<div>When you use WINDOW to calculate total window SHGC, you will find the SHGC will be reduced compared as the glaze one. It looks reasonable to me since the impact of window frame has been considered. From this point of view, the equation is not always correct. </div>
<div> </div>
<div>Cheney <br><br></div>
<div class="gmail_quote">On Fri, Sep 17, 2010 at 9:03 AM, D. Charlie Curcija <span dir="ltr"><<a href="mailto:curcija@designbuildersoftware.com">curcija@designbuildersoftware.com</a>></span> wrote:<br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">
<div lang="EN-US" vlink="purple" link="blue">
<div>
<p class="MsoNormal"><span style="COLOR: #1f497d; FONT-SIZE: 11pt">From this formula, it can be concluded that SHGC of frame is assumed to be 0.57, which is high. Very high. However, the formula may be provided for default (punitive) value if it does not have NFRC rating. This is to encourage people to get accurate NFRC values.</span></p>
<p class="MsoNormal"><span style="COLOR: #1f497d; FONT-SIZE: 11pt"> </span></p>
<p class="MsoNormal"><span style="COLOR: #1f497d; FONT-SIZE: 11pt">Charlie</span></p>
<p class="MsoNormal"><span style="COLOR: #1f497d; FONT-SIZE: 11pt"> </span></p>
<div>
<div style="BORDER-BOTTOM: medium none; BORDER-LEFT: medium none; PADDING-BOTTOM: 0in; PADDING-LEFT: 0in; PADDING-RIGHT: 0in; BORDER-TOP: #b5c4df 1pt solid; BORDER-RIGHT: medium none; PADDING-TOP: 3pt">
<p class="MsoNormal"><b><span style="FONT-SIZE: 10pt">From:</span></b><span style="FONT-SIZE: 10pt"> <a href="mailto:bldg-sim-bounces@lists.onebuilding.org" target="_blank">bldg-sim-bounces@lists.onebuilding.org</a> [mailto:<a href="mailto:bldg-sim-bounces@lists.onebuilding.org" target="_blank">bldg-sim-bounces@lists.onebuilding.org</a>] <b>On Behalf Of </b>Jon Matthews<br>
<b>Sent:</b> Friday, September 17, 2010 11:36 AM<br><b>To:</b> <a href="mailto:bldg-sim@lists.onebuilding.org" target="_blank">bldg-sim@lists.onebuilding.org</a><br><b>Subject:</b> [Bldg-sim] Assembly SHGC</span></p></div>
</div>
<div class="im">
<p class="MsoNormal"> </p>
<div>
<div>
<p class="MsoNormal">Hello All! I am confused to the formula that I found recently in the forum on Assembly SHGC. I think its SHGCassembly = 0.08 + (0.86)(SHGCglass) (cant find it now in the forum but I think it is something like this) which gives me a higher assembly SHGC of glass. Is this correct? I thought that assembly SHGC will be smaller than the SHGC of glass.</p>
</div>
<div>
<p class="MsoNormal"> </p></div>
<div>
<p class="MsoNormal">Thanks again to all!!</p></div>
<div>
<p class="MsoNormal"> </p></div>
<div>
<p class="MsoNormal">Jon</p></div></div>