<div>Hello Rohini, </div>
<div> </div>
<div>My understanding is, since zone 2A is cooling dominated area, ERV for cooling (at least 50%) should be included whereas that for heating can be ignored in the baseline model when you have >5000cfm and 70% fulfilled in your design.  </div>
<div><font face="comic sans ms,sans-serif"></font> </div>
<div><font face="comic sans ms,sans-serif">  Regards, </font></div>
<div><font face="comic sans ms,sans-serif"></font> </div>
<div><font face="comic sans ms,sans-serif">Cheney</font></div>
<div><font face="comic sans ms,sans-serif"></font> </div>
<div><font face="comic sans ms,sans-serif">LinkedIN @ </font><a href="http://ca.linkedin.com/pub/yu-cheney-chen/27/637/72b" target="_blank"><font face="comic sans ms,sans-serif">http://ca.linkedin.com/pub/yu-cheney-chen/27/637/72b</font></a><font face="comic sans ms,sans-serif"> </font></div>
<br>