Hi Omer<div><br></div><div>Precision coolers/ACs in server rooms should not be counted under process energy but if your baseline case HVAC system type is 5, 6, 7 or 8 (Table G 3.1.1A) you can model a separate HVAC system type for server rooms as per exceptions to G3.1.1. This could be either system 3 or 4. </div>
<div><br></div><div>Regards<br><br><div class="gmail_quote">On 19 February 2010 02:09, <span dir="ltr"><<a href="mailto:omoltay@mimtarch.com">omoltay@mimtarch.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex;">
Dear All,<br>
<br>
Would you consider precision coolers in server rooms to be process energy?<br>
This is how I would like to apply in my model for LEED EAc1 (essentially<br>
not modelling any precision coolers and dumping it away under the default<br>
25% value for process energy). Any opinions?<br>
<br>
Thank you,<br>
<br>
Omer Moltay, LEED AP<br>
<br>
_______________________________________________<br>
Bldg-sim mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
</blockquote></div><br><br></div><div>Regards<br clear="all"><br>-- <br>Hisham Ahmad<br><br>Energy Analyst<br>Environmental Design Solutions Pvt Ltd.<br>New Delhi, India<br>+91-9873065488<br>