<title>Sunspace Elements</title><link rel="stylesheet" type="text/css" href="../Theme/nav.css"><link rel="stylesheet" type="text/css" href="../Theme/lf.css"><link rel="stylesheet" type="text/css" href="../LinksExt/C1H_HTML.css"><link rel="stylesheet" type="text/css" href="../LinksExt/DOE22Vol3-Topics.css">


<div style="border-bottom: 1px solid rgb(153, 153, 153); position: relative; padding: 0px; background-color: transparent; width: 787px; display: none; border-top: 1px solid rgb(153, 153, 153); left: 0px;" id="nsbanner" class="d2h_main_nsbanner">

<div style="padding: 4px 10px 4px 22px; background-color: transparent; width: 100%; display: none;" id="TitleRow" class="d2h_main_titlerow">
<div style="display: none;" id="ienav" class="d2h_main_ienav">
<p class="d2h_main_linknav" align="left"><a id="D2HPrevious" class="D2HPreviousEnabled" href="spaceasasunspaces.htm"></a>  <a id="D2HNext" class="D2HNextEnabled" href="airflowcontrol.htm"></a></p></div></div></div>
<div style="padding: 5px 20px 0px 22px; background-color: transparent; width: 787px; height: 656px; overflow: auto; top: 0px;" id="nstext" class="d2h_main_nstext" valign="bottom">
<div style="padding: 0pt 0pt 10pt; margin: 0pt; width: 100%;" id="D2HTopicBody" class="d2h_main_topic">
<h3><a name="_Toc226183797">Sunspace Elements</a></h3>
<p class="BodyTextArialBold"><font style="background-color: rgb(49, 106, 197);" color="#ffffff">Interior Windows</font></p>
<p class="MsoBodyText"><font style="background-color: rgb(49, 106, 197);" color="#ffffff">Interior windows</font> can be specified by following an <font style="background-color: rgb(49, 106, 197);" color="#ffffff">INTERIOR</font>-WALL command by 
one or more <font style="background-color: rgb(49, 106, 197);" color="#ffffff">WINDOW</font> 
commands.  <font style="background-color: rgb(49, 106, 197);" color="#ffffff">Interior</font> 
walls can have <font style="background-color: rgb(49, 106, 197);" color="#ffffff">windows</font>. The keywords for <font style="background-color: rgb(49, 106, 197);" color="#ffffff">interior windows</font> are the 
same as those for exterior <font style="background-color: rgb(49, 106, 197);" color="#ffffff">windows</font>, with some exceptions:</p>
<p style="margin-left: 18pt;" class="MsoListNumber"><span style="font-family: &#39;Tms Rmn&#39;;">1.     </span>The following keywords are 
unused:<br><br>FRAME-WIDTH                   
SETBACK<br>GLARE-CTRL-PROB             
SHADING-DIVISION<br>GLASS-TYPE-SW                
SWITCH-CONTROL<br>GND-FORM-FACTOR           
SWITCH-SCH<br>INF-COEF                          SWITCH-SET-HI<br>LEFT-FIN-A, 
etc.                SWITCH-SET-LO<br>OVERHANG-A, etc.             
VIS-TRANS-SCH<br>RIGHT-FIN-A, etc.              WIN-SHADE-TYPE</p>
<p style="margin-left: 18pt;" class="MsoListNumber"><span style="font-family: &#39;Tms Rmn&#39;;">2.     </span>SKY-FORM-FACTOR multiplies the 
total diffuse radiation incident on an <font style="background-color: rgb(49, 106, 197);" color="#ffffff">interior window</font>.  If the <font style="background-color: rgb(49, 106, 197);" color="#ffffff">interior window</font> has a 
setback (relative to the sunspace) or there are obstructions inside the sunspace 
that shade the <font style="background-color: rgb(49, 106, 197);" color="#ffffff">interior 
window</font>, a value of SKY-FORM-FACTOR less than 1.0 should be specified (the 
default value is 1.0).</p>
<p class="MsoBodyText">Shading devices on <font style="background-color: rgb(49, 106, 197);" color="#ffffff">interior windows</font>, like Venetian blinds, drapes, or 
pull-down shades, can be simulated via the keywords SHADING-SCHEDULE and 
MAX-SOLAR-SCH.  Movable insulation on <font style="background-color: rgb(49, 106, 197);" color="#ffffff">interior windows</font> can be modeled using keywords 
CONDUCT-SCHEDULE and CONDUCT-TMIN-SCH.</p>
