<html><body bgcolor="#FFFFFF"><div><div>Marcus, thank you incorporating this language.</div><div><br></div><div>The one scenario we often see in our design guidance work is that a proposed design when compared with other design alternates does not necessarily provided the largest energy savings when compared against its own baseline case model. It is difficult to make a recommendation as consultants when we want to present the Owner with both real energy cost savings without compromising their LEED certification level targets.  <br><br></div><div>A recent paper presented by the Weidt Group at SimBuild touched on this issue:</div><div><br></div><div><a href="http://www.ibpsa.us/pub/simbuild2010/technicalPresentations/SB10-PPT-TS02A-03-Baker.pdf">http://www.ibpsa.us/pub/simbuild2010/technicalPresentations/SB10-PPT-TS02A-03-Baker.pdf</a></div><div><br></div><div><br><div><span class="Apple-style-span" style="-webkit-tap-highlight-color: rgba(26, 26, 26, 0.285156); -webkit-composition-fill-color: rgba(175, 192, 227, 0.21875); -webkit-composition-frame-color: rgba(77, 128, 180, 0.21875);"><br></span></div><div><span class="Apple-style-span" style="-webkit-tap-highlight-color: rgba(26, 26, 26, 0.296875); -webkit-composition-fill-color: rgba(175, 192, 227, 0.230469); -webkit-composition-frame-color: rgba(77, 128, 180, 0.230469); "><span class="Apple-style-span" style="-webkit-tap-highlight-color: rgba(26, 26, 26, 0.289062); -webkit-composition-fill-color: rgba(175, 192, 227, 0.222656); -webkit-composition-frame-color: rgba(77, 128, 180, 0.222656); ">Arpan Bakshi, LEED AP BD+C</span></span></div><div><span class="Apple-style-span" style="-webkit-tap-highlight-color: rgba(26, 26, 26, 0.285156); -webkit-composition-fill-color: rgba(175, 192, 227, 0.21875); -webkit-composition-frame-color: rgba(77, 128, 180, 0.21875);">YRG sustainability</span></div></div><div><br>On May 13, 2011, at 8:16 AM, "Marcus Sheffer" <<a href="mailto:sheffer@energyopportunities.com"><a href="mailto:sheffer@energyopportunities.com">sheffer@energyopportunities.com</a></a>> wrote:<br><br></div><div><span></span></div><blockquote type="cite"><div>

<div class="Section1">

<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";
color:#1F497D">If anyone has any good ideas about how to structure the LEED
credits to end the practice of validation models at the end and encourage/require
design phase modeling the folks on the USGBC EA TAG would love to hear them. 
The current proposed credit language from the first public comment phase is
listed below.<o:p></o:p></span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";
color:#1F497D"><o:p> </o:p></span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";
color:#76923C">NC, CS, SCHOOLS, RETAIL, WAREHOUSE & DISTRIBUTION CENTERS,
HOSPITALITY<o:p></o:p></span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";
color:#76923C">Establish an energy performance target no later than the
schematic design phase. The target must be established as kBTU per square
foot-year of source energy use. This target must be mapped on the same scale as
the baseline and proposed buildings, if the project follows Option 1.<o:p></o:p></span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";
color:#76923C"><o:p> </o:p></span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";
color:#76923C">OPTION 1. Whole Building Energy Simulation <o:p></o:p></span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";
color:#76923C">Analyze a minimum of at least nine efficiency measures during
the design process and account for the results in design decision-making.
Analysis can include energy simulation of efficiency opportunities, application
of past energy simulation analyses for similar projects to the project, or
application of published data from energy analyses performed for similar projects
to the project (such as AEDGs).<o:p></o:p></span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";
color:#76923C"><o:p> </o:p></span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";
color:#76923C">A minimum of six energy efficiency measures focused on load
reduction strategies appropriate for the facility must be analyzed. This
analysis must be performed during the schematic design phase.<o:p></o:p></span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";
color:#76923C"><o:p> </o:p></span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";
color:#76923C">A minimum of three energy efficiency measures focused on HVAC
related strategies must be analyzed (passive measures are acceptable). This
analysis must be performed before the conclusion of the design development
phase.<o:p></o:p></span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";
color:#76923C"><o:p> </o:p></span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";
color:#76923C">The results of the analysis must be summarized in a brief report
or memorandum.<o:p></o:p></span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";
color:#1F497D"><o:p> </o:p></span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";
color:#1F497D"><o:p> </o:p></span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";
color:#1F497D">The next version of LEED will be going out for public comment again
in July, I think, so please comment formally as well as discussing here.<o:p></o:p></span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";
color:#1F497D"><o:p> </o:p></span></p>

