size=2 face=Arial>I have a bit different view of this:</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=562255104-22032011><FONT color=#0000ff 
size=2 face=Arial></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=562255104-22032011><FONT color=#0000ff 
size=2 face=Arial>The load seen by the chiller is not just the load in the 
zones, but the load from the system.  The system load is what is required 
to cool the supply flow down to the supply air temperature (SAT) setpoint.  
The SAT is either fixed, or cold enough to satisfy the zone requiring the most 
cooling (the "critical" zone), assuming the zone loads are met.  All zones 
except for the critical zone don't need as much cooling.  In a VAV system, 
the cooling is reduced via reduced flow.  This reduced flow means less 
system load to the chiller plant.  In contrast, the CAV system load does 
not get reduced because some zones have lower loads.  The full fan flow 
needs to be cooled to the SAT.  In this case, the non-critical zones are 
kept from being overcooled by the addition of reheat.</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=562255104-22032011><FONT color=#0000ff 
size=2 face=Arial></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=562255104-22032011><FONT color=#0000ff 
size=2 face=Arial>Regards,</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=562255104-22032011><FONT color=#0000ff 
size=2 face=Arial>Bill</FONT></SPAN></DIV><BR>
<DIV dir=ltr lang=en-us class=OutlookMessageHeader align=left>
<HR tabIndex=-1>
<FONT size=2 face=Tahoma><B>From:</B> bldg-sim-bounces@lists.onebuilding.org 
[mailto:bldg-sim-bounces@lists.onebuilding.org] <B>On Behalf Of </B>Aaron 
Powers<BR><B>Sent:</B> Monday, March 21, 2011 8:11 AM<BR><B>To:</B> James V 
Dirkes II, PE<BR><B>Cc:</B> Deepak Tewari; 
bldg-sim@lists.onebuilding.org<BR><B>Subject:</B> Re: [Bldg-sim] Difference in 
chiller energy for VAV and CAV system<BR></FONT><BR></DIV>
<DIV></DIV>
<DIV>There are several things going on here:</DIV>
<DIV> </DIV>
<DIV>- Yes, the lower fan energy for VAV will add less heat to the chilled water 
loop.  This will propogate to the pumps, chillers, and heat 
rejection.</DIV>
<DIV>- Chilled water coils are complex heat-exchangers, which do not exibit 
linear behavior.  Reducing the air flow decreases the water-side coil 
effectiveness; therefore, at a given load, a CAV system will have a larger 
chilled water delta-T.</DIV>
<DIV>- With equivalent pumping schemes, this will result in pump savings for the 
CAV system (in the absence of 3-way valves).  I'm not sure about ePlus, but 
this can be demonstrated in the latest DOE2.2.</DIV>
<DIV>- In reality, the larger chilled water delta-T will decrease chiller lift 
and increase its efficiency.  Again I'm not sure about ePlus, but in 
DOE2.2, chiller curves are a function of a dT parameter which is the difference 
between condenser entering and chilled water leaving temperatures.  Its an 
attempt to account for chiller lift, but it does not give an efficiency credit 
for increasing the chilled water delta-T.  So, you will not see the chiller 
efficiency boost in DOE2 for CAV systems due to a greater chilled water 
delta-T.</DIV>
<DIV> </DIV>
<DIV>In my experience, the VAV fan savings (and reduced chilled water load 
savings) usually outweigh the pump and chiller savings for CAV.  However, 
it varies from building to building.  For example, if you had a rare 
building with a low air-side static pressure drop to begin with and a long, high 
head pumping system, then its possible that the CAV system will be more 
efficient overall.</DIV>
<DIV> </DIV>
<DIV>Aaron<BR></DIV>
<DIV class=gmail_quote>On Mon, Mar 21, 2011 at 8:13 AM, James V Dirkes II, PE 
<SPAN dir=ltr><<A href="mailto:jvd2pe@tds.net">jvd2pe@tds.net</A>></SPAN> 
wrote:<BR>
<BLOCKQUOTE 
style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" 
class=gmail_quote>
  <DIV lang=EN-US link="blue" vlink="purple">
  <DIV>
  <P class=MsoNormal><SPAN 
  style="COLOR: #1f497d; FONT-SIZE: 11pt">Deepak,</SPAN></P>
  <P class=MsoNormal><SPAN style="COLOR: #1f497d; FONT-SIZE: 11pt">Here are some 
  thoughts:</SPAN></P>
  <P><SPAN 
  style="FONT-FAMILY: Symbol; COLOR: #1f497d; FONT-SIZE: 11pt"><SPAN>·<SPAN 
  style="FONT: 7pt 'Times New Roman'">         
  </SPAN></SPAN></SPAN><SPAN style="COLOR: #1f497d; FONT-SIZE: 11pt">Less fan 
  energy  = less cooling load, since the fan energy is a part of the total 
  cooling load.</SPAN></P>
  <P><SPAN 
