<table cellspacing="0" cellpadding="0" border="0" ><tr><td valign="top" style="font: inherit;"><DIV>Kendra,</DIV>
<DIV> </DIV>
<DIV>I don't think the PIU approach is really the same - for one you are not modelling the cooling at the zonal level with chilled water like a chilled beam works. </DIV>
<DIV> </DIV>
<DIV>I haven't modeled a chilled beam with a VAV supply before - mostly because in the projects I've used chilled beams (labs) you restrict the supply to only ventilation air which is a constant set normally to around 6ACH. Have you tried using the Induction unit and assigning a schedule to the fresh air? I think you can vary the amount of outside air to each zone that way. </DIV>
<DIV> </DIV>
<DIV>Vishnu - if this is a lab building 20% for fan energy is not completely out of the question. Couple of things to check:</DIV>
<DIV> </DIV>
<DIV>1. When you come out of th eQUEST wizard the fan energy tab is normally described in terms of static pressure and not kW/cfm. Make sure you set those to default to activate the kW/cfm. You might have already done this because the kW/cfm option generally doesn't show up unless you do this.</DIV>
<DIV>2. to check if the fan energy is coming from your DOAS - try zeroing out the fan energy on the DOAS and see if that reduces your fan contribution. That way at least  you'll know if your barking up the right tree. </DIV>
<DIV>3. If this is a lab, make sure you model your exhaust correctly. While Chilled beam systems don't use fan energy on the supply side, the labs will use fans on the exhust side. These will need to be captured on the zonal exhaust level. </DIV>
<DIV>4. Unless your supplying air neutral from the DOAS, you will need to capture the cooling effects of the supply air (Kendra - this is where it gets tricky for a VAV supply). </DIV>
<DIV> </DIV>
<DIV>Hope this helps<BR></DIV>
<DIV><FONT face="arial, helvetica, sans-serif" color=#8b8b8b><STRONG>Vikram Sami</STRONG></FONT></DIV>
<DIV><STRONG><FONT face=Arial color=#8b8b8b></FONT></STRONG> </DIV>
<DIV>
<HR>
<DIV></DIV><BR><BR>--- On <B>Thu, 5/6/10, Kendra Tupper <I><ktupper@rmi.org></I></B> wrote:<BR>
<BLOCKQUOTE style="PADDING-LEFT: 5px; MARGIN-LEFT: 5px; BORDER-LEFT: rgb(16,16,255) 2px solid"><BR>From: Kendra Tupper <ktupper@rmi.org><BR>Subject: Re: [Bldg-sim] modeling chilled beams in eQuest<BR>To: "Ellen Franconi" <efranconi@rmi.org><BR>Cc: "vishnu" <vishnu@kalpakrit.com>, "bldg-sim" <bldg-sim@lists.onebuilding.org><BR>Date: Thursday, May 6, 2010, 8:42 AM<BR><BR>
<DIV id=yiv1373623647>The other thing at work here is that the Induction units and the DOAS are constant volume, so you're going to pay a fan energy penalty for this - so first, make sure you only have one zone per Induction unit in eQUEST.  In real life, the DOAS can send variables amounts of air (based on load) to chilled beams, but this can't be modeled with the Dummy zone/DOAS approach. If you change the system type to a Power Induction Unit (which is a VAV) and you zero out the fan power, this might work.<BR><BR>There is no induction ratio parameter then, but I have played around with that parameter in eQUEST and seen almost no impact from varying it.<BR><BR>I am attempting to modeling an active chilled beam system served by a VAV DOAS right now, so if anyone else has comments on the Power Induction Unit approach, please let me know!<BR><BR><BR clear=all>Kendra Tupper, PE, LEED AP<BR>Senior Consultant<BR>Built Environment Team<BR><BR>Rocky
 Mountain Institute  |  T  303-567-8641 |  F  303-245-7213  |  <A href="http://www.rmi.org/" target=_blank rel=nofollow>www.rmi.org</A><BR><BR><BR>
<DIV class=gmail_quote>On Thu, May 6, 2010 at 9:37 AM, Ellen Franconi <SPAN dir=ltr><<A href="http://us.mc656.mail.yahoo.com/mc/compose?to=efranconi@rmi.org" target=_blank rel=nofollow ymailto="mailto:efranconi@rmi.org">efranconi@rmi.org</A>></SPAN> wrote:<BR>
<BLOCKQUOTE class=gmail_quote style="PADDING-LEFT: 1ex; MARGIN: 0pt 0pt 0pt 0.8ex; BORDER-LEFT: rgb(204,204,204) 1px solid">Vishnu,<BR>I am not sure I completely follow what you did but perhaps you are not aware that the induction unit system includes a central fan for pretreating outside air delivered to the induction units. So if you used the "outside air from sys" approach,the central fan of the induction unit would still be modeled with its default parameters. Also, if you don't set the induction ratio high enough (e.g. default is 3, max value is 10), you will get return air mixing with your supply (e.g it will no longer be 100% OA), which will make your supply air flow higher. This will increase your fan energy use as well. <BR><BR>I don't think the eQUEST documentation includes a description of the induction unit system (TPIU or FPIU) but its relevant keywords can found in the DOE2.1E BDL Summary. You could also insert the following commands in
