Hi Kurt, <br><br>
We model a refrigerated warehouse using ESPr and TRNSYS.  We did not
try Energy+.<br>
The main reason was to evaluate the effect of the thermal mass stored
against the incoming product that was warmer.<br>
when we compare our result to those of the refrigeration contractor there
was a big difference.  Half of their calculated load<br>
And compare to actual energy consumption, it was close.<br><br>
So if you use energy+ be shure to include thermal mass.<br><br>
Martin<br>
 <br><br>
<br>
At 15:00 26/05/2011, Jeff Haberl wrote:<br>
<blockquote type=cite class=cite cite="">Kurt,<br><br>
We had this problem before in the mid-80s simulating an ice rink at a Rec
Center. This was published in an ASHRAE Transactions paper. We basically
got around the issue by fudging the "U x A x Delta-T"...in this
case fiddling with either the U or the A to adjust for the Delta-T.
Results worked well against metered data.<br><br>
Jeff<br><br>
8=!  8=)  :=)  8=)  ;=)  8=)  8=( 
8=)  8=()  8=)  8=|  8=)  :=') 
8=)8=?<br><br>
Jeff S. Haberl, Ph.D.,P.E.,
FASHRAE..............jhaberl@tamu.edu<br><br>
Professor............................................................Office
Ph: 979-845-6507<br><br>
Department of Architecture.............................Lab
Ph:979-845-6065<br><br>
Energy Systems Laboratory.............................FAX:
979-862-2457<br><br>
Texas A&M
University.....................................77843-3581<br><br>
College Station, Texas, USA,
77843..................URL:<a href="http://www.esl.tamu.edu/" eudora="autourl">
www.esl.tamu.edu</a><br><br>
8=/  8=)  :=)  8=)  ;=)  8=)  8=() 
8=)  :=)  8=)  8=!  8=)  8=? 8=)8=0<br>
________________________________________<br>
From: bldg-sim-bounces@lists.onebuilding.org
[bldg-sim-bounces@lists.onebuilding.org] on behalf of kcreamer@nc.rr.com
[kcreamer@nc.rr.com]<br>
Sent: Monday, May 23, 2011 9:19 PM<br>
To: bldg-sim@lists.onebuilding.org<br>
Subject: [Bldg-sim] Walk-in Coolers/Freezers<br><br>
Hi all,<br><br>
Is it possible to use EnergyPlus to model a walk-in cooler or
freezer?  I have tried but regardless of the temperature setpoint I
choose for the freezer, the modeled temperature does not want to drop
below about 42 F.<br><br>
Also, has anyone made a model of a cooler that accurately estimates
electricity loads?  I was able to model a cooler with a 45 F
setpoint but I was way under the electricity consumption estimates I
found for coolers/freezers on the web.  I think my problem was the
large amount of electrical usage for non-compressor loads ­ defrost
cycle, evaporator fan, condenser fan, etc.<br><br>
Kurt Creamer<br>
Apex, NC<br><br>
_______________________________________________<br>
Bldg-sim mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" eudora="autourl">
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to
BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG<br>
_______________________________________________<br>
Bldg-sim mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" eudora="autourl">
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to
BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</blockquote>
<x-sigsep><p></x-sigsep>
<hr>
<br>
Martin Roy, ing. PA LEED®, président<br>
Martin Roy et associés<br>
1805 chemin Oka, <br>
Deux-Montagnes, Qc<br>
J7R 1N3<br><br>
<br>
Tel: 450-623-0340<br>
Cell. 514-594-6352<br><br>
<a href="http://www.mra.qc.ca/" eudora="autourl">www.mra.qc.ca<br><br>
<br><br>
<br><br>
<br>
</a><b>Message de confidentialité <br>
</b>Ce courriel (de même que les fichiers joints) est strictement réservé
à l'usage de la personne ou de l'entité à qui il est adressé et peut
contenir de l'information privilégiée et confidentielle. Toute
divulgation, distribution ou copie de ce courriel est strictement
prohibée et peut être l’objet de poursuites judiciaires. Si vous avez
reçu ce courriel par erreur, veuillez nous en aviser  et le
supprimer de votre système informatique sans l'imprimer, le copier ou le
faire suivre a quiconque. <br><br>
<b>Devez-vous vraiment imprimer ce courriel ?  Pensons
environnement...<br>
</b></body>
</html>