<html><head><style type="text/css"><!-- DIV {margin:0px;} --></style></head><body><div style="font-family:times new roman, new york, times, serif;font-size:12pt"><DIV>Vishnu:</DIV>
<DIV> </DIV>
<DIV>I am guessing you let eQuest size the pumps. I will also bet you have the pumps set on STANDBY vs. DEMAND, Therefore, CHW pumps run all the time for the two chiller scenario, regardless if two chillers are needed.</DIV>
<DIV> </DIV>
<DIV>See if that helps.</DIV>
<DIV> </DIV>
<DIV><BR>
<P style="MARGIN: 0in 0in 0pt" class=MsoNormal><A name=_MailAutoSig><SPAN style="COLOR: #1f497d; mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes"><FONT face=Calibri>John R. Aulbach, PE, CEM<?xml:namespace prefix = o ns = "urn:schemas-microsoft-com:office:office" /><o:p></o:p></FONT></SPAN></A></P>
<P style="MARGIN: 0in 0in 0pt" class=MsoNormal><SPAN style="mso-bookmark: _MailAutoSig"><SPAN style="COLOR: #1f497d; mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes"><FONT face=Calibri>Senior Energy Engineer<o:p></o:p></FONT></SPAN></SPAN></P>
<DIV style="MARGIN: 0in 0in 0pt" class=MsoNormal><SPAN style="mso-bookmark: _MailAutoSig"><SPAN style="COLOR: #17365d; mso-fareast-font-family: 'Times New Roman'; mso-no-proof: yes"><FONT face=Calibri>
<HR style="COLOR: #17365d" align=left SIZE=2 width="30%" noShade>
</FONT></SPAN></SPAN></DIV>
<P style="MARGIN: 0in 0in 0pt" class=MsoNormal><FONT face=Calibri><SPAN style="mso-bookmark: _MailAutoSig"><B><SPAN style="FONT-VARIANT: small-caps; COLOR: navy; mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes">Partner</SPAN></B></SPAN><SPAN style="mso-bookmark: _MailAutoSig"><B><SPAN style="FONT-VARIANT: small-caps; COLOR: green; mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes"> </SPAN></B></SPAN><SPAN style="mso-bookmark: _MailAutoSig"><B><SPAN style="FONT-VARIANT: small-caps; COLOR: #006600; mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes">Energy</SPAN><SPAN style="FONT-VARIANT: small-caps; COLOR: navy; mso-no-proof: yes"><o:p></o:p></SPAN></B></SPAN></FONT></P>
<P style="MARGIN: 0in 0in 0pt" class=MsoNormal><SPAN style="mso-bookmark: _MailAutoSig"><SPAN style="COLOR: #1f497d; mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes"><FONT face=Calibri>1990 E. Grand Avenue, El Segundo, CA 90245<BR>W: 888-826-1216, X254| D: 310-765-7295 | F: 310-817-2745<o:p></o:p></FONT></SPAN></SPAN></P>
<P style="MARGIN: 0in 0in 0pt" class=MsoNormal><SPAN style="mso-bookmark: _MailAutoSig"></SPAN><A href="http://www.ptrenergy.com/"><FONT face=Calibri><SPAN style="mso-bookmark: _MailAutoSig"><SPAN style="mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes">www.ptrenergy.com</SPAN></SPAN><SPAN style="mso-bookmark: _MailAutoSig"></SPAN></FONT></A><SPAN style="mso-bookmark: _MailAutoSig"><SPAN style="COLOR: #1f497d; mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes"><FONT face=Calibri> </FONT></SPAN></SPAN><A href="mailto:%7C%20jaulbach@ptrenergy.com"><SPAN style="mso-bookmark: _MailAutoSig"><SPAN style="mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes"><FONT face=Calibri>| jaulbach@ptrenergy.com</FONT></SPAN></SPAN><SPAN style="mso-bookmark: _MailAutoSig"></SPAN></A><SPAN style="mso-bookmark:
