    Nope, not that I know of. Before this kind of summaries is
    implemented in EPlus, I think scripting is the way to get faster
    results. SQLite is really a powerful result analysis tool. What you
    describe below can be implemented relatively easily with some SQL
    statements.<br>
    <br>
    We have been trying to come up with a better way to communicate this
    kind of output to the client. I will share the results to this list
    once we finalize how to do this in EPlus.<br>
    <br>
    Thanks,<br>
    <br>
    Ery<br>
    <br>
    On 03/04/2011 05:04 PM, Karen Walkerman wrote:
    <blockquote
      cite="mid:AANLkTinEzWe+sayhTDQHj5Vn80wB768JC2m6icLCO4Yy@mail.gmail.com"
      type="cite">
      <div>Thanks Ery.<br>
      </div>
      <div><br>
      </div>
      <div>It helps.  It's just slow.  What I love about LS-C is that
        it's fast.  Do you know of a way to get a grouped report for all
        walls within a particular zone.  So instead of having hourly
        output for every wall in a space, you would have one for each:
        exterior walls, interior walls, etc?  This would make reviewing
        these outputs much faster!</div>
      <div><br>
      </div>
      <div>Thanks!</div>
      <div><br>
      </div>
      <div>Karen</div>
      <br>
      <div class="gmail_quote">On Fri, Mar 4, 2011 at 6:52 PM, Ery
        Djunaedy <span dir="ltr"><<a moz-do-not-send="true"
            href="mailto:ery.mailinglist@gmail.com">ery.mailinglist@gmail.com</a>></span>
        wrote:<br>
        <blockquote class="gmail_quote" style="margin: 0pt 0pt 0pt
          0.8ex; border-left: 1px solid rgb(204, 204, 204);
          padding-left: 1ex;">
          <div bgcolor="#ffffff" text="#000000">
            <div>Hi Karen,</div>
            <div> </div>
            <div>Same here, I always use LS-C when I use eQuest. Just
              adding the ventilaton load, then you will have the peak
              load. Its always fun to compare this number with what the
              mechanical engineer has.</div>
            <div> </div>
            <div>I said earlier, in EnergyPlus it is not nicely formated
              like LS-C. It does not mean you cannot have it. You can
              force EPlus to show the numbers. The internal gains are
              the easy ones, the windows are also relatively easy, the
              last pieces are the opaque "conduction" and the
              ventilation load. Which is not difficult.<br>
              <br>
              The problem is what peak to report? You will have the peak
              of the total gains, which will happen at a different
              timestep then the peak of the cooling load. And these two,
              in turn is different with the zone sizing report.<br>
              <br>
              I personally use the zone sizing reports as the peak
              loads, and I will get all the details by running the
              designday run with schedules consistent with the design
              day schedule.<br>
              <br>
              Hope this helps,<br>
              <font color="#888888"> <br>
                Ery<br>
                <br>
              </font></div>
            <div>
              <div class="h5">
                <div class="gmail_quote">On Fri, Mar 4, 2011 at 12:00
                  PM, Karen Walkerman <span dir="ltr"><<a
                      moz-do-not-send="true"
                      href="mailto:kwalkerman@gmail.com" target="_blank">kwalkerman@gmail.com</a>></span>
                  wrote:<br>
                  <blockquote style="border-left: 1px solid rgb(204,
                    204, 204); margin: 0px 0px 0px 0.8ex; padding-left:
                    1ex;" class="gmail_quote">
                    <div>Hi Ery,<br>
                    </div>
                    <div><br>
                    </div>
                    <div>Thanks for this explanation.  I have been
                      struggling with this topic as well as I do more
                      modeling in Energy Plus.  However, there is one
                      thing that you did not address above.  While
                      DOE2's LS-C report may not match exactly to what
                      systems are seeing as far as loads, it does give
                      an easily readable report which allows you to
                      check your inputs.  I review it quite often as a
                      quality control check for my models.  It also
                      allows me to target energy saving measures, and
                      helps me explain to clients why certain changes
                      might make sense for their building.  For example,
                      one client might be interested in increasing roof
                      insulation, but if they have a multi-story
                      building with a relatively small roof, and lots of
                      wall area, it makes more sense for them to reduce
                      thermal bridging in their wall construction.
                       Having a model-generated report makes this
                      process much faster for me.</div>
                    <div><br>
                    </div>
                    <div>Do you have any suggestions with regards to
                      Energy Plus of ways to achieve the above goals
                      with the currently available reports?</div>
                    <div><br>
                    </div>
                    <div>Thanks.</div>
                    <div><br>
                    </div>
                    <div>--</div>
                    <div>Karen</div>
                    <font color="#888888"><br>
                    </font>
                    <div class="gmail_quote">
                      <div>
                        <div>On Fri, Mar 4, 2011 at 12:26 PM, Ery
                          Djunaedy <span dir="ltr"><<a
                              moz-do-not-send="true"
                              href="mailto:ery.mailinglist@gmail.com"
                              target="_blank">ery.mailinglist@gmail.com</a>></span>
                          wrote:<br>
                        </div>
                      </div>
                      <blockquote style="border-left: 1px solid rgb(204,
                        204, 204); margin: 0px 0px 0px 0.8ex;
                        padding-left: 1ex;" class="gmail_quote">
                        <div>
                          <div>
                            <div text="#000000" bgcolor="#ffffff">Sandeep,<br>
                              <br>
                              This is what I call a legacy topic from
                              the DOE2 era. You better search the posts
                              in EnergyPlus support mailing list. Search
                              for "cooling load component", and you will
                              find an interesting discussion.<br>
                              <br>
                              In summary, you will not find a cooling
                              load component report in EnergyPlus nicely
                              formatted a-la LS-C report in eQuest/DOE2.<br>
                              <br>
                              If you try to match the total gains v.s.
