<html xmlns:v="urn:schemas-microsoft-com:vml" xmlns:o="urn:schemas-microsoft-com:office:office" xmlns:w="urn:schemas-microsoft-com:office:word" xmlns:x="urn:schemas-microsoft-com:office:excel" xmlns:p="urn:schemas-microsoft-com:office:powerpoint" xmlns:a="urn:schemas-microsoft-com:office:access" xmlns:dt="uuid:C2F41010-65B3-11d1-A29F-00AA00C14882" xmlns:s="uuid:BDC6E3F0-6DA3-11d1-A2A3-00AA00C14882" xmlns:rs="urn:schemas-microsoft-com:rowset" xmlns:z="#RowsetSchema" xmlns:b="urn:schemas-microsoft-com:office:publisher" xmlns:ss="urn:schemas-microsoft-com:office:spreadsheet" xmlns:c="urn:schemas-microsoft-com:office:component:spreadsheet" xmlns:odc="urn:schemas-microsoft-com:office:odc" xmlns:oa="urn:schemas-microsoft-com:office:activation" xmlns:html="http://www.w3.org/TR/REC-html40" xmlns:q="http://schemas.xmlsoap.org/soap/envelope/" xmlns:rtc="http://microsoft.com/officenet/conferencing" xmlns:D="DAV:" xmlns:Repl="http://schemas.microsoft.com/repl/" xmlns:mt="http://schemas.microsoft.com/sharepoint/soap/meetings/" xmlns:x2="http://schemas.microsoft.com/office/excel/2003/xml" xmlns:ppda="http://www.passport.com/NameSpace.xsd" xmlns:ois="http://schemas.microsoft.com/sharepoint/soap/ois/" xmlns:dir="http://schemas.microsoft.com/sharepoint/soap/directory/" xmlns:ds="http://www.w3.org/2000/09/xmldsig#" xmlns:dsp="http://schemas.microsoft.com/sharepoint/dsp" xmlns:udc="http://schemas.microsoft.com/data/udc" xmlns:xsd="http://www.w3.org/2001/XMLSchema" xmlns:sub="http://schemas.microsoft.com/sharepoint/soap/2002/1/alerts/" xmlns:ec="http://www.w3.org/2001/04/xmlenc#" xmlns:sp="http://schemas.microsoft.com/sharepoint/" xmlns:sps="http://schemas.microsoft.com/sharepoint/soap/" xmlns:xsi="http://www.w3.org/2001/XMLSchema-instance" xmlns:udcs="http://schemas.microsoft.com/data/udc/soap" xmlns:udcxf="http://schemas.microsoft.com/data/udc/xmlfile" xmlns:udcp2p="http://schemas.microsoft.com/data/udc/parttopart" xmlns:wf="http://schemas.microsoft.com/sharepoint/soap/workflow/" xmlns:dsss="http://schemas.microsoft.com/office/2006/digsig-setup" xmlns:dssi="http://schemas.microsoft.com/office/2006/digsig" xmlns:mdssi="http://schemas.openxmlformats.org/package/2006/digital-signature" xmlns:mver="http://schemas.openxmlformats.org/markup-compatibility/2006" xmlns:m="http://schemas.microsoft.com/office/2004/12/omml" xmlns:mrels="http://schemas.openxmlformats.org/package/2006/relationships" xmlns:spwp="http://microsoft.com/sharepoint/webpartpages" xmlns:ex12t="http://schemas.microsoft.com/exchange/services/2006/types" xmlns:ex12m="http://schemas.microsoft.com/exchange/services/2006/messages" xmlns:pptsl="http://schemas.microsoft.com/sharepoint/soap/SlideLibrary/" xmlns:spsl="http://microsoft.com/webservices/SharePointPortalServer/PublishedLinksService" xmlns:Z="urn:schemas-microsoft-com:" xmlns:st="" xmlns="http://www.w3.org/TR/REC-html40"><head><meta http-equiv=Content-Type content="text/html; charset=utf-8"><meta name=Generator content="Microsoft Word 12 (filtered medium)"><!--[if !mso]><style>v\:* {behavior:url(#default#VML);}
o\:* {behavior:url(#default#VML);}
w\:* {behavior:url(#default#VML);}
.shape {behavior:url(#default#VML);}
</style><![endif]--><style><!--
/* Font Definitions */
@font-face
{font-family:Wingdings;
panose-1:5 0 0 0 0 0 0 0 0 0;}
@font-face
{font-family:Wingdings;
panose-1:5 0 0 0 0 0 0 0 0 0;}
@font-face
{font-family:Calibri;
panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
{font-family:Tahoma;
panose-1:2 11 6 4 3 5 4 4 2 4;}
@font-face
{font-family:Verdana;
panose-1:2 11 6 4 3 5 4 4 2 4;}
@font-face
{font-family:"Stylus BT";
panose-1:2 14 4 2 2 2 6 2 3 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
{margin:0in;
margin-bottom:.0001pt;
font-size:12.0pt;
font-family:"Times New Roman","serif";
color:black;}
a:link, span.MsoHyperlink
{mso-style-priority:99;
color:blue;
