<div>Hi Deepa, </div>
<div> </div>
<div>My two cents. </div>
<div> </div>
<div>For your question, you need to know: </div>
<div> </div>
<div>1. the air volume in room and its pressure</div>
<div> </div>
<div>2. To achieve 5Pa, how much more air should be introduced - </div>
<div> </div>
<div>Higher pressure x air volume in room/atmospheric pressure </div>
<div> </div>
<div>Now you get the number for the static condition... ;)</div>
<div> </div>
<div>to maintain the pressure in a leaky room you have to pump in more air, right? </div>
<div> </div>
<div>3. from the ASHRAE Handbook of Fundamentals:<br><br>Q = 2610 x A x (DP)1/2<br><br>• Q is the room leakage flow rate in cfm,<br>• 2610 is a conversion factor,<br>• A is the net open crack area of the room (generally not measurable), and<br>
• DP is the differential pressure.<br></div>
<div>4. If you'd like to maintain certain pressure in the room, you need to supply 2+3 first. When the pressure is established in dynamic condition, you need to supply only 3 to maintain the pressure you want. </div>
<div> </div>
<div>This is only the theoretical calculation for your reference. <br></div>