<div>Obtaining a negative pressure difference also requires sealing the space. Door seals, and sealing walls. If you exhaust 0.5 cfm/sf from a room with chicken wire walls, you won't achieve any kind of measurable pressure difference.<br>
</div><div><br></div><div>I usually steer clients away from this credit for this very reason (difficulty coupled with measurability)</div><div><br></div><div>--</div><div>Karen</div><br><div class="gmail_quote">On Wed, Oct 6, 2010 at 3:36 PM, James V Dirkes II, PE <span dir="ltr"><<a href="mailto:jvd2pe@tds.net">jvd2pe@tds.net</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex;">
<div lang="EN-US" link="blue" vlink="purple">
<div>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">Personal opinion:</span></p>
<p><span style="font-size:11.0pt;font-family:Symbol;color:#1F497D"><span>·<span style="font:7.0pt "Times New Roman"">
</span></span></span><span style="font-size:11.0pt;color:#1F497D">5 Pa is difficult to (accurately) measure</span></p>
<p><span style="font-size:11.0pt;font-family:Symbol;color:#1F497D"><span>·<span style="font:7.0pt "Times New Roman"">
</span></span></span><span style="font-size:11.0pt;color:#1F497D">1 Pa is impossible outside of a lab</span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">I don’t know what they were thinking when making these requirements,
since they’re not too clear, but I suspect that if you demonstrate .5cfm
/ sq.ft. and no recirculation you’ll be OK.</span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"><img width="425" height="142"></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>
<p class="MsoNormal" align="center" style="text-align:center"><b><span style="font-size:13.5pt;color:#1F497D">The Building Performance Team<br>
</span></b><b><span style="color:#1F497D">James V. Dirkes II, P.E., LEED AP<br>
</span></b><span style="color:#1F497D">1631 Acacia Drive NW<br>
Grand Rapids, MI 49504<br>
616 450 8653</span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>
<div style="border:none;border-top:solid #B5C4DF 1.0pt;padding:3.0pt 0in 0in 0in">
<p class="MsoNormal" style="margin-left:.5in"><b><span style="font-size:10.0pt">From:</span></b><span style="font-size:10.0pt"> <a href="mailto:bldg-sim-bounces@lists.onebuilding.org" target="_blank">bldg-sim-bounces@lists.onebuilding.org</a>
[mailto:<a href="mailto:bldg-sim-bounces@lists.onebuilding.org" target="_blank">bldg-sim-bounces@lists.onebuilding.org</a>] <b>On Behalf Of </b>Deepa<br>
<b>Sent:</b> Wednesday, October 06, 2010 2:59 PM<br>
<b>To:</b> Bldg-Sim<br>
<b>Subject:</b> [Bldg-sim] Negative pressure for EQ cr 5</span></p>
</div><div><div class="h5">
<p class="MsoNormal" style="margin-left:.5in"> </p>
<div>
<p class="MsoNormal" style="margin-left:.5in">Hello all,</p>
</div>
<div>
<p class="MsoNormal" style="margin-left:.5in"> </p>
</div>
<div>
<p class="MsoNormal" style="margin-left:.5in">One of the requirements for EQ
Credit 5 is to prove that the areas such as the janitor's closet need to be
negatively pressurized to a minimum of 5Pa when doors are closed and
1Pa when doors are open. Generally, in mechanical drawings, the cfm values are
mentioned for exhaust fans. </p>
</div>
<div>
<p class="MsoNormal" style="margin-left:.5in"> </p>
</div>
<div>
<p class="MsoNormal" style="margin-left:.5in">I wanted some insight as to how
this pressure difference information can be obtained for both cases. Is there a
straightforward calculation? </p>
</div>
<div>
<p class="MsoNormal" style="margin-left:.5in"> </p>
</div>
<div>
<p class="MsoNormal" style="margin-left:.5in"> </p>
</div>
<div>
<p class="MsoNormal" style="margin-left:.5in">Thanks,</p>
</div>
<div>
<p class="MsoNormal" style="margin-left:.5in">Deepa</p>
</div>
</div></div></div>
</div>
<br>_______________________________________________<br>
Bldg-sim mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br>