 your input file.<BR><BR>DIAGNOSTICS  DEFAULTS ..   $ before the SYSTEM command and<BR>DIAGNOSTICS  CAUTIONS ..    $ after the SYSTEM command<BR><BR>Adding the above will show in the BDL file the value for all keywords not explicitly listed but with default values being used.<BR>Ellen<BR><BR>
<DIV class=gmail_quote>
<DIV>
<DIV></DIV>
<DIV class=h5>On Wed, May 5, 2010 at 11:14 PM, Vishnuraj Nair <SPAN dir=ltr><<A href="http://us.mc656.mail.yahoo.com/mc/compose?to=vishnu@kalpakrit.com" target=_blank rel=nofollow ymailto="mailto:vishnu@kalpakrit.com">vishnu@kalpakrit.com</A>></SPAN> wrote:<BR></DIV></DIV>
<BLOCKQUOTE class=gmail_quote style="PADDING-LEFT: 1ex; MARGIN: 0pt 0pt 0pt 0.8ex; BORDER-LEFT: rgb(204,204,204) 1px solid">
<DIV>
<DIV></DIV>
<DIV class=h5>
<DIV lang=EN-US>
<DIV>
<P class=MsoNormal><FONT face=Arial size=2><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">Dear friends,</SPAN></FONT></DIV>
<P class=MsoNormal><FONT face=Arial size=2><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Arial"> </SPAN></FONT></DIV>
<P class=MsoNormal><FONT face=Arial size=2><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">I am modeling the active chilled beams system using an induction unit. I have created a separate treated outside air system (TOAS) from where the fresh air would be supplied to </SPAN></FONT></DIV>
<P class=MsoNormal><FONT face=Arial size=2><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">the induction unit. I have hard coded the fresh air requirement for each zone at the outdoor air CFM field under outside air tab as well as under design flow cfm field under air flow tab</SPAN></FONT></DIV>
<P class=MsoNormal><FONT face=Arial size=2><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">so that the only the fresh air requirement is supplied to the zone. The cooling will be done by chilled beams modeled as induction unit.</SPAN></FONT></DIV>
<P class=MsoNormal><FONT face=Arial size=2><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Arial"> </SPAN></FONT></DIV>
<P class=MsoNormal><FONT face=Arial size=2><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">when I see the simulation report the amount of fan energy consumed is huge which is nearly about 20% percent of the overall energy consumption.</SPAN></FONT></DIV>
<P class=MsoNormal><FONT face=Arial size=2><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">So then I zeroed out the fan energy i.e kW/CFM for fans =0 and only the TOAS has the fan energy but the fan energy consumption decreased very little.</SPAN></FONT></DIV>
<P class=MsoNormal><FONT face=Arial size=2><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">I have no other source in the model for which the fan energy could be accountable for.</SPAN></FONT></DIV>
<P class=MsoNormal><FONT face=Arial size=2><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Arial"> </SPAN></FONT></DIV>
<P class=MsoNormal><FONT face=Arial size=2><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">Can anyone please tell what can be the reason for this or if I am missing out on something? </SPAN></FONT></DIV>
<P class=MsoNormal><FONT face=Arial size=2><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">Am I modeling the system right? How is the fan energy for this system to be modeled?</SPAN></FONT></DIV>
<P class=MsoNormal><FONT face=Arial size=2><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">Vishnuraj Nair</SPAN></FONT></DIV>
<P class=MsoNormal><FONT face=Arial size=2><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">Kalpakrit Sustainable Environments Pvt. Ltd.  </SPAN></FONT><FONT face=Garamond size=2><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Garamond"></SPAN></FONT></DIV>
<P class=MsoNormal><FONT face=Arial size=2><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">New Delhi</SPAN></FONT><FONT face=Garamond size=2><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Garamond"></SPAN></FONT></DIV>
