<font size="-1"><font face="Arial">Yes, that's the way it is.<br>
In one of our buildings we are using a 100% OA system and in another
with almost 50% OA where we are not cooling the air with a
refrigeration based cooling system for most part of the year.<br>
It uses Earth Air Tunnels Heat Exchanger and therefore we are able to
simply push through all the OA and release it in various zones via a
displacement ventilation system and finally exhaust it out above the
occupancy zone.<br>
Therefore, I feel that the OA for a baseline system must try and match
same ventilation rate and quality that the proposed system is meant to
provide!<br>
Best,<br>
Neeraj<br>
<br>
Neeraj Kapoor<br>
t: +91.99581.70018<br>
Kalpakrit Sustainable Environments PVt. Ltd.<br>
New Delhi, India<br>
<br>
</font></font>Vikram Sami wrote:
<blockquote
 cite="mid:55BA83825A482144A8637F9CAA981F761553F97E@las-mail.lordaecksargent.internal"
 type="cite">
  <style>
<!--
 
 _filtered {font-family:"Cambria Math";panose-1:2 4 5 3 5 4 6 3 2 4;}
 _filtered {font-family:Calibri;panose-1:2 15 5 2 2 2 4 3 2 4;}
 _filtered {font-family:Tahoma;panose-1:2 11 6 4 3 5 4 4 2 4;}
 _filtered {font-family:Garamond;panose-1:2 2 4 4 3 3 1 1 8 3;}
 _filtered {font-family:Webdings;panose-1:5 3 1 2 1 5 9 6 7 3;}
 _filtered {font-family:"Franklin Gothic Demi";panose-1:2 11 7 3 2 1 2 2 2 4;}
 
p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0in;margin-bottom:.0001pt;font-size:11.0pt;font-family:"Calibri", "sans-serif";}
a:link, span.MsoHyperlink
        {color:blue;text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {color:purple;text-decoration:underline;}
p.MsoAcetate, li.MsoAcetate, div.MsoAcetate
        {margin:0in;margin-bottom:.0001pt;font-size:8.0pt;font-family:"Tahoma", "sans-serif";}
span.BalloonTextChar
        {font-family:"Tahoma", "sans-serif";}
span.EmailStyle19
        {font-family:"Calibri", "sans-serif";color:windowtext;}
span.EmailStyle20
        {font-family:"Calibri", "sans-serif";color:#1F497D;}
span.EmailStyle21
        {font-family:"Calibri", "sans-serif";color:#1F497D;}
span.EmailStyle22
        {font-family:"Calibri", "sans-serif";color:#0000B4;}
.MsoChpDefault
        {font-size:10.0pt;}
 _filtered {margin:1.0in 1.0in 1.0in 1.0in;}
div.Section1
        {}
-->
  </style>
  <div class="Section1">
  <p class="MsoNormal"><span style="color: rgb(0, 0, 180);">I always
assumed that if you
went to 30% extra, you kept the baseline at 100%, and the designed
building at
130%, but after reading this, it does seem to make sense that you would
increase both occurrences. </span></p>
  <p class="MsoNormal"><span style="color: rgb(0, 0, 180);"> </span></p>
  <p class="MsoNormal"><span style="color: rgb(0, 0, 180);">Can anyone
from the EA Tag chime
in?</span></p>
  <p class="MsoNormal"><span style="color: rgb(0, 0, 180);"> </span></p>
  <div>
  <p class="MsoNormal" style=""><b><span
 style="font-size: 12pt; font-family: &quot;Garamond&quot;,&quot;serif&quot;; color: black;">Vikram
Sami,</span></b><span
 style="font-size: 12pt; font-family: &quot;Times New Roman&quot;,&quot;serif&quot;; color: rgb(0, 0, 180);">
  </span><span
 style="font-size: 12pt; font-family: &quot;Garamond&quot;,&quot;serif&quot;; color: black;">LEED
AP</span><span
 style="font-size: 12pt; font-family: &quot;Times New Roman&quot;,&quot;serif&quot;; color: rgb(0, 0, 180);">
