<p>Dear all,<br>
<br>
I'm currently working for a R&D center on District Heating and Cooling system supplying 90c hot water, which is mandatory in the area. No way to change to other chiller or system.<br>
<br>
It easily meets EAp2 requirements on heating compared to baseline but fails to meet for cooling compared baseline (electrical centrifugal chiller)<br>
We have set up the baseline based on ASHRAE Appendix G assuming electrical one for cooling on the baseline.<br>
I wonder if there are any exceptional ways to solve this problem. (i.e. baseline with other district cooling system).<br>
COP of absortion chiller of design building is of course much lower than baseline(electric) but cost of hot water is not low enough to compensate this COP gap.<br>
<br>
thank you in advance for sharing your ideas on this.<br>
<ul>
<ul type="disc">
<li>any similar cases
<li>any way to be exempted from USGBC</ul>
</ul>
<br>
best regards,<br>
<p>
<table border="0" cellspacing="0" cellpadding="0">
<tr valign="top"><td width="105" rowspan="2" valign="middle"><img width="1" height="1" src="cid:1__=C6BBFD1DDF86341A8f9e8a@bureauveritas.com" border="0" alt=""></td><td width="358" valign="middle"><b><font size="2" face="Arial">Seyong Choi </font></b><b><font size="2"> CV << ?k</font></b></td><td width="37" valign="middle"><font size="4"> </font></td></tr>
<tr valign="top"><td width="395" colspan="2"><font size="2" face="Arial">LEED GA, Business Developer<br>
Industry & Facilities division<br>
Bureau Veritas Korea<br>
Rm 1102, Keungil Tower, 677-25, <br>
Yeoksam-dong, Kangnam-gu, Seoul<br>
Tel: +82 2 555 8871 Fax: +82 2 555 8940 M.P: +82 11 9558 6346</font><u><font size="2" color="#0000FF" face="Arial"><br>
</font></u><a href="http://www.bureauveritas.co.kr/"><u><font size="2" color="#0000FF" face="Arial">www.bureauveritas.co.kr</font></u></a></td></tr>
</table>
<p><font size="4"> </font></body></html>