  style="FONT-FAMILY: Symbol; COLOR: #1f497d; FONT-SIZE: 11pt"><SPAN>·<SPAN 
  style="FONT: 7pt 'Times New Roman'">         
  </SPAN></SPAN></SPAN><SPAN style="COLOR: #1f497d; FONT-SIZE: 11pt">If the pump 
  is variable volume, the pump energy required for VAV fans will be slightly 
  less due to less fan heat to cool.</SPAN></P>
  <P><SPAN 
  style="FONT-FAMILY: Symbol; COLOR: #1f497d; FONT-SIZE: 11pt"><SPAN>·<SPAN 
  style="FONT: 7pt 'Times New Roman'">         
  </SPAN></SPAN></SPAN><SPAN style="COLOR: #1f497d; FONT-SIZE: 11pt">If you are 
  using the identical chiller for each system (VAV, CAV), then the chiller 
  should use less energy also, due to less fan and pump heat.</SPAN></P>
  <P><SPAN 
  style="FONT-FAMILY: Symbol; COLOR: #1f497d; FONT-SIZE: 11pt"><SPAN>·<SPAN 
  style="FONT: 7pt 'Times New Roman'">         
  </SPAN></SPAN></SPAN><SPAN style="COLOR: #1f497d; FONT-SIZE: 11pt">A more 
  common comparison would be to contrast a VAV chiller system with a CAV 
  packaged rooftop system.  For that comparison, the part load efficiencies 
  of chiller and compressor / DX coil will be a major factor. Dehumidification 
  will also be different for DX vs. chilled water coils.</SPAN></P>
  <P class=MsoNormal><SPAN 
  style="COLOR: #1f497d; FONT-SIZE: 11pt"></SPAN> </P>
  <DIV>
  <P style="TEXT-ALIGN: center" class=MsoNormal align=center><B><SPAN 
  style="COLOR: #1f497d; FONT-SIZE: 13.5pt">The Building Performance 
  Team<BR></SPAN></B><B><SPAN style="COLOR: #1f497d">James V. Dirkes II, P.E., 
  LEED AP<BR></SPAN></B><SPAN style="COLOR: #1f497d">1631 Acacia 
  Drive NW<BR>Grand Rapids, MI 49504<BR><A href="tel:616%20450%208653" 
  target=_blank>616 450 8653</A></SPAN></P></DIV>
  <P class=MsoNormal><SPAN 
  style="COLOR: #1f497d; FONT-SIZE: 11pt"></SPAN> </P>
  <DIV>
  <DIV 
  style="BORDER-BOTTOM: medium none; BORDER-LEFT: medium none; PADDING-BOTTOM: 0in; PADDING-LEFT: 0in; PADDING-RIGHT: 0in; BORDER-TOP: #b5c4df 1pt solid; BORDER-RIGHT: medium none; PADDING-TOP: 3pt">
  <P style="MARGIN-LEFT: 0.5in" class=MsoNormal><B><SPAN 
  style="FONT-SIZE: 10pt">From:</SPAN></B><SPAN style="FONT-SIZE: 10pt"> <A 
  href="mailto:bldg-sim-bounces@lists.onebuilding.org" 
  target=_blank>bldg-sim-bounces@lists.onebuilding.org</A> [mailto:<A 
  href="mailto:bldg-sim-bounces@lists.onebuilding.org" 
  target=_blank>bldg-sim-bounces@lists.onebuilding.org</A>] <B>On Behalf Of 
  </B>Deepak Tewari<BR><B>Sent:</B> Monday, March 21, 2011 2:31 AM<BR><B>To:</B> 
  <A href="mailto:bldg-sim@lists.onebuilding.org" 
  target=_blank>bldg-sim@lists.onebuilding.org</A><BR><B>Subject:</B> [Bldg-sim] 
  Difference in chiller energy for VAV and CAV system</SPAN></P></DIV></DIV>
  <DIV>
  <DIV></DIV>
  <DIV class=h5>
  <P style="MARGIN-LEFT: 0.5in" class=MsoNormal> </P>
  <DIV>
  <DIV>
  <P style="MARGIN-BOTTOM: 12pt; MARGIN-LEFT: 0.5in; MARGIN-RIGHT: 0in" 
  class=MsoNormal>Dear All,<BR><BR>I am comparing the energy performance of a 
  constant volume and variable volume system for a composite climate of India 
  (New Delhi) in EnergyPlus. The building area is 7500 sq m. The chiller 
  capacity is same for both the cases. The chilled water to the cooling coils is 
  supplied by a constant speed pump. <BR><BR>The savings in the fan energy is 
  evident due to variable speed of the supply fan in case of VAV. However i am 
  getting energy saving in cooling energy (chiller energy) also, in VAV compared 
  to CAV, which i feel is due to higher delta T (chilled water) across cooling 
  coil for CAV compared to VAV, this in turns increases the chiller electricity 
  consumption. However while discussions with some consultant, it is their 
  feeling that the cooling energy would remain same for both type of 
  systems.<BR><BR>I want to ask has someone else tried this simulation and would 
  there be any difference in cooling energy or not? <BR>Thanks in 
  advance.<BR>Deepak<BR><BR></P></DIV></DIV>
  <P style="MARGIN-LEFT: 0.5in" 
  class=MsoNormal> </P></DIV></DIV></DIV></DIV><BR>_______________________________________________<BR>Bldg-sim 
  mailing list<BR><A 
  href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" 
  target=_blank>http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</A><BR>To 
  unsubscribe from this mailing list send  a blank message to <A 
  href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</A><BR><BR></BLOCKQUOTE></DIV><BR><BR 
clear=all><BR>-- <BR>Sent from my DynaTAC 8000x<BR></BODY></HTML>