I've only done 90.1 modeling for Estidama PBRS, but I took a look into 90.2 out of interest. <br><br><font face="Arial" size="2"><span style="font-size: 10pt; font-family: Arial;"></span></font>

<ul style="margin-top: 0cm;" type="disc"><li class="MsoNormal"><font face="Arial" size="2"><span style="font-size: 10pt; font-family: Arial;">What heating and cooling systems
     should be used in the baseline (prescriptive) building?</span></font></li><ul><li style="text-align: left;" class="MsoNormal">From 90.2-2007 sec. 8.8.4.1., "equipment of the same DOE product class shall be used in the proposed design and prescriptive..."</li>
<li style="text-align: left;" class="MsoNormal">Therefore it depends on your proposed system...<br></li></ul><li class="MsoNormal"><font face="Arial" size="2"><span style="font-size: 10pt; font-family: Arial;">What ventilation system/ fan powers
     should be used in the baseline (prescriptive) building? </span></font></li><ul><li class="MsoNormal">8.8.4.3., the prescriptive design shall have a similar system meeting the prescriptive requirements"</li><li class="MsoNormal">
Also depends on system... I might use same fan powers for both or maybe try the 90.1 sec. G3.1.2.9. fan specs?<br></li></ul><li class="MsoNormal"><font face="Arial" size="2"><span style="font-size: 10pt; font-family: Arial;">What should the COPs/ EERs/
     efficiencies be for these systems?</span></font></li><ul><li class="MsoNormal">From 90.2-2007 sec. 6.9., the equipment performance shall be "in accordance with federal law or as specified in Table 6.9"</li>
<li class="MsoNormal">Therefore if no federal law, use table 6.9<br></li></ul></ul>Hopefully someone with more experience can answer the question more directly or correct me since I haven't submitted any PVRS, and I recommend raising a CCR to UPC if you still have trouble. <br>
<br>Cheers, and I hope you report your eventual solution!<br><br>Marcus<br>-- <br>Marcus Jones, LEED AP, M.Sc. <br><i>Freelance energy consultant</i><br><i>Vienna, Austria</i><br><br><br><div class="gmail_quote">On Tue, Apr 26, 2011 at 3:09 PM, Arpan Bakshi <span dir="ltr"><<a href="mailto:arpanbakshi@gmail.com">arpanbakshi@gmail.com</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin: 0pt 0pt 0pt 0.8ex; border-left: 1px solid rgb(204, 204, 204); padding-left: 1ex;"><div bgcolor="#FFFFFF" link="blue" vlink="purple" lang="EN-GB"><div>Claire</div><div><br></div>
<div>You are right, Estidama is still in a stage of infancy. When I work on an Estidama project I develop a baseline by identifying the climate to an ASHRAE climate zone based on the number of heating and cooling degree days. You can then make the case for ASHRAE climate zone 1 efficiencies as the code compliance standard and governing minimum performance.</div>
<div><br></div><div><br></div><div><br><br><div><span><br></span></div><div><span><span>Arpan Bakshi, LEED AP BD+C</span></span></div><div><span>YRG sustainability</span></div></div><div><div></div><div class="h5"><div><br>
On Apr 26, 2011, at 7:30 AM, "Claire Das Bhaumik" <<a href="mailto:ClaireDasBhaumik@hoarelea.com" target="_blank">ClaireDasBhaumik@hoarelea.com</a>> wrote:<br><br></div><div></div><blockquote type="cite"><div>











<div>

<p class="MsoNormal"><font face="Arial" size="2"><span style="font-size: 10pt; font-family: Arial;">I am carrying out modelling in support of an Estidama (PVRS
v1.0) assessment for a residential development in Abu Dhabi. </span></font></p>

<p class="MsoNormal"><font face="Arial" size="2"><span style="font-size: 10pt; font-family: Arial;"> </span></font></p>

<p class="MsoNormal"><font face="Arial" size="2"><span style="font-size: 10pt; font-family: Arial;">Estidama uses the use the Energy cost method in section 8 of
ASHRAE 90.2. However, 90.2 requires the use of HVAC efficiencies in accordance
with federal law. There is currently no federal law regarding efficiencies of
HVAC in Abu Dhabi, although there is the Abu Dhabi International Building
code, which I believe is not yet mandatory but does include minimum
efficiencies.</span></font></p>

<p class="MsoNormal"><font face="Arial" size="2"><span style="font-size: 10pt; font-family: Arial;"> </span></font></p>

<p class="MsoNormal"><font face="Arial" size="2"><span style="font-size: 10pt; font-family: Arial;">My questions are:</span></font></p>

<p class="MsoNormal"><font face="Arial" size="2"><span style="font-size: 10pt; font-family: Arial;"> </span></font></p>

<ul style="margin-top: 0cm;" type="disc">
 <li class="MsoNormal"><font face="Arial" size="2"><span style="font-size: 10pt; font-family: Arial;">What heating and cooling systems
     should be used in the baseline (prescriptive) building?</span></font></li>
 <li class="MsoNormal"><font face="Arial" size="2"><span style="font-size: 10pt; font-family: Arial;">What ventilation system/ fan powers
     should be used in the baseline (prescriptive) building? </span></font></li>
 <li class="MsoNormal"><font face="Arial" size="2"><span style="font-size: 10pt; font-family: Arial;">What should the COPs/ EERs/
     efficiencies be for these systems?</span></font></li>
</ul>

<p class="MsoNormal"><font face="Arial" size="2"><span style="font-size: 10pt; font-family: Arial;"> </span></font></p>

<p class="MsoNormal"><font face="Arial" size="2"><span style="font-size: 10pt; font-family: Arial;">Thanks,</span></font></p>

<p class="MsoNormal"><font face="Arial" size="2"><span style="font-size: 10pt; font-family: Arial;">Claire</span></font></p>

</div>

<b><font size="1"><p><font face="arial,helvetica,sans-serif">This email (and any attachment) is intended only for the attention of the addressee. It is STRICTLY CONFIDENTIAL and may be legally privileged. If you have received it in error any disclosure distribution or copying of all or any part of the contents is prohibited. While virus checked by Hoare Lea, the recipient remains responsible for the consequences of any virus received.</font></p>
</font></b>



</div></blockquote></div></div><blockquote type="cite"><div><span>_______________________________________________</span><br><span>Bldg-sim mailing list</span><br><span><a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a></span><br>
<span>To unsubscribe from this mailing list send  a blank message to <a href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank"></a><a href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a></span><br>
</div></blockquote></div><br>_______________________________________________<br>