<span style="font-size: 10pt;">Hi Will,</span><b><span style="font-size: 10pt;"><br><br></span></b><span style="font-size: 10pt;">I think your answer is here:</span><b><span style="font-size: 10pt;"><br><br>The fenestration area in the baseline 
building shall be equal to the fenestration area in the proposed 
building or 40% of the exterior wall, whichever is less.</span></b><br><br>Based on your table you need to reduce the window area to be 40% of the overall wall area, making it a band as described, except for the North wall with 0% glass as it is already less than 40%.<br>
<br>Happy Holidays!<br><br>Carol<br><br><div class="gmail_quote">On Wed, Dec 22, 2010 at 8:39 AM, Will Mak <span dir="ltr"><<a href="mailto:wmak@epsteinglobal.com">wmak@epsteinglobal.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin: 0pt 0pt 0pt 0.8ex; border-left: 1px solid rgb(204, 204, 204); padding-left: 1ex;">

<div link="blue" vlink="purple" lang="EN-US"><div><p class="MsoNormal"><span style="font-size: 10pt;">Hi all,</span></p><p class="MsoNormal"><span style="font-size: 10pt;"> </span></p><p class="MsoNormal"><span style="font-size: 10pt;">I am working on a project that has a large amount of glass. ASHRAE 90.1-2007 states this about baseline modeling for glass:</span></p>
<p class="MsoNormal"><span style="font-size: 10pt;"> </span></p><p class="MsoNormal"><b><span style="font-size: 10pt;">The fenestration area in the baseline building shall be equal to the fenestration area in the proposed building or 40% of the exterior wall, whichever is less. If it is necessary to reduce window area in the baseline building, then corresponding increases are made in the opaque walls such that the gross exterior wall area is unchanged between the proposed building and the baseline building.</span></b></p>
<p class="MsoNormal"><b><span style="font-size: 10pt;"> </span></b></p><p class="MsoNormal"><b><span style="font-size: 10pt;">Fenestration area in the baseline building shall be distributed among the thermal blocks and around the building in a uniform manner. In each thermal block, the fenestration area shall be equal to the window wall ratio for the baseline building (the maximum of 40% or the proposed building WWR) multiplied times the exterior wall area for the thermal block. If the thermal block has more than one exterior wall, window area is placed proportionally on each. </span></b></p>
<p class="MsoNormal"><b><span style="font-size: 10pt;"> </span></b></p><p class="MsoNormal"><b><span style="font-size: 10pt;">The window area is positioned in continuous horizontal bands on each exterior wall, although the configuration of window area on each wall is not significant since neither daylighting or self shading from the building is modeled. See Figure G-D. </span></b></p>
<p class="MsoNormal"><b><span style="font-size: 10pt;"> </span></b></p><p class="MsoNormal"><b><span style="font-size: 10pt;">While the prescriptive envelope requirements provide an exception for street-level, street-side vertical fenestration (e.g., store display windows), the building performance rating method does not. Window area in the baseline building is always determined as described above.</span></b></p>
<p class="MsoNormal"><b><span style="font-size: 10pt;"> </span></b></p><p class="MsoNormal"><span style="font-size: 10pt;">Based on the wordage above, I must develop the baseline model with either the same glass areas as the proposed building (essentially copying the proposed model and just updating U-values, etc.) or 40% of the exterior wall, whichever is smaller. Since I have roughly 60% of glazing, I will have to redistribute the glass into continuous horizontal bands on each exterior wall, similar to how ASHRAE 90.1-2004. However, as I began to look at the glass % of each exterior wall, I ran into a problem:</span></p>
<p class="MsoNormal"><span style="font-size: 10pt;"> </span></p><table style="border-collapse: collapse;" border="0" cellpadding="0" cellspacing="0"><tbody><tr style="min-height: 15pt;"><td style="border: 1pt solid windowtext; padding: 0in 5.4pt; min-height: 15pt;" nowrap valign="bottom">
<p class="MsoNormal" style="text-align: center;" align="center"><b><span style="font-size: 10pt; color: black;">Wall</span></b></p></td><td style="border-width: 1pt 1pt 1pt medium; border-style: solid solid solid none; border-color: windowtext windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 15pt;" nowrap valign="bottom">
<p class="MsoNormal" style="text-align: center;" align="center"><b><span style="font-size: 10pt; color: black;">Window SQ FT</span></b></p></td><td style="border-width: 1pt 1pt 1pt medium; border-style: solid solid solid none; border-color: windowtext windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 15pt;" nowrap valign="bottom">
<p class="MsoNormal" style="text-align: center;" align="center"><b><span style="font-size: 10pt; color: black;">Wall SQ FT</span></b></p></td><td style="border-width: 1pt 1pt 1pt medium; border-style: solid solid solid none; border-color: windowtext windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 15pt;" nowrap valign="bottom">
<p class="MsoNormal" style="text-align: center;" align="center"><b><span style="font-size: 10pt; color: black;">Total SQ FT</span></b></p></td><td style="border-width: 1pt 1pt 1pt medium; border-style: solid solid solid none; border-color: windowtext windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 15pt;" nowrap valign="bottom">
<p class="MsoNormal" style="text-align: center;" align="center"><b><span style="font-size: 10pt; color: black;">Window %</span></b></p></td></tr><tr style="min-height: 15pt;"><td style="border-width: medium 1pt 1pt; border-style: none solid solid; border-color: -moz-use-text-color windowtext windowtext; padding: 0in 5.4pt; min-height: 15pt;" nowrap valign="bottom">