  <br>
  </span><span
 style="font-size: 12pt; font-family: &quot;Garamond&quot;,&quot;serif&quot;; color: black;">Direct
Phone 404-253-1466 | Direct Fax 404-253-1366</span><span
 style="font-size: 12pt; font-family: &quot;Times New Roman&quot;,&quot;serif&quot;; color: rgb(0, 0, 180);">
  </span></p>
  <p class="MsoNormal" style=""><b><span
 style="font-size: 12pt; font-family: &quot;Garamond&quot;,&quot;serif&quot;; color: maroon;">L</span></b><b><span
 style="font-size: 10pt; font-family: &quot;Garamond&quot;,&quot;serif&quot;; color: maroon;">ORD</span></b><b><span
 style="font-size: 12pt; font-family: &quot;Garamond&quot;,&quot;serif&quot;; color: maroon;">,
A</span></b><b><span
 style="font-size: 10pt; font-family: &quot;Garamond&quot;,&quot;serif&quot;; color: maroon;">ECK</span></b><b><span
 style="font-size: 12pt; font-family: &quot;Garamond&quot;,&quot;serif&quot;; color: maroon;">
&amp; S</span></b><b><span
 style="font-size: 10pt; font-family: &quot;Garamond&quot;,&quot;serif&quot;; color: maroon;">ARGENT</span></b><b><span
 style="font-size: 12pt; font-family: &quot;Garamond&quot;,&quot;serif&quot;; color: maroon;">
A</span></b><b><span
 style="font-size: 10pt; font-family: &quot;Garamond&quot;,&quot;serif&quot;; color: maroon;">RCHITECTURE</span></b><b><span
 style="font-size: 12pt; font-family: &quot;Times New Roman&quot;,&quot;serif&quot;; color: rgb(0, 0, 180);"><br>
  <br>
  </span></b><span
 style="font-size: 12pt; font-family: &quot;Times New Roman&quot;,&quot;serif&quot;; color: rgb(0, 0, 180);"></span></p>
  </div>
  <p class="MsoNormal"><span style="color: rgb(0, 0, 180);"> </span></p>
  <div>
  <div
 style="border-style: solid none none; border-color: rgb(181, 196, 223) -moz-use-text-color -moz-use-text-color; border-width: 1pt medium medium; padding: 3pt 0in 0in;">
  <p class="MsoNormal"><b><span
 style="font-size: 10pt; font-family: &quot;Tahoma&quot;,&quot;sans-serif&quot;;">From:</span></b><span
 style="font-size: 10pt; font-family: &quot;Tahoma&quot;,&quot;sans-serif&quot;;">
<a class="moz-txt-link-abbreviated" href="mailto:bldg-sim-bounces@lists.onebuilding.org">bldg-sim-bounces@lists.onebuilding.org</a>
[<a class="moz-txt-link-freetext" href="mailto:bldg-sim-bounces@lists.onebuilding.org">mailto:bldg-sim-bounces@lists.onebuilding.org</a>] <b>On Behalf Of </b>Nathan
Miller<br>
  <b>Sent:</b> Thursday, November 19, 2009 4:42 PM<br>
  <b>To:</b> 'Rimes, Christie'; 'Steven Rutter';
<a class="moz-txt-link-abbreviated" href="mailto:bldg-sim@lists.onebuilding.org">bldg-sim@lists.onebuilding.org</a><br>
  <b>Subject:</b> Re: [Bldg-sim] Baseline Modeling for LEED</span></p>
  </div>
  </div>
  <p class="MsoNormal"> </p>
  <p class="MsoNormal"><span style="color: rgb(31, 73, 125);">I
disagree, I believe the models
should be same-same on ventilation rates. See section 90.1 (2004)
Section
G3.1.2.5. It states:</span></p>
  <p class="MsoNormal"><span style="color: rgb(31, 73, 125);"> </span></p>
  <p class="MsoNormal"><span style="color: rgb(31, 73, 125);">&#8220;Minimum
outdoor air
ventilation rates should be the same for the proposed and baseline
building
designs.&#8221;</span></p>
  <p class="MsoNormal"><span style="color: rgb(31, 73, 125);"> </span></p>
  <p class="MsoNormal"><span style="color: rgb(31, 73, 125);">In my
projects (including those
