<font face="Calibri">I just spent a while digging through all the
latest docs on modeling labs for a LEED analysis (90.1-2004,
90.1-2007, addenda, & Labs 21). This is my interpretation:<br>
</font>
<ul>
<li>If the <i>building</i> has fume hood exhaust over 15,000 cfm,
the Baseline system is VAV, and exhaust is turned down to at
least 50% for unoccupied hours. I am modeling the unoccupied
turn down rate the same in the Baseline as in the Proposed
models, because how low it can go at night depends on the type
of lab (ie: the project doesn't get more credit for turning down
to 20%). This is from Labs 21, and 90.1 (2004 or 2007) section
6.5.7.2.<br>
</li>
<li>A project can claim energy savings for demand controlled fume
hoods during occupied hours if the controls are automatic
(Labs21 has some schedules for guidance in modeling this).</li>
<li>Energy recovery is not modeled in the Baseline (see 90.1-2007
G3.1.2.10 Exception h).</li>
</ul>
Let me know if you have a different interpretation....I don't think
all these issues are laid out in detail for modelers yet.<br>
<font face="Calibri"><br>
</font>
<div class="moz-signature">
<meta http-equiv="content-type" content="text/html;
charset=ISO-8859-1">
<title></title>
<font color="#006600" face="Calibri"><b>Aleka Pappas</b></font><font
face="Calibri"><br>
</font>
<div class="moz-signature">
<div class="moz-signature">
<div class="moz-signature"><font face="Calibri"><small><font
color="#333399"><big><font color="#006600"><small>Building
Energy
Engineer</small></font></big></font></small></font>
<div class="moz-signature">
<div class="moz-signature">
<div class="moz-signature">
<div class="moz-signature">
<div class="moz-signature">
<div class="moz-signature">
<div class="moz-signature">
<div class="moz-signature">
<div class="moz-signature">
<pre class="moz-signature" cols="72"><font color="#333399" face="Calibri"><font color="#000066"><b>ENERMODAL ENGINEERING, INC.
</b><i>Inspiring energy and resource efficient buildings.</i><b>
</b><b><a class="moz-txt-link-abbreviated" href="http://www.enermodal.com/">www.enermodal.com</a></b>
</font><font color="#000066">1325 E. 16th Ave.
Denver, CO 80218
<a class="moz-txt-link-abbreviated" href="mailto:APappas@enermodal.com">APappas@enermodal.com</a>
Office: 303.861.2070/ Direct: 720.221.1082</font></font></pre>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
<br>
On 8/31/2010 12:35 PM, varun kulkarni wrote:
<blockquote
cite="mid:AANLkTinndohmsWvLHR72+ZZ4rkZ=gE1bkOUmhdh5kXeb@mail.gmail.com"
type="cite">
<div>I think it also depends on the software you are using to
model a fume hood. Because if exhaust is specified more than the
supply due to the hood, the software may disregard the lower
supply and equate the higher value of exhaust to the supply. I
am also trying to model a VAV exhaust fume hood and facing a
lot of problems doing it. So you have to figure out a way to
control you exhaust by altering your VAV supply.</div>
<div>If you know some other way, please let me know also :)<br>
<br>
</div>
<div class="gmail_quote">On Tue, Aug 31, 2010 at 2:23 PM, Sami,
Vikram <span dir="ltr"><<a moz-do-not-send="true"
href="mailto:Vikram.Sami@perkinswill.com">Vikram.Sami@perkinswill.com</a>></span>
wrote:<br>
<blockquote style="border-left: 1px solid rgb(204, 204, 204);
margin: 0px 0px 0px 0.8ex; padding-left: 1ex;"
class="gmail_quote">I think that depends on the total volume
of exhaust. I don't have it in front of me, but I think if
your exhaust is more than a certain amount you have to have
either energy recovery to fifty percent or vav flow.<br>
<br>
Sent from a mobile device<br>
<br>
-----Original Message-----<br>
From: Peter Simmonds [mailto:<a moz-do-not-send="true"
href="mailto:peter.simmonds@ibece.net">peter.simmonds@ibece.net</a>]<br>