<p class="MsoNormal"><span style="font-size: 10pt; color: black;">North</span></p></td><td style="border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 15pt;" nowrap valign="bottom">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt; color: black;">10727.76</span></p></td><td style="border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 15pt;" nowrap valign="bottom">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt; color: black;">8485.95</span></p></td><td style="border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 15pt;" nowrap valign="bottom">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt; color: black;">19213.71</span></p></td><td style="border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 15pt;" nowrap valign="bottom">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt; color: black;">55.83%</span></p></td></tr><tr style="min-height: 15pt;"><td style="border-width: medium 1pt 1pt; border-style: none solid solid; border-color: -moz-use-text-color windowtext windowtext; padding: 0in 5.4pt; min-height: 15pt;" nowrap valign="bottom">
<p class="MsoNormal"><span style="font-size: 10pt; color: black;">North-East</span></p></td><td style="border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 15pt;" nowrap valign="bottom">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt; color: black;">1812.26</span></p></td><td style="border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 15pt;" nowrap valign="bottom">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt; color: black;">2272.83</span></p></td><td style="border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 15pt;" nowrap valign="bottom">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt; color: black;">4085.09</span></p></td><td style="border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 15pt;" nowrap valign="bottom">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt; color: black;">44.36%</span></p></td></tr><tr style="min-height: 15pt;"><td style="border-width: medium 1pt 1pt; border-style: none solid solid; border-color: -moz-use-text-color windowtext windowtext; padding: 0in 5.4pt; min-height: 15pt;" nowrap valign="bottom">
<p class="MsoNormal"><span style="font-size: 10pt; color: black;">East</span></p></td><td style="border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 15pt;" nowrap valign="bottom">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt; color: black;">2645.52</span></p></td><td style="border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 15pt;" nowrap valign="bottom">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt; color: black;">1846.83</span></p></td><td style="border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 15pt;" nowrap valign="bottom">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt; color: black;">4492.35</span></p></td><td style="border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 15pt;" nowrap valign="bottom">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt; color: black;">58.89%</span></p></td></tr><tr style="min-height: 15pt;"><td style="border-width: medium 1pt 1pt; border-style: none solid solid; border-color: -moz-use-text-color windowtext windowtext; padding: 0in 5.4pt; min-height: 15pt;" nowrap valign="bottom">
<p class="MsoNormal"><span style="font-size: 10pt; color: black;">South-East</span></p></td><td style="border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 15pt;" nowrap valign="bottom">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt; color: black;">1683.46</span></p></td><td style="border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 15pt;" nowrap valign="bottom">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt; color: black;">1222.87</span></p></td><td style="border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 15pt;" nowrap valign="bottom">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt; color: black;">2906.33</span></p></td><td style="border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 15pt;" nowrap valign="bottom">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt; color: black;">57.92%</span></p></td></tr><tr style="min-height: 15pt;"><td style="border-width: medium 1pt 1pt; border-style: none solid solid; border-color: -moz-use-text-color windowtext windowtext; padding: 0in 5.4pt; min-height: 15pt;" nowrap valign="bottom">
<p class="MsoNormal"><span style="font-size: 10pt; color: black;">South</span></p></td><td style="border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 15pt;" nowrap valign="bottom">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt; color: black;">12595.36</span></p></td><td style="border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 15pt;" nowrap valign="bottom">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt; color: black;">3958.92</span></p></td><td style="border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 15pt;" nowrap valign="bottom">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt; color: black;">16554.28</span></p></td><td style="border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 15pt;" nowrap valign="bottom">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt; color: black;">76.09%</span></p></td></tr><tr style="min-height: 15pt;"><td style="border-width: medium 1pt 1pt; border-style: none solid solid; border-color: -moz-use-text-color windowtext windowtext; padding: 0in 5.4pt; min-height: 15pt;" nowrap valign="bottom">
<p class="MsoNormal"><span style="font-size: 10pt; color: black;">South-West</span></p></td><td style="border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 15pt;" nowrap valign="bottom">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt; color: black;">623.46</span></p></td><td style="border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 15pt;" nowrap valign="bottom">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt; color: black;">829.56</span></p></td><td style="border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 15pt;" nowrap valign="bottom">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt; color: black;">1453.02</span></p></td><td style="border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 15pt;" nowrap valign="bottom">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt; color: black;">42.91%</span></p></td></tr><tr style="min-height: 15pt;"><td style="border-width: medium 1pt 1pt; border-style: none solid solid; border-color: -moz-use-text-color windowtext windowtext; padding: 0in 5.4pt; min-height: 15pt;" nowrap valign="bottom">
