<html xmlns:v="urn:schemas-microsoft-com:vml" xmlns:o="urn:schemas-microsoft-com:office:office" xmlns:w="urn:schemas-microsoft-com:office:word" xmlns:x="urn:schemas-microsoft-com:office:excel" xmlns:p="urn:schemas-microsoft-com:office:powerpoint" xmlns:a="urn:schemas-microsoft-com:office:access" xmlns:dt="uuid:C2F41010-65B3-11d1-A29F-00AA00C14882" xmlns:s="uuid:BDC6E3F0-6DA3-11d1-A2A3-00AA00C14882" xmlns:rs="urn:schemas-microsoft-com:rowset" xmlns:z="#RowsetSchema" xmlns:b="urn:schemas-microsoft-com:office:publisher" xmlns:ss="urn:schemas-microsoft-com:office:spreadsheet" xmlns:c="urn:schemas-microsoft-com:office:component:spreadsheet" xmlns:odc="urn:schemas-microsoft-com:office:odc" xmlns:oa="urn:schemas-microsoft-com:office:activation" xmlns:html="http://www.w3.org/TR/REC-html40" xmlns:q="http://schemas.xmlsoap.org/soap/envelope/" xmlns:rtc="http://microsoft.com/officenet/conferencing" xmlns:D="DAV:" xmlns:Repl="http://schemas.microsoft.com/repl/" xmlns:mt="http://schemas.microsoft.com/sharepoint/soap/meetings/" xmlns:x2="http://schemas.microsoft.com/office/excel/2003/xml" xmlns:ppda="http://www.passport.com/NameSpace.xsd" xmlns:ois="http://schemas.microsoft.com/sharepoint/soap/ois/" xmlns:dir="http://schemas.microsoft.com/sharepoint/soap/directory/" xmlns:ds="http://www.w3.org/2000/09/xmldsig#" xmlns:dsp="http://schemas.microsoft.com/sharepoint/dsp" xmlns:udc="http://schemas.microsoft.com/data/udc" xmlns:xsd="http://www.w3.org/2001/XMLSchema" xmlns:sub="http://schemas.microsoft.com/sharepoint/soap/2002/1/alerts/" xmlns:ec="http://www.w3.org/2001/04/xmlenc#" xmlns:sp="http://schemas.microsoft.com/sharepoint/" xmlns:sps="http://schemas.microsoft.com/sharepoint/soap/" xmlns:xsi="http://www.w3.org/2001/XMLSchema-instance" xmlns:udcs="http://schemas.microsoft.com/data/udc/soap" xmlns:udcxf="http://schemas.microsoft.com/data/udc/xmlfile" xmlns:udcp2p="http://schemas.microsoft.com/data/udc/parttopart" xmlns:wf="http://schemas.microsoft.com/sharepoint/soap/workflow/" xmlns:dsss="http://schemas.microsoft.com/office/2006/digsig-setup" xmlns:dssi="http://schemas.microsoft.com/office/2006/digsig" xmlns:mdssi="http://schemas.openxmlformats.org/package/2006/digital-signature" xmlns:mver="http://schemas.openxmlformats.org/markup-compatibility/2006" xmlns:m="http://schemas.microsoft.com/office/2004/12/omml" xmlns:mrels="http://schemas.openxmlformats.org/package/2006/relationships" xmlns:spwp="http://microsoft.com/sharepoint/webpartpages" xmlns:ex12t="http://schemas.microsoft.com/exchange/services/2006/types" xmlns:ex12m="http://schemas.microsoft.com/exchange/services/2006/messages" xmlns:pptsl="http://schemas.microsoft.com/sharepoint/soap/SlideLibrary/" xmlns:spsl="http://microsoft.com/webservices/SharePointPortalServer/PublishedLinksService" xmlns:Z="urn:schemas-microsoft-com:" xmlns:st="" xmlns="http://www.w3.org/TR/REC-html40">
<head>
<META HTTP-EQUIV="Content-Type" CONTENT="text/html; charset=us-ascii">
<meta name=Generator content="Microsoft Word 12 (filtered medium)">
<!--[if !mso]>
<style>
v\:* {behavior:url(#default#VML);}
o\:* {behavior:url(#default#VML);}
w\:* {behavior:url(#default#VML);}
.shape {behavior:url(#default#VML);}
</style>
<![endif]-->
<style>
<!--
/* Font Definitions */
@font-face
{font-family:"Cambria Math";
panose-1:2 4 5 3 5 4 6 3 2 4;}
