<html><head><style type="text/css"><!-- DIV {margin:0px;} --></style></head><body><div style="font-family:times new roman, new york, times, serif;font-size:12pt"><DIV>Hello,</DIV>
<DIV> Has anybody encountered this error in latest eQuest 3.64. I have errors such as this one totaling to about 10,000. Following is the error listed in the bdl file.</DIV>
<DIV> </DIV>
<DIV>thanks.</DIV>
<DIV> </DIV>
<DIV> </DIV>
<DIV> </DIV>
<DIV> ******* "F5-6Core Zn (G.C16)" = ZONE<BR> ******* TYPE = CONDITIONED<BR> ******* SPACE = "F5-6Core Spc (G.C16)"<BR> ******* SIZING-OPTION = "ADJUST-LOADS"<BR> ******* DESIGN-COOL-T = 75<BR> ******* DESIGN-HEAT-T = 60<BR> ******* FLOW/AREA = 0.5<BR> ******* MIN-FLOW-RATIO = 0.4<BR> ******* TERMINAL-TYPE =
SERIES-PIU<BR> ******* OA-FLOW/PER = 50<BR> ******* COOL-TEMP-SCH = "OFSys2 (VAVS) Cool Sch"<BR> ******* ..<BR>*ERROR****************************************************************************************<BR>*ERROR*****MIN-FLOW-SCH in F5-6Core Zn (G.C16) has Maximum number of<BR> expression dependency lists (999768) exceeded.<BR>*ERROR****************************************************************************************<BR>*ERROR*****HEATING-CAPACITY in F5-6Core Zn (G.C16) has Maximum number of<BR> expression dependency lists (999768)
exceeded.<BR>*ERROR****************************************************************************************<BR>*ERROR*****COOLING-CAPACITY in F5-6Core Zn (G.C16) has Maximum number of<BR> expression dependency lists (999768) exceeded.<BR>*ERROR****************************************************************************************<BR>*ERROR*****COOL-SH-CAP in F5-6Core Zn (G.C16) has Maximum number of expression<BR> dependency lists (999768) exceeded.<BR>*ERROR****************************************************************************************<BR>*ERROR*****MULTIPLIER in F5-6Core Zn (G.C16) has Maximum number of expression<BR> dependency lists (999768)
exceeded.<BR>*ERROR****************************************************************************************<BR>*ERROR*****MAX-HEAT-RATE in F5-6Core Zn (G.C16) has Maximum number of<BR> expression dependency lists (999768) exceeded.<BR>*ERROR****************************************************************************************<BR>*ERROR*****MAX-COOL-RATE in F5-6Core Zn (G.C16) has Maximum number of<BR> expression dependency lists (999768) exceeded.<BR>*ERROR****************************************************************************************<BR>*ERROR*****BASEBOARD-RATING in F5-6Core Zn (G.C16) has Maximum number of<BR> expression dependency lists (999768)
exceeded.<BR>*ERROR****************************************************************************************<BR>*ERROR*****PANEL-LOSS-RATIO in F5-6Core Zn (G.C16) has Maximum number of<BR> expression dependency lists (999768) exceeded.<BR>*ERROR****************************************************************************************<BR>*ERROR*****AIR-CHANGES/HR in F5-6Core Zn (G.C16) has Maximum number of<BR> expression dependency lists (999768) exceeded.<BR>*ERROR****************************************************************************************<BR>*ERROR*****Value 0 of in SUBR-FUNCTIONS number 11 has The<BR> maximum number of</DIV>