text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
{mso-style-priority:99;
color:purple;
text-decoration:underline;}
p.MsoAcetate, li.MsoAcetate, div.MsoAcetate
{mso-style-priority:99;
mso-style-link:"Balloon Text Char";
margin:0in;
margin-bottom:.0001pt;
font-size:8.0pt;
font-family:"Tahoma","sans-serif";
color:black;}
p.MsoListParagraph, li.MsoListParagraph, div.MsoListParagraph
{mso-style-priority:34;
margin-top:0in;
margin-right:0in;
margin-bottom:0in;
margin-left:.5in;
margin-bottom:.0001pt;
font-size:12.0pt;
font-family:"Times New Roman","serif";
color:black;}
span.BalloonTextChar
{mso-style-name:"Balloon Text Char";
mso-style-priority:99;
mso-style-link:"Balloon Text";
font-family:"Tahoma","sans-serif";
color:black;}
span.spelle
{mso-style-name:spelle;}
span.grame
{mso-style-name:grame;}
span.EmailStyle21
{mso-style-type:personal;
font-family:"Calibri","sans-serif";
color:#1F497D;}
span.EmailStyle22
{mso-style-type:personal;
font-family:"Calibri","sans-serif";
color:#1F497D;}
span.EmailStyle23
{mso-style-type:personal-reply;
font-family:"Calibri","sans-serif";
color:#1F497D;}
.MsoChpDefault
{mso-style-type:export-only;
font-size:10.0pt;}
@page WordSection1
{size:8.5in 11.0in;
margin:1.0in 1.0in 1.0in 1.0in;}
div.WordSection1
{page:WordSection1;}
/* List Definitions */
@list l0
{mso-list-id:463699336;
mso-list-type:hybrid;
mso-list-template-ids:473045926 67698689 67698691 67698693 67698689 67698691 67698693 67698689 67698691 67698693;}
@list l0:level1
{mso-level-number-format:bullet;
mso-level-text:;
mso-level-tab-stop:none;
mso-level-number-position:left;
text-indent:-.25in;
font-family:Symbol;}
@list l0:level2
{mso-level-number-format:bullet;
mso-level-text:o;
mso-level-tab-stop:none;
mso-level-number-position:left;
text-indent:-.25in;
font-family:"Courier New";}
@list l0:level3
{mso-level-number-format:bullet;
mso-level-text:;
mso-level-tab-stop:none;
mso-level-number-position:left;
text-indent:-.25in;
font-family:Wingdings;}
ol
{margin-bottom:0in;}
ul
{margin-bottom:0in;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]--></head><body bgcolor=white lang=EN-US link=blue vlink=purple><div class=WordSection1><p class=MsoNormal><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'>Nick,<o:p></o:p></span></p><p class=MsoNormal><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'><o:p> </o:p></span></p><p class=MsoNormal><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'>Thank you for the response. My first energy modeling experience was with eQuest, but have been using Trane’s TRACE 700 more extensively. In addition to the bldg-sim lists, the TRACE support is an excellent resource for those using the software, especially when it comes to unmet hours.<o:p></o:p></span></p><p class=MsoNormal><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'><o:p> </o:p></span></p><p class=MsoNormal><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'>As you mention, and as I was alluding to in my third paragraph (starting with ‘Before taking this step,’), there are certainly other areas that should be addressed prior to adjusting the cooling and heating capacities. I was not trying to cover all of them and did not want to get too in depth, as there are numerous areas that could be contributing to the unmet load hours and a review of the model would be necessary to determine what changes must be made to remedy the model. I’d like to note that I said the model and not the unmet hours. As you and Carol have illustrated, I fully agree that we aren’t supposed to be trying to manipulate the model to give us our desired outcome, but rather provide an accurate model. I do not think anyone should be taking liberty with the capacities to such extremes just to meet the requirements for unmet load hours. I even scratched my head the first time I read through that section and thought, “well what’s the point?”