<div>There was a major discussion on this topic a few months ago, although it may have been on the eQuest list-serve, I don't remember. Try searching the archives.<br></div><div><br></div><div>The general conclusion was that the current requirements are that the baseline and proposed design models should have the same ventilation rates, BUT that this doesn't make that much sense as you could over-ventilate to the point where there is no added benefit to the occupants, and major additional energy use. The discussion was primarily around LEED EA Credit 1, and there was some correspondence between the simulation group and the LEED credit chair. I believe that they will be looking at modifying this requirement for LEED models in the future.</div>
<div><br></div><div>--</div><div>Karen</div><br><div class="gmail_quote">On Thu, Oct 28, 2010 at 9:32 AM, Grammy <span dir="ltr"><<a href="mailto:grammy.hkust@gmail.com">grammy.hkust@gmail.com</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex;"><font face="comic sans ms,sans-serif">In my opinion, the exception is means that keep the "design value" of OA same in both proposed and basline, but use DCV only in proposed.</font><div>
<font face="comic sans ms,sans-serif"><br>
</font></div><div><font face="comic sans ms,sans-serif">Because DCV can modify OA volume by the number of people in zone, and the OA requirement is dynamics in simulation - which is too hard to keep baseline same with, and also should not keep the same, if not where does the saving come from?<br>
</font><div><div class="h5"><br><div class="gmail_quote">On Thu, Oct 28, 2010 at 9:24 PM, Paul Riemer <span dir="ltr"><<a href="mailto:Paul.Riemer@dunhameng.com" target="_blank">Paul.Riemer@dunhameng.com</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
<div lang="EN-US" link="blue" vlink="blue">
<div>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">Section G.3.1.2.5 in 90.1-2007 has added an exception to the "shall
be the same" for models with demand controlled ventilation in the proposed
that is not required by Section 6.4.3.9. </span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">That alone is kind of confusing since it does not address what
the values should be when they are allowed to not be the same. </span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">I think they are trying to resolve the intersection of projects
that use more OA than Std 62.1 and utilize demand controlled ventilation.</span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">The most recent Trane Engineers broadcast promised more changes coming
to this section (as addendum DA?) but I do not have anything published to
reference.</span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">Paul Riemer</span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">Dunham</span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>
<div>
<div style="border:none;border-top:solid #B5C4DF 1.0pt;padding:3.0pt 0in 0in 0in">
<p class="MsoNormal" style="margin-left:.5in"><b><span style="font-size:10.0pt">From:</span></b><span style="font-size:10.0pt"> <a href="mailto:bldg-sim-bounces@lists.onebuilding.org" target="_blank">bldg-sim-bounces@lists.onebuilding.org</a>
[mailto:<a href="mailto:bldg-sim-bounces@lists.onebuilding.org" target="_blank">bldg-sim-bounces@lists.onebuilding.org</a>] <b>On Behalf Of </b>Kingsley,
Michael L.<br>
<b>Sent:</b> Thursday, October 28, 2010 7:50 AM<br>
<b>To:</b> Grammy; Jaigath Chandraprakash</span></p><div><div><br>
<b>Cc:</b> <a href="mailto:bldg-sim@lists.onebuilding.org" target="_blank">bldg-sim@lists.onebuilding.org</a><br>
<b>Subject:</b> Re: [Bldg-sim] G3.1.2.5 Clarification</div></div>
</div>
</div><div><div>
<p class="MsoNormal" style="margin-left:.5in"> </p>
<div>
<p class="MsoNormal" style="margin-left:.5in"><span style="font-size:10.0pt;color:navy">I agree. Standard 61.1 sets the minimum acceptable
ventilation rate. The design ventilation rate can be higher, and the
baseline rate should be the same as the real design.</span></p>
<p class="MsoNormal" style="margin-left:.5in"><span style="font-size:10.0pt;color:navy"> </span></p>
<div>
<p style="margin-left:.5in"><span style="font-size:10.0pt;color:navy">Best regards,</span></p>
<p style="margin-left:.5in"><span style="color:navy"> </span></p>
<p style="margin-left:.5in"><span style="font-size:10.0pt;color:navy">Mike</span></p>
<p style="margin-left:.5in"><span style="color:navy"> </span></p>
<p class="MsoNormal" style="margin-left:.5in"><b><span style="font-size:10.0pt;color:navy">Michael L. Kingsley, PhD, PE, LEED AP </span></b><span style="font-size:7.5pt;color:gray">| R. W.
