    Hi Gerfried,<br>
    <br>
    Do you mean KTH Sweden? You said LTH! KTH do some work with Equa
    Simulation AB and their system IDA ICE is very promising. The only
    item on the list it doesn't tick is the daylighting - and only then
    if you want output similar to Radiance. However, if you aren't
    interested in a daylight map it does have a fully integrated window
    shading and daylight model that interacts with the thermal
    simulation at runtime - like E+. To my knowledge, I am not aware
    that IES satisfies window shading models that interact with daylight
    controls at runtime - perhaps Pete Murray could comment.<br>
    <br>
    Best regards<br>
    <br>
    Chris<br>
    <br>
    On 25/04/2011 18:46, Radler63 wrote:
    <blockquote cite="mid:BAY151-ds136537214B129A0FF24FE3C6960@phx.gbl"
      type="cite">
      <meta content="text/html; charset=windows-1252"
        http-equiv="Content-Type">
      <style id="owaParaStyle">P {
        MARGIN-TOP: 0px; MARGIN-BOTTOM: 0px
}
</style>
      <div dir="ltr">
        <div style="font-family: 'Calibri'; color: rgb(0, 0, 0);
          font-size: 12pt;">
          <div>Hello,</div>
          <div> </div>
          <div>we tried out a software named PARASOL, developed by LTH
            SWEDEN. but since we wanted to model rollable blinds with
            PV-included, adding also a special control agorithm, we did
            our own model in python.</div>
          <div>by using PARASOL you may do some postprocessing for the 
            comfort factors.  also may point you to Mathcad which allows
            to do all at a macroscopic level with the help of some
            existing code and WYSIWYG coding.</div>
          <div> </div>
          <div>best regards</div>
          <div> </div>
          <div>Gerfried</div>
          <div> </div>
          <div>Her is the project brief <a moz-do-not-send="true"
              title="http://www.effiziente.st/sowa_en.htm"
              href="http://www.effiziente.st/sowa_en.htm">http://www.effiziente.st/sowa_en.htm</a></div>
          <div>and here a new questionnaire about building integrated
            solar <a moz-do-not-send="true"
              title="http://www.surveymonkey.com/s/HHNBJ2B"
              href="http://www.surveymonkey.com/s/HHNBJ2B">http://www.surveymonkey.com/s/HHNBJ2B</a></div>
          <div style="font-style: normal; display: inline; font-family:
            'Calibri'; color: rgb(0, 0, 0); font-size: small;
            font-weight: normal; text-decoration: none;">
            <div style="font: 10pt tahoma;">
              <div> </div>
              <div style="background: none repeat scroll 0% 0% rgb(245,
                245, 245);">
                <div style=""><b>From:</b> <a moz-do-not-send="true"
                    title="jhaberl@tamu.edu"
                    href="mailto:jhaberl@tamu.edu">Jeff Haberl</a> </div>
                <div><b>Sent:</b> Monday, April 25, 2011 6:55 PM</div>
                <div><b>To:</b> <a moz-do-not-send="true"
                    title="fakra@univ-reunion.fr"
                    href="mailto:fakra@univ-reunion.fr">ali hamada fakra</a>
                </div>
                <div><b>Cc:</b> <a moz-do-not-send="true"
                    title="bldg-sim@lists.onebuilding.org"
                    href="mailto:bldg-sim@lists.onebuilding.org">bldg-sim@lists.onebuilding.org</a>
                </div>
                <div><b>Subject:</b> Re: [Bldg-sim] Bldg-sim] Modeling
                  tool for daylight, Energy, Thermal comfort analysis</div>
              </div>
            </div>
            <div> </div>
          </div>
          <div style="font-style: normal; display: inline; font-family:
            'Calibri'; color: rgb(0, 0, 0); font-size: small;
            font-weight: normal; text-decoration: none;">
            <div style="font-family: tahoma; direction: ltr; color:
              rgb(0, 0, 0); font-size: 10pt;">
              <p>Hamada,</p>
              <p> </p>
              <p>I did not mention nor comment on CODYRUN as I am not
                familiar with this software.</p>
              <p> </p>
              <p>jeff</p>
              <div>
                <p> </p>
                <div><font size="2" color="#0000ff" face="Tahoma">8=! 
