<div>Thanks Ery.<br></div><div><br></div><div>It helps.  It's just slow.  What I love about LS-C is that it's fast.  Do you know of a way to get a grouped report for all walls within a particular zone.  So instead of having hourly output for every wall in a space, you would have one for each: exterior walls, interior walls, etc?  This would make reviewing these outputs much faster!</div>
<div><br></div><div>Thanks!</div><div><br></div><div>Karen</div><br><div class="gmail_quote">On Fri, Mar 4, 2011 at 6:52 PM, Ery Djunaedy <span dir="ltr"><<a href="mailto:ery.mailinglist@gmail.com">ery.mailinglist@gmail.com</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex;">

  

    
  
  <div bgcolor="#ffffff" text="#000000">
    <div>Hi Karen,</div>
    <div> </div>
    <div>Same here, I always use LS-C when I use eQuest. Just adding the
      ventilaton load, then you will have the peak load. Its always fun
      to compare this number with what the mechanical engineer has.</div>
    <div> </div>
    <div>I said earlier, in EnergyPlus it is not nicely formated like
      LS-C. It does not mean you cannot have it. You can force EPlus to
      show the numbers. The internal gains are the easy ones, the
      windows are also relatively easy, the last pieces are the opaque
      "conduction" and the ventilation load. Which is not difficult.<br>
      <br>
      The problem is what peak to report? You will have the peak of the
      total gains, which will happen at a different timestep then the
      peak of the cooling load. And these two, in turn is different with
      the zone sizing report.<br>
      <br>
      I personally use the zone sizing reports as the peak loads, and I
      will get all the details by running the designday run with
      schedules consistent with the design day schedule.<br>
      <br>
      Hope this helps,<br><font color="#888888">
      <br>
      Ery<br>
      <br>
    </font></div><div><div class="h5">
    <div class="gmail_quote">On Fri, Mar 4, 2011 at 12:00 PM, Karen
      Walkerman <span dir="ltr"><<a href="mailto:kwalkerman@gmail.com" target="_blank">kwalkerman@gmail.com</a>></span>
      wrote:<br>
      <blockquote style="border-left:1px solid rgb(204, 204, 204);margin:0px 0px 0px 0.8ex;padding-left:1ex" class="gmail_quote">
        <div>Hi Ery,<br>
        </div>
        <div><br>
        </div>
        <div>Thanks for this explanation.  I have been struggling with
          this topic as well as I do more modeling in Energy Plus.
           However, there is one thing that you did not address above.
           While DOE2's LS-C report may not match exactly to what
          systems are seeing as far as loads, it does give an easily
          readable report which allows you to check your inputs.  I
          review it quite often as a quality control check for my
          models.  It also allows me to target energy saving measures,
          and helps me explain to clients why certain changes might make
          sense for their building.  For example, one client might be
          interested in increasing roof insulation, but if they have a
          multi-story building with a relatively small roof, and lots of
          wall area, it makes more sense for them to reduce thermal
          bridging in their wall construction.  Having a model-generated
          report makes this process much faster for me.</div>
        <div><br>
        </div>
        <div>Do you have any suggestions with regards to Energy Plus of
          ways to achieve the above goals with the currently available
          reports?</div>
        <div><br>
        </div>
        <div>Thanks.</div>
        <div><br>
        </div>
        <div>--</div>
        <div>Karen</div>
        <font color="#888888"><br>
        </font>
        <div class="gmail_quote">
          <div>
            <div>On Fri, Mar 4, 2011 at 12:26 PM, Ery
              Djunaedy <span dir="ltr"><<a href="mailto:ery.mailinglist@gmail.com" target="_blank">ery.mailinglist@gmail.com</a>></span>
              wrote:<br>
            </div>
          </div>
          <blockquote style="border-left:1px solid rgb(204, 204, 204);margin:0px 0px 0px 0.8ex;padding-left:1ex" class="gmail_quote">
            <div>
              <div>
                <div text="#000000" bgcolor="#ffffff">Sandeep,<br>
                  <br>
                  This is what I call a legacy topic from the DOE2 era.
                  You better search the posts in EnergyPlus support
                  mailing list. Search for "cooling load component", and
                  you will find an interesting discussion.<br>
                  <br>
                  In summary, you will not find a cooling load component
                  report in EnergyPlus nicely formatted a-la LS-C report
                  in eQuest/DOE2.<br>
                  <br>
                  If you try to match the total gains v.s. the cooling
                  load for every time step, then you will be in for a
                  long ride. Take the solar radiation gain, for example.
