<html>
<body>
Its an interesting problem because if the DAOU is a system has over 5000
cfm and over 70% OA the baseline system requires heat recovery
(G3.1.2.10).  I know because I asked the question of ASHRAE as an
Interpretation Request.  Even though the individual systems served
by the DAOU have less than 70% OA, the baseline systems still require
heat recovery of at least 50% effectiveness.<br><br>
At 11:53 AM 4/22/2010, Carol Gardner wrote:<br>
<blockquote type=cite class=cite cite="">In my opinion, it should not be
modeled in the baseline building and outdoor air should be added to the
systems. <br>
Carol<br><br>
On Thu, Apr 22, 2010 at 8:11 AM, Seth P. Spangler
<<a href="mailto:sspangle@rmf.com">sspangle@rmf.com</a>>
wrote:<br>

<dl><br>

<dd>Hello All,<br><br>

<dd> <br><br>

<dd>For the majority of the LEED projects I work on I decouple the space
load from the ventilation load by using a dedicated outdoor air unit
(DAOU). Before GBCI took over the review process the proposed and
baseline models contained the same number of systems meaning if we used a
DOAU in the proposed model  - we modeled the same unit in the
baseline. I recently received a comment to remove the DOAU from the
baseline and add the ventilation air to the space load systems. For that
particular model it didn’t have a very big impact so I didn’t think twice
about it.<br><br>

<dd> <br><br>

<dd>The question – should a DOAU be modeled in the baseline case or
should the outdoor air load be added to the mechanical systems that take
care of the space load?<br><br>

<dd> <br><br>

<dd>Thanks<br><br>

<dd> <br><br>

<dd>Seth Spangler, LEED® AP <br><br>

<dd>Project Engineer<br><br>

<dd> <br><br>

<dd>RMF Engineering, Inc <br><br>

<dd>Ph: (843) 971-9639 ext:1497<br><br>

<dd>Fax: (843) 971-9641 <br><br>

<dd><a href="mailto:sspangle@rmf.com">sspangle@rmf.com</a><br><br>

<dd>_______________________________________________<br>

<dd>Bldg-sim mailing list<br>

<dd>
<a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org">
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>

<dd>To unsubscribe from this mailing list send  a blank message to
<a href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">
BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a><br><br>

</dl><br>
_______________________________________________<br>
Bldg-sim mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" eudora="autourl">
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to
BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</blockquote>
<x-sigsep><p></x-sigsep>
<br>
Chris Jones<br>
14 Oneida Avenue<br>
Toronto, ON M5J 2E3.<br>
Tel.  416-203-7465<br>
Fax. 416-946-1005<br><br>
</body>
</html>