<div>

<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Arial","sans-serif";
color:green">Marcus Sheffer</span><span style="color:#1F497D"><o:p></o:p></span></p>

<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Arial","sans-serif";
color:green">Energy Opportunities, Inc/a 7group Company</span><span style="color:#1F497D"><o:p></o:p></span></p>

<p class="MsoNormal"><span style="font-size:7.5pt;font-family:"Arial","sans-serif";
color:#1F497D">1200 E Camping Area Road, Wellsville, PA  17365</span><span style="color:#1F497D"><o:p></o:p></span></p>

<p class="MsoNormal"><span style="font-size:7.5pt;font-family:"Arial","sans-serif";
color:#1F497D">717-292-2636, </span><span style="color:#1F497D"><a href="mailto:sheffer@sevengroup.com"><span style="font-size:7.5pt;font-family:
"Arial","sans-serif"">sheffer@sevengroup.com</span></a><o:p></o:p></span></p>

<p class="MsoNormal"><span style="font-size:7.5pt;font-family:"Arial","sans-serif";
color:#1F497D"><a href="http://www.sevengroup.com"></a><a href="http://www.sevengroup.com"><a href="http://www.sevengroup.com">www.sevengroup.com</a></a></span><span style="color:#1F497D"><o:p></o:p></span></p>

</div>

<p class="MsoNormal"><span style="color:#1F497D"> </span><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p></o:p></span></p>

<div>

<div style="border:none;border-top:solid #B5C4DF 1.0pt;padding:3.0pt 0in 0in 0in">

<p class="MsoNormal"><b><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif"">From:</span></b><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif""> John Aulbach
[mailto:jra_sac@yahoo.com] <br>
<b>Sent:</b> Thursday, May 12, 2011 7:46 PM<br>
<b>To:</b> Carol Gardner; Marcus Sheffer<br>
<b>Cc:</b> <a href="mailto:bldg-sim@lists.onebuilding.org"></a><a href="mailto:bldg-sim@lists.onebuilding.org"><a href="mailto:bldg-sim@lists.onebuilding.org">bldg-sim@lists.onebuilding.org</a></a><br>
<b>Subject:</b> Re: [Bldg-sim] Energy Model Cost<o:p></o:p></span></p>

</div>

</div>

<p class="MsoNormal"><o:p> </o:p></p>

<div>

<div>

<p class="MsoNormal">OK, Carol..now you threw the "bait" out
there..older than dirt, eh?<o:p></o:p></p>

</div>

<div>

<p class="MsoNormal"> <o:p></o:p></p>

</div>

<div>

<p class="MsoNormal">I have done very limited LEED "type" modeling
where you compare 20 walls and 40 windows types (well, it seemed that
way). Correct me if I am wrong, but a Base model must be built to comply
with a certain level of ASHRAE 90.1 (now up to 2010 ??). With all of the
nuisances of eQuest 3.64, I am going to build the model from scrathc and put in
all the relevant baseline data in by hand.  And, by the way, the ASHRAE
baseline model might be an entirely different system.  I am just
completing an EPACT evaluation (ASHRAE 90.1-2001) and the Baseline HVAC was
screwe chillers, whereas the Actual building was packaged units with Turbocor compressors
(ask me how I did that).<o:p></o:p></p>

</div>

<div>

<p class="MsoNormal"> <o:p></o:p></p>

</div>

<div>

<p class="MsoNormal">It very much depends on the complexity of the building. A
40,000 sf office or a 500,000 sf hotel with casino facilites.<o:p></o:p></p>

</div>

<div>

<p class="MsoNormal"> <o:p></o:p></p>

</div>

<div>

<p class="MsoNormal">I am unfamiliar with the LEED paperwork to be filled out
after the modeling has been done. But I would not do anything of this type in
under 120 hours, preferably 160 hours. If the client thinks he can do better,
let him.<o:p></o:p></p>

</div>

<div>

<p class="MsoNormal"> <o:p></o:p></p>

</div>

<div>

<p class="MsoNormal">Contingency, contingency.<o:p></o:p></p>

</div>

<div>

<p class="MsoNormal"> <o:p></o:p></p>

</div>

<div>

<p class="MsoNormal">We won't discuss how old CAROL might be..<o:p></o:p></p>

</div>

<div>

<p class="MsoNormal"> <o:p></o:p></p>

</div>

<div>

<p class="MsoNormal">John A.<o:p></o:p></p>

</div>

<div>

<p class="MsoNormal"><o:p> </o:p></p>

<div>

<div class="MsoNormal" align="center" style="text-align:center"><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif"">

