<P>Vikram:</P>
<P> </P>
<P>I agree with James. Chiller energy would be measured in electric or gas units (energy input)..</P>
<P> </P>
<P>Ton-hours is a load (useful energy) function.</P>
<P> </P>
<P style="MARGIN: 0in 0in 0pt" class=MsoNormal><A name=_MailAutoSig><SPAN style="COLOR: #1f497d; mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes"><FONT face=Calibri>John R. Aulbach, PE, CEM<?xml:namespace prefix = o ns = "urn:schemas-microsoft-com:office:office" /><o:p></o:p></FONT></SPAN></A></P>
<P style="MARGIN: 0in 0in 0pt" class=MsoNormal><SPAN style="mso-bookmark: _MailAutoSig"><SPAN style="COLOR: #1f497d; mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes"><FONT face=Calibri>Senior Energy Engineer<o:p></o:p></FONT></SPAN></SPAN></P>
<DIV style="MARGIN: 0in 0in 0pt" class=MsoNormal><SPAN style="mso-bookmark: _MailAutoSig"><SPAN style="COLOR: #17365d; mso-fareast-font-family: 'Times New Roman'; mso-no-proof: yes"><FONT face=Calibri>
<HR style="COLOR: #17365d" align=left SIZE=2 width="30%" noShade>
</FONT></SPAN></SPAN></DIV>
<P style="MARGIN: 0in 0in 0pt" class=MsoNormal><FONT face=Calibri><SPAN style="mso-bookmark: _MailAutoSig"><B><SPAN style="FONT-VARIANT: small-caps; COLOR: navy; mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes">Partner</SPAN></B></SPAN><SPAN style="mso-bookmark: _MailAutoSig"><B><SPAN style="FONT-VARIANT: small-caps; COLOR: green; mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes"> </SPAN></B></SPAN><SPAN style="mso-bookmark: _MailAutoSig"><B><SPAN style="FONT-VARIANT: small-caps; COLOR: #006600; mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes">Energy</SPAN><SPAN style="FONT-VARIANT: small-caps; COLOR: navy; mso-no-proof: yes"><o:p></o:p></SPAN></B></SPAN></FONT></P>
<P style="MARGIN: 0in 0in 0pt" class=MsoNormal><SPAN style="mso-bookmark: _MailAutoSig"><SPAN style="COLOR: #1f497d; mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes"><FONT face=Calibri>1990 E. Grand Avenue, El Segundo, CA 90245<BR>W: 888-826-1216, X254| D: 310-765-7295 | F: 310-817-2745<o:p></o:p></FONT></SPAN></SPAN></P>
<P style="MARGIN: 0in 0in 0pt" class=MsoNormal><SPAN style="mso-bookmark: _MailAutoSig"></SPAN><A href="http://www.ptrenergy.com/"><FONT face=Calibri><SPAN style="mso-bookmark: _MailAutoSig"><SPAN style="mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes">www.ptrenergy.com</SPAN></SPAN><SPAN style="mso-bookmark: _MailAutoSig"></SPAN></FONT></A><SPAN style="mso-bookmark: _MailAutoSig"><SPAN style="COLOR: #1f497d; mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes"><FONT face=Calibri> </FONT></SPAN></SPAN><A href="mailto:%7C%20jaulbach@ptrenergy.com"><FONT face=Calibri><SPAN style="mso-bookmark: _MailAutoSig"><SPAN style="mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes">| jaulbach@ptrenergy.com</SPAN></SPAN><SPAN style="mso-bookmark: _MailAutoSig"></SPAN></FONT></A><SPAN style="mso-bookmark:
_MailAutoSig"><SPAN style="COLOR: #1f497d; mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes"><o:p></o:p></SPAN></SPAN></P><SPAN style="mso-bookmark: _MailAutoSig"></SPAN>
<P style="MARGIN: 0in 0in 0pt" class=MsoNormal><SPAN style="mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes"><o:p><FONT face=Calibri> </FONT></o:p></SPAN></P><BR>
<DIV style="FONT-FAMILY: times new roman, new york, times, serif; FONT-SIZE: 12pt"><FONT size=2 face=Tahoma>
<HR SIZE=1>