                    8=)  :=)  8=)  ;=)  8=)  8=(  8=)  8=()  8=)  8=| 
                    8=)  :=')  8=)8=?<br>
                    <br>
                    Jeff S. Haberl, Ph.D.,P.E.,
                    <a class="moz-txt-link-abbreviated" href="mailto:FASHRAE..............jhaberl@tamu.edu">FASHRAE..............jhaberl@tamu.edu</a><br>
                    <br>
                    Professor............................................................Office
                    Ph: 979-845-6507<br>
                    <br>
                    Department of
                    Architecture.............................Lab
                    Ph:979-845-6065<br>
                    <br>
                    Energy Systems
                    Laboratory.............................FAX:
                    979-862-2457<br>
                    <br>
                    Texas A&M
                    University.....................................77843-3581<br>
                    <br>
                    College Station, Texas, USA,
                    77843..................URL:www.esl.tamu.edu<br>
                    <br>
                    8=/  8=)  :=)  8=)  ;=)  8=)  8=()  8=)  :=)  8=) 
                    8=!  8=)  8=? 8=)8=0<br>
                  </font></div>
              </div>
              <div style="font-family: times new roman; color: rgb(0, 0,
                0); font-size: 16px;">
                <hr tabindex="-1">
                <div style="direction: ltr;" id="divRpF287411"><font
                    size="2" color="#000000" face="Tahoma"><b>From:</b>
                    ali hamada fakra [<a class="moz-txt-link-abbreviated" href="mailto:fakra@univ-reunion.fr">fakra@univ-reunion.fr</a>]<br>
                    <b>Sent:</b> Monday, April 25, 2011 4:23 AM<br>
                    <b>To:</b> Jeff Haberl<br>
                    <b>Cc:</b> <a class="moz-txt-link-abbreviated" href="mailto:bldg-sim@lists.onebuilding.org">bldg-sim@lists.onebuilding.org</a><br>
                    <b>Subject:</b> Re: [Bldg-sim] Bldg-sim] Modeling
                    tool for daylight, Energy, Thermal comfort analysis<br>
                  </font><br>
                </div>
                <div>Dear Prof. Haberl,
                  <div> </div>
                  <div>Is that your remarks are addressed directlty to
                    me ? is what I do understand that you criticize the
                    software CODYRUN ? If this is not the case, I
                    apologize to you for that question.</div>
                  <div> </div>
                  <div>best regards.</div>
                  <div> </div>
                  <div>A. H. Fakra</div>
                  <div>
                    <div> </div>
                    <div>
                      <div>Le 25 avr. 11 à 06:49, Jeff Haberl a écrit :</div>
                      <br class="Apple-interchange-newline">
                      <blockquote type="cite"><span style="widows: 2;
                          text-transform: none; text-indent: 0px;
                          letter-spacing: normal; border-collapse:
                          separate; font: medium helvetica; white-space:
                          normal; orphans: 2; color: rgb(0, 0, 0);
                          word-spacing: 0px;" class="Apple-style-span">
                          <div style="word-wrap: break-word;">
                            <div style="font-family: tahoma; direction:
                              ltr; color: rgb(0, 0, 0); font-size:
                              10pt;">
                              <div style="line-height: normal; margin:
                                0in 0in 0pt;"><span style="font-family:
                                  'Times New Roman',serif; color: black;
                                  font-size: 12pt;">Hamada,</span></div>
                              <div style="line-height: normal; margin:
                                0in 0in 0pt;"><span style="font-family:
                                  'Times New Roman',serif; color: black;
                                  font-size: 12pt;"></span> </div>
                              <div style="line-height: normal; margin:
                                0in 0in 0pt;"><span style="font-family:
                                  'Times New Roman',serif; color: black;
                                  font-size: 12pt;">Unfortunately,
                                  you've chosen the worst possible
                                  building for analysis. There are
                                  several reasons for this.</span></div>
                              <div style="line-height: normal; margin:
                                0in 0in 0pt;"><span style="font-family:
                                  'Times New Roman',serif; color: black;
                                  font-size: 12pt;"></span> </div>
                              <div style="line-height: normal; margin:
                                0in 0in 0pt;"><span style="font-family:
                                  'Times New Roman',serif; color: black;
                                  font-size: 12pt;">First, there is no
                                  single U.S. tool that does an accurate
                                  analysis of what you are asking for.