<hr size="1" width="100%" align="center">

</span></div>

<p class="MsoNormal"><b><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif"">From:</span></b><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif""> Carol Gardner
<<a href="mailto:cmg750@gmail.com"><a href="mailto:cmg750@gmail.com">cmg750@gmail.com</a></a>><br>
<b>To:</b> <a href="mailto:sheffer@energyopportunities.com"></a><a href="mailto:sheffer@energyopportunities.com"><a href="mailto:sheffer@energyopportunities.com">sheffer@energyopportunities.com</a></a><br>
<b>Cc:</b> <a href="mailto:bldg-sim@lists.onebuilding.org"></a><a href="mailto:bldg-sim@lists.onebuilding.org"><a href="mailto:bldg-sim@lists.onebuilding.org">bldg-sim@lists.onebuilding.org</a></a><br>
<b>Sent:</b> Thu, May 12, 2011 2:59:12 PM<br>
<b>Subject:</b> Re: [Bldg-sim] Energy Model Cost<br>
</span><br>
Marcus,<br>
<br>
You have inadvertently hit upon why IBPSA worked with ASHRAE to create a BEMP
certification. That's Building Energy Modeling Professional (BEMP). <br>
<br>
Some of us who have been in the field for awhile began to worry a couple of
years ago when so many new energy modelers began appearing on the listserv with
questions. Their questions indicated a lack of training and experience that was
worrisome. What made it worrisome was that they didn't seem to realize that
they were as inexperienced as they were; they didn't appear to be pursuing
training to learn how to do what they were doing; and we were uncertain as to
how or if they were practicing quality control. We hoped that by creating a
path to certification that we would give clients one more qualification to look
for in their modelers.<br>
<br>
If you have been in this industry for any length of time, and by industry I
mean the overall construction industry, you know that you don't get a lot of
chances if your work doesn't pan out. If your energy model says I have a LEED
Gold building and I'm going to save $4,000/year and what I really get is LEED
Silver and $1,000/year, I am not going to be happy. So, I will probably not
give you any more work but, even worse for all of us, I'll start expressing
doubts about the whole process. LEED - what is it good for?<br>
<br>
So, now we all have more training, right? We read our ASHRAE Handbooks and
technical manuals so we know how to model the difficult stuff. We can find any
topic in the DOE2 Manuals, all of which are one line, available, and easily
searchable. <br>
<br>
So now we are so good we can do these models in 40-80 hours. Really? Not me and
I've been doing it longer than everyone, except you, John Aulbach. So I'm going
to join Marcus in his rant because he's on to something.<br>
<br>
It's up to us to not under bid this work. It's up to us to educate our clients
about the importance of quality in this process. If they think they are getting
the same analysis in 40 hours that they used to get in 120 hours, they need to
be led around to rethinking that and to be reminded that GIGO.<br>
<br>
Cheers,<br>
<br>
Carol<br>
<br>
<br>
Thu, May 12, 2011 at 2:31 PM, Marcus Sheffer <<a href="mailto:sheffer@energyopportunities.com" target="_blank"></a><a href="mailto:sheffer@energyopportunities.com"><a href="mailto:sheffer@energyopportunities.com">sheffer@energyopportunities.com</a></a>>
wrote:<o:p></o:p></p>

<div>

<blockquote style="border:none;border-left:solid #CCCCCC 1.0pt;padding:0in 0in 0in 6.0pt;
margin-left:4.8pt;margin-right:0in">

<div>

<div>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span style="color:#1F497D">In our experience a final model, done right, would take
about 80 hours.</span><o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span style="color:#1F497D"> </span><o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span style="color:#1F497D">WARNING – frustrated modeling rant to follow:</span><o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span style="color:#1F497D"> </span><o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span style="color:#1F497D">Doing just a final model however completely misses the
point as to why we model – it is to guide design decisions!  </span><o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span style="color:#1F497D"> </span><o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span style="color:#1F497D">If I saw this RFP and all it asked me for was a model to
determine LEED points, during or after design, I would try to educate the
potential client about the purpose of modeling.</span><o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span style="color:#1F497D"> </span><o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span style="color:#1F497D">Unfortunately too many projects pursuing LEED are only
doing the minimum when it comes to modeling and almost completely missing all
the benefits.  Too often the “market” transforms only based on a least
first cost denominator basis that results in little real transformation. 
Doing models to determine LEED points does not transform the market, save any
energy, and just circumvents the purpose behind LEED. (the next version
actually requires design phase modeling!)</span><o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span style="color:#1F497D"> </span><o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span style="color:#1F497D">Any “modeler” who does only final models without
attempting to explain to the owner why this is a bad idea should be “drummed
out of the corp” in my humble opinion.</span><o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span style="color:#1F497D"> </span><o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span style="color:#1F497D">The problem is that if you respond to this RFP with 120
or 160 or more hours to really do the design phase modeling right, you will go
up against the “modeler” who claims to be able to do it in far less time. 
So how do we get the folks who issue the RFPs to ask for a proper scope of work
so that they can compare fees on a level playing field?  It is unfortunate
that we are even having a discussion about doing modeling work in opposition to
its purpose.</span><o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span style="color:#1F497D"> </span><o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span style="color:#1F497D">Sorry for the rant but I feel better now. </span><span style="font-family:Wingdings;color:#1F497D">J</span><span style="color:#1F497D">
</span><o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span style="color:#1F497D"> </span><o:p></o:p></p>