<P class=MsoNormal><FONT face=Arial size=2><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">Tel: +91.124.4309490-92 Ext: 312 , Fax: +91.124.4309493</SPAN></FONT></DIV>
<P class=MsoNormal><FONT face=Arial size=2><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">E-mail : <A href="http://us.mc656.mail.yahoo.com/mc/compose?to=vishnu@kalpakrit.com" target=_blank rel=nofollow ymailto="mailto:vishnu@kalpakrit.com">vishnu@kalpakrit.com</A></SPAN></FONT><FONT size=2><SPAN style="FONT-SIZE: 10pt"></SPAN></FONT></DIV>
<P class=MsoNormal><I><FONT face=Arial size=1><SPAN style="FONT-SIZE: 8pt; FONT-STYLE: italic; FONT-FAMILY: Arial">Disclaimer: The information contained in this message is confidential and may be legally privileged. The message is intended solely for the addressee(s). If you are not the intended recipient, you are hereby notified that any use, dissemination, or reproduction is strictly prohibited and may be unlawful. If you are not the intended recipient, please contact the sender by return e-mail and destroy all copies of the original message. The views expressed in this e-mail message (including any attachments) are those of the individual sender except where the sender expressly, and with authority, states them to be the views of Kalpakrit or its group companies and the same shall be subject to the terms and conditions in governing contract in writing, if any. Kalpakrit or its group companies have all authority to check all emails being
 exchanged using the above address.</SPAN></FONT></I><FONT face=Arial size=1><SPAN style="FONT-SIZE: 8pt; FONT-FAMILY: Arial"></SPAN></FONT></DIV>
<P class=MsoNormal><FONT face="Times New Roman" size=1><SPAN style="FONT-SIZE: 8pt"> </SPAN></FONT></DIV>
<P class=MsoNormal><FONT face=Webdings color=#008040 size=4><SPAN style="FONT-SIZE: 13.5pt; COLOR: rgb(0,128,64); FONT-FAMILY: Webdings">ü</SPAN></FONT><FONT size=1><SPAN style="FONT-SIZE: 8pt"> </SPAN></FONT><FONT face="Arial Narrow" color=#008040 size=2><SPAN lang=EN-GB style="FONT-SIZE: 10pt; COLOR: rgb(0,128,64)">Please consider the environment before printing this email.</SPAN></FONT><FONT size=1><SPAN style="FONT-SIZE: 8pt"></SPAN></FONT></DIV>
<P class=MsoNormal><FONT face="Times New Roman" size=3><SPAN style="FONT-SIZE: 12pt"> </SPAN></FONT></DIV></DIV></DIV><BR></DIV></DIV>_______________________________________________<BR>Bldg-sim mailing list<BR><A href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" target=_blank rel=nofollow>http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</A><BR>To unsubscribe from this mailing list send  a blank message to <A href="http://us.mc656.mail.yahoo.com/mc/compose?to=BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG" target=_blank rel=nofollow ymailto="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</A><BR><BR></BLOCKQUOTE></DIV><BR><BR clear=all><BR>-- <BR>Ellen Franconi, PhD, LEED AP<BR>Senior Consultant, Built Environment Team<BR><BR>Rocky Mountain Institute<BR>1820 Folsom Street<BR>Boulder, CO 80302<BR>303.567.8609 (Desk)<BR>303.245.7213 (Fax)<BR><BR>Rocky Mountain Institute drives the
 efficient and restorative use of<BR>resources, creating a world thriving, verdant, and secure, for all, for ever.<BR><BR><A href="http://www.rmi.org/" target=_blank rel=nofollow>http://www.rmi.org</A><BR><BR>_______________________________________________<BR>Bldg-sim mailing list<BR><A href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" target=_blank rel=nofollow>http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</A><BR>To unsubscribe from this mailing list send  a blank message to <A href="http://us.mc656.mail.yahoo.com/mc/compose?to=BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG" target=_blank rel=nofollow ymailto="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</A><BR><BR></BLOCKQUOTE></DIV><BR></DIV><BR>-----Inline Attachment Follows-----<BR><BR>
<DIV class=plainMail>_______________________________________________<BR>Bldg-sim mailing list<BR><A href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" target=_blank>http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</A><BR>To unsubscribe from this mailing list send  a blank message to <A href="http://us.mc656.mail.yahoo.com/mc/compose?to=BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG" ymailto="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</A><BR></DIV></BLOCKQUOTE></td></tr></table><br>