
</div></div>