<html><head><style type="text/css"><!-- DIV {margin:0px;} --></style></head><body><div style="font-family:times new roman, new york, times, serif;font-size:12pt"><DIV>Thank you very much Nick. I really appreciate your help on this.</DIV>
<DIV> <BR>I really got confused with this when I got a commnet recently saying that the "baseline case per section 9.4.1.2 were not modeled" and was asked to revised the baseline. So I ended up with no savings. This is in conflict with Table G3.1.6 that you have pointed out which says that No automatic lighting controls shall be modeled in the baseline building design. </DIV>
<DIV> </DIV>
<DIV>Does it mean that I am wrong when I applied also 10% savings to my baseline? This is where I got confused since 9.4.1.1.b also mentions occupant sensor that shall turn lighting off within 30 mins of occupant leaving the space. </DIV>
<DIV style="FONT-SIZE: 12pt; FONT-FAMILY: times new roman, new york, times, serif"> </DIV>
<DIV style="FONT-SIZE: 12pt; FONT-FAMILY: times new roman, new york, times, serif"> </DIV>
<DIV style="FONT-SIZE: 12pt; FONT-FAMILY: times new roman, new york, times, serif"><BR>
<DIV style="FONT-SIZE: 12pt; FONT-FAMILY: times new roman, new york, times, serif"><FONT face=Tahoma size=2>
<HR SIZE=1>
<B><SPAN style="FONT-WEIGHT: bold">From:</SPAN></B> Nick Caton <ncaton@smithboucher.com><BR><B><SPAN style="FONT-WEIGHT: bold">To:</SPAN></B> Jaigath Chandraprakash <cjaigath@yahoo.com>; bldg-sim@lists.onebuilding.org<BR><B><SPAN style="FONT-WEIGHT: bold">Sent:</SPAN></B> Mon, October 4, 2010 10:38:08 PM<BR><B><SPAN style="FONT-WEIGHT: bold">Subject:</SPAN></B> RE: [Bldg-sim] Automatic Lighting Shutoff Mandatory Provision Question<BR></FONT><BR>
<META http-equiv=x-dns-prefetch-control content=off>
<STYLE>
<!--
_filtered {font-family:"MS Mincho";panose-1:2 2 6 9 4 2 5 8 3 4;}
_filtered {font-family:"Cambria Math";panose-1:2 4 5 3 5 4 6 3 2 4;}
_filtered {font-family:Calibri;panose-1:2 15 5 2 2 2 4 3 2 4;}
_filtered {font-family:Tahoma;panose-1:2 11 6 4 3 5 4 4 2 4;}
_filtered {font-family:"Stylus BT";panose-1:2 14 4 2 2 2 6 2 3 4;}
_filtered {panose-1:2 2 6 9 4 2 5 8 3 4;}
p.MsoNormal, li.MsoNormal, div.MsoNormal
{margin:0in;margin-bottom:.0001pt;font-size:12.0pt;font-family:"serif";}
a:link, span.MsoHyperlink
{color:blue;text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
{color:purple;text-decoration:underline;}
p.MsoAcetate, li.MsoAcetate, div.MsoAcetate
{margin:0in;margin-bottom:.0001pt;font-size:8.0pt;font-family:"sans-serif";}
span.EmailStyle17
{font-family:"sans-serif";color:#1F497D;}
span.BalloonTextChar
{font-family:"sans-serif";}
.MsoChpDefault
{font-size:10.0pt;}
_filtered {margin:1.0in 1.0in 1.0in 1.0in;}
div.Section1
{}
-->
</STYLE>
<DIV class=Section1>
<P class=MsoNormal><SPAN style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'sans-serif'">Jaigath,</SPAN></P>
<P class=MsoNormal><SPAN style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'sans-serif'"> </SPAN></P>
<P class=MsoNormal><SPAN style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'sans-serif'">Appendix G allows us to take credit for automatic controls <U>in addition to</U> (beyond) what’s required in 9.4.1 for minimum compliance. One of the options here is to have programmable (time-of-day) shutoff for interior lighting circuits, and you can infer from between Table G3.1 and G3.2 of Appendix G that baseline models are taken to feature only such timeclock controls for automatic shutoff. Further, it’s taken that the lighting scheduling being kept identical between the proposed and baseline adequately reflects the minimum requirements, so you aren’t supposed to try to explicitly model the programmable shutoff. </SPAN></P>
<P class=MsoNormal><SPAN style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'sans-serif'"> </SPAN></P>
<P class=MsoNormal><SPAN style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'sans-serif'">If you have occupancy sensors throughout a building which only requires programmable shutoff, that’s an example of having automatic controls beyond what 9.4.1 requires – and you’d get to take 10% off your proposed LPD in all spaces where such short-term shutoff isn’t already required (per following section 9.4.1.2).</SPAN></P>
<P class=MsoNormal><SPAN style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'sans-serif'"> </SPAN></P>