                              the cooling load for every time step, then
                              you will be in for a long ride. Take the
                              solar radiation gain, for example. The
                              GAIN for a particular time step is not
                              necessarily converted into cooling LOAD at
                              the next time step. If your building is
                              thermally massive, then the delay plays an
                              important role and it could be hours
                              before the solar radiation GAIN becomes an
                              actual LOAD as seen by the thermostat. Do
                              not forget about this, if you try to match
                              the cooling load report with the total
                              gains.<br>
                              <br>
                              If you are talking about peak cooling
                              load, then you will need to focus on the
                              zone sizing report. Calculating the gains
                              component is easy because the schedule is
                              always 100% on. You just need to quantify
                              the ventilation load.<br>
                              <br>
                              Please note that the report suggested by
                              Paul below is the convection report. I
                              imagine that you would expect a conduction
                              report? EnergyPlus zones technically
                              cannot see conduction through opaque
                              surfaces, in the sense of A*U*DeltaT. They
                              can only see convection and radiation. In
                              fact, if you try to match A*U*DeltaT for
                              external wall with this report (Surface
                              Int Convection Heat Rate) then you will
                              have a hard time explaining. If you keep
                              this in mind, the differences can be
                              easily explained.<br>
                              <br>
                              Cheeers,<br>
                              <font color="#888888"><br>
                                Ery</font>
                              <div><br>
                                <br>
                                On 03/04/2011 07:07 AM, Paul Raftery
                                wrote:
                                <blockquote type="cite">
                                  <div>Hi Sandeep,</div>
                                  <div><br>
                                  </div>
                                  <div>A full list of the available
                                    output variables are given in the
                                    .rdd file (it is one of the files
                                    output from the simulation). Simply
                                    copy the relevant line from that
                                    file into your .idf (or .imf) file,
                                    rerun the simulation, and the new
                                    variable(s) will be output to the
                                    .csv and .eso files.</div>
                                  <div><br>
                                  </div>
                                  <div>e.g. Adding this line to the
                                    input file  will give you the
                                    convective heat gain from all
                                    interior surfaces in your model.</div>
                                  <div>Output:Variable,*,Surface Int
                                    Convection Heat Rate,hourly; !- Zone
                                    Average [W]</div>
                                  <div><br>
                                  </div>
                                  <div>Regards,</div>
                                  <div>Paul</div>
                                  <br>
                                  <div class="gmail_quote">On 4 March
                                    2011 13:50, Sandeep Kachhawa <span
                                      dir="ltr"><<a
                                        moz-do-not-send="true"
                                        href="mailto:sandeep.kachhawa@gmail.com"
                                        target="_blank">sandeep.kachhawa@gmail.com</a>></span>
                                    wrote:<br>
                                    <blockquote style="border-left: 1px
                                      solid rgb(204, 204, 204); margin:
                                      0pt 0pt 0pt 0.8ex; padding-left:
                                      1ex;" class="gmail_quote">
                                      <div>Dear All</div>
                                      <div> </div>
                                      <div>Can we get the individual
                                        break-up of cooling load in <b>EnergyPlus</b>?
                                        Internal loads (People,
                                        Equipment & Lighting),
                                        Infiltration loads and Window 
                                        gains are available but the <b>gians
                                          from Walls and Roof is
                                          missing. </b>Surely EnergyPlus

                                        does calculate all the above
                                        loads to size the Cooling
                                        Equipment but there is no such
                                        specific output.</div>
                                      <div> </div>
                                      <div>Regards</div>
                                      <div>Sandeep Kachhawa</div>
                                      <br>
                                    </blockquote>
                                  </div>
                                </blockquote>
                                <br>
                              </div>
                            </div>
                            <br>
                          </div>
                        </div>
                        <div>_______________________________________________<br>
                          Bldg-sim mailing list<br>
                          <a moz-do-not-send="true"
href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org"
                            target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
                          To unsubscribe from this mailing list send  a
                          blank message to <a moz-do-not-send="true"
                            href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG"
                            target="_blank">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
                          <br>
                        </div>
                      </blockquote>
                    </div>
                    <br>
                  </blockquote>
                </div>
                <br>
                <br>
              </div>
            </div>
          </div>
          <br>
          _______________________________________________<br>
          Bldg-sim mailing list<br>
          <a moz-do-not-send="true"
href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org"
            target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
          To unsubscribe from this mailing list send  a blank message to
          <a moz-do-not-send="true"
            href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
          <br>
        </blockquote>
      </div>
      <br>
    </blockquote>
    <br>
  </body>
</html>