<p class="MsoBodyText">For an accurate calculation of the solar radiation 
transmitted by a sunspace <font style="background-color: rgb(49, 106, 197);" color="#ffffff">interior window</font>, it is important to specify the X and Y 
coordinates of the <font style="background-color: rgb(49, 106, 197);" color="#ffffff">window</font>.  These coordinates are measured with respect to the 
lower-left hand corner of the <font style="background-color: rgb(49, 106, 197);" color="#ffffff">INTERIOR</font>-WALL as viewed in the NEXT-TO space (see “<font style="background-color: rgb(49, 106, 197);" color="#ffffff">INTERIOR</font>-WALL Command” in 
the <i>DOE-2.2 Dictionary</i>). The position of exterior <font style="background-color: rgb(49, 106, 197);" color="#ffffff">windows</font> should also be 
carefully specified. The program will only recognize <font style="background-color: rgb(49, 106, 197);" color="#ffffff">interior windows</font> in an 
<font style="background-color: rgb(49, 106, 197);" color="#ffffff">interior</font> wall 
between a sunspace and a non-sunspace.</p>
<p class="MsoBodyText">Sliding glass doors can be modeled as <font style="background-color: rgb(49, 106, 197);" color="#ffffff">interior windows</font>.  If the 
<font style="background-color: rgb(49, 106, 197);" color="#ffffff">interior</font> wall 
containing the glass door has AIR-FLOW-TYPE = FREE-DOORWAY (see WALL-PARAMETERS, 
below), the door will be assumed to be open and convection through the opening 
will be calculated if T(sunspace) - T(adjacent space) &gt; AIR-FLOW-CTRL-DT.</p>
<p class="MsoBodyText">Additional control of the opening and closing of the door 
can be obtained by using SS-FLOW-SCH (see description of ZONE keywords, 
below).</p>
<p class="MsoBodyText">An unglazed opening in a sunspace <font style="background-color: rgb(49, 106, 197);" color="#ffffff">interior</font> wall can be 
input as a <font style="background-color: rgb(49, 106, 197);" color="#ffffff">window</font> 
with GLASS-TYPE-CODE = 0. The program will calculate the solar radiation passing 
through the opening by using a transmittance of 1.0 for all angles of incidence. 
WALL-PARAMETERS data, described below, would be entered for the <font style="background-color: rgb(49, 106, 197);" color="#ffffff">INTERIOR</font>-WALL to specify 
the convective air flow through the opening.</p>
<p class="BodyTextArialBold"><font style="background-color: rgb(49, 106, 197);" color="#ffffff">Interior</font> Doors</p>
<p class="MsoBodyText">Unlike exterior walls, <font style="background-color: rgb(49, 106, 197);" color="#ffffff">interior</font> walls in cannot 
have doors.  However, an opaque <font style="background-color: rgb(49, 106, 197);" color="#ffffff">interior</font> door with a conductance significantly different 
from the sunspace <font style="background-color: rgb(49, 106, 197);" color="#ffffff">interior</font> wall containing it can be input as a separate 
<font style="background-color: rgb(49, 106, 197);" color="#ffffff">interior</font> wall.  
Alternatively, the door can simply be ignored if the conduction across it is 
small compared to the overall conduction across the wall.  The program will 
calculate convection through a fully or partially open door if AIR-FLOW-TYPE = 
FREE-DOORWAY and appropriate values of DOORWAY-H and DOORWAY-W are specified 
(see WALL-PARAMETERS, below).</p>
<p class="BodyTextArialBold">Use Glass Type not Shading Coefficient for 
Sunspaces</p>
<p class="MsoBodyText">You should use GLASS-TYPE-CODE rather than SHADING-COEF for 
sunspace exterior <font style="background-color: rgb(49, 106, 197);" color="#ffffff">windows</font>. This allows the program to accurately calculate 
the hourly direct and diffuse radiation transmitted by the glazing.  This is not 
possible with SHADING-COEF except for standard 1/8&quot; clear glass.</p>