Sent: Tuesday, August 31, 2010 12:09 PM Central Standard
Time<br>
To: <a moz-do-not-send="true"
href="mailto:bldg-sim@lists.onebuilding.org">bldg-sim@lists.onebuilding.org</a><br>
Subject: [Bldg-sim] Modeling fume hood exhausts<br>
<br>
Can anyone tell me when modeling a lab system with fume hoods
as to whether the baseline systems are to be modeled as
constant volume?<br>
<br>
(subsequent alternatives will have variable volume fume
hoods).<br>
<br>
<br>
<br>
Peter Simmonds,Ph.D.<br>
Senior Associate<br>
<br>
IBE Consulting Engineers<br>
14130 Riverside Drive, Suite 201<br>
Sherman Oaks, CA 91423<br>
p: (818) 377-8220 x246 f: (818) 377-8230<br>
<br>
<a moz-do-not-send="true" href="http://www.ibece.com/"
target="_blank">www.ibece.com</a> <<a
moz-do-not-send="true" href="http://www.ibece.com/"
target="_blank">http://www.ibece.com/</a>><br>
Ideas for the built environment<br>
<br>
This e-mail message, including any attachments, is for the
sole use of the intended recipient(s) and may contain
confidential and privileged information. Any unauthorized
review, use, disclosure, or distribution is prohibited. If you
are not the intended recipient, please contact the sender by
reply e-mail and destroy all copies of the original message.<br>
<br>
<br>
<br>
<br>
This email and any files transmitted with it are confidential
and intended solely for the addressee. If you are not the
named addressee you should not disseminate, distribute, copy,
or alter this email.<br>
_______________________________________________<br>
Bldg-sim mailing list<br>
<a moz-do-not-send="true"
href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org"
target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to
<a moz-do-not-send="true"
href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
</blockquote>
</div>
<br>
<br clear="all">
<br>
-- <br>
<p style="margin: 0in 0in 0pt;"><a moz-do-not-send="true"
name="SafeHtmlFilter__MailAutoSig"><span><font size="3"><font
face="Calibri">Thanks and Best Regards,</font></font></span></a></p>
<p style="margin: 0in 0in 0pt;"><span><span><font size="3"
face="Calibri"> </font></span></span></p>
<p style="margin: 0in 0in 0pt;"><span><span><font size="3"><font
face="Calibri">Sincerely,</font></font></span></span></p>
<p style="margin: 0in 0in 0pt;"><span><span><font size="3"><font
face="Calibri">Varun Kulkarni , M.S. , EIT</font></font></span></span></p>
<p style="margin: 0in 0in 0pt;"><span><span><font size="3"><font
face="Calibri">RMF Engineering</font></font></span></span></p>
<p style="margin: 0in 0in 0pt;"><span><span><font size="3"><font
face="Calibri">5520, Research Park Drive, Suite 300</font></font></span></span></p>
<p style="margin: 0in 0in 0pt;"><span><span><font size="3"><font
face="Calibri">Baltimore, MD - 21228</font></font></span></span></p>
<p style="margin: 0in 0in 0pt;"><span><span><font size="3"
face="Calibri"> </font></span></span></p>
<p style="margin: 0in 0in 0pt;"><span><span><font size="3"><font
face="Calibri">Office : 410-576-0505 ext. 5352</font></font></span></span></p>
<p style="margin: 0in 0in 0pt;"><span><span><font size="3"><font
face="Calibri">Mobile: (+1)405-385-1928</font></font></span></span></p>
<p style="margin: 0in 0in 0pt;"><span><span><font size="3"
face="Calibri"> </font></span></span></p>
<p style="margin: 0in 0in 0pt;"><span><span><font size="3"><font
face="Calibri">Note: Please do not print, unless
required.</font></font></span></span></p>
<p> </p>
<br>
<pre wrap="">
<fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
Bldg-sim mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a>
To unsubscribe from this mailing list send a blank message to <a class="moz-txt-link-abbreviated" href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
</blockquote>
</body>
</html>