 _MailAutoSig"><SPAN style="COLOR: #1f497d; mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes"><o:p></o:p></SPAN></SPAN></P></DIV>
<DIV style="FONT-FAMILY: times new roman, new york, times, serif; FONT-SIZE: 12pt"><BR>
<DIV style="FONT-FAMILY: times new roman, new york, times, serif; FONT-SIZE: 12pt"><FONT size=2 face=Tahoma>
<HR SIZE=1>
<B><SPAN style="FONT-WEIGHT: bold">From:</SPAN></B> Vishnuraj Nair <vishnu@kalpakrit.com><BR><B><SPAN style="FONT-WEIGHT: bold">To:</SPAN></B> bldg-sim@lists.onebuilding.org<BR><B><SPAN style="FONT-WEIGHT: bold">Sent:</SPAN></B> Wed, March 17, 2010 4:26:51 AM<BR><B><SPAN style="FONT-WEIGHT: bold">Subject:</SPAN></B> [Bldg-sim] Equest:Variation in pumping energy for Baseline system 8<BR></FONT><BR>
<STYLE>
<!--
 
 _filtered {font-family:Garamond;panose-1:2 2 4 4 3 3 1 1 8 3;}
 _filtered {font-family:Webdings;panose-1:5 3 1 2 1 5 9 6 7 3;}
 _filtered {font-family:"Arial Narrow";panose-1:2 11 5 6 2 2 2 3 2 4;}
 
p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0pt;margin-bottom:.0001pt;font-size:12.0pt;font-family:"Times New Roman";}
a:link, span.MsoHyperlink
        {color:blue;text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {color:purple;text-decoration:underline;}
span.EmailStyle17
        {font-family:Arial;color:windowtext;}
ins
        {text-decoration:none;}
span.msoIns
        {text-decoration:underline;}
 _filtered {margin:72.0pt 90.0pt 72.0pt 90.0pt;}
div.Section1
        {}
-->
</STYLE>

<DIV class=Section1>
<P class=MsoNormal><FONT size=2 face=Arial><SPAN style="FONT-FAMILY: Arial; FONT-SIZE: 10pt">Dear friends, </SPAN></FONT></P>
<P class=MsoNormal><FONT size=2 face=Arial><SPAN style="FONT-FAMILY: Arial; FONT-SIZE: 10pt">I am working on two projects of core and shell where the baseline system is system 8 i.e VAV with fan powered boxes.</SPAN></FONT></P>
<P class=MsoNormal><FONT size=2 face=Arial><SPAN style="FONT-FAMILY: Arial; FONT-SIZE: 10pt">There are two different building which are very similar in nature (not same) and situated at same location.</SPAN></FONT></P>
<P class=MsoNormal><FONT size=2 face=Arial><SPAN style="FONT-FAMILY: Arial; FONT-SIZE: 10pt">However there are differences in the way the two models are behaving.</SPAN></FONT></P>
<P class=MsoNormal><FONT size=2 face=Arial><SPAN style="FONT-FAMILY: Arial; FONT-SIZE: 10pt">I have shown the breakdown of different end uses as a percentage of overall baseline energy consumption</SPAN></FONT></P>
<P class=MsoNormal><B><FONT size=2 face=Arial><SPAN style="FONT-FAMILY: Arial; FONT-SIZE: 10pt; FONT-WEIGHT: bold"> </SPAN></FONT></B></P>
<P class=MsoNormal><B><FONT size=2 face=Arial><SPAN style="FONT-FAMILY: Arial; FONT-SIZE: 10pt; FONT-WEIGHT: bold">Project 1</SPAN></FONT></B></P>
<P class=MsoNormal><FONT size=2 face=Arial><SPAN style="FONT-FAMILY: Arial; FONT-SIZE: 10pt">Plug loads:        25.5 % </SPAN></FONT></P>
<P class=MsoNormal><FONT size=2 face=Arial><SPAN style="FONT-FAMILY: Arial; FONT-SIZE: 10pt">Interior Lighting: 16%</SPAN></FONT></P>
<P class=MsoNormal><FONT size=2 face=Arial><SPAN style="FONT-FAMILY: Arial; FONT-SIZE: 10pt">Cooling energy:  28.7%</SPAN></FONT></P>