<p class="BodyTextArialBold">Use Custom Weighting Factors for Sunspaces</p>
<p class="MsoBodyText">Custom Weighting Factors (CWFs) should be used for 
sunspaces for several reasons:</p>
<p style="margin-left: 18pt;" class="MsoListNumber"><span style="font-family: &#39;Tms Rmn&#39;;">1.     </span>For high conductance spaces, the 
precalculated (ASHRAE) weighting factors overestimate heating and cooling 
loads.  The overestimate can be as high as 25-30% for heavily glazed spaces.</p>
<p style="margin-left: 18pt;" class="MsoListNumber"><span style="font-family: &#39;Tms Rmn&#39;;">2.     </span>CWFs account for loss of solar gain 
due to reflection of sunlight back out of exterior <font style="background-color: rgb(49, 106, 197);" color="#ffffff">windows</font>.</p>
<p style="margin-left: 18pt;" class="MsoListNumber"><span style="font-family: &#39;Tms Rmn&#39;;">3.     </span>CWFs give a more accurate 
calculation of the generally large temperature swings in a solar-driven 
space.</p>
<p style="margin-left: 18pt;" class="MsoListNumber"><span style="font-family: &#39;Tms Rmn&#39;;">4.     </span>CWFs will automatically be 
calculated for any space with FLOOR-WEIGHT = 0 (the default value).  Otherwise, 
the program will use ASHRAE weighting factors.</p>
<p class="BodyTextArialBold">Positioning Surfaces</p>
<p class="MsoBodyText">For an accurate calculation of solar radiation falling on 
the <font style="background-color: rgb(49, 106, 197);" color="#ffffff">interior</font> walls 
of a sunspace, the bounding surfaces of the sunspace need to be geometrically 
positioned. This applies to the exterior walls and roofs and their associated 
<font style="background-color: rgb(49, 106, 197);" color="#ffffff">windows</font>, and the 
<font style="background-color: rgb(49, 106, 197);" color="#ffffff">interior</font> walls and 
their associated <font style="background-color: rgb(49, 106, 197);" color="#ffffff">windows</font>. We recommend that a sunspace <font style="background-color: rgb(49, 106, 197);" color="#ffffff">interior</font> wall be defined 
in the sunspace rather than in the adjacent room.  Otherwise, the adjacent room 
must be properly located with respect to the sunspace.  If this is not done, the 
<font style="background-color: rgb(49, 106, 197);" color="#ffffff">interior</font> walls and 
<font style="background-color: rgb(49, 106, 197);" color="#ffffff">windows</font> will be 
mispositioned relative to the sunspace exterior <font style="background-color: rgb(49, 106, 197);" color="#ffffff">windows</font>, and the 
projection of solar radiation from the <font style="background-color: rgb(49, 106, 197);" color="#ffffff">windows</font> onto the <font style="background-color: rgb(49, 106, 197);" color="#ffffff">interior</font> walls will be incorrect.  This will give a wrong 
calculation of the solar radiation transferred from sunspace to room.  Even in 
this case, there will be no fictitious overall solar gain or loss since the 
solar that stays in the sunspace plus that transferred to adjacent rooms is 
constrained by the program to equal that entering the sunspace.  There will, 
however, be an error message if the transferred solar exceeds the entering 
solar, which would give a net negative solar gain in the sunspace.  This may 
occur if <font style="background-color: rgb(49, 106, 197);" color="#ffffff">interior</font> 
walls or <font style="background-color: rgb(49, 106, 197);" color="#ffffff">windows</font> on 
them overlap, if a multiplier is used on an <font style="background-color: rgb(49, 106, 197);" color="#ffffff">interior window</font>, or if a 
multiplier is used on rooms adjacent to a sunspace.</p>
<p class="BodyTextArialBold">Massive <font style="background-color: rgb(49, 106, 197);" color="#ffffff">Interior</font> Walls</p>