<o:p></o:p></span></p><p class=MsoNormal><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'><o:p> </o:p></span></p><p class=MsoNormal><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'>My response wasn’t meant to suggest that modelers wildly vary cooling and heating capacities to obtain their desired results, but to clarify that Neeraj’s comment (copied below) was in fact contrary to what ASHRAE requires in Appendix G. Perhaps a few disclaimers were in order </span><span style='font-size:11.0pt;font-family:Wingdings;color:#1F497D'>J</span><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'><o:p></o:p></span></p><p class=MsoNormal><span style='font-size:10.0pt;font-family:"Arial","sans-serif"'>Correct me if I am wrong but on the contrary I think that ASHARE baseline PRM fixes the cooling and heating capacities to 1.15 and 1.25 respectively and the user is allowed to bump up the supply CFM in increments if necessary.<o:p></o:p></span></p><p class=MsoNormal><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'><o:p> </o:p></span></p><p class=MsoNormal><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'>In conclusion, I offer these bullet points:<o:p></o:p></span></p><p class=MsoListParagraph style='text-indent:-.25in;mso-list:l0 level1 lfo1'><![if !supportLists]><span style='font-size:11.0pt;font-family:Symbol;color:#1F497D'><span style='mso-list:Ignore'>·<span style='font:7.0pt "Times New Roman"'> </span></span></span><![endif]><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'>Design airflow rates are <b><u>set</u></b> using a 20-degree delta T between supply air and room space<o:p></o:p></span></p><p class=MsoListParagraph style='margin-left:1.0in;text-indent:-.25in;mso-list:l0 level2 lfo1'><![if !supportLists]><span style='font-size:11.0pt;font-family:"Courier New";color:#1F497D'><span style='mso-list:Ignore'>o<span style='font:7.0pt "Times New Roman"'> </span></span></span><![endif]><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'>These shall not be adjusted to “fix” unmet hours<o:p></o:p></span></p><p class=MsoListParagraph style='text-indent:-.25in;mso-list:l0 level1 lfo1'><![if !supportLists]><span style='font-size:11.0pt;font-family:Symbol;color:#1F497D'><span style='mso-list:Ignore'>·<span style='font:7.0pt "Times New Roman"'> </span></span></span><![endif]><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'>Baseline cooling and heating capacities are initially set to 115% and 125% respectively<o:p></o:p></span></p><p class=MsoListParagraph style='margin-left:1.0in;text-indent:-.25in;mso-list:l0 level2 lfo1'><![if !supportLists]><span style='font-size:11.0pt;font-family:"Courier New";color:#1F497D'><span style='mso-list:Ignore'>o<span style='font:7.0pt "Times New Roman"'> </span></span></span><![endif]><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'>These may be adjusted incrementally, but should not be relied upon to “fix” a poorly produced model. In fact, their adjustment should be considered last, after all other approaches have failed.<o:p></o:p></span></p><p class=MsoListParagraph style='text-indent:-.25in;mso-list:l0 level1 lfo1'><![if !supportLists]><span style='font-size:11.0pt;font-family:Symbol;color:#1F497D'><span style='mso-list:Ignore'>·<span style='font:7.0pt "Times New Roman"'> </span></span></span><![endif]><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'>It is important to understand what an unmet hour is and why they occur<o:p></o:p></span></p><p class=MsoListParagraph style='margin-left:1.0in;text-indent:-.25in;mso-list:l0 level2 lfo1'><![if !supportLists]><span style='font-size:11.0pt;font-family:"Courier New";color:#1F497D'><span style='mso-list:Ignore'>o<span style='font:7.0pt "Times New Roman"'> </span></span></span><![endif]><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'>It is of even greater importance to remedy the cause of the