                                  There are some that perform simplified
                                  analysis of most of the parameters you
                                  are looking for, but none do it all
                                  right (that I’m aware of). Some of the
                                  European codes are getting close, for
                                  example ESPr and/or IES/VE, but each
                                  has its limitations.</span></div>
                              <div style="line-height: normal; margin:
                                0in 0in 0pt;"><span style="font-family:
                                  'Times New Roman',serif; color: black;
                                  font-size: 12pt;"></span> </div>
                              <div style="line-height: normal; margin:
                                0in 0in 0pt;"><span style="font-family:
                                  'Times New Roman',serif; color: black;
                                  font-size: 12pt;">To estimate the
                                  thermal analysis with Visual DOE
                                  (i.e., DOE-2.1e) or EQUEST (i.e.,
                                  DOE-2.2) you’d need to have at least
                                  one zone that is conditioned in order
                                  to simulate conditions in an
                                  unconditioned space. So, although it
                                  is possible to perform such a
                                  simulation, you have to go to great
                                  lengths to do this with canned
                                  simulations such as DOE-2.1e and
                                  DOE-2.2. One successful project that
                                  did this for a Buddhist temple was
                                  done by Dr. Sreshthaputra, which you
                                  can read about in:</span></div>
                              <div style="line-height: normal; margin:
                                0in 0in 0pt;"><span style="font-family:
                                  'Times New Roman',serif; color: black;
                                  font-size: 12pt;"></span> </div>
                              <div style="line-height: normal;
                                text-indent: -0.25in; margin: 0in 0in
                                0pt 0.25in;"><span style="font-family:
                                  'Times New Roman',serif; color: black;
                                  font-size: 12pt;">Sreshthaputra, A.,
                                  Haberl, J., Andrews, M. 2004.
                                  “Improving Building Design and
                                  Operation .of a Thai Buddhist Temple,”<span
                                    class="Apple-converted-space"> </span><i>Energy
                                    and Buildings</i>, Vol. 36, pp.
                                  481-494.</span></div>
                              <div style="line-height: normal;
                                text-indent: -0.25in; margin: 0in 0in
                                0pt 0.25in;"><span style="font-family:
                                  'Times New Roman',serif; color: black;
                                  font-size: 12pt;"></span> </div>
                              <div style="line-height: normal;
                                text-indent: -0.25in; margin: 0in 0in
                                0pt 0.25in;"><span style="font-family:
                                  'Times New Roman',serif; color: black;
                                  font-size: 12pt;">Or in his thesis:</span></div>
                              <div style="line-height: normal;
                                text-indent: -0.25in; margin: 0in 0in
                                0pt 0.25in;"><span style="font-family:
                                  'Times New Roman',serif; color: black;
                                  font-size: 12pt;"></span> </div>
                              <div style="line-height: normal;
                                text-indent: -0.25in; margin: 0in 0in
                                0pt 0.25in;"><span style="font-family:
                                  'Times New Roman',serif; color: black;
                                  font-size: 12pt;">Atch Sreshthaputra,
                                  2004. “</span><span
                                  style="font-family: 'Times New
                                  Roman',serif; color: black; font-size:
                                  12pt;">Building Design and Operation
                                  for Improving Thermal Comfort in
                                  Naturally Ventilated Buildings in a
                                  Hot and Humid Climate,” Department of
                                  Architecture, Texas A&M
                                  University.</span></div>
                              <div style="line-height: normal;
                                text-indent: -0.25in; margin: 0in 0in
                                0pt 0.25in;"><span style="font-family:
                                  'Times New Roman',serif; color: black;
                                  font-size: 12pt;"></span> </div>
                              <div style="line-height: normal;
                                text-indent: -0.25in; margin: 0in 0in
                                0pt 0.25in;"><span style="font-family:
                                  'Times New Roman',serif; color: black;
                                  font-size: 12pt;">In this work, which
                                  was calibrated to real data from the
                                  temple, Atch created a fictitious zone
                                  that did nothing, then proceeded to
                                  model the temple as a unconditioned
                                  zone, which worked with one exception
                                  that it did not handle the air flows.