<P class=MsoNormal><FONT size=2 face=Arial><SPAN style="FONT-FAMILY: Arial; FONT-SIZE: 10pt">Fan energy:       21%</SPAN></FONT></P>
<P class=MsoNormal><FONT size=2 face=Arial><SPAN style="FONT-FAMILY: Arial; FONT-SIZE: 10pt">Pumps:             <FONT color=red><SPAN style="COLOR: red">6.3 %</SPAN></FONT></SPAN></FONT></P>
<P class=MsoNormal><FONT size=2 face=Arial><SPAN style="FONT-FAMILY: Arial; FONT-SIZE: 10pt">Space heating:  0.1%</SPAN></FONT></P>
<P class=MsoNormal><FONT size=2 face=Arial><SPAN style="FONT-FAMILY: Arial; FONT-SIZE: 10pt">Domestic hot water + Exterior Lighting: 1.3 %</SPAN></FONT></P>
<P class=MsoNormal><B><FONT size=2 face=Arial><SPAN style="FONT-FAMILY: Arial; FONT-SIZE: 10pt; FONT-WEIGHT: bold"> </SPAN></FONT></B></P>
<P class=MsoNormal><B><FONT size=2 face=Arial><SPAN style="FONT-FAMILY: Arial; FONT-SIZE: 10pt; FONT-WEIGHT: bold">Project 2</SPAN></FONT></B></P>
<P class=MsoNormal><FONT size=2 face=Arial><SPAN style="FONT-FAMILY: Arial; FONT-SIZE: 10pt">Plug loads:        24 % </SPAN></FONT></P>
<P class=MsoNormal><FONT size=2 face=Arial><SPAN style="FONT-FAMILY: Arial; FONT-SIZE: 10pt">Interior lighting:  15%</SPAN></FONT></P>
<P class=MsoNormal><FONT size=2 face=Arial><SPAN style="FONT-FAMILY: Arial; FONT-SIZE: 10pt">Cooling energy:  18%</SPAN></FONT></P>
<P class=MsoNormal><FONT size=2 face=Arial><SPAN style="FONT-FAMILY: Arial; FONT-SIZE: 10pt">Fan energy:       25%</SPAN></FONT></P>
<P class=MsoNormal><FONT size=2 face=Arial><SPAN style="FONT-FAMILY: Arial; FONT-SIZE: 10pt">Pumps:             <FONT color=red><SPAN style="COLOR: red">15 %</SPAN></FONT></SPAN></FONT></P>
<P class=MsoNormal><FONT size=2 face=Arial><SPAN style="FONT-FAMILY: Arial; FONT-SIZE: 10pt">Space heating:  0.3%</SPAN></FONT></P>
<P class=MsoNormal><FONT size=2 face=Arial><SPAN style="FONT-FAMILY: Arial; FONT-SIZE: 10pt">Domestic hot water + Exterior Lighting: 1.3%</SPAN></FONT></P>
<P class=MsoNormal><FONT size=2 face=Arial><SPAN style="FONT-FAMILY: Arial; FONT-SIZE: 10pt"> </SPAN></FONT></P>
<P class=MsoNormal><FONT size=2 face=Arial><SPAN style="FONT-FAMILY: Arial; FONT-SIZE: 10pt"> </SPAN></FONT></P>
<P class=MsoNormal><FONT size=2 face=Arial><SPAN style="FONT-FAMILY: Arial; FONT-SIZE: 10pt">It can be seen that the energy consumed due to plug loads and interior lighting as a percentage of baseline are all most equal in both the cases.</SPAN></FONT></P>
<P class=MsoNormal><FONT size=2 face=Arial><SPAN style="FONT-FAMILY: Arial; FONT-SIZE: 10pt">Can anyone suggest possible explanation or give hints as to why the pumping energy as a percentage of baseline has more than doubled in the</SPAN></FONT></P>
<P class=MsoNormal><FONT size=2 face=Arial><SPAN style="FONT-FAMILY: Arial; FONT-SIZE: 10pt"> second case given that the characteristics of chiller, condenser and pump remain same ,given it is the baseline case. </SPAN></FONT></P>
<P class=MsoNormal><FONT size=2 face=Arial><SPAN style="FONT-FAMILY: Arial; FONT-SIZE: 10pt">One difference is that the first project uses two chillers as it has conditioned area more than 1, 20,000 sq ft while the second project has only</SPAN></FONT></P>
<P class=MsoNormal><FONT size=2 face=Arial><SPAN style="FONT-FAMILY: Arial; FONT-SIZE: 10pt"> one chiller ,its conditioned area being less than 1, 20,000</SPAN></FONT></P>