unmet hour rather than “fudging” the numbers<o:p></o:p></span></p><p class=MsoListParagraph style='margin-left:1.0in;text-indent:-.25in;mso-list:l0 level2 lfo1'><![if !supportLists]><span style='font-size:11.0pt;font-family:"Courier New";color:#1F497D'><span style='mso-list:Ignore'>o<span style='font:7.0pt "Times New Roman"'> </span></span></span><![endif]><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'>Refer to your software’s Building Temperature Profile report, if such a report exists, to help find the source (space, system, etc) of the unmet hours<o:p></o:p></span></p><p class=MsoListParagraph style='margin-left:1.0in;text-indent:-.25in;mso-list:l0 level2 lfo1'><![if !supportLists]><span style='font-size:11.0pt;font-family:"Courier New";color:#1F497D'><span style='mso-list:Ignore'>o<span style='font:7.0pt "Times New Roman"'> </span></span></span><![endif]><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'>Thermostat Drift Points and Utilization Schedules have been primary culprits<o:p></o:p></span></p><p class=MsoListParagraph style='margin-left:1.5in;text-indent:-.25in;mso-list:l0 level3 lfo1'><![if !supportLists]><span style='font-size:11.0pt;font-family:Wingdings;color:#1F497D'><span style='mso-list:Ignore'>§<span style='font:7.0pt "Times New Roman"'> </span></span></span><![endif]><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'>Other areas affecting unmet hours include but are not limited to the following: Thermostat placement, fan cycle operation, optimum starts, building envelope entries, Ventilation (outside air) schedules<o:p></o:p></span></p><p class=MsoNormal><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'><o:p> </o:p></span></p><p class=MsoNormal><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'>Happy modeling!<o:p></o:p></span></p><p class=MsoNormal><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'><o:p> </o:p></span></p><div><p class=MsoNormal><b><span style='font-size:8.0pt;font-family:"Verdana","sans-serif"'>Michael M. Collarin, EIT, LEED AP BD+C </span></b><b><span style='font-size:7.0pt;font-family:"Verdana","sans-serif";color:green'>|</span></b><b><span style='font-size:7.0pt;font-family:"Calibri","sans-serif";color:green'> </span></b><b><span style='font-size:7.0pt;font-family:"Verdana","sans-serif";color:green'>Elm Engineering, Inc. | 212 S Tryon St | Suite 1375 | Charlotte, NC 28281</span></b><b><span style='font-size:7.0pt;font-family:"Arial","sans-serif";color:green'><o:p></o:p></span></b></p><p class=MsoNormal><span style='font-size:8.0pt;font-family:"Verdana","sans-serif";color:green;letter-spacing:.9pt'>PHONE 704-335-0396 Ext. 108</span><span style='font-size:8.0pt;font-family:"Verdana","sans-serif";color:green'>|<b> </b>FAX 704-335-0399<b> </b>|</span><b><span style='font-size:8.0pt;font-family:"Verdana","sans-serif";color:gray'> </span></b><span style='font-size:8.0pt;font-family:"Verdana","sans-serif";color:gray'><a href="http://www.elmengr.com/" title="blocked::http://www.elmengr.com/"><span style='font-family:"Arial","sans-serif"'>www.elmengr.com</span></a></span><span style='color:#1F497D'><o:p></o:p></span></p></div><p class=MsoNormal><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'><o:p> </o:p></span></p><div><div style='border:none;border-top:solid #B5C4DF 1.0pt;padding:3.0pt 0in 0in 0in'><p class=MsoNormal><b><span style='font-size:10.0pt;font-family:"Tahoma","sans-serif";color:windowtext'>From:</span></b><span style='font-size:10.0pt;font-family:"Tahoma","sans-serif";color:windowtext'> Nick Caton [mailto:ncaton@smithboucher.com] <br><b>Sent:</b> Friday, November 19, 2010 5:57 PM<br><b>To:</b> Michael Collarin; Nearedge; cjaigath@yahoo.com<br><b>Cc:</b> bldg-sim@lists.onebuilding.org<br><b>Subject:</b> RE: [Bldg-sim] Adjusting Capacity for Unmet Cooling<o:p></o:p></span></p></div></div><p class=MsoNormal><o:p> </o:p></p><p