                  The GAIN for a particular time step is not necessarily
                  converted into cooling LOAD at the next time step. If
                  your building is thermally massive, then the delay
                  plays an important role and it could be hours before
                  the solar radiation GAIN becomes an actual LOAD as
                  seen by the thermostat. Do not forget about this, if
                  you try to match the cooling load report with the
                  total gains.<br>
                  <br>
                  If you are talking about peak cooling load, then you
                  will need to focus on the zone sizing report.
                  Calculating the gains component is easy because the
                  schedule is always 100% on. You just need to quantify
                  the ventilation load.<br>
                  <br>
                  Please note that the report suggested by Paul below is
                  the convection report. I imagine that you would expect
                  a conduction report? EnergyPlus zones technically
                  cannot see conduction through opaque surfaces, in the
                  sense of A*U*DeltaT. They can only see convection and
                  radiation. In fact, if you try to match A*U*DeltaT for
                  external wall with this report (Surface Int Convection
                  Heat Rate) then you will have a hard time explaining.
                  If you keep this in mind, the differences can be
                  easily explained.<br>
                  <br>
                  Cheeers,<br>
                  <font color="#888888"><br>
                    Ery</font>
                  <div><br>
                    <br>
                    On 03/04/2011 07:07 AM, Paul Raftery wrote:
                    <blockquote type="cite">
                      <div>Hi Sandeep,</div>
                      <div><br>
                      </div>
                      <div>A full list of the available output variables
                        are given in the .rdd file (it is one of the
                        files output from the simulation). Simply copy
                        the relevant line from that file into your .idf
                        (or .imf) file, rerun the simulation, and the
                        new variable(s) will be output to the .csv and
                        .eso files.</div>
                      <div><br>
                      </div>
                      <div>e.g. Adding this line to the input file  will
                        give you the convective heat gain from all
                        interior surfaces in your model.</div>
                      <div>Output:Variable,*,Surface Int Convection Heat
                        Rate,hourly; !- Zone Average [W]</div>
                      <div><br>
                      </div>
                      <div>Regards,</div>
                      <div>Paul</div>
                      <br>
                      <div class="gmail_quote">On 4 March 2011 13:50,
                        Sandeep Kachhawa <span dir="ltr"><<a href="mailto:sandeep.kachhawa@gmail.com" target="_blank">sandeep.kachhawa@gmail.com</a>></span>
                        wrote:<br>
                        <blockquote style="border-left:1px solid rgb(204, 204, 204);margin:0pt 0pt 0pt 0.8ex;padding-left:1ex" class="gmail_quote">
                          <div>Dear All</div>
                          <div> </div>
                          <div>Can we get the individual break-up of
                            cooling load in <b>EnergyPlus</b>? Internal
                            loads (People, Equipment & Lighting),
                            Infiltration loads and Window  gains are
                            available but the <b>gians from Walls and
                              Roof is missing. </b>Surely EnergyPlus
                            does calculate all the above loads to size
                            the Cooling Equipment but there is no such
                            specific output.</div>
                          <div> </div>
                          <div>Regards</div>
                          <div>Sandeep Kachhawa</div>
                          <br>
                        </blockquote>
                      </div>
                    </blockquote>
                    <br>
                  </div>
                </div>
                <br>
              </div>
            </div>
            <div>_______________________________________________<br>
              Bldg-sim mailing list<br>
              <a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
              To unsubscribe from this mailing list send  a blank
              message to <a href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
              <br>
            </div>
          </blockquote>
        </div>
        <br>
      </blockquote>
    </div>
    <br>
    <br>
  </div></div></div>

<br>_______________________________________________<br>
Bldg-sim mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br>