<div>Milda,</div>
<div> </div>
<div>If you did notice, HAP uses two different weather files. one for design and other for simulation. And if you dig into it you'll find out that they both are different. The simulation weather is the real time (actual) temperature and other data recorded at the airports for an extended period, which cannot be overridden, while design weather data is based on extreme or peak weather as defined by ASHRAE which you can change in the program.</div>


<div><br>Now if you are looking at LEED unmet load hours they may not be necessarily due to air sytem size, but may also be due to your plant insufficient capacity. Download HAP e help 014 from here :<a href="http://www.commercial.carrier.com/commercial/hvac/general/0,,CLI1_DIV12_ETI3906_MID1738,00.html">http://www.commercial.carrier.com/commercial/hvac/general/0,,CLI1_DIV12_ETI3906_MID1738,00.html</a>.</div>


<div>In here you will find a pdf saying understanding the LEED unmet load hours in HAP.</div>
<div> </div>
<div>Simulation results is just for us to know how the building would run in real time when sized on the design results. In simulation , HAP takes credit of internal heat gains, which reduces your heating load, which is OK in real time. While in design , internal heat gain is ignored in heating load calcualtions. This is just one of the difference in simulation and design in HAP.</div>


<div> </div>
<div>I hope this helps Milda.<br><br><br></div>
<div class="gmail_quote">On Tue, Apr 5, 2011 at 12:01 PM, milda margarin <span dir="ltr"><<a href="mailto:empire999@hotmail.com">empire999@hotmail.com</a>></span> wrote:<br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">
<div>hi Varun 
<div>
<div style="TEXT-INDENT: 0px !important"> thanks for your reply! I have another question though based on your statement that the system should be based on the 'design results'; I thought the whole point of using simulations is to predict the peak capacity required and then base your design on this? (possibly by applying safety factors according to real life experience).</div>


<div style="TEXT-INDENT: 0px !important">And how can you have unmet loads when you design based on the peak load? In that case the 'peak load' is not the maximum load?</div>
<div style="TEXT-INDENT: 0px !important">Further comments anybody?</div>
<div style="TEXT-INDENT: 0px !important"> best regards</div>
<div style="TEXT-INDENT: 0px !important">Milda</div><br>
<div class="hm">
<hr>
From: <a href="mailto:seldomvarun@gmail.com" target="_blank">seldomvarun@gmail.com</a><br>Date: Tue, 29 Mar 2011 07:51:29 -0400<br>Subject: Re: [Bldg-sim] ASHRAE 90.1 Appendix G3.1.2.2<br>To: <a href="mailto:empire999@hotmail.com" target="_blank">empire999@hotmail.com</a></div>


<div>
<div></div>
<div class="h5"><br><br>
<div>Milda,</div>
<div>I think if you are performorming energy simulations for the baseline, it doesnt matter what is this 25% and 15% upsizing is used for, as it used only as much capacity it needs. And your system size should be based on the design results and not simulation results (that also proposed model).</div>


<div>But nevertheless I always interpret this as you said in your first point, to cover uncertainity in building simulation. </div>
<div>I also think it helps baseline to reduce its unmet load hours.</div>
<div> </div>
<div>I hope this helps.<br><br></div>
<div>On Tue, Mar 29, 2011 at 3:27 AM, milda margarin <span dir="ltr"><<a href="mailto:empire999@hotmail.com" target="_blank">empire999@hotmail.com</a>></span> wrote:<br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; PADDING-LEFT: 1ex">
<div><span style="FONT-FAMILY: Tahoma, Verdana, Arial, sans-serif; COLOR: rgb(42,42,42)">hi , I already submitted this question but there were no responses so I'd like to try again: 
<div style="LINE-HEIGHT: 17px"> could somebody share some insight to the ASHRAE 90.1 Appendix G3.1.2.2 point regarding heating and cooling equipment sizing based on building energy simulations. It is stated that the equipment should be oversized by a factor of 1.25 for heating and 1.15 for cooling. Are these "safety factors" based on the uncertainty associated with building energy simulations or a requirement that makes sure that the system can respond quickly enough during startup? Why are there different factors applied for heating and cooling?</div>