@font-face
{font-family:Calibri;
panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
{font-family:Tahoma;
panose-1:2 11 6 4 3 5 4 4 2 4;}
@font-face
{font-family:Webdings;
panose-1:5 3 1 2 1 5 9 6 7 3;}
@font-face
{font-family:Garamond;
panose-1:2 2 4 4 3 3 1 1 8 3;}
@font-face
{font-family:"Franklin Gothic Demi";
panose-1:2 11 7 3 2 1 2 2 2 4;}
@font-face
{font-family:"Arial Black";
panose-1:2 11 10 4 2 1 2 2 2 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
{margin:0in;
margin-bottom:.0001pt;
font-size:11.0pt;
font-family:"Calibri","sans-serif";}
a:link, span.MsoHyperlink
{mso-style-priority:99;
color:blue;
text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
{mso-style-priority:99;
color:purple;
text-decoration:underline;}
p.MsoAcetate, li.MsoAcetate, div.MsoAcetate
{mso-style-priority:99;
mso-style-link:"Balloon Text Char";
margin:0in;
margin-bottom:.0001pt;
font-size:8.0pt;
font-family:"Tahoma","sans-serif";}
span.BalloonTextChar
{mso-style-name:"Balloon Text Char";
mso-style-priority:99;
mso-style-link:"Balloon Text";
font-family:"Tahoma","sans-serif";}
span.EmailStyle19
{mso-style-type:personal;
font-family:"Calibri","sans-serif";
color:windowtext;}
span.EmailStyle20
{mso-style-type:personal;
font-family:"Calibri","sans-serif";
color:#1F497D;}
span.EmailStyle21
{mso-style-type:personal;
font-family:"Calibri","sans-serif";
color:#1F497D;}
span.EmailStyle22
{mso-style-type:personal;
font-family:"Calibri","sans-serif";
color:#0000B4;}
span.EmailStyle23
{mso-style-type:personal;
color:black;}
span.EmailStyle24
{mso-style-type:personal-reply;
font-family:"Calibri","sans-serif";
color:#1F497D;}
.MsoChpDefault
{mso-style-type:export-only;
font-size:10.0pt;}
@page Section1
{size:8.5in 11.0in;
margin:1.0in 1.0in 1.0in 1.0in;}
div.Section1
{page:Section1;}
-->
</style>
<!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
</head>
<body lang=EN-US link=blue vlink=purple>
<div class=Section1>
<p class=MsoNormal><i><span style='color:#1F497D'>“</span><span
style='color:black'>These are separate credits – the modeling takes place based
on the proposed design in comparison to a baseline that is only restricted by
90.1.”<o:p></o:p></span></i></p>
<p class=MsoNormal><i><span style='color:black'><o:p> </o:p></span></i></p>
<p class=MsoNormal><span style='color:black'>This is absolutely correct. The
credit is separate and therefore becomes part of your design regardless of
EAc1. Once part of your design you are required to follow the guidelines of
90.1 which says to keep the same ventilation rate schedules.<o:p></o:p></span></p>
<p class=MsoNormal><span style='color:black'><o:p> </o:p></span></p>
<p class=MsoNormal><span style='color:black'>Also the increased ventilation is
not always a penalty on the energy side by comparison. DOAS can have increased
ventilation and still use less energy when utilizing a double wheel system.</span><span
style='color:#1F497D'><o:p></o:p></span></p>
<p class=MsoNormal><span style='color:#1F497D'><o:p> </o:p></span></p>
<div>
<p class=MsoNormal style='margin-bottom:12.0pt;line-height:15.0pt'><span
style='font-size:8.0pt;font-family:"Arial Black","sans-serif";color:#1F497D'>Alan
Jackson, LEED AP<br>
KlingStubbins</span><span style='color:#1F497D'><o:p></o:p></span></p>
</div>