<P class=MsoNormal><SPAN style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'sans-serif'">Note Table G3.2 also has a corresponding distinction between building smaller than and larger than 5,000ft2 – offering more credit for buildings using a means of automatic shutoff where no such controls are even minimally required.</SPAN></P>
<P class=MsoNormal><SPAN style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'sans-serif'"> </SPAN></P>
<P class=MsoNormal><SPAN style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'sans-serif'">~Nick</SPAN></P>
<DIV>
<P class=MsoNormal><SPAN style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'sans-serif'"><IMG id=Picture_x0020_1 height=37 alt=cid:489575314@22072009-0ABB width=119></SPAN><B><SPAN style="FONT-SIZE: 11pt; COLOR: #2d4d5e; FONT-FAMILY: 'sans-serif'"></SPAN></B></P>
<P class=MsoNormal><B><SPAN style="FONT-SIZE: 11pt; COLOR: #2d4d5e; FONT-FAMILY: 'sans-serif'"> </SPAN></B></P>
<P class=MsoNormal><B><SPAN style="FONT-SIZE: 11pt; COLOR: #2d4d5e; FONT-FAMILY: 'sans-serif'">NICK CATON, E.I.T.</SPAN></B><B><SPAN style="COLOR: #2d4d5e; FONT-FAMILY: 'sans-serif'"></SPAN></B></P>
<P class=MsoNormal><SPAN style="FONT-SIZE: 7.5pt; COLOR: #cc9900; FONT-FAMILY: 'sans-serif'">PROJECT ENGINEER</SPAN><SPAN style="FONT-SIZE: 7.5pt; COLOR: #cc9900"></SPAN></P>
<P class=MsoNormal><SPAN style="FONT-SIZE: 10pt; COLOR: #2d4d5e; FONT-FAMILY: 'sans-serif'">25501 west valley parkway</P>
<P class=MsoNormal><SPAN style="FONT-SIZE: 10pt; COLOR: #2d4d5e; FONT-FAMILY: 'sans-serif'">olathe ks 66061</SPAN></P></SPAN>
<P class=MsoNormal><SPAN style="FONT-SIZE: 10pt; COLOR: #2d4d5e; FONT-FAMILY: 'sans-serif'">direct 913 344.0036</SPAN></P>
<P class=MsoNormal><SPAN style="FONT-SIZE: 10pt; COLOR: #2d4d5e; FONT-FAMILY: 'sans-serif'">fax 913 345.0617</SPAN></P>
<P class=MsoNormal><I><SPAN style="FONT-SIZE: 10pt; COLOR: #2d4d5e; FONT-FAMILY: 'sans-serif'">Check out our new web-site @ </SPAN></I><SPAN style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'sans-serif'"><A title=blocked::www.smithboucher.com rel=nofollow><SPAN style="FONT-SIZE: 10pt; COLOR: blue">www.smithboucher.com</SPAN></A></SPAN><U><SPAN style="FONT-SIZE: 10pt; COLOR: blue; FONT-FAMILY: 'sans-serif'"> </SPAN></U><SPAN style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'sans-serif'"></SPAN></P></DIV>
<P class=MsoNormal><SPAN style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'sans-serif'"> </SPAN></P>
<DIV>
<DIV style="BORDER-RIGHT: medium none; PADDING-RIGHT: 0in; BORDER-TOP: #b5c4df 1pt solid; PADDING-LEFT: 0in; PADDING-BOTTOM: 0in; BORDER-LEFT: medium none; PADDING-TOP: 3pt; BORDER-BOTTOM: medium none">
<P class=MsoNormal><B><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: 'sans-serif'">From:</SPAN></B><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: 'sans-serif'"> bldg-sim-bounces@lists.onebuilding.org [mailto:bldg-sim-bounces@lists.onebuilding.org] <B>On Behalf Of </B>Jaigath Chandraprakash<BR><B>Sent:</B> Monday, October 04, 2010 9:01 AM<BR><B>To:</B> bldg-sim@lists.onebuilding.org<BR><B>Subject:</B> [Bldg-sim] Automatic Lighting Shutoff Mandatory Provision Question</SPAN></P></DIV></DIV>
<P class=MsoNormal> </P>
<DIV>
<DIV>
<DIV>
<P class=MsoNormal>Hello All,</P></DIV>
<DIV>
<P class=MsoNormal> </P></DIV>
<DIV>
<DIV>
<P class=MsoNormal>I am confused on the mandatory provision 9.4.1.1 which states that building larger than 5000 ft2 shall have automatic control device. Does it mean that mid-rise and high rise building cannot claim for credit in occupancy sensors shown in Table G3.2 because their GFA is more than 5000 ft2 and only small office can claim for this credit? I am sure I am not interpreting this section correct since from what I read, other modelers are claiming for savings for buildings with more than 5000 ft2 area for occupancy sensors even if mandatory requirements states that this is required which means baseline building will also have occupancy sensors.</P></DIV>
<DIV>
<P class=MsoNormal> </P></DIV>
<DIV>
<P class=MsoNormal>Can someone correct me on this? </P></DIV>
<DIV>
<P class=MsoNormal> </P></DIV>
<DIV>
<P class=MsoNormal>Thank you,</P></DIV>
<DIV>
<P class=MsoNormal> </P></DIV>
<DIV>
<P class=MsoNormal> </P></DIV>
<DIV>
<P class=MsoNormal>C. Jaigath </P></DIV></DIV></DIV></DIV>