Hi Alex, <br><br>
You can not modify reference case in EE4 but you can modify it in
DOE.<br>
Reference case is based on MNECB and to have a electric heat in the
reference case, the propose building have to use electricity more than
50% for heating. <br><br>
Martin<br><br>
<br><br>
At 11:16 30/05/2011, Alex Blue wrote:<br>
<blockquote type=cite class=cite cite="">Content-Language: en-US<br>
Content-Type: multipart/alternative;<br>
<x-tab> </x-tab>
boundary="_000_DDC6CEED88CBED46868D11CF3A96EC8223FFBD7FVA3DIAXVS1C1RED_"<br>
<br>
I am using EE4 to model an office building with natural gas RTU’s but
electric reheats at the zone level. The reference building is
only using natural gas for heating, rather than gas + electricity as in
the proposed design. I’m getting very nice energy savings overall,
but since my electricity use for the proposed case is actually higher
than that of the reference, the cost has not gone down much at all
(electricity is a lot more expensive here than natural gas.)<br>
<br>
Is there any way to get EE4 to model the electric zone reheat capacity in
its reference case? <br>
<br>
I have the RTU’s defined with electric zone reheat coils. <br>
<br>
Thanks!<br>
<br>
Alex Blue, EIT<br>
<br>
<br>
P.S. I’m new to the list, so hi! Nice to meet you all.<br>
_______________________________________________<br>
Bldg-sim mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" eudora="autourl">
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</blockquote>
<x-sigsep><p></x-sigsep>
<hr>
<br>
Martin Roy, ing. PA LEED®, président<br>
Martin Roy et associés<br>
1805 chemin Oka, <br>
Deux-Montagnes, Qc<br>
J7R 1N3<br><br>
<br>
Tel: 450-623-0340<br>
Cell. 514-594-6352<br><br>
<a href="http://www.mra.qc.ca/" eudora="autourl">www.mra.qc.ca<br><br>
<br><br>
<br><br>
<br>
</a><b>Message de confidentialité <br>
</b>Ce courriel (de même que les fichiers joints) est strictement réservé
à l'usage de la personne ou de l'entité à qui il est adressé et peut
contenir de l'information privilégiée et confidentielle. Toute
divulgation, distribution ou copie de ce courriel est strictement
prohibée et peut être l’objet de poursuites judiciaires. Si vous avez
reçu ce courriel par erreur, veuillez nous en aviser et le
supprimer de votre système informatique sans l'imprimer, le copier ou le
faire suivre a quiconque. <br><br>
<b>Devez-vous vraiment imprimer ce courriel ? Pensons
environnement...<br>
</b></body>
</html>