<p class="MsoBodyText">Sunspace <font style="background-color: rgb(49, 106, 197);" color="#ffffff">interior</font> walls are often fairly heavy, leading to a 
significant time delay in the heat transfer across them by conduction.  Such 
walls should be described by response factors, i.e., with a delayed-type 
construction.</p>
<p class="MsoBodyText">The order of defining layers in a delayed <font style="background-color: rgb(49, 106, 197);" color="#ffffff">interior</font> wall is from 
&quot;outside&quot; to &quot;inside&quot;, where &quot;outside&quot; is the side of the wall in the NEXT-TO 
space, and &quot;inside&quot; is the side in the space in which the wall was defined. If, 
as recommended, the <font style="background-color: rgb(49, 106, 197);" color="#ffffff">interior</font> wall is defined in the sunspace, then the outside 
of the wall is the side in the adjacent room.</p>
<p class="MsoBodyText">Delayed conduction through <font style="background-color: rgb(49, 106, 197);" color="#ffffff">interior</font> walls is 
calculated only for sunspace <font style="background-color: rgb(49, 106, 197);" color="#ffffff">interior</font> walls. For other <font style="background-color: rgb(49, 106, 197);" color="#ffffff">interior</font> walls the hourly 
conduction is quick.</p>
<p class="MsoBodyText">Delayed conduction through an <font style="background-color: rgb(49, 106, 197);" color="#ffffff">interior</font> between two 
non-sunspaces can be obtained simply by assigning SUNSPACE = YES to one of the 
spaces, even though the space is not actually a sunspace.  In this case, If the 
solar flux on the &quot;sunspace&quot; side of the wall is small, it is recommended that 
INSIDE-SOL-ABS = (0,0) be input for the wall in order to zero out absorption of 
solar radiation.  Otherwise, all <font style="background-color: rgb(49, 106, 197);" color="#ffffff">interior</font> and exterior walls and <font style="background-color: rgb(49, 106, 197);" color="#ffffff">windows</font> in the &quot;sunspace&quot; 
should be geometrically positioned as described above in &quot;Positioning of 
Sunspace Surfaces&quot;.</p>
<p class="BodyTextArialBold">Moisture from Plants and Trees</p>
<p class="MsoBodyText">Atriums often have plants and trees. Moisture transpiring 
from leaves and evaporating from soil can produce a significant latent load. You 
can model this load using the source keywords in SPACE as follows:</p>
<p class="DOE-2Input">   SOURCE-TYPE        = PROCESS<br>SOURCE-LATENT      = 
1.0<br>SOURCE-SENSIBLE    = 0.0<br>SOURCE-POWER       = [latent load in Btu/hr 
or W]<br>SOURCE-SCHEDULE    = U-name of schedule</p>
<p class="BodyTextArialBold">Baffles and Louvers</p>
<p class="MsoBodyText">Baffles and louvers on sunspace exterior <font style="background-color: rgb(49, 106, 197);" color="#ffffff">windows</font>, which block 
and/or diffuse incoming beam radiation, can be modeled as blinds using the <font style="background-color: rgb(49, 106, 197);" color="#ffffff">WINDOW</font>-LAYERS keyword in 
the <font style="background-color: rgb(49, 106, 197);" color="#ffffff">WINDOW</font> command. 
See “<font style="background-color: rgb(49, 106, 197);" color="#ffffff">Window</font> Layers 
Method” in the <font style="background-color: rgb(49, 106, 197);" color="#ffffff">Window</font> topic. The blinds can be <font style="background-color: rgb(49, 106, 197);" color="#ffffff">interior</font>, exterior or 
between pane. They can be controlled in different ways to manage solar 
gain.</p></div></div><br><br><div class="gmail_quote">On Thu, May 27, 2010 at 3:54 PM, Nick Caton <span dir="ltr">&lt;<a href="mailto:ncaton@smithboucher.com">ncaton@smithboucher.com</a>&gt;</span> wrote:<br><blockquote class="gmail_quote" style="margin: 0pt 0pt 0pt 0.8ex; border-left: 1px solid rgb(204, 204, 204); padding-left: 1ex;">