class=MsoNormal><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'>Hi Michael,<o:p></o:p></span></p><p class=MsoNormal><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'><o:p> </o:p></span></p><p class=MsoNormal><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'>I’d like to offer a quick heads up – your interpretation of what 90.1 has to say regarding addressing unmet hours is spot on and well-stated, no disagreements here. Neeraj however is indirectly making a pretty valid point that I’d hate for anyone to miss…<o:p></o:p></span></p><p class=MsoNormal><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'><o:p> </o:p></span></p><p class=MsoNormal><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'>If you only ever approach addressing unmet hours by bumping the oversizing factors, you may well be missing something critical. I for one was in this train of thought when I started out. To the letter of the standard, indeed this is all we’re *prescribed* to do to remedy the situation, but this approach will not always work, and may result in baseline models with a very skewed performance – suffice it to say skewed is not always a *good* thing, even if it does make your performance numbers look good.<o:p></o:p></span></p><p class=MsoNormal><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'> <o:p></o:p></span></p><p class=MsoNormal><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'>Whenever I have unmet hours, I’ve learned through others on these lists to investigate the “why” and “when” of those unmet hours as a first step. More often than not, unmet hours in my models, when they do occur, have nothing to do with lacking heating or cooling capacity – fan (airflow) scheduling conflicts, thermostat setpoints and unrealistic deadbands are the primary culprits. The systems effectively aren’t running as frequently or for a duration as they should be.<o:p></o:p></span></p><p class=MsoNormal><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'><o:p> </o:p></span></p><p class=MsoNormal><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'>When this is the case, and I can assure Neeraj is not alone in this experience, fluffing the oversizing factor may appear to “remedy” the issue, but often as not may *not* be enough to pull your baseline/proposed models into the prescribed requirements for unmet hours. In some cases, you might even make the situation worse. I’m pretty sure the spirit of the standard, by specifying a maximum number of unmet hours, is to allow both the proposed and baseline systems to run when they need to satisfy the loads<o:p></o:p></span></p><p class=MsoNormal><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'><o:p> </o:p></span></p><p class=MsoNormal><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'>For whatever combination of reasons, and luck may be a part of it, it has been a long while since I’ve created an autosizing 90.1 baseline model whose unmet hours did not ring in at either zero or the single digits, and as such did not require any adjustments. I personally feel this has had a lot to do with understanding the mechanics behind what defines and can cause an unmet hour – as you’re getting at with consideration to drift points. <o:p></o:p></span></p><p class=MsoNormal><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'><o:p> </o:p></span></p><p class=MsoNormal><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'>As you say, future versions of 90.1 may be more nuanced, but I personally feel the manner in which unmet hours are currently addressed does a disservice to those aspiring to be quality energy modelers – one can easily be misled to believe an unmet load hour is a problem in and of itself with an easy “fix,” without recognizing it’s really a symptom of a problem... bumping capacities without first addressing the cause of unmet hours is something like a doctor only giving you a band-aid for a cut when what you need is a tetanus shot!