<html><head><style type="text/css"><!-- DIV {margin:0px;} --></style></head><body><div style="font-family:times new roman, new york, times, serif;font-size:12pt"><DIV>Is it correct that the EER and COP efficiencies listed in Tables 6.8.1 for packaged equipments includes fan energy thus I still have to separate fan power? Or are these effiency already exclude fan energy?</DIV>
<DIV> </DIV>
<DIV>So for a 2.85 COP, 375 cfm, 12000 Btu/h unit and using the fan power in Appendix G I would end up with baseline bhp of 0.323 and Pfan of .319 and COP of 4.19. Can anyone confirm this? I think the COP I am geting is too high for a baseline?</DIV>
<DIV> </DIV>
<DIV>Thanks.</DIV>
<DIV> </DIV>
<DIV> </DIV>
<DIV>Jaigath</DIV>