<div link="blue" vlink="purple" lang="EN-US">

<div>

<p class="MsoNormal"><span style="color: rgb(31, 73, 125);">Alan,  </span></p>

<p class="MsoNormal"><span style="color: rgb(31, 73, 125);"> </span></p>

<p class="MsoNormal"><span style="color: rgb(31, 73, 125);">To my understanding, you simply
cannot put a window on an interior wall.  The best approximation may be as
follows:</span></p>

<p><span style="color: rgb(31, 73, 125);"><span>1.<span style="font: 7pt &quot;Times New Roman&quot;;">      
</span></span></span><span style="color: rgb(31, 73, 125);">Keep the internal
wall in it’s entirety – this will model heat transfer to the
adjoining space correctly… if it’s a large internal window consider
adjusting the internal partition’s properties to match the effective
thermal mass/U-value.</span></p>

<p><span style="color: rgb(31, 73, 125);"><span>2.<span style="font: 7pt &quot;Times New Roman&quot;;">      
</span></span></span><span style="color: rgb(31, 73, 125);">Create a new
external wall, of any construction layers, on top of the interior wall with the
exact (maybe rounded) area of the window</span></p>

<p><span style="color: rgb(31, 73, 125);"><span>3.<span style="font: 7pt &quot;Times New Roman&quot;;">      
</span></span></span><span style="color: rgb(31, 73, 125);">Create a window on
that exterior wall with that exact area and with matching properties to the
real glazing with one exception:  Give it a ridiculously low U-value to effectively
eliminate what would be the modeled thermal transfer interactions with the
exterior.</span></p>

<p><span style="color: rgb(31, 73, 125);"><span>4.<span style="font: 7pt &quot;Times New Roman&quot;;">      
</span></span></span><span style="color: rgb(31, 73, 125);">Assign window shades
to model the solar shading effects of the adjacent space (ceiling/walls).</span></p>

<p class="MsoNormal"><span style="color: rgb(31, 73, 125);"> </span></p>

<p class="MsoNormal"><span style="color: rgb(31, 73, 125);">Best of luck!</span></p>

<p class="MsoNormal"><span style="color: rgb(31, 73, 125);"> </span></p>

<p class="MsoNormal"><span style="color: rgb(31, 73, 125);">~Nick</span></p>

<div>

<p class="MsoNormal"><span style="color: rgb(31, 73, 125);"><img src="cid:image002.jpg@01CAFDC5.8CBBE830" alt="cid:489575314@22072009-0ABB" width="119" height="37"></span><b><span style="color: rgb(45, 77, 94);"></span></b></p>


<p class="MsoNormal"><b><span style="color: rgb(45, 77, 94);"> </span></b></p>

<p class="MsoNormal"><b><span style="color: rgb(45, 77, 94);">NICK CATON, E.I.T.</span></b><b><span style="font-size: 12pt; color: rgb(45, 77, 94);"></span></b></p>

<p class="MsoNormal"><span style="font-size: 7.5pt; color: rgb(204, 153, 0);">PROJECT ENGINEER</span><span style="font-size: 7.5pt; font-family: &quot;Times New Roman&quot;,&quot;serif&quot;; color: rgb(204, 153, 0);"></span></p>


<p class="MsoNormal"><span style="font-size: 10pt; color: rgb(45, 77, 94);">25501 west
valley parkway</span></p>

<p class="MsoNormal"><span style="font-size: 10pt; color: rgb(45, 77, 94);">olathe ks 66061</span></p>

<p class="MsoNormal"><span style="font-size: 10pt; color: rgb(45, 77, 94);">direct 913
344.0036</span></p>

<p class="MsoNormal"><span style="font-size: 10pt; color: rgb(45, 77, 94);">fax 913
345.0617</span></p>

<p class="MsoNormal"><i><span style="font-size: 10pt; color: rgb(45, 77, 94);">Check out
our new web-site @ </span></i><span style="color: rgb(31, 73, 125);"><a href="http://www.smithboucher.com" title="blocked::www.smithboucher.com" target="_blank"><span style="font-size: 10pt;">www.smithboucher.com</span></a></span><u><span style="font-size: 10pt; color: blue;"> </span></u><span style="color: rgb(31, 73, 125);"></span></p>


</div>

<p class="MsoNormal"><span style="color: rgb(31, 73, 125);"> </span></p>

<div>

<div style="border-width: 1pt medium medium; border-style: solid none none; border-color: rgb(181, 196, 223) -moz-use-text-color -moz-use-text-color; padding: 3pt 0in 0in;">

<p class="MsoNormal"><b><span style="font-size: 10pt;">From:</span></b><span style="font-size: 10pt;">
<a href="mailto:bldg-sim-bounces@lists.onebuilding.org" target="_blank">bldg-sim-bounces@lists.onebuilding.org</a>
[mailto:<a href="mailto:bldg-sim-bounces@lists.onebuilding.org" target="_blank">bldg-sim-bounces@lists.onebuilding.org</a>] <b>On Behalf Of </b>Jackson,
Alan<br>
<b>Sent:</b> Thursday, May 27, 2010 5:47 PM<div class="im"><br>
<b>To:</b> <a href="mailto:bldg-sim@lists.onebuilding.org" target="_blank">bldg-sim@lists.onebuilding.org</a><br>
</div><b>Subject:</b> Re: [Bldg-sim] Interior window creation</span></p>