<o:p></o:p></span></p><p class=MsoNormal><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'><o:p> </o:p></span></p><p class=MsoNormal><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'>It may be worth mentioning that my experience is dominantly within the world of eQuest/DOE2. I would not be surprised to find other engines/software have varying “typical” causes of unmet hours.<o:p></o:p></span></p><p class=MsoNormal><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'><o:p> </o:p></span></p><p class=MsoNormal><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'>Anyway, that’s my two cents, for what it’s worth =) – hope it might help lead others along the path!<o:p></o:p></span></p><p class=MsoNormal><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'><o:p> </o:p></span></p><p class=MsoNormal><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'>~Nick<o:p></o:p></span></p><p class=MsoNormal><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'><o:p> </o:p></span></p><div><p class=MsoNormal><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'><img border=0 width=119 height=37 id="Picture_x0020_1" src="cid:image001.jpg@01CB8A56.F6E25640" alt="cid:489575314@22072009-0ABB"></span><b><span style='font-size:11.0pt;font-family:"Stylus BT","sans-serif";color:#2D4D5E'><o:p></o:p></span></b></p><p class=MsoNormal><b><span style='font-size:11.0pt;font-family:"Stylus BT","sans-serif";color:#2D4D5E'><o:p> </o:p></span></b></p><p class=MsoNormal><b><span style='font-size:11.0pt;font-family:"Stylus BT","sans-serif";color:#2D4D5E'>NICK CATON, E.I.T.</span></b><b><span style='font-family:"Stylus BT","sans-serif";color:#2D4D5E'><o:p></o:p></span></b></p><p class=MsoNormal><span style='font-size:7.5pt;font-family:"Calibri","sans-serif";color:#CC9900'>PROJECT ENGINEER</span><span style='font-size:7.5pt;color:#CC9900'><o:p></o:p></span></p><p class=MsoNormal><span style='font-size:10.0pt;font-family:"Calibri","sans-serif";color:#2D4D5E'>25501 west valley parkway<o:p></o:p></span></p><p class=MsoNormal><span style='font-size:10.0pt;font-family:"Calibri","sans-serif";color:#2D4D5E'>olathe ks 66061<o:p></o:p></span></p><p class=MsoNormal><span style='font-size:10.0pt;font-family:"Calibri","sans-serif";color:#2D4D5E'>direct 913 344.0036<o:p></o:p></span></p><p class=MsoNormal><span style='font-size:10.0pt;font-family:"Calibri","sans-serif";color:#2D4D5E'>fax 913 345.0617<o:p></o:p></span></p><p class=MsoNormal><i><span style='font-size:10.0pt;font-family:"Calibri","sans-serif";color:#2D4D5E'>Check out our new web-site @ </span></i><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'><a href="www.smithboucher.com" title="blocked::www.smithboucher.com"><span style='font-size:10.0pt'>www.smithboucher.com</span></a></span><u><span style='font-size:10.0pt;font-family:"Calibri","sans-serif";color:blue'> </span></u><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'><o:p></o:p></span></p></div><p class=MsoNormal><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'><o:p> </o:p></span></p><div><div style='border:none;border-top:solid #B5C4DF 1.0pt;padding:3.0pt 0in 0in 0in'><p class=MsoNormal><b><span style='font-size:10.0pt;font-family:"Tahoma","sans-serif";color:windowtext'>From:</span></b><span style='font-size:10.0pt;font-family:"Tahoma","sans-serif";color:windowtext'> bldg-sim-bounces@lists.onebuilding.org [mailto:bldg-sim-bounces@lists.onebuilding.org] <b>On Behalf Of </b>Michael Collarin<br><b>Sent:</b> Friday, November 19, 2010 1:46 PM<br><b>To:</b> Nearedge; cjaigath@yahoo.com<br><b>Cc:</b> bldg-sim@lists.onebuilding.org<br><b>Subject:</b> Re: [Bldg-sim] Adjusting Capacity for Unmet Cooling<o:p></o:p></span></p></div></div><p class=MsoNormal><o:p> </o:p></p><p