                                  To get around this Atch ran CFD with a
                                  program that used a 3D model from the
                                  CHAM engine, then passed the airflows
                                  back to DOE-2 each hour to do the run,
                                  which calculated the dynamic heat
                                  transfer, then back to the CFD for the
                                  next hour’s airflow, etc., (taking 24
                                  hours to simulate 24 hours on 2003ish
                                  Pentium, not exactly fast).</span></div>
                              <div style="line-height: normal;
                                text-indent: -0.25in; margin: 0in 0in
                                0pt 0.25in;"><span style="font-family:
                                  'Times New Roman',serif; color: black;
                                  font-size: 12pt;"></span> </div>
                              <div style="line-height: normal;
                                text-indent: -0.25in; margin: 0in 0in
                                0pt 0.25in;"><span style="font-family:
                                  'Times New Roman',serif; color: black;
                                  font-size: 12pt;">Second, you can
                                  probably get an estimate of the
                                  daylighting using DOE-2.1e or DOE-2.2
                                  that should be accurate for and
                                  sidelights if you know the internal
                                  geometry, including surface
                                  characteristics, since they use the
                                  split-flux method. More accurate
                                  daylighting simulations can be done
                                  with RADIANCE or annual simulations
                                  with DAYSIM, or perhaps one of the new
                                  annual variants of RADIANCE.</span></div>
                              <div style="line-height: normal;
                                text-indent: -0.25in; margin: 0in 0in
                                0pt 0.25in;"><span style="font-family:
                                  'Times New Roman',serif; color: black;
                                  font-size: 12pt;"></span> </div>
                              <div style="line-height: normal;
                                text-indent: -0.25in; margin: 0in 0in
                                0pt 0.25in;"><span style="font-family:
                                  'Times New Roman',serif; color: black;
                                  font-size: 12pt;">Third, true
                                  calculations of thermal comfort would
                                  require CFD and a internal radiation
                                  network (should interior surfaces get
                                  hot or cold), which further complicate
                                  things.</span></div>
                              <div style="line-height: normal;
                                text-indent: -0.25in; margin: 0in 0in
                                0pt 0.25in;"><span style="font-family:
                                  'Times New Roman',serif; color: black;
                                  font-size: 12pt;"></span> </div>
                              <div style="line-height: normal;
                                text-indent: -0.25in; margin: 0in 0in
                                0pt 0.25in;"><span style="font-family:
                                  'Times New Roman',serif; color: black;
                                  font-size: 12pt;">So, it can be done,
                                  but there are only a few efforts in
                                  the literature that give solid advice
                                  on how to do this, probably more as
                                  time goes on. Getting all this in one
                                  package is probably not there yet.