<p class="MsoNormal"><span style="font-size: 10pt; color: black;">West</span></p></td><td style="border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 15pt;" nowrap valign="bottom">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt; color: black;">3282.3</span></p></td><td style="border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 15pt;" nowrap valign="bottom">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt; color: black;">2924.38</span></p></td><td style="border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 15pt;" nowrap valign="bottom">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt; color: black;">6206.68</span></p></td><td style="border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 15pt;" nowrap valign="bottom">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt; color: black;">52.88%</span></p></td></tr><tr style="min-height: 15pt;"><td style="border-width: medium 1pt 1pt; border-style: none solid solid; border-color: -moz-use-text-color windowtext windowtext; padding: 0in 5.4pt; min-height: 15pt;" nowrap valign="bottom">
<p class="MsoNormal"><span style="font-size: 10pt; color: black;">North</span></p></td><td style="border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 15pt;" nowrap valign="bottom">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt; color: black;">0</span></p></td><td style="border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 15pt;" nowrap valign="bottom">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt; color: black;">104.26</span></p></td><td style="border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 15pt;" nowrap valign="bottom">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt; color: black;">104.26</span></p></td><td style="border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 15pt;" nowrap valign="bottom">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt; color: black;">0.00%</span></p></td></tr><tr style="min-height: 15pt;"><td style="border-width: medium 1pt 1pt; border-style: none solid solid; border-color: -moz-use-text-color windowtext windowtext; padding: 0in 5.4pt; min-height: 15pt;" nowrap valign="bottom">
<p class="MsoNormal"><span style="font-size: 10pt; color: black;">Total</span></p></td><td style="border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 15pt;" nowrap valign="bottom">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt; color: black;">33370.12</span></p></td><td style="border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 15pt;" nowrap valign="bottom">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt; color: black;">21645.6</span></p></td><td style="border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 15pt;" nowrap valign="bottom">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt; color: black;">55015.72</span></p></td><td style="border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 15pt;" nowrap valign="bottom">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt; color: black;">60.66%</span></p></td></tr></tbody></table><p class="MsoNormal"><span style="font-size: 10pt;"> </span></p><p class="MsoNormal">
<span style="font-size: 10pt;">There is not enough exterior wall space to redistribute glazing to drop the percentages for each wall to 40%. Do I just reduce each wall to 40% glazing with continuous horizontal bands?</span></p>
<p class="MsoNormal"><span style="font-size: 10pt;"> </span></p><p class="MsoNormal"><span style="font-size: 10pt;">Thanks!</span></p><p class="MsoNormal"><span style="font-size: 10pt;"> </span></p><p class="MsoNormal"><b><span style="font-size: 14pt; color: rgb(199, 91, 18);">William Mak, LEED Green Associate</span></b><span style="font-size: 9pt; color: rgb(31, 73, 125);"><br>
</span><span style="font-size: 8pt; color: black;">Mechanical Design Engineer</span><span style="font-size: 9pt; color: black;"><br></span><span style="font-size: 9pt; color: rgb(31, 73, 125);"><br></span><b><span style="font-size: 10pt; color: rgb(199, 91, 18);">EPSTEIN</span></b><span style="font-size: 9pt; color: rgb(31, 73, 125);"><br>
</span><span style="font-size: 8pt; color: black;">Architecture<br>Interiors<br>Engineering<br>Construction<br><br>600 West Fulton Street<br>Chicago, Illinois 60661-1259<br><br>D: (312) 429-8116<br>F: (312) 559-1217<br>E:</span><span style="font-size: 8pt; color: rgb(0, 112, 192);"> <a href="mailto:wmak@epsteinglobal.com" target="_blank">wmak@epsteinglobal.com</a></span><span style="font-size: 8pt; color: black;"><br>
W:</span><span style="font-size: 8pt; color: rgb(199, 91, 18);"> <a href="http://www.epsteinglobal.com/" target="_blank"><span style="color: rgb(199, 91, 18);">www.epsteinglobal.com</span></a></span><span style="font-size: 9pt; color: black;"><br>
<br></span><span style="font-size: 10pt; font-family: Webdings; color: rgb(0, 176, 80);">รพ</span><span style="font-size: 8pt; color: black;"> Epstein is a firm believer in sustainability. We ask that you please consider the environment before printing this e-mail.</span></p>
<p class="MsoNormal"> </p></div></div><br>_______________________________________________<br>
Bldg-sim mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br><br clear="all"><br>-- <br>Carol Gardner PE<br>
<div style="visibility: hidden; left: -5000px;" id="avg_ls_inline_popup"></div><style type="text/css">#avg_ls_inline_popup{position: absolute;z-index: 9999;padding: 0px 0px;margin-left: 0px;margin-top: 0px;overflow: hidden;word-wrap: break-word;color: black;font-size: 10px;text-align: left;line-height: 130%;}</style>