<div style="LINE-HEIGHT: 17px">thanks!</div>
<div style="LINE-HEIGHT: 17px">Milda</div>
<div><br></div></span></div><br>_______________________________________________<br>Bldg-sim mailing list<br><a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>

To unsubscribe from this mailing list send  a blank message to <a href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a><br><br></blockquote></div><br><br clear="all">
<br>
-- <br>
<p><a name="12f26654f361a7cc_SafeHtmlFilter__MailAutoSig"><span><font size="3"><font face="Calibri">Thanks and Best Regards,</font></font></span></a></p>
<p><span><span><font size="3" face="Calibri"> </font></span></span></p>
<p><span><span><font size="3"><font face="Calibri">Sincerely,</font></font></span></span></p>
<p><span><span><font size="3"><font face="Calibri">Varun Kulkarni , M.S. , EIT</font></font></span></span></p>
<p><span><span><font size="3"><font face="Calibri">RMF Engineering</font></font></span></span></p>
<p><span><span><font size="3"><font face="Calibri">5520, Research Park Drive, Suite 300</font></font></span></span></p>
<p><span><span><font size="3"><font face="Calibri">Baltimore, MD - 21228</font></font></span></span></p>
<p><span><span><font size="3" face="Calibri"> </font></span></span></p>
<p><span><span><font size="3"><font face="Calibri">Office : <a href="tel:410-576-0505" target="_blank">410-576-0505</a> ext. 5352</font></font></span></span></p>
<p><span><span><font size="3"><font face="Calibri">Mobile: <a href="tel:%28%2B1%29405-385-1928" target="_blank">(+1)405-385-1928</a></font></font></span></span></p>
<p><span><span><font size="3" face="Calibri"> </font></span></span></p>
<p><span><span><font size="3"><font face="Calibri">Note: Please do not print, unless required.</font></font></span></span></p> <br><br></div></div></div></div></blockquote></div><br><br clear="all"><br>-- <br>
<p style="MARGIN: 0in 0in 0pt"><a name="SafeHtmlFilter__MailAutoSig"><span><font size="3"><font face="Calibri">Thanks and Best Regards,</font></font></span></a></p>
<p style="MARGIN: 0in 0in 0pt"><span><span><font size="3" face="Calibri"> </font></span></span></p>
<p style="MARGIN: 0in 0in 0pt"><span><span><font size="3"><font face="Calibri">Sincerely,</font></font></span></span></p>
<p style="MARGIN: 0in 0in 0pt"><span><span><font size="3"><font face="Calibri">Varun Kulkarni , M.S. , EIT</font></font></span></span></p>
<p style="MARGIN: 0in 0in 0pt"><span><span><font size="3"><font face="Calibri">RMF Engineering</font></font></span></span></p>
<p style="MARGIN: 0in 0in 0pt"><span><span><font size="3"><font face="Calibri">5520, Research Park Drive, Suite 300</font></font></span></span></p>
<p style="MARGIN: 0in 0in 0pt"><span><span><font size="3"><font face="Calibri">Baltimore, MD - 21228</font></font></span></span></p>
<p style="MARGIN: 0in 0in 0pt"><span><span><font size="3" face="Calibri"> </font></span></span></p>
<p style="MARGIN: 0in 0in 0pt"><span><span><font size="3"><font face="Calibri">Office : 410-576-0505 ext. 5352</font></font></span></span></p>
<p style="MARGIN: 0in 0in 0pt"><span><span><font size="3"><font face="Calibri">Mobile: (+1)405-385-1928</font></font></span></span></p>
<p style="MARGIN: 0in 0in 0pt"><span><span><font size="3" face="Calibri"> </font></span></span></p>
<p style="MARGIN: 0in 0in 0pt"><span><span><font size="3"><font face="Calibri">Note: Please do not print, unless required.</font></font></span></span></p>
<p> </p><br>