                                  Probably still a good topic for a
                                  Ph.D. thesis.</span></div>
                              <p style="line-height: normal;
                                text-indent: -0.25in; margin: 0in 0in
                                0pt 0.25in;" class="MsoNormal"><span
                                  style="font-family: 'Times New
                                  Roman',serif; color: black; font-size:
                                  12pt;"></span> </p>
                              <div style="line-height: normal;
                                text-indent: -0.25in; margin: 0in 0in
                                0pt 0.25in;"><span style="font-family:
                                  'Times New Roman',serif; color: black;
                                  font-size: 12pt;">Jeff</span></div>
                              <p style="margin-top: 0px; margin-bottom:
                                0px;"> </p>
                              <div>
                                <p style="margin-top: 0px;
                                  margin-bottom: 0px;"> </p>
                                <div><font size="2" color="#0000ff"
                                    face="Tahoma">8=!  8=)  :=)  8=) 
                                    ;=)  8=)  8=(  8=)  8=()  8=)  8=| 
                                    8=)  :=')  8=)8=?<br>
                                    <br>
                                    Jeff S. Haberl, Ph.D.,P.E.,
                                    FASHRAE..............<a
                                      moz-do-not-send="true"
                                      href="mailto:jhaberl@tamu.edu"
                                      target="_blank">jhaberl@tamu.edu</a><br>
                                    <br>
                                    Professor............................................................Office
                                    Ph: 979-845-6507<br>
                                    <br>
                                    Department of
                                    Architecture.............................Lab
                                    Ph:979-845-6065<br>
                                    <br>
                                    Energy Systems
                                    Laboratory.............................FAX:
                                    979-862-2457<br>
                                    <br>
                                    Texas A&M
                                    University.....................................77843-3581<br>
                                    <br>
                                    College Station, Texas, USA,
                                    77843..................URL:<a
                                      moz-do-not-send="true"
                                      href="http://www.esl.tamu.edu"
                                      target="_blank">www.esl.tamu.edu</a><br>
                                    <br>
                                    8=/  8=)  :=)  8=)  ;=)  8=)  8=() 
                                    8=)  :=)  8=)  8=!  8=)  8=? 8=)8=0<br>
                                  </font></div>
                              </div>
                              <div style="font-family: 'Times New
                                Roman'; color: rgb(0, 0, 0); font-size:
                                16px;">
                                <hr tabindex="-1">
                                <div style="direction: ltr;"
                                  id="divRpF938488"><font size="2"
                                    color="#000000" face="Tahoma"><b>From:</b><span
                                      class="Apple-converted-space"> </span><a
                                      moz-do-not-send="true"
                                      href="mailto:bldg-sim-bounces@lists.onebuilding.org"
                                      target="_blank">bldg-sim-bounces@lists.onebuilding.org</a><span
                                      class="Apple-converted-space"> </span>[<a
                                      moz-do-not-send="true"
                                      href="mailto:bldg-sim-bounces@lists.onebuilding.org"
                                      target="_blank">bldg-sim-bounces@lists.onebuilding.org</a>]
                                    on behalf of ali hamada fakra [<a
                                      moz-do-not-send="true"
                                      href="mailto:fakra@univ-reunion.fr"
                                      target="_blank">fakra@univ-reunion.fr</a>]<br>
                                    <b>Sent:</b><span
                                      class="Apple-converted-space"> </span>Thursday,
                                    April 21, 2011 11:32 PM<br>
                                    <b>To:</b><span
                                      class="Apple-converted-space"> </span><a
                                      moz-do-not-send="true"
                                      href="mailto:bldg-sim@lists.onebuilding.org"
                                      target="_blank">bldg-sim@lists.onebuilding.org</a><br>
                                    <b>Subject:</b><span
                                      class="Apple-converted-space"> </span>[Bldg-sim]
                                    Bldg-sim] Modeling tool for
                                    daylight, Energy, Thermal comfort
                                    analysis<br>
                                  </font><br>
                                </div>
                                <div>
                                  <div>Message: 2</div>