<B><SPAN style="FONT-WEIGHT: bold">From:</SPAN></B> "James V Dirkes II, PE" <jvd2pe@tds.net><BR><B><SPAN style="FONT-WEIGHT: bold">To:</SPAN></B> "Sami, Vikram" <Vikram.Sami@perkinswill.com>; "bldg-sim@lists.onebuilding.org" <Bldg-sim@lists.onebuilding.org><BR><B><SPAN style="FONT-WEIGHT: bold">Sent:</SPAN></B> Fri, September 10, 2010 2:30:19 PM<BR><B><SPAN style="FONT-WEIGHT: bold">Subject:</SPAN></B> Re: [Bldg-sim] A Question about chilled water usage<BR></FONT><BR>
<STYLE>
<!--
_filtered {font-family:"Cambria Math";panose-1:2 4 5 3 5 4 6 3 2 4;}
_filtered {font-family:Calibri;panose-1:2 15 5 2 2 2 4 3 2 4;}
_filtered {font-family:Tahoma;panose-1:2 11 6 4 3 5 4 4 2 4;}
p.MsoNormal, li.MsoNormal, div.MsoNormal
{margin:0in;margin-bottom:.0001pt;font-size:11.0pt;font-family:"sans-serif";}
a:link, span.MsoHyperlink
{color:blue;text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
{color:purple;text-decoration:underline;}
p.MsoAcetate, li.MsoAcetate, div.MsoAcetate
{margin:0in;margin-bottom:.0001pt;font-size:8.0pt;font-family:"sans-serif";}
span.BalloonTextChar
{font-family:"sans-serif";}
span.EmailStyle19
{font-family:"sans-serif";color:windowtext;}
span.EmailStyle20
{font-family:"sans-serif";color:#1F497D;}
.MsoChpDefault
{font-size:10.0pt;}
_filtered {margin:1.0in 1.0in 1.0in 1.0in;}
div.WordSection1
{}
-->
</STYLE>
<DIV class=WordSection1>
<P class=MsoNormal><SPAN style="COLOR: #1f497d"> </SPAN></P>
<P class=MsoNormal><SPAN style="COLOR: #1f497d">Dear Vikram,</SPAN></P>
<P class=MsoNormal><SPAN style="COLOR: #1f497d">I think that the definition of ton-hours is inherently an “cooling energy delivered” or “useful energy”, metric.</SPAN></P>
<P class=MsoNormal><SPAN style="COLOR: #1f497d"> </SPAN></P>
<DIV>
<P style="TEXT-ALIGN: center" class=MsoNormal align=center><B><SPAN style="FONT-FAMILY: 'serif'; COLOR: #1f497d; FONT-SIZE: 13.5pt">The Building Performance Team<BR></SPAN></B><B><SPAN style="FONT-FAMILY: 'serif'; COLOR: #1f497d; FONT-SIZE: 12pt">James V. Dirkes II, P.E., LEED AP<BR></SPAN></B><SPAN style="FONT-FAMILY: 'serif'; COLOR: #1f497d; FONT-SIZE: 12pt">1631 Acacia Drive NW<BR>Grand Rapids, MI 49504<BR>616 450 8653</SPAN></P></DIV>
<P class=MsoNormal><SPAN style="COLOR: #1f497d"> </SPAN></P>
<DIV>
<DIV style="BORDER-BOTTOM: medium none; BORDER-LEFT: medium none; PADDING-BOTTOM: 0in; PADDING-LEFT: 0in; PADDING-RIGHT: 0in; BORDER-TOP: #b5c4df 1pt solid; BORDER-RIGHT: medium none; PADDING-TOP: 3pt">
<P style="MARGIN-LEFT: 0.5in" class=MsoNormal><B><SPAN style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10pt">From:</SPAN></B><SPAN style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10pt"> bldg-sim-bounces@lists.onebuilding.org [mailto:bldg-sim-bounces@lists.onebuilding.org] <B>On Behalf Of </B>Sami, Vikram<BR><B>Sent:</B> Friday, September 10, 2010 4:23 PM<BR><B>To:</B> bldg-sim@lists.onebuilding.org<BR><B>Subject:</B> [Bldg-sim] A Question about chilled water usage</SPAN></P></DIV></DIV>
<P style="MARGIN-LEFT: 0.5in" class=MsoNormal> </P>
<P style="MARGIN-LEFT: 0.5in" class=MsoNormal>I’m looking at utility data for a building on a college campus that has a central utility plant. They list cooling energy in ton-hrs and It seems really high for all buildings across the board. </P>
<P style="MARGIN-LEFT: 0.5in" class=MsoNormal> </P>
<P style="MARGIN-LEFT: 0.5in" class=MsoNormal>However – if you assume that ton-hrs is the metered chilled water usage and not the chiller energy, its not that bad. For example if the chilled water usage is 1 ton-hrs, that’s 12,000 BTU’s of cooling energy delivered. However, if whats being measured is chilled water usage (and not chiller energy), then 1 ton-hr is not the energy consumed by the chiller – that should be 12,000BTU/COP of the chiller. So if the chiller COP is 4 – then that’s only 3,000 BTU’s of energy consumed to deliver that ton-hr.</P>