class=MsoNormal><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'>Neeraj, it is in fact the contrary. <o:p></o:p></span></p><p class=MsoNormal><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'><o:p> </o:p></span></p><p class=MsoNormal><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'>ASHRAE 90.1-2007 Appendix G requires you to model Baseline Airflow Rate using a 20-degree F temperature difference between the supply air and room air temperatures. Therefore, if your room set point is 75F for cooling, set your cooling leaving air temperature to 55F and vice versa for heating; 72F heating set point requires a 92F leaving air temperature. This establishes your CFM airflow within the model. Do not vary these to adjust unmet hours.<o:p></o:p></span></p><p class=MsoNormal><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'><o:p> </o:p></span></p><p class=MsoNormal><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'>If you have unmet heating or cooling hours (over 300 or greater than 50 between baseline and proposed), you may incrementally adjust the baseline cooling and heating capacities (originally oversized 15% and 25% respectively) accordingly to reduce the overall unmet hours (below 300) or the difference between baseline and proposed (within 50).<o:p></o:p></span></p><p class=MsoNormal><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'><o:p> </o:p></span></p><p class=MsoNormal><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'>Before taking this step, be sure to look at your thermostat drift points. If the cooling set point is 75, but the cooling drift point is 84, when the space is unoccupied this would allow the space to move toward 84 degrees. When the space becomes occupied and the simulation tries to cool to 75, the system will not be able to achieve this within the allotted time (1 hour) and you will have an unmet cooling hour. <o:p></o:p></span></p><p class=MsoNormal><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'><o:p> </o:p></span></p><p class=MsoNormal><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'>There are some changes to ASHRAE 90.1-2010 that will effect unmet hours, but for the time being, if you are modeling a project using 2007 or 2004, this method should help you eliminate the unmet hours.<o:p></o:p></span></p><p class=MsoNormal><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'><o:p> </o:p></span></p><p class=MsoNormal><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'>Regards,<o:p></o:p></span></p><p class=MsoNormal><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'><o:p> </o:p></span></p><div><p class=MsoNormal><b><span style='font-size:8.0pt;font-family:"Verdana","sans-serif"'>Michael M. Collarin, EIT, LEED AP BD+C </span></b><b><span style='font-size:7.0pt;font-family:"Verdana","sans-serif";color:green'>|</span></b><b><span style='font-size:7.0pt;font-family:"Calibri","sans-serif";color:green'> </span></b><b><span style='font-size:7.0pt;font-family:"Verdana","sans-serif";color:green'>Elm Engineering, Inc. | 212 S Tryon St | Suite 1375 | Charlotte, NC 28281</span></b><b><span style='font-size:7.0pt;font-family:"Arial","sans-serif";color:green'><o:p></o:p></span></b></p><p class=MsoNormal><span style='font-size:8.0pt;font-family:"Verdana","sans-serif";color:green;letter-spacing:.9pt'>PHONE 704-335-0396 Ext. 108</span><span style='font-size:8.0pt;font-family:"Verdana","sans-serif";color:green'>|<b> </b>FAX 704-335-0399<b> </b>|</span><b><span style='font-size:8.0pt;font-family:"Verdana","sans-serif";color:gray'> </span></b><span style='font-size:8.0pt;font-family:"Verdana","sans-serif";color:gray'><a href="http://www.elmengr.com/" title="blocked::http://www.elmengr.com/"><span style='font-family:"Arial","sans-serif"'>www.elmengr.com</span></a></span><span style='color:#1F497D'><o:p></o:p></span></p></div><p class=MsoNormal><span