<P class=MsoNormal><FONT size=2 face=Arial><SPAN style="FONT-FAMILY: Arial; FONT-SIZE: 10pt">Vishnuraj Nair</SPAN></FONT></P>
<P class=MsoNormal><FONT size=2 face=Arial><SPAN style="FONT-FAMILY: Arial; FONT-SIZE: 10pt">Kalpakrit Sustainable Environments Pvt. Ltd.  </SPAN></FONT><FONT size=2 face=Garamond><SPAN style="FONT-FAMILY: Garamond; FONT-SIZE: 10pt"></SPAN></FONT></P>
<P class=MsoNormal><FONT size=2 face="Times New Roman"><SPAN style="FONT-SIZE: 10pt"><FONT face=Arial><SPAN style="FONT-FAMILY: Arial">New Delhi</SPAN></FONT><U style="TEXT-DECORATION: none"><SPAN class=msoIns> </SPAN></U><U style="TEXT-DECORATION: none"><SPAN class=msoIns></SPAN></U></SPAN></FONT><FONT size=2 face=Garamond><SPAN style="FONT-FAMILY: Garamond; FONT-SIZE: 10pt"></SPAN></FONT></P>
<P class=MsoNormal><FONT size=2 face=Arial><SPAN style="FONT-FAMILY: Arial; FONT-SIZE: 10pt">Tel: +91.124.4309490-92 Ext: 312 , Fax: +91.124.4309493</SPAN></FONT></P>
<P class=MsoNormal><FONT size=2 face=Arial><SPAN style="FONT-FAMILY: Arial; FONT-SIZE: 10pt">E-mail : </SPAN></FONT><A href="mailto:vishnu@kalpakrit.com" rel=nofollow target=_blank ymailto="mailto:vishnu@kalpakrit.com"><FONT size=2 face=Arial><SPAN style="FONT-FAMILY: Arial; FONT-SIZE: 10pt">vishnu@kalpakrit.com</SPAN></FONT></A><FONT size=2><SPAN style="FONT-SIZE: 10pt"></SPAN></FONT></P>
<P class=MsoNormal><I><FONT size=1 face=Arial><SPAN style="FONT-STYLE: italic; FONT-FAMILY: Arial; FONT-SIZE: 8pt">Disclaimer: The information contained in this message is confidential and may be legally privileged. The message is intended solely for the addressee(s). If you are not the intended recipient, you are hereby notified that any use, dissemination, or reproduction is strictly prohibited and may be unlawful. If you are not the intended recipient, please contact the sender by return e-mail and destroy all copies of the original message. The views expressed in this e-mail message (including any attachments) are those of the individual sender except where the sender expressly, and with authority, states them to be the views of Kalpakrit or its group companies and the same shall be subject to the terms and conditions in governing contract in writing, if any. Kalpakrit or its group companies have all authority to check all emails being
 exchanged using the above address.</SPAN></FONT></I><FONT size=1 face=Arial><SPAN style="FONT-FAMILY: Arial; FONT-SIZE: 8pt"></SPAN></FONT></P>
<P class=MsoNormal><FONT size=1 face="Times New Roman"><SPAN style="FONT-SIZE: 8pt"> </SPAN></FONT></P>
<P class=MsoNormal><FONT color=#008040 size=4 face=Webdings><SPAN style="FONT-FAMILY: Webdings; COLOR: #008040; FONT-SIZE: 13.5pt">ü</SPAN></FONT><FONT size=1><SPAN style="FONT-SIZE: 8pt"> </SPAN></FONT><FONT color=#008040 size=2 face="Arial Narrow"><SPAN style="FONT-FAMILY: 'Arial Narrow'; COLOR: #008040; FONT-SIZE: 10pt" lang=EN-GB>Please consider the environment before printing this email.</SPAN></FONT><FONT size=1><SPAN style="FONT-SIZE: 8pt"></SPAN></FONT></P>
<P class=MsoNormal><FONT size=3 face="Times New Roman"><SPAN style="FONT-SIZE: 12pt"> </SPAN></FONT></P></DIV></DIV></DIV></div><br>

      </body></html>