that include 30% additional outside air), I have always used the same
outdoor
air flow rates, unless I was taking credit for demand control
ventilation in
the proposed case (see the exception allowed in that same ASHRAE
section). </span></p>
  <p class="MsoNormal"><span style="color: rgb(31, 73, 125);"> </span></p>
  <div>
  <p class="MsoNormal"><span
 style="font-size: 12pt; font-family: &quot;Franklin Gothic Demi&quot;,&quot;sans-serif&quot;; color: rgb(31, 73, 125);">Nathan
Miller</span><span
 style="font-size: 12pt; font-family: &quot;Times New Roman&quot;,&quot;serif&quot;; color: rgb(31, 73, 125);"></span></p>
  <p class="MsoNormal"><i><span
 style="font-size: 10pt; font-family: &quot;Times New Roman&quot;,&quot;serif&quot;; color: rgb(31, 73, 125);">Senior
Energy Engineer/Mechanical Engineer</span></i></p>
  <p class="MsoNormal"><span
 style="font-size: 10pt; font-family: &quot;Times New Roman&quot;,&quot;serif&quot;; color: rgb(31, 73, 125);">direct:
206.788.4577</span></p>
  <p class="MsoNormal"><span
 style="font-size: 10pt; font-family: &quot;Times New Roman&quot;,&quot;serif&quot;; color: rgb(31, 73, 125);">fax:
206.285.7111 </span><span style="color: rgb(31, 73, 125);"></span></p>
  </div>
  <p class="MsoNormal"><span style="color: rgb(31, 73, 125);"> </span></p>
  <div>
  <div
 style="border-style: solid none none; border-color: rgb(181, 196, 223) -moz-use-text-color -moz-use-text-color; border-width: 1pt medium medium; padding: 3pt 0in 0in;">
  <p class="MsoNormal"><b><span
 style="font-size: 10pt; font-family: &quot;Tahoma&quot;,&quot;sans-serif&quot;;">From:</span></b><span
 style="font-size: 10pt; font-family: &quot;Tahoma&quot;,&quot;sans-serif&quot;;">
<a class="moz-txt-link-abbreviated" href="mailto:bldg-sim-bounces@lists.onebuilding.org">bldg-sim-bounces@lists.onebuilding.org</a>
[<a class="moz-txt-link-freetext" href="mailto:bldg-sim-bounces@lists.onebuilding.org">mailto:bldg-sim-bounces@lists.onebuilding.org</a>] <b>On Behalf Of </b>Rimes,
Christie<br>
  <b>Sent:</b> Thursday, November 19, 2009 1:32 PM<br>
  <b>To:</b> Steven Rutter; <a class="moz-txt-link-abbreviated" href="mailto:bldg-sim@lists.onebuilding.org">bldg-sim@lists.onebuilding.org</a><br>
  <b>Subject:</b> Re: [Bldg-sim] Baseline Modeling for LEED</span></p>
  </div>
  </div>
  <p class="MsoNormal"> </p>
  <p class="MsoNormal"><span style="color: rgb(31, 73, 125);">In my
experience you do
not increase the baseline energy model as you are being awarded
(gaining that
point) when you achieve the ventilation credit. There are a few similar
situations in LEED where by achieving one credit will prevent you from
achieving
another but this happens to everyone so it works out to be somewhat
fair. </span></p>
  <p class="MsoNormal"><span style="color: rgb(31, 73, 125);"> </span></p>
  <div>
  <p class="MsoNormal"><span style="color: rgb(31, 73, 125);"><img
 id="_x0000_i1026" src="cid:part1.07050109.05010208@yahoo.com"
 alt="Christie Rimes, 
Building Simulation Analyst
WSP Flack + Kurtz
405 Howard Street, Suite 500
San Francisco, CA 94105
Direct: 415.402.2727
Main Tel: 415.398.3833
Fax: 415.433.5311
website: http://www.wspfk.com
vCard: http://vcards.wspfk.com/vcardloader.php?filename=flackkurtz-christie-rimes-wspfk-com-1255981339.vcf
image: "
 height="170" width="591"></span></p>
  </div>