<div>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span style="font-size:10.0pt;color:green">Marcus Sheffer</span><o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span style="font-size:10.0pt;color:green">Energy Opportunities, Inc/a 7group Company</span><o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span style="font-size:7.5pt;color:#1F497D">1200 E Camping Area Road, Wellsville,
PA  17365</span><o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span style="font-size:7.5pt;color:#1F497D">717-292-2636, </span><span style="color:#1F497D"><a href="mailto:sheffer@sevengroup.com" target="_blank"><span style="font-size:7.5pt">sheffer@sevengroup.com</span></a></span><o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span style="font-size:7.5pt;color:#1F497D"><a href="http://www.sevengroup.com/" target="_blank"></a><a href="http://www.sevengroup.com"><a href="http://www.sevengroup.com">www.sevengroup.com</a></a></span><o:p></o:p></p>

</div>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span style="color:#1F497D"> </span><o:p></o:p></p>

<div>

<div style="border:none;border-top:solid #B5C4DF 1.0pt;padding:3.0pt 0in 0in 0in">

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><b><span style="font-size:10.0pt">From:</span></b><span style="font-size:10.0pt"> <a href="mailto:bldg-sim-bounces@lists.onebuilding.org" target="_blank"></a><a href="mailto:bldg-sim-bounces@lists.onebuilding.org"><a href="mailto:bldg-sim-bounces@lists.onebuilding.org">bldg-sim-bounces@lists.onebuilding.org</a></a>
[mailto:<a href="mailto:bldg-sim-bounces@lists.onebuilding.org" target="_blank"></a><a href="mailto:bldg-sim-bounces@lists.onebuilding.org"><a href="mailto:bldg-sim-bounces@lists.onebuilding.org">bldg-sim-bounces@lists.onebuilding.org</a></a>]
<b>On Behalf Of </b>Demba Ndiaye<br>
<b>Sent:</b> Thursday, May 12, 2011 4:28 PM<br>
<b>To:</b> Omar Delgado; <a href="mailto:bldg-sim@lists.onebuilding.org" target="_blank"></a><a href="mailto:bldg-sim@lists.onebuilding.org"><a href="mailto:bldg-sim@lists.onebuilding.org">bldg-sim@lists.onebuilding.org</a></a><br>
<b>Subject:</b> Re: [Bldg-sim] Energy Model Cost</span><o:p></o:p></p>

</div>

</div>

<div>

<div>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"> <o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span style="color:#1F497D">Omar,</span><o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span style="color:#1F497D"> </span><o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span style="color:#1F497D">I would expect, for a building this size, approximately
40 hours (multiply by your hourly rate). The 40 hours include EAp2/EAc1 LEED
documentation, and any review you may have to respond to later.</span><o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span style="color:#1F497D"> </span><o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span style="color:#1F497D">Now, given that you have never done a LEED model, it will
take you more time, possibly up to 40 more hours.</span><o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span style="color:#1F497D"> </span><o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span style="color:#1F497D">HTH,</span><o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span style="color:#1F497D"> </span><o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span style="color:#1F497D">_______________</span><o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span style="color:#1F497D">Demba NDIAYE</span><o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span style="color:#1F497D"> </span><o:p></o:p></p>

<div>

<div style="border:none;border-top:solid #B5C4DF 1.0pt;padding:3.0pt 0in 0in 0in">

