<!DOCTYPE HTML PUBLIC "-//W3C//DTD HTML 4.0 Transitional//EN">
<HTML><HEAD>
<META http-equiv=Content-Type content="text/html; charset=us-ascii">
<META content="MSHTML 6.00.6000.16981" name=GENERATOR></HEAD>
<BODY>
<DIV dir=ltr align=left><SPAN class=099524016-25032010><FONT face=Arial 
color=#0000ff size=2>Maybe you can tell me what the COP of a chiller means 
then, given that it varies with load, how do you come up with a single COP for a 
chiller?  Or is it just the average COP given the operating conditions that 
the chiller experiences?  Or are you talking about the integrated part load 
value?  </FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=099524016-25032010><FONT face=Arial 
color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=099524016-25032010><FONT face=Arial 
color=#0000ff size=2>But yes, however you define the efficiency, (COP, EER, or 
Power/Ton), I am geussing that the load removed per unit of input will have to 
increase by 25%.</FONT></SPAN></DIV>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left><SPAN 
class=099524016-25032010><FONT face=Arial color=#0000ff 
size=2> </FONT></SPAN></DIV>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left><SPAN 
class=099524016-25032010><FONT face=Arial color=#0000ff size=2>Matthew 
Kimball</FONT></SPAN></DIV>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left><SPAN 
class=099524016-25032010><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN> </DIV>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left><SPAN 
class=099524016-25032010> </SPAN></DIV>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>
<HR tabIndex=-1>
</DIV>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left><FONT face=Tahoma 
size=2><B>From:</B> bldg-sim-bounces@lists.onebuilding.org 
[mailto:bldg-sim-bounces@lists.onebuilding.org] <B>On Behalf Of </B>amit 
bhansali<BR><B>Sent:</B> Thursday, March 25, 2010 11:49 AM<BR><B>To:</B> 
bldg-sim@lists.onebuilding.org<BR><B>Subject:</B> [Bldg-sim] Chiller 
Efficiency<BR></FONT><BR></DIV>
<DIV></DIV>
<DIV><BR clear=all>Hi Bldg-Sim Community,</DIV>
<DIV>I had a confusion that you all might be help out.</DIV>
<DIV>When someone says that they want a chiller with 25% more efficiency than 
the baseline dictated by ASHRAE 90.1, does it mean the COP should be 25% 
greater?<BR>-- <BR>Thanks<BR><BR>Sincerely,<BR>Amit Bhansali, M.S. , 
EIT<BR>Command Commissioning, LLC<BR>8410, Sterling St<BR>Irving, TX  75063 
<BR><BR><A 
href="http://www.command-cx.com/">www.command-cx.com</A><BR><BR>Please do not 
print this e-mail unless necessary<BR></DIV><DIV> </DIV><br>NOTICE - This communication may contain confidential and privileged information that is for the sole use of the intended recipient. Any viewing, copying or distribution of, or reliance on this message by unintended recipients is strictly prohibited. If you have received this message in error, please notify us immediately by replying to the message and deleting it from your computer.</BODY></HTML>