<p class=MsoNormal><span style='color:#1F497D'><o:p> </o:p></span></p>
<div>
<div style='border:none;border-top:solid #B5C4DF 1.0pt;padding:3.0pt 0in 0in 0in'>
<p class=MsoNormal><b><span style='font-size:10.0pt;font-family:"Tahoma","sans-serif"'>From:</span></b><span
style='font-size:10.0pt;font-family:"Tahoma","sans-serif"'>
bldg-sim-bounces@lists.onebuilding.org
[mailto:bldg-sim-bounces@lists.onebuilding.org] <b>On Behalf Of </b>David S
Eldridge<br>
<b>Sent:</b> Thursday, November 19, 2009 6:31 PM<br>
<b>To:</b> bldg-sim@lists.onebuilding.org<br>
<b>Subject:</b> Re: [Bldg-sim] Baseline Modeling for LEED<o:p></o:p></span></p>
</div>
</div>
<p class=MsoNormal><o:p> </o:p></p>
<p class=MsoNormal><span style='color:black'>Quick answer:<o:p></o:p></span></p>
<p class=MsoNormal><span style='color:black'><o:p> </o:p></span></p>
<p class=MsoNormal><span style='color:black'>90.1 does not care if you are
pursuing EQC2, use the same OA quantities in baseline and proposed for EAC1.<o:p></o:p></span></p>
<p class=MsoNormal><span style='color:black'><o:p> </o:p></span></p>
<p class=MsoNormal><span style='color:black'><o:p> </o:p></span></p>
<p class=MsoNormal><span style='color:black'>Long answer:<o:p></o:p></span></p>
<p class=MsoNormal><span style='color:black'><o:p> </o:p></span></p>
<p class=MsoNormal><span style='color:black'>These are separate credits – the
modeling takes place based on the proposed design in comparison to a baseline that
is only restricted by 90.1. The OA requirement should be the same in both
models subject to any DCV or exceptional calcs or technologies. This is
not affected by other LEED credits. <o:p></o:p></span></p>
<p class=MsoNormal><span style='color:black'><o:p> </o:p></span></p>
<p class=MsoNormal><span style='color:black'>The credit for increased
ventilation takes place “before” modeling starts. This is besides the
many cases for laboratories or hospitals where the local code ventilation
requirements are much greater than ASHRAE 62.1 already – the proposed design is
in effect already taking the EAC1 penalty but earning the credit for increased
ventilation under the best practice design. You wouldn’t relax the
baseline ventilation to less than 30% in these cases!<o:p></o:p></span></p>
<p class=MsoNormal><span style='color:black'><o:p> </o:p></span></p>
<p class=MsoNormal><span style='color:black'>I’m sure there are some proposed
buildings out there that condition OA very effectively, and may gain EAC1 gross
energy cost savings by having increased ventilation, but even where that effect
occurs there is the question of percentage savings applying to a larger
energy consumption and cost.<o:p></o:p></span></p>
<p class=MsoNormal><span style='color:black'><o:p> </o:p></span></p>
<p class=MsoNormal><span style='color:black'>Overall if you gain EAC1 points by
pursuing increased ventilation, I think you have worked well within the system
– good for you in designing a system to condition outside air so
effectively. For many projects (other than labs or hospitals which may
have to use that quantity of OA anyway) I would expect EQC2 could be trading
for an EAC1 credit, so you’ll have to prioritize. Both are rewarded from
USGBC, but EAC1 is also rewarded in lower utility bills.<o:p></o:p></span></p>
<p class=MsoNormal><span style='color:black'><o:p> </o:p></span></p>