Beck, An SAIC Company</span></p>
<p class="MsoNormal" style="margin-left:.5in"><span style="font-size:7.5pt;color:gray">Senior Engineer/Project Manager</span></p>
<p class="MsoNormal" style="margin-left:.5in"><span style="font-size:7.5pt;color:gray">Energy, Environment & Infrastructure Solutions</span></p>
<p class="MsoNormal" style="margin-left:.5in"><span style="font-size:7.5pt;color:gray">office: 315.437.1869 x205 | mobile: 315.373.4081</span></p>
<p style="margin-left:.5in"><span style="color:navy"> </span></p>
</div>
<div>
<div class="MsoNormal" align="center" style="margin-left:.5in;text-align:center">
<hr size="2" width="100%" align="center">
</div>
<p class="MsoNormal" style="margin-left:.5in"><b><span style="font-size:10.0pt">From:</span></b><span style="font-size:10.0pt">
<a href="mailto:bldg-sim-bounces@lists.onebuilding.org" target="_blank">bldg-sim-bounces@lists.onebuilding.org</a>
[mailto:<a href="mailto:bldg-sim-bounces@lists.onebuilding.org" target="_blank">bldg-sim-bounces@lists.onebuilding.org</a>] <b>On Behalf Of </b>Grammy<br>
<b>Sent:</b> Thursday, October 28, 2010 8:38 AM<br>
<b>To:</b> Jaigath Chandraprakash<br>
<b>Cc:</b> <a href="mailto:bldg-sim@lists.onebuilding.org" target="_blank">bldg-sim@lists.onebuilding.org</a><br>
<b>Subject:</b> Re: [Bldg-sim] G3.1.2.5 Clarification</span></p>
</div>
<p class="MsoNormal" style="margin-left:.5in"> </p>
<p class="MsoNormal" style="margin-left:.5in"><span style="font-family:"Comic Sans MS"">In my opinion:</span></p>
<div>
<p class="MsoNormal" style="margin-left:.5in"> </p>
</div>
<div>
<p class="MsoNormal" style="margin-left:.5in"><span style="font-family:"Comic Sans MS"">For LEED, the OA
should increase 30% first. This is the propose requirement.</span></p>
</div>
<div>
<p class="MsoNormal" style="margin-left:.5in"> </p>
</div>
<div>
<p class="MsoNormal" style="margin-left:.5in"><span style="font-family:"Comic Sans MS"">Then for energy
model, the baseline model should equal to proposed, which means the baseline OA
is also 30% more than 62.1 requirement.</span></p>
</div>
<div>
<p class="MsoNormal" style="margin-left:.5in"> </p>
<div>
<p class="MsoNormal" style="margin-left:.5in">On Thu, Oct 28, 2010 at 6:07 PM, Jaigath Chandraprakash <<a href="mailto:cjaigath@yahoo.com" target="_blank">cjaigath@yahoo.com</a>> wrote:</p>
<div>
<div>
<div>
<p class="MsoNormal" style="margin-left:.5in">Hello,</p>
</div>
<div>
<p class="MsoNormal" style="margin-left:.5in"> </p>
</div>
<div>
<p class="MsoNormal" style="margin-left:.5in">G3.1.2.5 states that minimum ventilation rates will be
the same for proposed building and baseline building. Does it mean that if
my building design OA rate is increased by 30%, my model will still be
based on the minimum OA required by 62.1 and is still equal to the baseline
building OA? Meaning my proposed building wont be penalized by supplying more
OA?</p>
</div>
<div>
<p class="MsoNormal" style="margin-left:.5in"> </p>
</div>
<div>
<p class="MsoNormal" style="margin-left:.5in"> </p>
</div>
<div>
<p class="MsoNormal" style="margin-left:.5in">Thanks in advance.</p>
</div>
<div>
<p class="MsoNormal" style="margin-left:.5in"> </p>
</div>
<div>
<p class="MsoNormal" style="margin-left:.5in"> </p>
</div>
<div>
<p class="MsoNormal" style="margin-left:.5in">Jaigath</p>
</div>
</div>
<p class="MsoNormal" style="margin-left:.5in"> </p>
</div>
<p class="MsoNormal" style="margin-left:.5in"><br>
_______________________________________________<br>
Bldg-sim mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a></p>
</div>
<p class="MsoNormal" style="margin-left:.5in"> </p>
</div>
</div>
</div></div></div>
</div>
</blockquote></div><br></div></div></div>