<P style="MARGIN-LEFT: 0.5in" class=MsoNormal> </P>
<P style="MARGIN-LEFT: 0.5in" class=MsoNormal>So – to get to the point – does anyone know if campuses monitor their chilled water usage (in ton-hrs) as chiller energy or cooling delivered?</P>
<P style="MARGIN-LEFT: 0.5in" class=MsoNormal> </P>
<P style="MARGIN-LEFT: 0.5in" class=MsoNormal>(I hope this makes snese)</P>
<P style="MARGIN-LEFT: 0.5in" class=MsoNormal> </P>
<P style="MARGIN-LEFT: 0.5in" class=MsoNormal><B><SPAN style="FONT-FAMILY: 'sans-serif'; COLOR: gray; FONT-SIZE: 9pt">Vikram Sami</SPAN></B><SPAN style="FONT-FAMILY: 'sans-serif'; COLOR: gray; FONT-SIZE: 9pt">, LEED AP</SPAN></P>
<P style="MARGIN-LEFT: 0.5in" class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; COLOR: gray; FONT-SIZE: 9pt">Sustainable Design Analyst</SPAN></P>
<P style="MARGIN-LEFT: 0.5in" class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; COLOR: gray; FONT-SIZE: 9pt">1382 Peachtree St. NE, Atlanta, GA 30309</SPAN></P>
<P style="MARGIN-LEFT: 0.5in" class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; COLOR: gray; FONT-SIZE: 9pt">t: 404-443-7462 f: </SPAN><SPAN style="FONT-FAMILY: 'sans-serif'; COLOR: gray; FONT-SIZE: 9pt" lang=ES>404.892.5823 </SPAN><SPAN style="FONT-FAMILY: 'sans-serif'; COLOR: gray; FONT-SIZE: 9pt"> e: vikram.sami@perkinswill.com </SPAN><A href="http://www.perkinswill.com/" rel=nofollow target=_blank><SPAN style="FONT-FAMILY: 'sans-serif'; COLOR: gray; FONT-SIZE: 9pt; TEXT-DECORATION: none">www.perkinswill.com</SPAN></A><SPAN style="FONT-FAMILY: 'sans-serif'; COLOR: gray; FONT-SIZE: 9pt"></SPAN></P>
<P style="MARGIN-BOTTOM: 3pt; MARGIN-LEFT: 0.5in; MARGIN-RIGHT: 0in" class=MsoNormal><B><SPAN style="FONT-FAMILY: 'sans-serif'; COLOR: gray; FONT-SIZE: 9pt">Perkins+Will.</SPAN></B><SPAN style="FONT-FAMILY: 'sans-serif'; COLOR: gray; FONT-SIZE: 9pt"> </SPAN><SPAN style="FONT-FAMILY: 'sans-serif'; COLOR: #add425; FONT-SIZE: 9pt">Ideas + buildings that honor the broader goals of society</SPAN><SPAN style="FONT-FAMILY: 'sans-serif'; COLOR: green; FONT-SIZE: 9pt"></SPAN></P>
<P style="MARGIN-LEFT: 0.5in" class=MsoNormal><B><SPAN style="FONT-FAMILY: 'sans-serif'; COLOR: gray; FONT-SIZE: 8pt"><IMG id=Picture_x0020_0 border=0 alt=75logo_only.gif src="cid:1.1163888661@web52801.mail.re2.yahoo.com" width=38 height=33></SPAN></B><SPAN style="FONT-FAMILY: 'sans-serif'; COLOR: gray; FONT-SIZE: 9pt">Years of Design Innovation</SPAN><B><SPAN style="FONT-FAMILY: 'sans-serif'; COLOR: gray; FONT-SIZE: 8pt"></SPAN></B></P>
<P style="MARGIN-BOTTOM: 0pt; MARGIN-LEFT: 0.5in; MARGIN-RIGHT: 0in" class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; COLOR: gray; FONT-SIZE: 6pt">This email and any files transmitted with it are confidential and intended solely for the addressee. </SPAN></P>
<P style="MARGIN-BOTTOM: 0pt; MARGIN-LEFT: 0.5in; MARGIN-RIGHT: 0in" class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; COLOR: gray; FONT-SIZE: 6pt">If you are not the named addressee you should not disseminate, distribute, copy, or alter this email.</SPAN></P>
<P style="MARGIN-LEFT: 0.5in" class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; COLOR: gray; FONT-SIZE: 6pt"> </SPAN></P>
<P style="MARGIN-LEFT: 0.5in" class=MsoNormal><B><SPAN style="FONT-FAMILY: 'sans-serif'; COLOR: gray; FONT-SIZE: 6pt">Please consider the environment before printing this email.</SPAN></B></P>
<P style="MARGIN-LEFT: 0.5in" class=MsoNormal> </P>
<P style="MARGIN-LEFT: 0.5in" class=MsoNormal> </P></DIV></DIV></DIV>
<P> </P></div><br>
</body></html>