<p class=MsoNormal><span style='color:black'>David<o:p></o:p></span></p>
<p class=MsoNormal><span style='color:black'>http://www.grummanbutkus.com<o:p></o:p></span></p>
<p class=MsoNormal><span style='color:black'><o:p> </o:p></span></p>
<p class=MsoNormal><span style='color:black'><o:p> </o:p></span></p>
<p class=MsoNormal><span style='color:black'><o:p> </o:p></span></p>
<div style='border:none;border-left:solid blue 1.5pt;padding:0in 0in 0in 4.0pt'>
<div>
<div style='border:none;border-top:solid #B5C4DF 1.0pt;padding:3.0pt 0in 0in 0in'>
<p class=MsoNormal><b><span style='font-size:10.0pt;font-family:"Tahoma","sans-serif"'>From:</span></b><span
style='font-size:10.0pt;font-family:"Tahoma","sans-serif"'>
bldg-sim-bounces@lists.onebuilding.org
[mailto:bldg-sim-bounces@lists.onebuilding.org] <b>On Behalf Of </b>Vikram Sami<br>
<b>Sent:</b> Thursday, November 19, 2009 4:20 PM<br>
<b>To:</b> Nathan Miller; Rimes, Christie; Steven Rutter;
bldg-sim@lists.onebuilding.org<br>
<b>Subject:</b> Re: [Bldg-sim] Baseline Modeling for LEED<o:p></o:p></span></p>
</div>
</div>
<p class=MsoNormal><o:p> </o:p></p>
<p class=MsoNormal><span style='color:#0000B4'>I always assumed that if you
went to 30% extra, you kept the baseline at 100%, and the designed building at
130%, but after reading this, it does seem to make sense that you would
increase both occurrences. <o:p></o:p></span></p>
<p class=MsoNormal><span style='color:#0000B4'><o:p> </o:p></span></p>
<p class=MsoNormal><span style='color:#0000B4'>Can anyone from the EA Tag chime
in?<o:p></o:p></span></p>
<p class=MsoNormal><span style='color:#0000B4'><o:p> </o:p></span></p>
<div>
<p class=MsoNormal style='mso-margin-top-alt:auto'><b><span style='font-size:
12.0pt;font-family:"Garamond","serif";color:black'>Vikram Sami,</span></b><span
style='font-size:12.0pt;font-family:"Times New Roman","serif";color:#0000B4'> </span><span
style='font-size:12.0pt;font-family:"Garamond","serif";color:black'>LEED AP</span><span
style='font-size:12.0pt;font-family:"Times New Roman","serif";color:#0000B4'> <br>
</span><span style='font-size:12.0pt;font-family:"Garamond","serif";color:black'>Direct
Phone 404-253-1466 | Direct Fax 404-253-1366</span><span style='font-size:12.0pt;
font-family:"Times New Roman","serif";color:#0000B4'> <o:p></o:p></span></p>
<p class=MsoNormal style='margin-bottom:12.0pt'><b><span style='font-size:12.0pt;
font-family:"Garamond","serif";color:maroon'>L</span></b><b><span
style='font-size:10.0pt;font-family:"Garamond","serif";color:maroon'>ORD</span></b><b><span
style='font-size:12.0pt;font-family:"Garamond","serif";color:maroon'>, A</span></b><b><span
style='font-size:10.0pt;font-family:"Garamond","serif";color:maroon'>ECK</span></b><b><span
style='font-size:12.0pt;font-family:"Garamond","serif";color:maroon'> & S</span></b><b><span
style='font-size:10.0pt;font-family:"Garamond","serif";color:maroon'>ARGENT</span></b><b><span
style='font-size:12.0pt;font-family:"Garamond","serif";color:maroon'> A</span></b><b><span
style='font-size:10.0pt;font-family:"Garamond","serif";color:maroon'>RCHITECTURE</span></b><span
style='font-size:12.0pt;font-family:"Times New Roman","serif";color:#0000B4'><o:p></o:p></span></p>
</div>
<p class=MsoNormal><span style='color:#0000B4'><o:p> </o:p></span></p>
<div>