                                  Date: Thu, 21 Apr 2011 10:47:20 +0530
                                  (IST)<br>
                                  From: Rathna Shree <<a
                                    moz-do-not-send="true"
                                    href="mailto:rathnashreep@yahoo.in"
                                    target="_blank">rathnashreep@yahoo.in</a>><br>
                                  To: bldg <<a moz-do-not-send="true"
href="mailto:bldg-sim@lists.onebuilding.org" target="_blank">bldg-sim@lists.onebuilding.org</a>><br>
                                  Subject: [Bldg-sim] Modeling tool for
                                  daylight, Energy,<span
                                    style="white-space: pre;"
                                    class="Apple-tab-span"> </span>Thermal<br>
                                  <span style="white-space: pre;"
                                    class="Apple-tab-span"></span>comfort
                                  analysis<br>
                                  Message-ID: <<a
                                    moz-do-not-send="true"
                                    href="mailto:935834.21570.qm@web95906.mail.in.yahoo.com"
                                    target="_blank">935834.21570.qm@web95906.mail.in.yahoo.com</a>><br>
                                  Content-Type: text/plain;
                                  charset="utf-8"<br>
                                  <br>
                                  Dear All,<br>
                                  <br>
                                  Can you please suggest the best
                                  modeling tool which has the
                                  capabilities to perform Daylight
                                  simulation, Thermal comfort analysis
                                  in non AC spaces of a building and
                                  Energy simulation.<br>
                                  <br>
                                  I am using dialux for daylight
                                  simulation, Visual Doe for Energy
                                  simulation and Transys for Thermal
                                  comfort analysis. I am inputting the
                                  same details thrice in different
                                  softwares. So is there any software
                                  which can perform all the 3 analysis
                                  in one go.<br>
                                  <br>
                                  Regards,<br>
                                  Rathnashree 
                                  <div> </div>
                                  <div> </div>
                                  <div>------------------------------------------------------------</div>
                                  <div> </div>
                                  <div>Hello Rathmashree,</div>
                                  <div> </div>
                                  <div>I suggest you use CODYRUN. Is a
                                    french software dedicated to both
                                    research and consulting firms. You
                                    can make the 3 studies (Energy
                                    simulation, Daylight and thermal
                                    confort).that you want at the same
                                    time. For more information about
                                    this software, you can write to 
                                    Professor Harry Boyer (Founder of
                                    the software) to this mail : <a
                                      moz-do-not-send="true"
                                      href="mailto:harry.boyer@univ-reunion.fr"
                                      target="_blank">harry.boyer@univ-reunion.fr</a> </div>
                                  <div> </div>
                                  <div>Best regards,</div>
                                  <div> </div>
                                  <div>PhD / Engineer A. H. Fakra</div>
                                  <div> </div>
                                  <div> </div>
                                </div>
                              </div>
                            </div>
                          </div>
                        </span><br class="Apple-interchange-newline">
                      </blockquote>
                    </div>
                    <div> </div>
                  </div>
                </div>
              </div>
            </div>
            <p>
            </p>
            <hr>
            _______________________________________________<br>
            Bldg-sim mailing list<br>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
            To unsubscribe from this mailing list send  a blank message
            to <a class="moz-txt-link-abbreviated" href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
          </div>
        </div>
      </div>
      <pre wrap="">
<fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
Bldg-sim mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
    </blockquote>
    <br>
    <div class="moz-signature">-- <br>
      <div>
        <p>Chris Yates <span style="color: rgb(79, 98, 40);">C Eng
            MCIBSE</span></p>
        <p><i style="">Building Physics Consultant<o:p></o:p></i></p>
        <p>Tel:<span style="">   </span>+447960731576</p>
        <p>Email: <a class="moz-txt-link-abbreviated" href="mailto:chris.malcolm.yates@gmail.com">chris.malcolm.yates@gmail.com</a></p>
        <p>Skype: <span class="SpellE">christopher.m.yates</span></p>
      </div>
    </div>
  </body>
</html>