</div>

</div><div><div></div><div class="h5">

<p class="MsoNormal"> </p>

<p class="MsoNormal"><span style="color: rgb(31, 73, 125);">I am attaching the pd2 and inp,
just so someone can confirm they get the same error. I am on a 64-bit machine
so I have been getting weird warnings and error to begin with back when I was
using the wizard.</span></p>

<p class="MsoNormal"><span style="color: rgb(31, 73, 125);"> </span></p>

<div>

<p class="MsoNormal" style="margin-bottom: 12pt; line-height: 15pt;"><span style="font-size: 8pt; color: rgb(31, 73, 125);">Alan
Jackson, LEED AP<br>
KlingStubbins</span><span style="color: rgb(31, 73, 125);"></span></p>

</div>

<p class="MsoNormal"><span style="color: rgb(31, 73, 125);"> </span></p>

<div>

<div style="border-width: 1pt medium medium; border-style: solid none none; border-color: rgb(181, 196, 223) -moz-use-text-color -moz-use-text-color; padding: 3pt 0in 0in;">

<p class="MsoNormal"><b><span style="font-size: 10pt;">From:</span></b><span style="font-size: 10pt;">
<a href="mailto:bldg-sim-bounces@lists.onebuilding.org" target="_blank">bldg-sim-bounces@lists.onebuilding.org</a>
[mailto:<a href="mailto:bldg-sim-bounces@lists.onebuilding.org" target="_blank">bldg-sim-bounces@lists.onebuilding.org</a>] <b>On Behalf Of </b>Jackson,
Alan<br>
<b>Sent:</b> Thursday, May 27, 2010 6:43 PM<br>
<b>To:</b> <a href="mailto:bldg-sim@lists.onebuilding.org" target="_blank">bldg-sim@lists.onebuilding.org</a><br>
<b>Subject:</b> [Bldg-sim] Interior window creation</span></p>

</div>

</div>

<p class="MsoNormal"> </p>

<p class="MsoNormal">I am attempting to create an interior window to allow solar
gains to pass through a sunspace to an adjacent space. I am getting to the
following warning when attempting to create a window component on the interior
wall.</p>

<p class="MsoNormal"> </p>

<p class="MsoNormal"><img src="cid:image003.png@01CAFDC5.8CBBE830" width="428" border="0" height="119"></p>

<p class="MsoNormal"> </p>

<p class="MsoNormal">As a work around I changed the wall to EXTERIOR-WALL in
order to add the windows then planned on changing back to INTERIOR-WALL but
when I open the project I get a warning saying “A PARENT EXTERIOR-WALL
must be defined before ..”</p>

<p class="MsoNormal"> </p>

<p class="MsoNormal">I know you can create interior windows and use them in conjunction
with sunspaces as the DOE2 manual specifically calls out this scenario. </p>

<p class="MsoNormal"> </p>

<p class="MsoNormal">What am I doing wrong?</p>

<p class="MsoNormal"> </p>

<p class="MsoNormal"> </p>

<p class="MsoNormal" style="margin-bottom: 12pt; line-height: 15pt;"><span style="font-size: 8pt;">Alan Jackson,
LEED AP<br>
KlingStubbins</span><span style="font-size: 12pt; font-family: &quot;Times New Roman&quot;,&quot;serif&quot;;"></span></p>

<p class="MsoNormal"> </p>

</div></div></div>

</div>


<br>_______________________________________________<br>
Bldg-sim mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br><br clear="all"><br>-- <br>Carol Gardner PE<br>
<div style="visibility: hidden; display: inline;" id="avg_ls_inline_popup"></div><style type="text/css">#avg_ls_inline_popup {  position:absolute;  z-index:9999;  padding: 0px 0px;  margin-left: 0px;  margin-top: 0px;  width: 240px;  overflow: hidden;  word-wrap: break-word;  color: black;  font-size: 10px;  text-align: left;  line-height: 13px;}</style>