<DIV>-NOTE- - - DATA FOR F5-6Core Zn (G.C16)<BR>-INPUT - - - - - - - - - - - - - - - - - - - - - - - - TYPE = CONDITIONED<BR>-INPUT - - MIN-FLOW-RATIO = 0.4000 FRAC.OR MULT.<BR>-INPUT -
- FLOW/AREA = 0.5000 CFM/SQFT<BR>-INPUT - - OA-FLOW/PER = 50.0000 CFM<BR>-INPUT -
- DESIGN-HEAT-T = 60.0000 F<BR>-INPUT - - DESIGN-COOL-T = 75.0000 F<BR>-INPUT -
- COOL-TEMP-SCH = OFSys2 (VAVS) Cool Sch<BR>-INPUT - - SIZING-OPTION = ADJUST-LOADS<BR>-INPUT - -
TERMINAL-TYPE = SERIES-PIU<BR>-INPUT - - SPACE = F5-6Core Spc (G.C16)<BR>-DEFAULT - ZONE-REPORTS = YES<BR>-DEFAULT
- ICE-RINK = NO<BR>-DEFAULT - C-REHEAT-CAP = 0.0000 BTU/HR<BR>-DEFAULT
- C-HTG-SETBACK = 1.0000<BR>-DEFAULT - C-EXH-FAN-BHP = 0.0000 HP<BR>-DEFAULT
- C-EF-DRIVE-EFF = 1.0000 FRAC.OR MULT.<BR>-DEFAULT - C-EXH-FAN-NOM-HP = 0.0000 HP<BR>-DEFAULT
- C-ZONE-FAN-BHP = 0.0000 HP<BR>-DEFAULT - C-ZF-FAN-DRV-EFF = 1.0000 FRAC.OR MULT.<BR>-DEFAULT
- C-ZF-NOM-HP = 0.0000 HP<BR>-DEFAULT - C-C-ZFAN-KW/FLOW = 0.0017 KW/CFM<BR>-DEFAULT
- C-C-EXH-KW/FLOW = 0.0017 KW/CFM<BR>-DEFAULT - C-C-CHW-COIL-Q = 0.0000 GAL/MIN<BR>-DEFAULT
- C-C-HW-COIL-Q = 0.0000 GAL/MIN<BR>-DEFAULT - C-C-BBRD-COIL-Q = 0.0000 GAL/MIN<BR>-DEFAULT
- C-C-THERM-TYPE = 0.0000<BR>-DEFAULT - C-C-THERM-BAND = 33.8000 F<BR>-DEFAULT
- C-C-OA-MET-DEF = 0.0000<BR>-DEFAULT - C-C-OA-FLOW = 0.0000 CFM<BR>-DEFAULT
- C-C-OA-FLOW/PER = 0.0000 CFM<BR>-DEFAULT - C-C-OA-CHANGES = 0.0000<BR>-DEFAULT
- C-C-EXH-FLOW = 0.0000 CFM<BR>-DEFAULT - C-C-REHEAT = 0.0000<BR>-DEFAULT
- C-C-MIN-FLOW-RAT = 1.0000 FRAC.OR MULT.<BR>-DEFAULT - C-C-PROP-ZR-1 = 0.0000<BR>-DEFAULT
- C-C-PROP-ZR-2 = 0.0000<BR>-DEFAULT - C-C-PROP-ZR-3 = 0.0000</DIV>
<DIV> </DIV>
<DIV> ******* "F5-6Core Pl Zn (G.C46)" = ZONE<BR> ******* TYPE = UNCONDITIONED<BR> ******* SPACE = "F5-6Core Plnm (G.C46)"<BR> ******* SIZING-OPTION = "ADJUST-LOADS"<BR> ******* DESIGN-COOL-T = 80<BR> ******* DESIGN-HEAT-T = 60<BR> ******* ..<BR>*ERROR****************************************************************************************<BR>*ERROR*****MULTIPLIER in F5-6Core Pl Zn (G.C46) has Maximum number of<BR> expression
dependency lists (999768) exceeded.<BR>*ERROR****************************************************************************************<BR>*ERROR*****FLOOR-MULTIPLIER in F5-6Core Pl Zn (G.C46) has Maximum number of<BR> expression dependency lists (999768) exceeded.<BR>*ERROR****************************************************************************************<BR>*ERROR*****LIGHT-ELEC-METER in F5-6Core Pl Zn (G.C46) has Maximum number of<BR> expression dependency lists (999768) exceeded.<BR>*ERROR****************************************************************************************<BR>*ERROR*****TASK-ELEC-METER in F5-6Core Pl Zn (G.C46) has Maximum number of<BR> expression dependency lists (999768)