<div style='border:none;border-top:solid #B5C4DF 1.0pt;padding:3.0pt 0in 0in 0in'>
<p class=MsoNormal><b><span style='font-size:10.0pt;font-family:"Tahoma","sans-serif"'>From:</span></b><span
style='font-size:10.0pt;font-family:"Tahoma","sans-serif"'>
bldg-sim-bounces@lists.onebuilding.org
[mailto:bldg-sim-bounces@lists.onebuilding.org] <b>On Behalf Of </b>Nathan
Miller<br>
<b>Sent:</b> Thursday, November 19, 2009 4:42 PM<br>
<b>To:</b> 'Rimes, Christie'; 'Steven Rutter'; bldg-sim@lists.onebuilding.org<br>
<b>Subject:</b> Re: [Bldg-sim] Baseline Modeling for LEED<o:p></o:p></span></p>
</div>
</div>
<p class=MsoNormal><o:p> </o:p></p>
<p class=MsoNormal><span style='color:#1F497D'>I disagree, I believe the models
should be same-same on ventilation rates. See section 90.1 (2004) Section
G3.1.2.5. It states:<o:p></o:p></span></p>
<p class=MsoNormal><span style='color:#1F497D'><o:p> </o:p></span></p>
<p class=MsoNormal><span style='color:#1F497D'>“Minimum outdoor air ventilation
rates should be the same for the proposed and baseline building designs.”<o:p></o:p></span></p>
<p class=MsoNormal><span style='color:#1F497D'><o:p> </o:p></span></p>
<p class=MsoNormal><span style='color:#1F497D'>In my projects (including those
that include 30% additional outside air), I have always used the same outdoor
air flow rates, unless I was taking credit for demand control ventilation in
the proposed case (see the exception allowed in that same ASHRAE section). <o:p></o:p></span></p>
<p class=MsoNormal><span style='color:#1F497D'><o:p> </o:p></span></p>
<div>
<p class=MsoNormal><span style='font-size:12.0pt;font-family:"Franklin Gothic Demi","sans-serif";
color:#1F497D'>Nathan Miller</span><span style='font-size:12.0pt;font-family:
"Times New Roman","serif";color:#1F497D'><o:p></o:p></span></p>
<p class=MsoNormal><i><span style='font-size:10.0pt;font-family:"Times New Roman","serif";
color:#1F497D'>Senior Energy Engineer/Mechanical Engineer<o:p></o:p></span></i></p>
<p class=MsoNormal><span style='font-size:10.0pt;font-family:"Times New Roman","serif";
color:#1F497D'>direct: 206.788.4577<o:p></o:p></span></p>
<p class=MsoNormal><span style='font-size:10.0pt;font-family:"Times New Roman","serif";
color:#1F497D'>fax: 206.285.7111 </span><span style='color:#1F497D'><o:p></o:p></span></p>
</div>
<p class=MsoNormal><span style='color:#1F497D'><o:p> </o:p></span></p>
<div>
<div style='border:none;border-top:solid #B5C4DF 1.0pt;padding:3.0pt 0in 0in 0in'>
<p class=MsoNormal><b><span style='font-size:10.0pt;font-family:"Tahoma","sans-serif"'>From:</span></b><span
style='font-size:10.0pt;font-family:"Tahoma","sans-serif"'>
bldg-sim-bounces@lists.onebuilding.org [mailto:bldg-sim-bounces@lists.onebuilding.org]
<b>On Behalf Of </b>Rimes, Christie<br>
<b>Sent:</b> Thursday, November 19, 2009 1:32 PM<br>
<b>To:</b> Steven Rutter; bldg-sim@lists.onebuilding.org<br>
<b>Subject:</b> Re: [Bldg-sim] Baseline Modeling for LEED<o:p></o:p></span></p>
</div>
</div>
<p class=MsoNormal><o:p> </o:p></p>
<p class=MsoNormal><span style='color:#1F497D'>In my experience you do
not increase the baseline energy model as you are being awarded (gaining that
point) when you achieve the ventilation credit. There are a few similar
situations in LEED where by achieving one credit will prevent you from
