Hi Vinay,<div><br></div><div>I presume by 'not higher always' you mean an object which varies airflow at the zone level depending on load (say you are modelling a VAV box in that zone). EnergyPlus doesn't look at the exhaust airflow requirements when figuring out the supply airflow to the zone. It calculates supply airflow based on what is needed to maintain space conditions assuming that this airflow does not exceed the max or min design airflow (take a look at the Engineering Reference included in EPlus documentation).</div>
<div><br></div><div>So the minimum supply airflow must be greater than the exhaust airflow at each timestep. </div><div><br></div><div>You can do this easily by ensuring that the VAV box max design airflow multiplied by the VAV box minimum airflow fraction is greater than the exhaust fan airflow.</div>
<div><br></div><div>Regards,</div><div>Paul<br><br><div class="gmail_quote">On 13 July 2010 14:30, Vinay Devanathan <span dir="ltr"><<a href="mailto:vinay.devanathan@gmail.com">vinay.devanathan@gmail.com</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex;">Paul,<br><br>Thanks for your reply. I understand that the supply airflow should be equal or greater than the exhaust airflow. But, the design airflow from auto-sized runs give me higher CFM than my exhaust fan CFM. But, the problem maybe, it is not higher always. Is there any method using which I can simulate my Zone Exhaust fan operation proportional to the supply fan operation so that the exhaust fan doesn't pull out a constant CFM?<br>
<br>Thank you.<br><br>Regards,<br><font color="#888888">Vinay</font><div><div></div><div class="h5"><br>
<br><div class="gmail_quote">On Tue, Jul 13, 2010 at 4:21 AM, Paul Raftery <span dir="ltr"><<a href="mailto:p.raftery@gmail.com" target="_blank">p.raftery@gmail.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0pt 0pt 0pt 0.8ex;border-left:1px solid rgb(204, 204, 204);padding-left:1ex">
Hi Vinay,<div><br></div><div>You are getting that error because EnergyPlus does not currently take exhaust fans into account when autosizing zone airflows. In your case, EnergyPlus sized the supply airflow for that zone lower than the exhaust flow rate, and that's why you are getting that error.</div>
<div><br></div><div>To fix this, you can 'force' the supply airflow to be equal to or larger than the exhaust airflow at all timesteps. You can do this by setting the autosize value in the airflow parameter for the air terminal unit object for that zone equal to the exhaust airflow. For example, where you are using constant volume reheat:</div>
<div><br></div><div><div>!- =========== ALL OBJECTS IN CLASS: AIRTERMINAL:SINGLEDUCT:CONSTANTVOLUME:REHEAT ===========</div><div><br></div><div>AirTerminal:SingleDuct:ConstantVolume:Reheat,</div><div> ObjectName, !- Name</div>
<div> Schedule, !- Availability Schedule Name</div><div> OutletNode, !- Air Outlet Node Name</div><div> InletNode, !- Air Inlet Node Name</div>
<div> autosize <b><u>(change this to exhaust airflow)</u></b>, !- Maximum Air Flow Rate {m3/s}</div><div> HWInletNode, !- Hot Water or Steam Inlet Node Name</div><div> RHCoilType, !- Reheat Coil Object Type</div>
<div> RHCoilName, !- Reheat Coil Name</div><div> autosize, !- Maximum Hot Water or Steam Flow Rate {m3/s}</div><div> 0, !- Minimum Hot Water or Steam Flow Rate {m3/s}</div>
<div> 0.001; !- Convergence Tolerance</div><div><br></div>Regards,</div><div>Paul</div><div><br><div class="gmail_quote"><div><div></div><div>On 12 July 2010 16:46, Vinay Devanathan <span dir="ltr"><<a href="mailto:vinay.devanathan@gmail.com" target="_blank">vinay.devanathan@gmail.com</a>></span> wrote:<br>
</div></div><blockquote class="gmail_quote" style="margin:0pt 0pt 0pt 0.8ex;border-left:1px solid rgb(204, 204, 204);padding-left:1ex"><div><div></div><div>Hello All,<br><br>I am using EnergyPlus to model a building according to ASHRAE App. G for baseline case. I included Zone exhaust fans in the baseline as advised, in a fashion similar to what is prescribed in the proposed design. But, when I auto-size the model with this Zone Exhaust Fan object, I get a warning message saying - <br>
<br>** ~~~ ** there is unbalanced exhaust air flow. <br>** ~~~ ** Unless there is balancing infiltration / ventilation air flow, this will result in<br>** ~~~ ** load due to induced outdoor air being neglected in the simulation.<br>
<br>And, I think the design loads are increased due to this, which would probably cause over-sizing. <br><br>Any help in solving this issue would be greatly appreciated. <br><br>Thank you.<br><br>Regards,<br><font color="#888888">Vinay<br>
</font><br></div></div>_______________________________________________<br>
Bldg-sim mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br><br clear="all"><br>-- <br>Regards,<br>Paul<br><br><br>=====================<br>Contact Details<br>=====================<br>Paul Raftery, BEng(Hons) (Mech), Fulbright Fellow, IRCSET Scholar<br>
Informatics Research Unit for Sustainable Engineering (IRUSE) Galway,<br>Department of Civil Engineering,<br>National University of Ireland, Galway,<br>University Road,<br>Galway,<br>Ireland.<br><br>Landline: +353 91 49 3086<br>
Mobile: +353 85 125 4999<br>Skype: praftery<br>
</div>
</blockquote></div><br>
</div></div></blockquote></div><br><br clear="all"><br>-- <br>Regards,<br>Paul<br><br><br>=====================<br>Contact Details<br>=====================<br>Paul Raftery, BEng(Hons) (Mech), Fulbright Fellow, IRCSET Scholar<br>
Informatics Research Unit for Sustainable Engineering (IRUSE) Galway,<br>Department of Civil Engineering,<br>National University of Ireland, Galway,<br>University Road,<br>Galway,<br>Ireland.<br><br>Landline: +353 91 49 3086<br>
Mobile: +353 85 125 4999<br>Skype: praftery<br>
</div>