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><b><span style="font-size:10.0pt">From:</span></b><span style="font-size:10.0pt"> <a href="mailto:bldg-sim-bounces@lists.onebuilding.org" target="_blank"></a><a href="mailto:bldg-sim-bounces@lists.onebuilding.org"><a href="mailto:bldg-sim-bounces@lists.onebuilding.org">bldg-sim-bounces@lists.onebuilding.org</a></a>
[mailto:<a href="mailto:bldg-sim-bounces@lists.onebuilding.org" target="_blank"></a><a href="mailto:bldg-sim-bounces@lists.onebuilding.org"><a href="mailto:bldg-sim-bounces@lists.onebuilding.org">bldg-sim-bounces@lists.onebuilding.org</a></a>]
<b>On Behalf Of </b>Omar Delgado<br>
<b>Sent:</b> Thursday, May 12, 2011 7:08 PM<br>
<b>To:</b> <a href="mailto:bldg-sim@lists.onebuilding.org" target="_blank"></a><a href="mailto:bldg-sim@lists.onebuilding.org"><a href="mailto:bldg-sim@lists.onebuilding.org">bldg-sim@lists.onebuilding.org</a></a><br>
<b>Subject:</b> [Bldg-sim] Energy Model Cost</span><o:p></o:p></p>

</div>

</div>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"> <o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto">Greetings
everyone,<o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"> <o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto">I
have a question regarding the cost of an energy model for a LEED project. Every
energy model I've done so far has been for <o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto">existing
buildings, mainly for optimization purposes. However, I received an RFP to model
a five-story, 41,500 sq. ft. building<o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto">that's
currently on the design phase and is pursuing the LEED-NC Silver certification.
I really have no idea what would be a fair <o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto">price
for this model since I'm going to have to use Appendix G (ASHRAE 90.1) to
evaluate the difference between the base <o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto">and
proposed buildings. I don't know how much extra effort this will take. I know
the procedure, just haven't done it before.<o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"> <o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto">Can
you shed any light on this issue?<o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"> <o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto">Thanks
in advance!<o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"> <o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><i><span lang="ES-PR" style="font-size:10.0pt;font-family:Papyrus">Omar A. Delgado Colón,
P.E., MEnvM., LEED AP BD&C</span></i><o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><i><span style="font-size:10.0pt;font-family:Papyrus">Vice President</span></i><o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><b><span style="color:#FF8000">Ener</span>Mech</b><o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span style="font-size:10.0pt">PMB 340</span><o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span style="font-size:10.0pt">130 Winston Churchill Ave.</span><o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span lang="ES-PR" style="font-size:10.0pt">San Juan, PR 00926-6018</span><o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span lang="ES-PR" style="font-size:10.0pt">Cel. (787) 224-6537</span><o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span lang="ES-PR"><a href="http://odelgado@enermechpr.com" target="_blank"></a><a href="mailto:odelgado@enermechpr.com"><a href="mailto:odelgado@enermechpr.com">odelgado@enermechpr.com</a></a></span><o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span lang="ES-PR"><a href="mailto:info@enermechpr.com" target="_blank"></a><a href="mailto:info@enermechpr.com"><a href="mailto:info@enermechpr.com">info@enermechpr.com</a></a></span><o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><a href="http://www.enermechpr.com/" target="_blank"><span lang="ES-PR">www.enermechpr.com</span></a><o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span lang="ES-PR"> </span><o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span lang="ES-PR"> </span><o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span lang="ES-PR"> </span><o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span style="font-size:8.0pt;color:#74B230"><image001.gif> <i>Please consider your
environmental responsibility before printing this e-mail</i></span><o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;margin-bottom:12.0pt"><span style="font-size:8.0pt;color:#1F497D">This Email is covered by the Electronics
Communications Privacy Act, 18 U.S.C. Sections 2510-2521 and is legally
priviliged. The information in this email is personal and confidential and is
intended solely for the addressee(s). Access to this email by anyone else is
unauthorized. If you are not an intended recipient, you must not read, use or
disseminate the information contained in the email. Any views expressed in this
message are those of the individual sender and may be subject to
Attorney/Client privilege and/or Work Product. You are hereby notified that any
dissemination, distribution or copying of this communications is strictly
prohibited.</span><o:p></o:p></p>

<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"> <o:p></o:p></p>

</div>

</div>

</div>

</div>

<p class="MsoNormal" style="margin-bottom:12.0pt"><br>
_______________________________________________<br>
Bldg-sim mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org"></a><a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org"><a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a></a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank"></a><a href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG"><a href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a></a><o:p></o:p></p>

</blockquote>

</div>

<p class="MsoNormal"><br>
<br clear="all">
<br>
-- <br>
Carol Gardner PE<o:p></o:p></p>

</div>

</div>

</div>

</div>




</div></blockquote><blockquote type="cite"><div><span>_______________________________________________</span><br><span>Bldg-sim mailing list</span><br><span><a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org"><a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a></a></span><br><span>To unsubscribe from this mailing list send  a blank message to <a href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG"></a><a href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG"><a href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a></a></span><br></div></blockquote></div><div></div></body></html>