exceeded.<BR>*ERROR****************************************************************************************<BR>*ERROR*****EQUIP-ELEC-METER in F5-6Core Pl Zn (G.C46) has Maximum number of<BR> expression dependency lists (999768) exceeded.<BR>*ERROR****************************************************************************************<BR>*ERROR*****SOURCE-ELEC-METE in F5-6Core Pl Zn (G.C46) has Maximum number of<BR> expression dependency lists (999768) exceeded.<BR>*ERROR****************************************************************************************<BR>*ERROR*****HEAT-ELEC-METER in F5-6Core Pl Zn (G.C46) has Maximum number of<BR> expression dependency lists (999768)
exceeded.<BR>*ERROR****************************************************************************************<BR>*ERROR*****COOL-ELEC-METER in F5-6Core Pl Zn (G.C46) has Maximum number of<BR> expression dependency lists (999768) exceeded.<BR>*ERROR****************************************************************************************<BR>*ERROR*****HTREJ-ELEC-METER in F5-6Core Pl Zn (G.C46) has Maximum number of<BR> expression dependency lists (999768) exceeded.<BR>*ERROR****************************************************************************************<BR>*ERROR*****AUX-ELEC-METER in F5-6Core Pl Zn (G.C46) has Maximum number of<BR> expression dependency lists (999768)
exceeded.<BR>*ERROR****************************************************************************************<BR>*ERROR*****Value 0 of in SUBR-FUNCTIONS number 11 has The<BR> maximum number of</DIV>
<DIV>-NOTE- - - DATA FOR F5-6Core Pl Zn (G.C46)<BR>-INPUT - - - - - - - - - - - - - - - - - - - - - - - - TYPE = UNCONDITIONED<BR>-INPUT - - DESIGN-HEAT-T = 60.0000 F<BR>-INPUT -
- DESIGN-COOL-T = 80.0000 F<BR>-INPUT - - SIZING-OPTION = ADJUST-LOADS<BR>-INPUT -
- SPACE = F5-6Core Plnm (G.C46)<BR>-DEFAULT - SS-VENT-CST = 5.0000<BR>-DEFAULT
- SS-VENT-WND = 0.0000 1/KNOT<BR>-DEFAULT - SS-VENT-TEMP = 0.0000 1/R<BR>-DEFAULT
- SS-VENT-LIMIT-T = 120.0000 F<BR>-DEFAULT - SS-VENT-KW/FLOW = 0.0000 KW/CFM<BR>-DEFAULT
- ZONE-REPORTS = NO<BR>-DEFAULT - C-REHEAT-CAP = 0.0000 BTU/HR<BR>-DEFAULT
- C-HTG-SETBACK = 1.0000<BR>-DEFAULT - C-EXH-FAN-BHP = 7.0000 HP<BR>-DEFAULT
- C-EF-DRIVE-EFF = 1.0000 FRAC.OR MULT.<BR>-DEFAULT - C-EXH-FAN-NOM-HP = 0.0000 HP<BR>-DEFAULT
- C-ZONE-FAN-BHP = 0.0000 HP<BR>-DEFAULT - C-ZF-FAN-DRV-EFF = 1.0000 FRAC.OR MULT.<BR>-DEFAULT
- C-ZF-NOM-HP = 0.0000 HP<BR>-DEFAULT - C-C-ZFAN-KW/FLOW = 0.0017 KW/CFM<BR>-DEFAULT
- C-C-EXH-KW/FLOW = 0.0017 KW/CFM<BR>-DEFAULT - C-C-CHW-COIL-Q = 0.0000 GAL/MIN<BR>-DEFAULT
- C-C-HW-COIL-Q = 0.0000 GAL/MIN<BR>-DEFAULT - C-C-BBRD-COIL-Q = 0.0000 GAL/MIN<BR>-DEFAULT
- C-C-THERM-TYPE = 0.0000<BR>-DEFAULT - C-C-THERM-BAND = 33.8000 F<BR>-DEFAULT
- C-C-OA-MET-DEF = 0.0000<BR>-DEFAULT - C-C-OA-FLOW = 0.0000 CFM<BR>-DEFAULT
- C-C-OA-FLOW/PER = 0.0000 CFM<BR>-DEFAULT - C-C-OA-CHANGES = 0.0000<BR>-DEFAULT
- C-C-EXH-FLOW = 0.0000 CFM<BR>-DEFAULT - C-C-REHEAT = 0.0000<BR>-DEFAULT
- C-C-MIN-FLOW-RAT = 1.0000 FRAC.OR MULT.<BR>-DEFAULT - C-C-PROP-ZR-1 = 0.0000<BR>-DEFAULT
- C-C-PROP-ZR-2 = 0.0000<BR>-DEFAULT - C-C-PROP-ZR-3 = 0.0000<BR></DIV></div><br>
</body></html>