yep.  been around for years.  i've had this problem with leed
reviewer's interpreting it this way all the way back to leed 2.1 even
though 90.1 is quite clear it is the building design, not heating
design separate from cooling design.<br>
<br>
approach from amit seems best.  does the "contact review team" show up
somewhere in your leed 3 options?  it might be best to address the
matter by quoting chapter & verse from 90.1 app g as you should get
a response faster than from the main usgbc/gbci contact form.<br>
<br>
On 6/10/11 7:58 AM, amit bhansali wrote:
<blockquote
 cite="mid:BANLkTi=rq+=bPnG9cSY6cgr62w-ZJdb6Kg@mail.gmail.com"
 type="cite">
  <div>Hi Rob,</div>
  <div>I have had the same problem before for one of our projects. I
have taken the screenshot of section 1.3 in template and submitted it
with a narrative to GBCI explaining whats wrong with the results
produced. It seems that there is some mistake in their program behind
that form. I would suggest you to try the same.<br>
  </div>
  <div class="gmail_quote">On 10 June 2011 09:32, Rob Hudson <span
 dir="ltr"><<a moz-do-not-send="true" href="mailto:rdh4176@gmail.com">rdh4176@gmail.com</a>></span>
wrote:<br>
  <blockquote
 style="border-left: 1px solid rgb(204, 204, 204); margin: 0px 0px 0px 0.8ex; padding-left: 1ex;"
 class="gmail_quote">I just need a clarification, and rather wait for a
response from LEED, i figured i'd ask you guys.  I looked through the
archives and couldn't find anything that adressed this issue.  
    <div><br>
    </div>
    <div>
    <div>In the most recent version of the LEED Online template, i have
entered in my unmet hours as follows:</div>
    <div><br>
    </div>
    <div>                                 proposed            baseline</div>
    <div>unmet heating                 8                         91</div>
    <div>unmet cooling                 120                       1</div>
    <div><br>
    </div>
    <div>Now, if you sum them up and take the difference you get 128-92
= 36 which is a pass in my book.  However the LEED Online template is
saying that it isn't a pass because:</div>
    <div>91-8 = 83 (Fail)</div>
    <div>120-1 = 119 (Fail)</div>
    <div><br>
    </div>
    <div>so what i then did was enter in numbers as follows:</div>
    <div><br>
    </div>
    <div>
    <div>                                 proposed            baseline</div>
    <div>unmet heating                 299                     250</div>
    <div>unmet cooling                 299                     250</div>
    </div>
    <div><br>
    </div>
    <div>This should not be allowed to pass because proposed = 598 and
baseline = 500 unmet hours, even the difference is 98 ours, which
fails, but the LEED Online passes this scenario.</div>
    <div><br>
    </div>
    <div>Any thoughts or has anyone dealt with this recently?</div>
    <div>-- <br>
Rob Hudson<br>
    </div>
    </div>
    <br>
_______________________________________________<br>
Bldg-sim mailing list<br>
    <a moz-do-not-send="true"
 href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org"
 target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a
 moz-do-not-send="true"
 href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
    <br>
  </blockquote>
  </div>
  <br>
  <br clear="all">
  <br>
-- <br>
Thanks<br>
  <br>
Sincerely,<br>
Amit Bhansali, LEED Green Associate, M.S. , EIT<br>
Command Commissioning, LLC<br>
8410, Sterling St<br>
Irving, TX  75063 <br>
  <br>
Office :(972)-929-1199 (Ext:328)<br>
 Mobile: (+1)972-207-5180<br>
             (+1)405-312-1047<br>
  <br>
  <a moz-do-not-send="true" href="http://www.command-cx.com/"
 target="_blank">www.command-cx.com</a><br>
  <a moz-do-not-send="true" href="http://www.godparents.in/"
 target="_blank">www.godparents.in</a><br>
Please do not print this e-mail unless necessary<br>
  <pre wrap="">
<fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
Bldg-sim mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a>
  </pre>
</blockquote>
<br>
</body>
</html>