<BODY contentEditable=true onload=parent.init()><P></P>
<P style="MARGIN: 0in 0in 0pt" class=MsoNormal><SPAN style="FONT-SIZE: 12pt"><FONT face=Calibri>The warehouse I am looking at is a rectangular building, just under 1.5 million sf and with a ceiling height of 41 ft.<SPAN style="mso-spacerun: yes">  </SPAN>Maximum occupancy is 50 people mostly in 12,000 sf of administrative offices with 10 ft ceiling. Why maintain the entire mass of air occupying the space volume in the warehouse at 75 deg F in summer and 70 deg F in winter?<SPAN style="mso-spacerun: yes">  </SPAN>Can the proposed warehouse model use just ventilation and save energy.<SPAN style="mso-spacerun: yes">  </SPAN>The percent energy savings for LEED certification is enormous.<SPAN style="mso-spacerun: yes">  </SPAN>Mechanical floors are heated (to prevent pipe freezing) and ventilated.<SPAN style="mso-spacerun: yes">  </SPAN>Underground parking is ventilated.<SPAN style="mso-spacerun: yes">  </SPAN>
Does ASHRAE Std90 for commercial buildings include industrial buildings (steel plants)? <SPAN style="mso-spacerun: yes"> </SPAN>The definition only mentions area and number floors.  I might have got it wrong.  I have only worked on commercial that house people.</FONT></SPAN></P>
<P><B></B> </P>
<P><B>----- Original Message -----</B></P>
<P></P><B>From</B>: James Hansen <JHANSEN@ghtltd.com>
<P></P><B>Date</B>: Thursday, June 10, 2010 7:02 pm
<P></P><B>Subject</B>: RE: [Bldg-sim] Warehouse
<P></P>
<P></P>> I�ve modeled a few self storage facilities before, and also had <BR>> this question.  As far as I could tell, System 7 really was the <BR>> right system for my baseline building, and my condensing furnaces <BR>> with split system AC units actually had less energy consumption <BR>> than the chilled water / boiler system.  Go figure�  <BR>> <BR>> <BR>> <BR>> From: bldg-sim-bounces@lists.onebuilding.org [mailto:bldg-sim- <BR>> bounces@lists.onebuilding.org] On Behalf Of Varkie C Thomas <BR>> Sent: Thursday, June 10, 2010 6:41 PM <BR>> To: Varkie C Thomas <BR>> Cc: 'bldg-sim@lists.onebuilding.org' <BR>> Subject: Re: [Bldg-sim] Warehouse <BR>> <BR>> <BR>> <BR>> Since I got no replies, it was must have been a dumb question.  I <BR>> assume Std90 systems and plant are for the baseline only and for <BR>> the proposed you can use something else.  A proposed packaged VAVS <BR>
> with furnace heating and DX cooling produced nearly the same <BR>> kbtu/sqft/yr (0.1 difference) as the baseline of chilled water and <BR>> hot water. <BR>> <BR>> <BR>> The information contained in this communication is confidential, <BR>> may be privileged, and is intended only for the use of the <BR>> addressee.  It is the property of GHT Limited.  Unauthorized use, <BR>> disclosure or copying of this communication or any part thereof is <BR>> strictly prohibited and may be unlawful.  If you have received <BR>> this communication in error, please notify me immediately by <BR>> return e-mail or by e-mail to ght@ghtltd.com, and destroy this <BR>> communication and all copies thereof, including all attachments.  <BR>> Thank you. <BR>> <BR>> <BR>> <BR>> </BODY>