style='font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D'><o:p> </o:p></span></p><div><div style='border:none;border-top:solid #B5C4DF 1.0pt;padding:3.0pt 0in 0in 0in'><p class=MsoNormal><b><span style='font-size:10.0pt;font-family:"Tahoma","sans-serif";color:windowtext'>From:</span></b><span style='font-size:10.0pt;font-family:"Tahoma","sans-serif";color:windowtext'> Nearedge [mailto:near_ej@yahoo.com] <br><b>Sent:</b> Friday, November 12, 2010 12:51 AM<br><b>To:</b> cjaigath@yahoo.com<br><b>Cc:</b> bldg-sim@lists.onebuilding.org<br><b>Subject:</b> Re: [Bldg-sim] Adjusting Capacity for Unmet Cooling<o:p></o:p></span></p></div></div><p class=MsoNormal><o:p> </o:p></p><p class=MsoNormal style='margin-bottom:12.0pt'><span style='font-size:10.0pt;font-family:"Arial","sans-serif"'>Hello Jaigath,<br>Using the performance rating method (PRM), in my experience it is usually an issue of low supply CFM.<br>Correct me if I am wrong but on the contrary I think that ASHARE baseline PRM fixes the cooling and heating capacities to 1.15 and 1.25 respectively and the user is allowed to bump up the supply CFM in increments if necessary.<br>I have a feeling that the issue of unmet load hours has been discussed many times before -- so, the archives will be a good resource as well.<br>Best,<br>Neeraj</span><o:p></o:p></p><div><p class=MsoNormal><span class=spelle><span style='font-size:10.0pt;font-family:"Arial","sans-serif"'>Neeraj</span></span><span style='font-size:10.0pt;font-family:"Arial","sans-serif"'> <span class=spelle>Kapoor</span><br>t: +91.99581.70018</span><o:p></o:p></p><p class=MsoNormal style='margin-bottom:12.0pt'><span class=grame><span style='font-size:10.0pt;font-family:"Arial","sans-serif"'>e</span></span><span style='font-size:10.0pt;font-family:"Arial","sans-serif"'>: <span class=spelle>neeraj</span>[at]<span class=spelle>kalpakrit</span>[dot]com<br><span class=spelle>Kalpakrit</span> Sustainable Environments Pvt. Ltd.<br><a href="http://www.kalpakrit.com">www.kalpakrit.com</a></span><o:p></o:p></p><table class=MsoNormalTable border=0 cellpadding=0 width=405 style='width:303.75pt'><tr><td valign=top style='padding:1.5pt 1.5pt 1.5pt 1.5pt'><p class=MsoNormal><u><span style='font-size:10.0pt;font-family:"Arial","sans-serif"'>Office Address</span></u><span style='font-size:10.0pt;font-family:"Arial","sans-serif"'>:<br>610-A <span class=spelle>Udyog</span> <span class=spelle>Vihar</span>, Phase-5,<br><span class=spelle>Gurgaon</span>, Haryana - 122016<br>t: +91.124.430.9490/ 1/ 2<br>f: +91.124.430.9493</span><o:p></o:p></p></td><td valign=top style='padding:1.5pt 1.5pt 1.5pt 1.5pt'><p class=MsoNormal><u><span style='font-size:10.0pt;font-family:"Arial","sans-serif"'>Registered Address</span></u><span style='font-size:10.0pt;font-family:"Arial","sans-serif"'>:<br>101 <span class=spelle>Anupam</span> Apartments,<br><span class=spelle>Mehrauli-Badarpur</span> Road,<br>New Delhi - 110068</span><o:p></o:p></p></td></tr></table><p class=MsoNormal> <o:p></o:p></p></div><p class=MsoNormal>On 11-11-2010 10:30, Jaigath Chandraprakash wrote: <o:p></o:p></p><div><div><p class=MsoNormal>Hello All,<o:p></o:p></p></div><div><p class=MsoNormal>I would like to know how other increase their baseline capacity when they have unmet load. I have a PSZHP system and in one system, I got more than 400 hrs unmet load. I usually just increase the TR cooling capacity until I get a lower unmet load but in this case, I think the unmet load is due to low supply cfm. Is it ok to adjust also the supply fan cfm? I am thinking that G3.1.2.2 only requires me to adjust only the cooling capacity. Do others adjust both cfm and cooling load?<o:p></o:p></p></div><div><p class=MsoNormal>Thanks,<o:p></o:p></p></div><div><p class=MsoNormal>Jaigath<o:p></o:p></p></div></div><p class=MsoNormal><o:p> </o:p></p><p class=MsoNormal><o:p> </o:p></p></div>
</body></html>