  <p class="MsoNormal"><span style="color: rgb(31, 73, 125);"> </span></p>
  <div>
  <div
 style="border-style: solid none none; border-color: rgb(181, 196, 223) -moz-use-text-color -moz-use-text-color; border-width: 1pt medium medium; padding: 3pt 0in 0in;">
  <p class="MsoNormal"><b><span
 style="font-size: 10pt; font-family: &quot;Tahoma&quot;,&quot;sans-serif&quot;;">From:</span></b><span
 style="font-size: 10pt; font-family: &quot;Tahoma&quot;,&quot;sans-serif&quot;;">
<a class="moz-txt-link-abbreviated" href="mailto:bldg-sim-bounces@lists.onebuilding.org">bldg-sim-bounces@lists.onebuilding.org</a>
[<a class="moz-txt-link-freetext" href="mailto:bldg-sim-bounces@lists.onebuilding.org">mailto:bldg-sim-bounces@lists.onebuilding.org</a>] <b>On Behalf Of </b>Steven
Rutter<br>
  <b>Sent:</b> Thursday, November 19, 2009 1:25 PM<br>
  <b>To:</b> <a class="moz-txt-link-abbreviated" href="mailto:bldg-sim@lists.onebuilding.org">bldg-sim@lists.onebuilding.org</a><br>
  <b>Subject:</b> [Bldg-sim] Baseline Modeling for LEED</span></p>
  </div>
  </div>
  <p class="MsoNormal"> </p>
  <p class="MsoNormal">All,</p>
  <p class="MsoNormal">There is a credit in LEED (EQc2.0) that involves
increasing
the required ventilation rate by 30%. In trying to achieve this credit,
the amount of energy would have to increase to condition that
additional 30%
OSA. Does anyone know if you are supposed to increase the baseline
energy
model&#8217;s ventilation rate so it has the same ventilation rate as the
proposed building? Thank you in advance for your help.</p>
  <p class="MsoNormal"> </p>
  <p class="MsoNormal"> </p>
  <p class="MsoNormal"><b><span
 style="font-family: &quot;Tahoma&quot;,&quot;sans-serif&quot;; color: gray;">Steven
Rutter, LEED</span></b><b><sup><span
 style="font-size: 9pt; font-family: &quot;Tahoma&quot;,&quot;sans-serif&quot;; color: gray;">&reg;</span></sup></b><b><sup><span
 style="font-family: &quot;Tahoma&quot;,&quot;sans-serif&quot;; color: gray;"> </span></sup></b><b><span
 style="font-family: &quot;Tahoma&quot;,&quot;sans-serif&quot;; color: gray;">AP, EIT</span></b></p>
  <p class="MsoNormal"> </p>
  <p class="MsoNormal" style="margin-bottom: 12pt;"><img
 id="Picture_x0020_1" src="cid:part2.00040106.00030106@yahoo.com"
 alt="cid:665444518@16012009-36B3" height="44" width="180"><br>
  <b><span style="font-family: &quot;Tahoma&quot;,&quot;sans-serif&quot;; color: gray;">3850
Happy
Lane|Sacramento, CA 95827<br>
O:916-368-0336|F:916-368-0337|C:916-717-7484</span></b><span
 style="font-family: &quot;Times New Roman&quot;,&quot;serif&quot;;"></span></p>
  <p class="MsoNormal" style=""><span
 style="font-size: 18pt; font-family: Webdings; color: green;">P</span><span
 style="font-size: 12pt; font-family: &quot;Times New Roman&quot;,&quot;serif&quot;;"> </span><span
 style="font-size: 7.5pt; font-family: &quot;Arial&quot;,&quot;sans-serif&quot;; color: green;">Please
consider the environment before printing this email.</span><span
 style="font-size: 12pt; font-family: &quot;Times New Roman&quot;,&quot;serif&quot;;"> </span></p>
  <p class="MsoNormal"> </p>
  <p class="MsoNormal"> </p>
  </div>
</blockquote>
<br>



      <!--1--><hr size=1></hr> 
The INTERNET now has a personality. YOURS! <a href="http://in.rd.yahoo.com/tagline_yyi_1/*http://in.yahoo.com/" target="_blank">See your Yahoo! Homepage</a>.</body></html>