achieving another but this happens to everyone so it works out to be somewhat
fair. <o:p></o:p></span></p>
<p class=MsoNormal><span style='color:#1F497D'><o:p> </o:p></span></p>
<div>
<p class=MsoNormal><span style='color:#1F497D'><img width=591 height=170
id="_x0000_i1026" src="cid:image001.png@01CA69B5.F12F5AD0"
alt="Christie Rimes,
Building Simulation Analyst
WSP Flack + Kurtz
405 Howard Street, Suite 500
San Francisco, CA 94105
Direct: 415.402.2727
Main Tel: 415.398.3833
Fax: 415.433.5311
website: http://www.wspfk.com
vCard: http://vcards.wspfk.com/vcardloader.php?filename=flackkurtz-christie-rimes-wspfk-com-1255981339.vcf
image: "><o:p></o:p></span></p>
</div>
<p class=MsoNormal><span style='color:#1F497D'><o:p> </o:p></span></p>
<div>
<div style='border:none;border-top:solid #B5C4DF 1.0pt;padding:3.0pt 0in 0in 0in'>
<p class=MsoNormal><b><span style='font-size:10.0pt;font-family:"Tahoma","sans-serif"'>From:</span></b><span
style='font-size:10.0pt;font-family:"Tahoma","sans-serif"'>
bldg-sim-bounces@lists.onebuilding.org
[mailto:bldg-sim-bounces@lists.onebuilding.org] <b>On Behalf Of </b>Steven
Rutter<br>
<b>Sent:</b> Thursday, November 19, 2009 1:25 PM<br>
<b>To:</b> bldg-sim@lists.onebuilding.org<br>
<b>Subject:</b> [Bldg-sim] Baseline Modeling for LEED<o:p></o:p></span></p>
</div>
</div>
<p class=MsoNormal><o:p> </o:p></p>
<p class=MsoNormal>All,<o:p></o:p></p>
<p class=MsoNormal>There is a credit in LEED (EQc2.0) that involves increasing
the required ventilation rate by 30%. In trying to achieve this credit,
the amount of energy would have to increase to condition that additional 30%
OSA. Does anyone know if you are supposed to increase the baseline energy
model’s ventilation rate so it has the same ventilation rate as the proposed
building? Thank you in advance for your help.<o:p></o:p></p>
<p class=MsoNormal><o:p> </o:p></p>
<p class=MsoNormal><o:p> </o:p></p>
<p class=MsoNormal><b><span style='font-family:"Tahoma","sans-serif";
color:gray'>Steven Rutter, LEED</span></b><b><sup><span style='font-size:9.0pt;
font-family:"Tahoma","sans-serif";color:gray'>®</span></sup></b><b><sup><span
style='font-family:"Tahoma","sans-serif";color:gray'> </span></sup></b><b><span
style='font-family:"Tahoma","sans-serif";color:gray'>AP, EIT</span><o:p></o:p></b></p>
<p class=MsoNormal><o:p> </o:p></p>
<p class=MsoNormal style='margin-bottom:12.0pt'><img width=180 height=44
id="Picture_x0020_1" src="cid:image002.jpg@01CA69B5.F12F5AD0"
alt="cid:665444518@16012009-36B3"><br>
<b><span style='font-family:"Tahoma","sans-serif";color:gray'>3850 Happy
Lane|Sacramento, CA 95827<br>
O:916-368-0336|F:916-368-0337|C:916-717-7484</span></b><span style='font-family:
"Times New Roman","serif"'><o:p></o:p></span></p>
<p class=MsoNormal style='mso-margin-top-alt:auto;mso-margin-bottom-alt:auto'><span
style='font-size:18.0pt;font-family:Webdings;color:green'>P</span><span
style='font-size:12.0pt;font-family:"Times New Roman","serif"'> </span><span
style='font-size:7.5pt;font-family:"Arial","sans-serif";color:green'>Please
consider the environment before printing this email.</span><span
style='font-size:12.0pt;font-family:"Times New Roman","serif"'> <o:p></o:p></span></p>
<p class=MsoNormal><o:p> </o:p></p>
<p class=MsoNormal><o:p> </o:p></p>
</div>
</div>
</body>
</html>